15
Recently moved into a 1950s-built house and am swapping out some of the older receptacles.
On one particular ungrounded circuit there are four receptacles. The first two are as expected - the two black wires were connected to the gold screws in the existing receptacles and the two white wires to the two silver screws. However, for the last two receptacles this was reversed - the incoming black wires were hooked up to the silver screws with the black hooked up to the gold screws.
In installing the new receptacles I switched the wiring so that the black wires are connected to the gold screws and the white wires to the silver screws.
My questions:
  1. How does one test to determine whether the black wire is really hot or if there was some mixup within the wall? I know there are receptacle testers, but I've heard that the polarity testing does not work for ungrounded receptacles.
  2. Is there any harm in having reverse polarity on an ungrounded wire? Is there potential harm to the devices that use the receptacle? Currently, these two receptacles are not being used, but I plan on plugging in a TV, DVD player, etc. into one of them.
Scott Mitchell
  • 933
    A [non-contact voltage tester](http://www.service.kleintools.com/Tool/PRD/Category/Non-Contact%20Voltage%20Testers%20TESTERS-CIRCUTVOLT-NONCONTACT) will go off near the hot, but should not near the neutral. – Tester101 Jan 19 '12 at 13:10
    @Tester101 I was going to suggest this too. It usually helps if you seperate the hot and neutral wires as far as they can be seperated before using the NC tester. – Steven Jan 19 '12 at 15:17
    @Steven You shouldn't even have to remove the receptacle. Stick the probe in/near one slot, then the other. The tip should fit into the receptacle slots, but not be long enough to touch the contacts (I think this is a well thought out design aspect). – Tester101 Jan 19 '12 at 15:48
6 Answers6
22
It is difficult to test without a ground reference. One way to do this is with a very sensitive (very high impedance) voltmeter such as a digital voltmeter. Make absolutely sure you are not grounded (and no pets or children are around). Make sure the digital voltmeter is definitely on the voltage setting. Plug one probe into one hole of the outlet, while the other probe is stretched out some distance. There should be a "phantom voltage" reading of somewhere between a few volts to nearly the full line voltage (for you in North America that would be around 120 volts) when plugged into the hot side. On the cold (neutral) side, there can also be some phantom voltage but it should be much less.
There is a potential harm in having the polarity reversed. Lamps with screw in bulb sockets should always be polarized so the rim of the socket (which is more easily touched) is connected to the cold side. That way to be shocked you'd have to stick your finger all the way inside the socket (you would not do that). With the polarity reversed, the hazard exists at the rim, which may have some exposure even with the bulb all the way in.
The hazard can also exist with older appliances that have the cold side intentionally connected to the appliance metallic frame. That was the only way to make them safer before the grounded outlets became widespread. But it required the outlet polarity be correct.
You can mitigate the hazard by using a ground fault current interrupting (GFCI) receptacle even without a ground wire available. These devices do their intended function even without a ground wire attached. The test button also should work (it cheats by running its 5ma current test between hot on the load side and neutral on the supply side ... not ground). If you find a device where the test function fails to trip it, do not use it. Mark the device as "UNgrounded" for circuits with no ground available. Do not use an alternate ground source that is not part of the supply cable for this purpose. Never use the neutral as a ground.
The most common hazard to people is being grounded when coming into contact with one wire that happens to be hot. The GFCI will trip in this situation even though the current is as low as 2ma. If a metal appliance has internally faulted where a hot wire has nicked or damaged insulation and is contacting the frame, this hazard exists with the frame of the appliance. In grounded situations the ground wire would cause that to short circuit.
A. I. Breveleri
  • 14,190
  • 44
Skaperen
  • 1,360
    The circuit is connected at the service panel with a GFCI breaker, so that sounds like good news. The electrician will be coming back out in a few weeks for some final permit-related work on work that was done a month or two ago. Perhaps I'll just leave the receptacle unused until then and ask the electrician to determine if the polarity is indeed reversed. Thanks – Scott Mitchell Jan 18 '12 at 23:36
    That would be a safer way. – Skaperen Jan 19 '12 at 09:57
In addition to lamps that Skaperen mentions, any other switched device will often switch only the hot connection. So if you have the polarity reversed, the internals of the device may always be hot (e.g. metal tongs in the toaster). The easier way to test is to get a ground. Try a wire connected to your copper plumbing pipes, or even better, a long extension cord connected to a grounded outlet somewhere else. Then a cheap contact based voltage tester between the ground and the hot wire can be measured.
As always, if you're not sure what you're doing, have the electrician do it. And turn off the power when handling electrical wire (only turning it back on temporarily for your test).
BMitch
  • 42,687
  • 197
If the non-contact voltage sensor is not an option, build yourself one of these:
(An outlet cheater, with the ground wire hooked to a bit of wire). Connect the ground wire to the third prong of an extension cord at a properly grounded outlet. Now you can test as many 2 wire outlets as your extension cord will reach. As with the @Skaperen answer, exclude children, pets and most adults during testing.
Bryce
  • 10,693
  • 108
with any voltage tester, hot to ground should have voltage while neutral to ground shouldn't (or much lower),
if you are missing a ground a grounded extension cable from another (grounded socket) will work or a voltage tester that can test against your own potential (just a google link no affiliation)
ratchet freak
  • 11,624
  • 33
I used an old neon AC tester and a proximity detector. Put both of the probes on the neon AC tester onto the the same slot in the outlet, then hold the proximity tester near the bulb - or the part of the tester farthest from the outlet. Do the same for the other slot.
The continuity tester will light for the hot slot- and not so for the neutral.
Bill Y
The methods above can kill you. Instead, just buy a Electrical Receptacle Wall Plug AC Outlet Ground Tester from Amazon for $5.
Oliver
    There is no device that you can plug into an *ungrounded* outlet that will tell you if the polarity is reversed. The detectors that check for reversed polarity do so by comparing the two prongs to the ground pin, which is impossible if there is no ground pin. – Hank Dec 08 '15 at 17:53
  • Agreed. The plug-in testers do not have access to enough information to determine if hot and neutral are swapped on an ungrounded outlet. – Billy left SE for Codidact Jan 05 '16 at 03:42