My house is new construction and approaching its one year warranty anniversary mid April.
The house has its back to a cornfield where it gets pretty windy.. i think the highest this year way 65mph.. a couple times. These are 3 tab asphalt shingles not architectural ones.
I have had a few occurances after they have set on a hot day with some pieces of shingles blowing off here and there.
When these were installed, it was around Feburary of 2016, so they didn't correctly ser until April or May.. we had a few instances where they blew off badly from wind because they were flopping around before setting. They were corrected before move in.
So far the builder says the roof spot repairs fall under the one year warranty.. after that i am on my own per them, but clearly im fighting it.
When these were installed in winter, were they supposed to be manually sealed or glued in anyway to prevent what happened during cold months?
Below are a few pictures of the shingles blowing in the wind after first installed, and recently with a few missing shingles. Could these shingles be a side effect from improper installation? Or just not able to withstand the wind.. if the latter, well what to i do other than spot trear shingles blowing off every year?
enter image description here   enter image description here
eaglei22
  • 1,075
  • 40
  • The first two pictures are recent, the bottom two are from last late winter when roof was first put in. Two occasions the shingles got ruined because of lack of hot day to set the shingles.. and clearly no glue was used to hold them down. – eaglei22 Mar 29 '17 at 03:34
    It's common for "builders" to use the cheapest shingles they can, to reduce building costs. To make matters worse, they often install the shingles in the cold winter months so that the builder can be productive all year round. These two factors often lead to exactly the problem you're seeing. Unfortunately for you, you're probably going to be patching the roofing until you replace it. – Tester101 Mar 29 '17 at 11:10
  • My warning to others (sorry, too late for you), is to make sure your builder is using quality products, and especially insist on better roofing materials. it might cost a bit more up front, but it's cheaper than replacing the whole thing. – Tester101 Mar 29 '17 at 11:10
  • Ask the builder for the warranty information on the shingles. The repairs *may* be covered by the shingle manufacturer, **if** the shingles were properly installed, and the wind speed was not greater than the speed listed in the warranty (Some cheaper shingles only warranty up to 60 MPH winds). – Tester101 Mar 29 '17 at 11:32
    Thanks tester. Apparently the warranty is only for 54mph... anything more to them is considered "an act of god" thats a joke.. 55mph is act of god wind. I tell you i def learned a lot from this process. And that is no matter how friendly they (all builders) seem, or no matter the "quality" products they claim to be giving you they are all full of shit and don't be afraid to challange them or give them a hard time. In the end they ust want your money and can care less about you. – eaglei22 Mar 29 '17 at 12:26
  • I asked around for a few quotes for a roof inspection. Is it worth having one? Or from the pictures does the roof look fine, just wrong material for the location. – eaglei22 Mar 29 '17 at 12:27
  • An inspector is going to tell you the same thing I did. Those shingles are cheap junk, and should be replaced. 54 mph warranty is terrible, and tells me that it's a bottom tier product. It really is a shame that builders do this to people, especially given the amount of money folks are spending on these homes. – Tester101 Mar 29 '17 at 12:45
    When shopping for shingles, you'll hear terms like "*25 year shingles*", "*30 year shingles*", etc. This is usually the warranty term, and gives you an indication of how long the roof should last. Those shingles, are 5 year shingles (at best). They typically just barely outlast the home warranty. – Tester101 Mar 29 '17 at 12:45
  • Well i was hoping to get an inspector to get a write up from a certified company to tell them things that are wrong. There arent even nails shown from the attic... see the latest picture i added – eaglei22 Mar 29 '17 at 12:48
    When you do replace the roofing, make sure they strip the roof . You don't want those crap shingles under the new roofing material. And make sure it's installed in the summer, so that the shingles can seal properly. – Tester101 Mar 29 '17 at 12:49
  • If it's for legal action, then definitely get an inspector to write a full report on the roof. Make sure he's as strict as possible, and doesn't let any minor detail slide. – Tester101 Mar 29 '17 at 12:54
  • Well right just in case. I figured I would do it from a roofing company.. as the general inspectors might not know as much details. – eaglei22 Mar 29 '17 at 12:56
    Yes, get a highly rated roofing company to do the inspection. While they're there, get a quote on a new roof. – Tester101 Mar 29 '17 at 12:59
  • No manufacturer labels shingles with 25 or 30 anymore. The warranties were a joke, being prorated after a short initial term, and only covering materials. Manufacturers assume home transfer will occur long before then, which often voids the warranty anyway. Word to the wise, use only architectural shingles from a good brand. They don't fail at anywhere near the rate of 3-tab, in my experience. – isherwood Mar 29 '17 at 14:25
  • Regarding builders... I come from a family where quality actually meant something. It stings to read the comments above mentioning greed and deceit, but it's true. "Square footage" builders are like that. However, it's as much the fault of buyers. When they start out asking "how many square feet can I get for X dollars?", they create the situation where unscrupulous briefcase builders take advantage. The moral of the story? Select your builder very carefully--you rely on them for everything--and change the way you think about value in a home. – isherwood Mar 29 '17 at 14:27
    @isherwood I will change my statement to big company/cookie cutter neighborhood builders. My dad went through the same thing 20 yrs ago with the same style builder. I figured 20 yrs later and advancements quality would come easy. Nope, they still find their ways to short change you. BUT, I do not have experience with custom builders which sounds like what you are referring too, and custom builders normally are family owned and would be someone I would look to to build a home far away from everyone and cookie cutter/ HOA neighborhoods. – eaglei22 Mar 29 '17 at 15:40
  • @isherwood Unfortunately, most new homes built in the US are built by "big builders", and are built in the cheapest way possible. These companies buy up large plots of land (usually from struggling farmers, or land that nobody else wants), divide it up, and build as many homes as possible on it. If you own/buy your own plot of land, you're likely not going to deal with one of these types of builders. In which case you'll have more control over the quality of the building materials, and end up with a better home. – Tester101 Mar 29 '17 at 16:55
  • @isherwood Manufacturers may not label shingles as 25 year, 30 year, etc. anymore, but roofing contractors still tend to use these terms (at least in my experience). – Tester101 Mar 29 '17 at 16:57
  • I think the reason 54 mph is important is because gale force winds start at 54 mph. There are shingles now that are rated up to 120 mph. Well worth the cost... – Lee Sam Mar 29 '17 at 23:58
  • @Tester101 okay, posted an answer of the contractor's findings. – eaglei22 Apr 01 '17 at 21:09
  • Two words, metal roof ! – Alaska Man Oct 04 '19 at 22:11
It's good that the roof is not leaking (you didn't mention that) but improper installation will create leaks in the future. So, verifying a few key items and then officially notifying your builder (by certified, return receipt mail) of incorrect installation will protect your rights. I'd check the following:
  1. Number of nails in each shingle: Each roofing manufacturer requires a certain number of nails into each shingle, usually 4 minimum. Depending on your location, it could be 5 or 6, depending if you are located in a "high wind area". (Where I live, 65 mph winds would require 5 nails per shingle.) You'll find this info on each wrapper around each bundle of shingles. If no wrapper is around, you can find it on the manufacturer's website. If you don't know the name of the manufacturer, call the builder.
  2. Nail Placement: I see this wrong on a lot of jobs. If nails are placed too high, then the nail will not penetrate the top of the shingle on the layer directly below. Nails should be above the top of the cut out in the 3-tab shingle, but about 1" below the mastic strip. Most roofers want to nail "in" the mastic strip. This is bad for two reasons: a) it misses the shingle directly below, so there are only 4 nails holding the shingle on the roof instead of 8 nails, and b) it creates a little dip in the shingle because it causes the shingle to bend down over the top edge of the lower shingle.
  3. Lack of Hand-Tabbing: Most shingles do NOT require hand tabbing, unless you are in a "high wind area". Hand tabbing is placing a quarter size dab of roofing mastic "by hand" under each shingle. However, most roofing manufacturers require hand tabbing "if the shingles have not self-sealed in a sufficient time." This is a bit arbitrary, but "sufficient time" means "within the guarantee period." (You can get that confirmed by the roofing manufacturer.) So, the way to test this is to go up on the roof and try to lift a shingle tab (bend a shingle tab up). I'd try about a third of the shingle tabs. The roofer will tell you the shingles will "self tab" down. That means they anticipate the sun heating the shingle up until it sticks to the mastic strip under each tab. The problem is that it may not get warm enough in your area or the nails are not set flush and the nails are holding the shingles up above the mastic strip. (See #7, below.)
  4. Too large of exposure: Three tab shingles should have only a 5 5/8" exposure. Most roofers will stretch that to 6" or 6. 1/2". That gives the opportunity for the wind to lift more of the shingle and creates improper nailing, (missing the top of the lower shingle, etc.)
  5. Too short of nails: Nails should completely penetrate the plywood. Can you see the nails from inside the attic?
  6. Roof sheathing is too thin: 1/2" plywood or 5/8" particle board minimum, I think. Check with manufacturer. Again, this info is on the wrapper.
  7. Nails or staples are not set flush: That is to say the nails are held up slightly (maybe 1/8") which keeps the shingle from self-sealing.
These are the things that lead to blow off, but other typical bad roofing issues are: A) no starter course, B) shingle ends are not staggered, C) blown off shingles not repaired correctly and the holes in the paper underlayment not sealed correctly where nails have withdrawn from blow off.
One thing that seems odd is that various shingles are blowing off. Usually, one shingle blows off and it takes 10-12 more shingles above it in a "V" shape pattern. This indicates to me, that the nails are not in the correct position below the mastic strip, (see item #2, above.)
Also, where I live, by law, roofing has to be guaranteed for 2 years not 1 year. So, your guarantee period may go another year. You can verify that with your state's Construction Contractors Board (CCB). Also, check the roofing manufacturer's wrapper.
Lee Sam
  • 23,095
  • 44
  • Thanks Lee for all the great i formation . No i do not see one nail from the attic. I will post a picture i had taken. Of the light, but shows the ceiling. – eaglei22 Mar 29 '17 at 12:35
  • The roof in the rear is about 30ft from the ground. So i planned on hiring an inspector from a roofing company.. the shingles were laid in February i believe and they definitely were nlt glued down.. and from tbe pictures above the shingles blew off twice. – eaglei22 Mar 29 '17 at 12:37
  • Particle board on a roof? Not on my watch. Perhaps you meant OSB. Around here, 1/2" OSB is the de facto standard. Good answer otherwise. – isherwood Mar 29 '17 at 14:20
  • Wow, no nails penetrating the roof sheathing. How did they do that? Good move to have an expert review the roof. – Lee Sam Mar 29 '17 at 16:20
  • Were they stapled rather than nailed? – Ecnerwal Mar 29 '17 at 19:44
  • Im am not sure. I will am going to have someone go up there to inspect it. – eaglei22 Mar 29 '17 at 21:30
  • Thr current issue appears to be more with the part the shingle should be sticking to as the nailed parts have not blown off (yet). – eaglei22 Mar 29 '17 at 21:31
  • In any event, if the roof sheathing is less than 3/4" I think the staples should penetrate through the roof sheathing anyway. So, have your local expert check that out too. If just the "tabs" are blowing off, then yes, the issue is about the self-sealing or hand-tabbing. The – Lee Sam Mar 29 '17 at 21:36
  • The manufacturer will – Lee Sam Mar 29 '17 at 21:36
  • The manufacturer will make the call on the requirement for hand-tabbing. However, if the shingles are not installed correctly, then you need a new roof, regardless the length of the nail or staple. I'd have your local expert review everything and give you a written report. – Lee Sam Mar 29 '17 at 21:40
    Get an expert opinion and the tell the builder you want a new roof or compensation to get one put on. Tell him your lawyer will be in touch. – BrianK Mar 30 '17 at 03:31
  • Funny thing is how little interest contractors show in doing an inspection job... i have had one contact me back so far to do it for $350. Trying to find it for $250 or so. – eaglei22 Mar 30 '17 at 15:18
  • @isherwood, Okay, got the inspection, and posted answer. – eaglei22 Apr 01 '17 at 21:08
  • @BrianK I posted results of inspection. – eaglei22 Apr 02 '17 at 00:00
Had a licensed contractor come and inspect my roof. These were his findings:
  • Shingles revealed high nailing patterns not consistent with manufactures installation requirements.
  • Nails were consistently over driven and/or not flush.
  • All slopes showed evidence of improper nailing patterns
  • Previous repairs were completed in unsatisfactory fashion. Wind damaged shingles were not removed and replaced, the damaged shingles were glued in place.
  • The overall condition of this 25 year 3-tab roofing system is "Poor" based on improper installation.
I attached pictures. What a shame. Inspection took place today, showed the builder my evidence, along with some strong words. Awaiting their response.
http://imageshack.com/a/img924/8687/0onjRI.jpg
http://imageshack.com/a/img924/8072/uUWtCA.jpg
http://imageshack.com/a/img922/1356/VVUwTl.jpg
http://imageshack.com/a/img923/6800/0umPGx.jpg
http://imageshack.com/a/img924/5292/J3rXzM.jpg
http://imageshack.com/a/img923/8106/Vog0AB.jpg
http://imageshack.com/a/img923/6155/nZNuzs.jpg
http://imageshack.com/a/img923/8168/dctexv.jpg
http://imageshack.com/a/img923/873/l5gstc.jpg
http://imageshack.com/a/img922/944/TyaGLl.jpg
http://imageshack.com/a/img924/9531/AbcCu5.jpg
eaglei22
  • 1,075
  • 40
  • So, I see too great of exposure, damaged shingles and improper nailing. I would guess the shingles are not sealed either, if you can pick them up and photograph the nails. Don't forget to notify both the General Contractor (the company you signed the contract with) and the roofing company in writing (certified mail with return receipt). – Lee Sam Apr 02 '17 at 04:28
  • @Lee I read on the internet it is acceptable to glue down with roofing glue torn or ripped shingles.. is this really acceptable? Especially on a brand new roof? – eaglei22 Apr 02 '17 at 04:30
  • I messaged the builder first, and will wait on their response first. Also, what do you mean by too great of exposure? – eaglei22 Apr 02 '17 at 04:31
    No, that is repair for old roofs without a guarantee. Glue / mastic applied shingles are not acceptable for guarantee. Also, it needs to be replaced because of the improper nailing and that some shingles have too much exposure. The installation requirements are mandatory...not a recommendation. – Lee Sam Apr 02 '17 at 04:35
  • Exposure for each shingle should be 5 5/8". I see in one of your pictures the bottom of one of the shingles look like they are about 1/2" above the cut-out of the lower shingle. That's a no-no and will give you a shingle exposure of 6" or so. – Lee Sam Apr 02 '17 at 04:40
  • Thanks @Lee for that information. This roof is screwed. I imagine the builder isn't going to give in easily. – eaglei22 Apr 02 '17 at 05:00
    Remember to turn your claim into the Construction Contractors Board (CCB) in your state too. Good luck. – Lee Sam Apr 02 '17 at 05:07
  • @eaglei22 did you ever get a response back from the builder, which it seems was Ryland Homes? – mjuarez Apr 18 '18 at 07:39
    @mjuarez Yes. Given the evidence they ended up replacing the roof. – eaglei22 Apr 19 '18 at 00:43