3

I'm looking for feedback on my plan before I begin the panel replacement, so thanks for your input. I already have a permit and am allowed to do all the work myself as long as it passes 2014 NEC code upon inspection.

My primary goal is to remove the 60 yr old aluminum wire and replace with copper and upgrade the panel box replacing all breakers as every current breaker is some weird double breaker that has two flip switches and two circuits in every slot on the box. Not enough room in current box if removing all doubles for singles.

I'm done running new wire throughout the house and ready to shove the new home run wires to the new box, this is where i have uncertainty as I'm trying to future proof. I anticipate a second HVAC for the second floor (i live in the south and this is the standard now for getting the upstairs below 85 in summer). Thus, future box would have about 15 20AMP breakers, 4 50 AMP breakers (HVAC) 3 30 AMP (tankless water heater) one stove at 40 AMP and dryer at 30 AMP. (presently have 1 30 for tank water heater and a 70/50 for hvac, which is oversight from hvac replacement done last summer and should be 50/50). I have a 200 AMP service presently, if i require more the local company will run a second 200AMP line to the house.

Questions:

  1. My Amperage total in these breakers is way over 200, i understand not all are used simultaneously such as AC/Heat, etc, but should i consider the upgrade to 400?
  2. the HVAC and water heater are all in the crawlspace (in this area my crawlspace is 7ft tall with plenty of access space), I think it would be wise to run 1 25 ft #6 wire from the panel (or second 200 AMP service) using a 100AMP breaker and create a subpanel (or second panel entirely with service upgrade) then run #6 CU wire to the HVAC and water heater, this would be 10-15ft for each. This excludes the second floor airflow handler that would eventually be in the attic- that is going to be directly above the main panel and would likely run it through that panel to keep wire distance shortest.
  3. What am I overlooking?

---UPDATE---

Based on feedback, further research and opening up my panel box. I'm thinking I'll consider not replacing the panel as i have a 200 30/42 box, but several of these tandem breakers are not in proper slots so I can fix that while ripping out all the AL wire and putting in new breakers and CU- I may do away with most of them as they're unneeded if i do the subpanel. I still think a sub panel is a good idea given all the big stuff is centralized - even though that means a flipped breaker would be under the house...

New question, last time i was in the box replacing a breaker that was shooting sparks into the house i thought my main lines were copper, they clearly are not. an electrician friend thinks they look fine, but should i consider a CU replacement all the way to the meter?

enter image description here

on the left is my trial/error breaker description, on the right is a hole patch from previous owner, not sure what the reason was

on the left is my trial/error breaker description, on the right is a hole patch from previous owner, not sure what the reason was

isherwood
  • 129,178
  • 7
  • 160
  • 386
  • 1
    6Cu on a 100A breaker?? – Harper - Reinstate Monica May 21 '17 at 01:38
  • What square footage is your house, how many kitchen receptacle circuits do you have installed right now, and what are the nameplate ratings on your major appliances (HVAC, stove, water heater, dryer)? Also, it sounds like you should be a) looking to redo your ductwork to take off the 2nd floor returns at ceiling level (yes, stack effect and hygric buoyancy are things, but you don't need to hurl BTUs at them), *and* you ***really shouldn't*** put that air handler in the attic -- it belongs *inside* the space it conditions! – ThreePhaseEel May 21 '17 at 02:52
  • @Harper using graph for distance and amperage i deduced #6 wire for 2 pole 100 amp. I'm not an electrician so this and any suggestion i have here is educated guess from reading NEC codes. open to critique, in fact welcoming it – Ryan Hollingsworth May 21 '17 at 15:13
  • @ThreePhaseEel 3000 sq ft home. Kitchen has a stove, 40, and 4 other circuits all on 20 AMP breakers. Microwave and single LED light are one, fridge is by itself. I actually am fighting with the HVAC company that redid my ductwork still, a lot of mistakes/shortcuts made. Current system is a 5ton package system so all outsite, attic one would be a split reducing duct length - excuse HVAC company is using for poor performance. (had a 3 ton before) – Ryan Hollingsworth May 21 '17 at 15:16
  • Is there a reason you can't put the second air handler in a 2nd floor closet or somesuch? – ThreePhaseEel May 21 '17 at 16:41
  • Also, why the tankless electric heater? It's a *massive* peak load when it's running, which is not kind to the electric grid. Good tank heaters are capable of being quite efficient, and there are less peak-power-hungry ways to get instant hot water (such as a demand-pumped system, or a well-insulated recirculation system) – ThreePhaseEel May 21 '17 at 16:43
  • Also, what's the nameplate rating on that stove of yours? – ThreePhaseEel May 21 '17 at 16:44
  • Do you have a copy of the 2014 NEC? If not, you should either buy a copy, or sign up for an NFPA account to get free read-only access to an online version. Read and understand the code, before you start work. – Tester101 May 21 '17 at 20:03
  • @ThreePhaseEel that's actually the plan. the location in the attic would some day (funds allowing) be a closet upstairs after we do an add-on to the house. Agree with your observations on tankless, i have been told they are better overall with power consumption, which is why I'd consider it- when my 80 gal dies (hopefully not any time soon!) – Ryan Hollingsworth May 21 '17 at 20:40
  • @Tester101 yes, i've been over it numerous times. there's a difference in reading it and understanding it correctly, which is why i stopped here. thanks for the help – Ryan Hollingsworth May 21 '17 at 20:44
  • I still need the nameplate ratings for those heavy appliances... – ThreePhaseEel May 21 '17 at 21:36
  • Anything larger than 6AWG should be aluminum. Not least, *the lugs are aluminum* at that size. If you go copper, you create a *dissimilar metals* problem you didn't have before. Now why do you think aluminum wire is bad? All those nasty stories you've heard. What's the root cause of those nasty stories? That's right, *dissimilar metals*. – Harper - Reinstate Monica May 22 '17 at 07:48
  • @Harper again, i'm no electrician, but as i've been gutting my house i've found over a dozen places where the AL wire has arced and melted its insulation in sections so i've kind of declared war on all of it in my house. my main lines from the meter are AL, from the street to the meter is CU (haven't confirmed visually, but that's what i am told) all that's AL presently is the main line, and double pole breaker lines. Also, all my HRs go AL to CU at a junction connected properly with nolax. – Ryan Hollingsworth May 22 '17 at 15:28
  • @Harper the only place I will use aluminum is for a residential feeder. I won't use aluminum for motor wiring at the mill because even when oxide inhibitors and properly torqued I have not seen proper sized aluminum hold up for large loads. The OP has a problem with aluminum as do I and you question his knowledge and or ability. Just by replacing residential aluminum wiring with copper he will have made his home safer as he noted there were many problems with the original install that was most likely done by a professional electrician. – Ed Beal Jan 30 '18 at 20:26
  • @EdBeal I deleted that comment but my concern over the limits of his knowledge was about *other things he had said* like #6 for 100A. It certainly had nothing to do with his anti-Al stance -- though, my comment first promoted Al *then* warned, so I see how it looked that way. **My apologies.** – Harper - Reinstate Monica Jan 30 '18 at 22:34

3 Answers3

2

First, the aluminum wire

In the 1960s, owing to a copper shortage, they rushed to market aluminum wire made from transmission line alloys, for 15-30A branch circuits. Electricians used it with common receptacles and switches listed for Cu-only, and in the rush, nothing was properly tested. On top of that, the work was often badly performed because housing booms tend to draw from the bottom of the barrel skillwise. I hardly need to tell you how that went: the things you saw were indeed your house almost burning down, and they were due to arcing. There are two good fixes:

  • Tear it all out -- kill it with fire before it kills you with fire.
  • Feed it from AFCI breakers, which will detect and trip on arc faults before they melt insulation. Then at leisure move through the house, and either tear it out, or clean up all the terminations of every wire, using CO-ALR rated receptacles/switches and Alumiconns instead of wire nuts.

As a backgrounder, copper has been commercially viable since 9000 BC, aluminum since 1950 thanks to smelting processes which use electricity. Obviously Al arrived in an electrical system long built-out and with pre-existing stock of gear made for Cu-only. The AA-1350 alloy, developed for steel-core transmission lines not small-wire terminations, was also a problem. All done in a rush.

Regardless, it can be argued that Cu is the bad actor because it doesn't have a good elasticity range and likes to work-harden. Al wire on Cu lugs doesn't work, but Cu wire on Al lugs works fine - as seen on Alumiconns, CO/ALR receptacles, and the lugs on your panel. You need to get the torques right because of dissimilar metal expansion/contraction rates. The right torque lets the Al flex and spring back as Cu changes size.

The new AA-8000 alloys are safe for 15-30A branch circuit wiring, but I won't use it because the inspector hates it, the buyer hates it, there's no cost savings, and it's too oddball. Like a lot of people, I start looking at Al for 60A+ (#4-), the larger, the more likely.

Needed service

As I look at your numbers, first, on-demand water heat, awesome. Even better if it's several units near point of use, because then you're not paying or waiting for hot water to cross the house. It's common for all-electric houses in the snowbelt to have 400A service.

I don't understand 4x50A for air conditioning. This seems like both too little and too much for a heat pump, the pump proper doesn't need 50 and the emergency heat usually needs more than 50. Critical issue is which will be used at the same time. If you need to run 4x50A at once, you're gonna need a second service.

Subpanel

I think a subpanel is a great idea and I would go 200 or 225A. Stay with QO if you like, great commercial-tier panel type. I would confer with the power company about where to locate this if it's to be the future main panel for a second service (keeping in mind one option is to put the main breaker outside as part of the meter pan, and feed this as a subpanel). Set it up so you can do both:

  • For now, feed it with as you plan, a 100A or 125A breaker and correct size wire.
  • later, make it the "main" panel of the second service.

Spaces: You say nine 2-pole breakers (seems low, but alright, 18 spaces) plus you say 15 singles (but I count 18 singles in your panel already with the double-stuff's).

Using double-stuff breakers is bad news, especially on a panel with 3/4" wide breakers. Most circuits are or will require AFCI or GFCI (and you want AFCI on any AL branch circuits). Those don't come in double-stuff, not even on 1" breakers.

Now we're at 36 spaces optimistically, you have 30 now. I would recommend at least a 30 space subpanel but given the small cost delta, I'd go 40 or 42. 40 is not unreasonable for a 200A service.

Existing panel

As far as the existing fat 200A aluminum wires, The lugs are aluminum. I would call the power company, have them pull the meter, inspect them at all ends for deterioration, clean 'em up, use the No-Ox.

Change the meter-panel run to Cu if it's really going to bother you. Copper on an aluminum lug will work if you get the torques right.

What am I overlooking? See the two large wires landed on the neutral lug and dissimilar metals to boot? That is illegal, a recipe for disaster, and a lost neutral can do far more damage than a lost hot. If the stranded Cu cable is your wire to your grounding electrode, that should go to your ground bus. If you absolutely need both wires to land there, then get the correct lug for this, which has voids for 2 wires.

enter image description here Nope. Try enter image description here Src GALCO


It sounds like you prefer running 6 AWG wire. Paralleling is absolutely not allowed, you cannot run two #6's for 100A instead of one #1Al or #3Cu. If you want to keep your heavy-wire runs to a minimum, don't be bashful about putting the subpanel right next to the main panel. That is completely kosher.

For a short run, I'd be inclined to use copper (damn the dissimilar metals) because it will flex easier and be less likely to unclip the breaker.

Harper - Reinstate Monica
  • 295,284
  • 26
  • 275
  • 720
0

Believe it or not, Single occupancy dwelling units have more code calculations and rules than almost any other building. Its because you consider diversity not connected load. In the State of Texas the largest meter box allowed is a 320A which the Utility Company calls a nominal 400A meter and will allow you to attach 2 - 200A panels or Breakers to your residence and the main means of disconnect must be placed at the same location. A parallel service will not be allowed.

When you do calculation for the service. Breaker sizes mean next to nothing. You need specific information about your equipment and appliances. Either nameplate or code equivalence. You need to get a professional to do this for you. No one will be wanting to do this for free. You might get a small independent Engineer to work it out or a master electrician. I suspect you are trying to get the electrical contractor to do it for free promising him he would get the job, but no electrical contractor I know, in this area, would do it without a signed contract for the job.

Sidebar: In general when I see someone talking about an electrical instantaneous water heater. I try to talk them out of it. The main reason is the cost of installation and the stress it puts on the electrical service. If you're convinced this is what you want, then go with it. If you're just thinking about it, try and find other people who have installed and used one and ask for their unbiased opinion. I would suggest other people you know, but you could also go online, just use good judgement.

Buy the way I have nothing against gas instantaneous water heaters.

Also, buy the way a plumber once told me they were to be called water heaters not hot water heaters because if the water is already hot why would we be heating it.

  • thanks for the feedback. As far as load calculations i haven't even had an electrician show up yet so that has not even come up in conversation. I live in one bedroom while i'm gutting the rest (wasn't the plan, but ya know..) so i literally own nothing to help with calculations other than the things i mentioned in original post. I am considering a tankless water heater because they boast a 35% less annual energy consumption. While i could see them using more while actively being used (3 double pole breakers!?) What are your reasons for being against them? – Ryan Hollingsworth May 21 '17 at 20:36
  • 2
    The reason why electric central tankless heaters are not a good idea for a house in the US is that the peak current draw is so large that this makes the installation more costly than it is worth. I question the claim of savings of electric power. Electric resistance hot water tanks have excellent insulation, have few maintenance needs, and are relatively inexpensive. If you are determined to lower your electric bill, you might consider a heat pump water heater. They do make more noise and would presumably have more maintenance needs. – Jim Stewart May 21 '17 at 22:10
  • i like to keep energy savings in mind while fixing systems within the house. thanks for the feedback, I appreciate it. I currently have an 80 gal electric. my only complaint with it is it is places flush on the ground rendering the water spicket unusable at the base. I may elevate it when i redo plumbing. thanks for feedback. – Ryan Hollingsworth May 22 '17 at 00:53
  • FWIW , Having installed both gas and electric on demand water heaters I would not recommend a single electric because of the power and I am a licensed electrician. They may save a small amount but the systems are limited in how hot they can get the water with multiple items using hot water. The last one I installed was replaced the next spring with a tank type. As they did not have gas avaiable and the next size up would require a 400 amp service where they would be required to pay for a new transformer any savings in energy would have been taken away for the life of the system plus some. – Ed Beal Jul 24 '17 at 19:19
-1

The size of your main breaker should not be bigger than the capacity of the feed to the house will support. If you think you need a larger main breaker than the feed to your house supports, you need to upgrade the electrical service coming into your house. Do not just put in a larger main breaker based on the number and size of the circuits in your house.

If your current panel is 200 amps and your main breaker has never tripped, then a 200 amp main breaker is enough. I ran my home with a 75 amp main breaker for many years, even with a whole house air conditioner and typical appliances (fridge/freezer, dishwasher, dehumidifier). BTW, the main breaker handles 220v and the various circuits typically are 110 v, so the main breaker of 200 amp is really 400 amp.

Relatively few houses have a main breaker large enough to service all the circuits at max load. So if you have 25 circuits each 20 am service you do NOT need a 500 amp main breaker.

Yehuda_NYC
  • 1,321
  • 11
  • 27
  • 44
  • Wow, some real mis information here. Code allows the service feed wires to be 83% of the main breaker. You have it backwards the service is sized by the breaker/ panel. Saying just because the main has not tripped is no way to say the load is safe, did you know that A 200 amp inverse time breaker can pass 300 amps without tripping for 15 minutes, his panel is a square D and for 1 second that breaker can pass 3000 amps no tripping (from Snyder's trip curves). Last there are quite a few homes that I have wired you could turn every appliance, light heat, AC everything and the main would hold. – Ed Beal Jan 30 '18 at 22:04
  • Ran out of room, you need to look at article 220 in the NEC to understand how services are sized. – Ed Beal Jan 30 '18 at 22:10
  • @EdBeal I did not say "the service is sized by the breaker/ panel." My first sentence says the opposite. What did I write that led you to write that? As to capacity, the main breaker tripping would indicate a capacity problem. So, the main breaker not tripping is an indication that there is no capacity problem. – Yehuda_NYC Jan 31 '18 at 00:10
  • @EdBeal I updated my answer to reflect your comment about "quite a few homes....every appliance." – Yehuda_NYC Jan 31 '18 at 14:10
  • This is what I am saying you have it backwards the service feeder IS sized by the panel/ main breaker, you can always have a larger feeder than required but it cannot be less than 83% of the main breaker / panel ampacity. – Ed Beal Jan 31 '18 at 14:24
  • @EdBeal. I clarified first paragraph based on your comment. – Yehuda_NYC Jan 31 '18 at 14:56