We have experienced a failure or short in one leg of a buried 3 wire 2.0-gauge aluminum cable that runs 150’ from our house to a detached garage (2 hots and a neutral, no ground -USE-2 RHH 60 MIL XLP). I hope to locate and repair the short and am looking for your advice and the most economical way to find the short.
The location where the cable is buried can be located from old photos left by the previous owner which show the original trench. In addition, we have confirmed the location of the buried AC power cables by sending a signal down the lines and picking it up with an AM radio. (We wound a 20-gauge wire half a dozen times around the spark plug cable of our four-stroke lawnmower, attached the other end of the 20-gauge wire to one end of the damaged 2.0-gauge aluminum power cable, started the lawn mower, then swept the portable AM radio over the ground surface near the locations we thought it was buried.) The mower magneto induced a signal onto the buried 2.0-gauge cable which the AM radio could track over the ground surface. The cable path is now marked out on the ground. However, I do not know how to locate the short so we can dig down to the cable and repair the bad spot.
A call to all rental shops in my town, Olympia WA, reveal that I can rent a cable locator, but none of our local rental shops has a fault finder. Your advice is appreciated. My own best solution at this point, would require buying a fault finder such as AEMC CA7024 Fault Mapper Cable Length Meter and Fault Locator ($525), Amazon Link, or Armada GFL3000 Ground Fault Locator ($900) GFL3000 on Amazon
Do any of you have a recommendation for this situation?
Further details: The problems on this line began a few weeks ago when we suddenly lost power on several light and outlet circuits in the garage. We’ve had a few loaded dump trucks running over the trench line area during our wet spring. I suspect they may have pushed a rock through or caused a break. The nonfunctioning circuits were simply shut off in the garage at their respective breakers on the garage subpanel. I scheduled the problem for service.
However, within two weeks the Double Pole breaker controlling this buried 2.0 gauge aluminum cable began tripping at the main panel in the house. I replaced the original 60 Amp breaker on this cable in the house breaker panel with a new 100 Amp breaker (the 2.0-gauge aluminum cable is rated for 100 amps). The new 100-amp breaker instantly tripped. Reset, and it instantly tripped again.
Went back to the garage panel, completely disconnected the A leg or phase of the buried 2.0 cable from the garage breaker panel. Went back to the house and turned on the new 100 Amp breaker. It still tripped. Disconnected the A leg of the buried 2.0 wire from the house breaker panel and turned on the new 100-amp double pole breaker with just the “B” leg connected. Then went back to the garage subpanel and discovered that the now completely disconnected A leg of the buried 2.0-gauge cable still had a small variable voltage. Our meter measured 1.5 to 5 volts (variable) between the disconnected A leg and the Neutral, and 2.0 to 2.5 volts between the A leg and ground. There was no voltage between neutral and ground.
The B leg of the buried 2.0-gauge cable measured 118 Volts. Our multi-meter measured 115 volts between the disconnected A leg and the hot B leg. When both hots (A and B) of this cable are disconnected at the house breaker panel, then there is no voltage anywhere in the garage subpanel. We are currently running the garage with only 120 volts (the B leg) of the buried 2.0-gauge aluminum cable remains connected. What do you think my best option is to find this fault?
David Davido
  • 115
    A time domain reflectometer is the device to use, which is exactly what those devices you linked are. They will be able to tell you a distance to the fault. – Steve Apr 20 '17 at 17:50
  • Another option to the TDR type of detector is a 'thumper' which periodically dumps a high-energy charge into the cable. You then walk along the cable route with a listening device pressed to the ground and listen for the 'thump' as the charge hits the fault location. – brhans Apr 20 '17 at 17:58
  • @Steve is right - the pros use a TDR. It gives a precise measurement to the end of the cable, Run it from each end then start digging. Check local equipment rental shops and you might be able to use one for a single day without buying it. – SDsolar Apr 20 '17 at 19:29
    Did the trucks run the length of it or cross at a particular spot? Honestly I'm surprised you're seeing so *little* phantom voltage on the disconnected wire. We often hear about 50-60 volts. Fyi... It's not 2.0 gauge like Web 2.0, it's 00 gauge (get it? two 0) or 2/0 and is pronounced two-ought. It's a throwback to the age of goofy measures like penny-nails. Our Metric brothers use mm^2. – Harper - Reinstate Monica Apr 20 '17 at 20:45
  • Can an underground cable like this even be legally patched underground, or would code require a whole new line to be pulled to maintain insulation and wire integrity as a single underground run? – Milwrdfan Apr 25 '17 at 17:34
  • @Steve, Thank you all. I appreciate your indication that I am on the right track with the devices intended to be used here. My initial search was unable to locate either a TDR or Thumper fault finder for rent in my area. Fluke does have $200 fault finders (Fluke TS90, & T3 Innovation SS200). Unfortunately, both are intended for small diameter copper wire, and reviews indicate they work poorly or not at all on larger gauge aluminum. Don't want to spend $500 just to locate the fault, -but will if necessary. – David Davido Apr 25 '17 at 22:14
  • @brhans, Thank you for suggesting the option of using a thumper. In fact, a thumper could identify the precise fault location. TDR tools will require ,easuring the length of this cable from either/both ends which requires considerable measurement. There are both vertical and horizontal runs that are behind walls from the garage sub panel, and from the house panel the cable runs both behind the wall and under the floor. It should be doable either way. But a clear thump at the fault of this buried cable could eliminate miscalculation. – David Davido Apr 25 '17 at 22:35
  • @Harper, We had four dump loads running across the location of the buried cable almost perpendicular to it, but each truck at a different location. The cable is about 30" deep. I did dig up one location. It was enough to realize that the potential need to dig up all eight possibilities is not preferred -unless digging can save $500. It took two hours to uncover, inspect and recover one location. The trench has sand at the bottom, but much less sand and very sharp rocky soil over the cable. Thanks for clarifying the gauge terminology. This would be 2 gauge Aluminum then, not 00 or 2.0. – David Davido Apr 25 '17 at 22:45
  • @ScottEvans, Thank you Scott. I did read somewhere in the NEC that splices should be accessible -which in this case would mean installing a concrete box over the splice location. If anyone knows of a code section that prohibits splicing underground cable, I'd like to know it. – David Davido Apr 25 '17 at 23:02
  • I believe there are solutions for doing splices in underground cable without an access point. @DavidDavido might want to take a polaroid of this moment, because me saying this just doesn't happen: *hire an electrician*. Specifically, and be upfront about this, for use of his equipment to locate the break. Be clear upfront that you intend to "take it from there". Somebody who's a bit hungry or bored will pitch you a price you can live with. – Harper - Reinstate Monica Apr 26 '17 at 02:08
  • @Harper Excellent Idea to hire an electrician to do the locate! Wonderful. If the breaker won't hold long enough to put a load on the line as suggested by Feetwet, calling electricians will be my next move. Many thanks. – David Davido Apr 27 '17 at 04:59
Cheapest and easiest: Put a load (e.g., incandescent light bulb) on the short circuit (A to neutral). Then follow the cable with a non-contact AC current detector. The detector will stop beeping where the (first) short circuit is, since that is where the current is able to loop back in the cable.
If the voltage across the short is really that low, you may have to use a very low resistance load to get enough current to detect above ground (assuming the cable was properly buried).
feetwet
  • 2,597
  • 52
  • Thank you for your answer. It is what I was looking for -cheap and more actionable than searching to rent a high priced tool, or for the lowest price to buy one. Will give it a try and vote up the answer if we can make it work. – David Davido Apr 25 '17 at 23:07
  • A non contact AC current detector isn't going to work 30 inches away from the cable in open air, let alone through 30 inches of dirt. – Billy left SE for Codidact Sep 25 '17 at 16:57
  • @BillyC. - Mine do. And "dirt" would have to have extraordinarily high metal content to significantly attenuate 60Hz EMR. – feetwet Sep 25 '17 at 17:00
  • @feetwet What model do you have? I have a Klein NCVT-2SEN nd its range is 3 inches at best. Any further and it would be useless. if it went off for any voltage within 3 feet, most areas within a dwelling would be alerting and you couldn't meaningfully tell the difference between two outlets a food apart. – Billy left SE for Codidact Sep 25 '17 at 18:48
  • @BillyC. This question is about tracing outside a dwelling, so I bet I could crank the sensitivity of my $10 Craftsman AC probe to do it, although normally I use an Extech TG20 tracer. – feetwet Sep 25 '17 at 20:00