As the title suggests, is a disconnect switch located near the outdoor unit of a mini-split legally mandated or a convenience item? In my case, the breaker panel is about 20' from the outdoor unit, and the mini split is on a dedicated (and labeled) circuit.
Since local codes may vary, I am in the US. I don't believe my city has any regulation requiring a switch, but I am less sure about the national level.
ThreePhaseEel
  • 81,744
  • 227
Hari
  • 2,200
  • What's the nameplate rating on this mini-split? You might be able to use an ordinary wall switch in a suitable box/cover combo for the disconnect... – ThreePhaseEel Apr 05 '17 at 22:19
    Actually, I know I can. It lists an MCA of 10A and an MOP of 15A, so I was planning to use a weatherproof switch cover on the junction box serving the mini split ODU, if needed. – Hari Apr 05 '17 at 23:23
  • I thought all but the smallest of these mini-splits required 230 V. In the US this means a double pole switch. – Jim Stewart Apr 06 '17 at 03:00
  • I can't just use two switches? The nearby box is a 2-gang (for convenience) and all the covers have two switches anyway... – Hari Apr 06 '17 at 05:00
  • @HariGanti No, you need to interrupt all live wires simultaneously. – SomeoneSomewhereSupportsMonica Apr 06 '17 at 08:10
  • Why not just use the metal switch box and double pole switches normally used for standard a/c units? These are weather and animal resistant and designed for surface mounting. It's going to cost more, but probably not *that* much more. Some of these boxes have breakers installed that also serve as switches, but mine just has a double pole toggle switch. Some have a "pull out" connector which is removed to disconnect. Hari, what is the power requirement for your mini-split and how many BTU/h is its rating? – Jim Stewart Apr 06 '17 at 10:15
    @JimStewart Just trying to use existing equipment. They don't cost much, I am aware. Anyway, as I said earlier, 10A @ 240V, 9kBTU/hr nominal cooling, 10.8kBTU/hr nominal heating. In case you're curious: https://www.acwholesalers.com/hvac/pdf/lg/lg-ductless/LS090HSV4-sb.pdf – Hari Apr 06 '17 at 18:07
  • I guess it's only 8.7A, but that difference is minor. – Hari Apr 06 '17 at 18:15
    Amazing, 2 kW moves 10 kBTU/h which cools or heats a good sized room. The SEER 21 does the trick. – Jim Stewart Apr 07 '17 at 01:01
It is legally mandated, and part of the National Electrical Code (NFPA70). NEC is adopted across most of the US.
National Electrical Code 2014
Chapter 4 Equipment for General Use
Article 440 Air-conditioning and Refrigerating Equipment
440.14 Location. Disconnecting means shall be located within sight from and readily accessible from the air-conditioning or refrigerating equipment. The disconnecting means shall be permitted to be installed on or within the air-conditioning or refrigerating equipment.
The disconnecting means shall not be located on panels that are designed to allow access to the air-conditioning or refrigeration equipment or to obscure the equipment nameplate(s).
It's largely a safety precaution to ensure the power is off if someone is servicing the unit.
If your breaker panel is 20' away and within sight of the unit, it's probably acceptable as a disconnect means but of course your AHJ (inspector) will have to agree. If you can't see it, you'll have to put in a separate disconnecting means.
gregmac
  • 28,910
  • 84
  • It's *around the corner* meaning within 20', but on a different wall of the house. At any rate, per @ThreePhaseEel, I plan to use a simple wall switch in a weatherproof cover on the junction box serving the unit. – Hari Apr 05 '17 at 23:25
  • It depends on where you live and if the breaker has lock out lugs. Also the required service outlet. If within site 50' per NEC definitions "in site from" and can be locked out this fulfills the requirement but it requires lugs. I believe because even with the door locked the cover can be removed on many panels. – Ed Beal Apr 05 '17 at 23:32
  • Yeah, I don't have lock-out lugs, but the box locks without the ability to remove the panel. – Hari Apr 06 '17 at 05:02
  • @hariGante Assuming your unit is 240V, a simple wall switch won't do. The feed actually consists of two hot wires and both must be switched. A "spa disconnect" will do what you need. – DoxyLover Apr 06 '17 at 16:47
    There are double pole toggles. Available locally – NPM Aug 12 '17 at 21:03