41
I am building a new house and am planning to hardwire network cables into each room.
Can I run CAT5/6 cables parallel to electrical wires without introducing any general safety issues or losing much in connection quality?
Wiring runs for up to 25 metres from patch panel and distribution board in garage to rooms.
My research indicates that is should be fine if they are in separate conduits or if the CAT cables are shielded.
Steven
  • 27,594
  • 53
  • 88
Martin
  • 513
10 Answers10
36
While a shielded Cat5/6 cable is designed to protect itself from outside interferance, it isn't recommended to run them side-by-side to your electrical wiring. Typical is to run electrical down one stud and the Cat5/6 down a different stud. Basically do the same as you would for telco.
Chef Flambe
  • 476
  • Thanks for the answer. Apologies for my ignorance; do you mean conduit with "stud"? –  Jan 16 '12 at 09:18
  • Using conduit is overkill, though useful if you want to run more after the wall is closed up. Attaching them to stud (what holds up the wall) is fine. –  Jan 16 '12 at 13:09
  • @Martin "Stud" is the term used for the 2x4s that run vertically in your walls. He is just saying that you should run it on the other side of that wood. – Kellenjb Jan 16 '12 at 15:04
    I believe he's suggesting using a different stud; not the other side of the same one, for (e.g.) 16" of separation, not 1-1/2". –  Jan 16 '12 at 16:33
    That makes sense. I'm from South Africa and we build using bricks and mortar. No wood at all. So the wiring and cables place inside PVC pipes and are then covered with concrete – Martin Jan 17 '12 at 13:04
  • Inverse square law says that distance is a good thing. The fields die off rapidly with distance so you can run them in parallel but at a distance. Sixteen inches should be good, two feet would be better. The fields are stronger with higher current, so I'd recommend 3-6 feet away from service entry cables. Old CRT screens were pretty good for detecting this. I once had to install a computer in a bedroom. You could place it in either corner, but centered in the wall was the 200 amp service cable. Wibbly screens for all! – Fiasco Labs Nov 04 '12 at 17:35
    http://archive.org/details/gov.law.nfpa.nec.2011 While this is a link, and therefore link rot may set in, the NEC is available for download through Archive.org. 800.133(A)(2) states that Communications wires and cables shall be separated by at least 50mm (2 in.) from conductors of any electrical light, power, Class 1 non-power-limited fire alarm or medium-power network-powered broadband communications circuits. Exceptions are if separate raceways or conduit are used for separating the communications cables/wires from the power conductors. – Fiasco Labs Nov 04 '12 at 18:12
    While Ethernet falls under low power communications and 800 rules, running POE (Power Over Ethernet) will change its classification to Class 2 or Class 3 power and require consulting 725 rules for its installation. – Fiasco Labs Nov 04 '12 at 18:23
  • As far as running data lines in parallel to the main power, I have seen places where this was done. I have also replaced equipment where this was done. I have undone this type of wiring, and I have to no longer had to replace the equipment. I'll let the real electricians quote the rules. I try to use them, or at least make sure my contractors use them. Do not run parallel to main power without 16 in of separation (don't know the real rule but anything less no.) All crosses should be done at 90 degrees. Interference is one issue, but I believe the larger problem will be induction. – Andrew Sep 09 '16 at 16:22
  • What about for outdoor buried cable in conduit(s)? – alexw Apr 19 '20 at 18:21
  • @alexw You may want to open a separate question for this inquiry rather than commenting here. – lmat - Reinstate Monica Apr 21 '20 at 15:43
29
You want to keep low voltage and high voltage separate so that stray nails, screws, and staples installed by less attentive individuals in the future can't puncture the cables and turn your low voltage wire into high voltage. There is always a chance some idiot is going to stick something electrically conductive where he ought not, and he probably shouldn't pay with his life for the mistake. (Nor should the home owner employing the idiot.) That's good to keep in mind even outside of construction/home improvement situations.
I have no idea what code actually says, but conduit is probably sufficient for the task, and shielded cable isn't. Distance would be the best option.
Jay Kominek
  • 472
    800.133(A)(2) states that Communications wires and cables shall be separated by at least 50mm (2 in.) from conductors of any electrical light, power, Class 1 non-power-limited fire alarm or medium-power network-powered broadband communications circuits. -> Their concern is not with electrical interference, merely power safety. More distance is better. – Fiasco Labs Nov 04 '12 at 18:14
    Electrical interference are not their problem. It actually still is a problem, but it just won't kill you. – Nelson Sep 24 '20 at 05:19
I'm not sure how much the separation needs to be. One thing I found says 24" unless things are shielded. If one or the other is shielded by metal conduit then you could use 12". If both are shielded 6". It was all alphabet soup. I could not find a official standard.
Data cables, coax, and low voltage in general should not run parallel to mains power. While people mention the need to avoid interference, the main thing to watch out for is induction. Interference will be annoying to equipment, but stray voltages will be destructive.
I had someone run coax along 120 AC in my house. It ruined a few cable boxes, a network router, and at least one motherboard. Once I moved the coax over a few feet these problems went away.
So two feet for parallel runs with any required crossings happening at 90 degrees is the rule I personally use.
Andrew
  • The router and mobo were damaged by lightning strikes. The circuit was heavily loaded and would often trip during thunder storms. It had a GFCI breaker. Once the coax was moved away these problems ceased. 6 months of problems became 10 years or no more damaged equipment. – Andrew Mar 25 '15 at 00:08
  • It make a lot of sense that induction is an important problem, thanks. – Olivier 'Ölbaum' Scherler May 22 '16 at 18:11
  • The general guideline I've followed for parallel AC and data wires is about 1 inch per 10 volts. So one foot away for 110/120, and two feet of separation for 220/240. Empirically and anecdotally, that has worked well in my homes (I've rewired a few for myself now) and the small office where I provided that guidance to the electrician we hired for the remodel. The audio engineer there didn't complain, and I didn't notice any data issues with the network I managed, for whatever that's worth. – dannysauer May 11 '20 at 15:45
As others have mentioned, there could be some interference. Most likely there is not a safety issue here if you are running parallel to standard plastic-sheathed NM / romex wire, but you may see reduced speeds. It's certainly not against code. You should at least use CAT 5e over CAT 5, as it is shielded better and can almost work at Gigabit speeds. CAT 6a would be your best bet, but probably a little overkill for you. When I built, I ran 5e in my house, and tried to keep it away from the the electrical as much as I could. There was some crossover and parallel runs, but it was kept at a min and I have been getting near gigabit speeds.
Note, manufactures have been using the term CAT6e, which does not appear to be a true spec. Seems like they are loosely using that as CAT6 with extra shielding. CAT6a on wikipedia.
Here is an article I found: differences between cat5 cat5e cat6 and cat6e cables
mohlsen
  • 6,241
  • 38
  • 44
Its very simple; just don't put your Ethernet cables near any of power cables. Run your data cables 10" to 12" from your power cables. For future updates, put your cables inside conduit so that you can pull more cables or replace cables in the future.
Craig Tullis
  • 5,866
Hytham
    The actual separation is about 4-inches, iirc. This information can be found but it's been a while since I installed mine. You can run data cables closer but only if they are perpendicular to the electric lines. Of course, the farther away the better. – Rob Nov 04 '12 at 14:19
    You might want to motivate your answer with explanations, like others did here. – Olivier 'Ölbaum' Scherler May 22 '16 at 18:10
I work in the cctv/security area. A bloke I work with ran the cat 5e utp next to a 3 phase cable for only 2-3 meyers(yes, I know) it fried the ipcamera. When I went to inspect, i touched the metal plug of the camera and it almost threw me off the ladder. I thought I connected it to 220vAC instead of 12dc. Don't do it. The whole thing apparently becomes a capacitor and it shocks like hell. Hope it helps!
I was told if the cable was rated at the same voltage as your power.you could even run them in the same pipe. Plus cat5 is twisted which also reduces electromagnetic interference. I actually had to put data and power in the same pipe for a fuel station
user15011
    While twisted wiring reduces the impact of EM interference, my concern is if high voltage ever gets into low voltage wiring. Connectors and devices attached to low voltage/data connections do not expect high voltage over those connections. One short from a nail that misses a stud from the hot wire to the low voltage wiring, and you'll fry some devices at best, or electrocute a person at worst. – BMitch Sep 10 '13 at 01:10
I think not a good idea, every power cable creates an electromagnetic field http://en.wikipedia.org/wiki/Electromagnetic_induction which will influence the other cables at least will lead to disturbances and errors.
ChrisF
  • 16,868
  • 74
    What does your program for calculating voltage drop in industrial pumping stations have to do with running data wiring through a wall? – Niall C. Jan 17 '12 at 19:07
  • I've edited out the irrelevant part of the answer. – ChrisF Jan 18 '12 at 09:52
    Inverse square law says that the fields decrease rapidly with distance. The strength of the fields is dependent on the voltage and amperage in the power cables. Higher current requires greater separation. – Fiasco Labs Nov 04 '12 at 17:40
Any cat cable that isn't S/FTP or F/FTP is going to cause problems if you simply want the outlets to be relatively close to the electrical ones (6" or so between the two), specially in the long run.
You don't want to go cheap with ethernet cables and this is important as there are good reasons for it.
Same thing goes with doors and windows of the house when you are buying or building a new one, or just want to change them as it's time for it after so many years... that's right, you don't go cheap.
Focusrite
Be sure to use cables rated for in-wall Riser (CMR) use. That's a safety issue in the event of a fire. Use Plenum is rarely required in homes.
    Plenum (CMP) is only required if the cable is installed in a [plenum space](http://en.wikipedia.org/wiki/Plenum_space). Riser (CMR) is required for between floors so long as the space is not used for environmental air. The only differences really are plenum is self-extinguishing and low-smoke. – gregmac Jan 18 '12 at 00:06
    Also, this is not a very good answer to the actual question, and would have been better as a comment. – gregmac Jan 18 '12 at 00:07
