When I move 8 breakers from main panel to a subpanel (a few feet away) can I simply move the hot and neutral only to subpanel? The 8 breakers are grounded in the main panel already.
A 100 amp breaker feeds the subpanel (240V) using aluminum SE 2-2-2-4. I got subpanel neutral bus connected to main neutral bus. I got subpanel ground bus connected to main ground bus.
The subpanel has ground and neutral disconnected. Any NEC code reference would be welcome.
The right side of main panel (16 red wire twist caps) extend the 12 AWG wire to middle panel.
Picture of setup: enter image description here
ThreePhaseEel
  • 81,744
  • 227
ptay
  • 221
The grounding should be fine...
What you're doing here is running multiple circuits (the feeder out to the subpanel and the branch circuits back) through a single raceway with a single equipment grounding conductor, as implicitly provided for in NEC 250.122(C):
(C) Multiple Circuits. Where a single equipment grounding conductor is run with multiple circuits in the same raceway, cable, or cable tray, it shall be sized for the largest overcurrent device protecting conductors in the raceway, cable, or cable tray. Equipment grounding conductors installed in cable trays shall meet the minimum requirements of 392.10(B)(1)(c).
This, plus the fact that a single EGC can branch into multiple EGCs downstream of a panel when a multi-circuit raceway splits into individual circuits, means that you are fine on the grounding standpoint.
However, that poor, sweltering feeder cable isn't!
That feeder cable, on the other hand, is very not-fine. Putting 18 current-carrying wires (8 branch circuit hots and neutrals each, as well as the 2 feeder hots) into a single raceway forces a whopping 50% derate on the conductors (as per Table 310.15(B)(3)(a)), and 30" is a bit too long for the short-raceway provisions in 310.15(B)(3)(a) point 2, which are limited to raceways 24" or shorter. This means that your 2/2/2/4 SE cable is limited to 50A(!) and your 12AWG branch circuit wires can only handle 15A.
Fixing this would require re-running the middle panel's feeder and returning branch circuits using properly sized wires -- the branch-circuit wires would need to be bumped up to 10AWG, and the feeder hot wires would need to be bumped up to 1/0AWG (although a smaller neutral could be acceptable here, depending on the amount of unbalanced load anticipated in the subpanel). With your 1.5" EMT, the 10AWG THHN branch circuit wires (at 13.61mm2 of fill each), and compact stranded XHHW-2 singles for the feeder hot conductors, this leaves you with 422.96mm2 of fill used out of 526mm2 usable, before accounting for the neutral -- a full-size 1/0AWG neutral takes up another 102.6mm2 of fill, pushing you to the very limit of what that conduit can handle.
As a result, I'd recommend replacing it with 2" EMT to provide room for growth, or running two more EMTs (1/2" will do, with 72mm2 used vs 78mm2 usable) to allow the use of 12AWG wire for the branch circuits coming back via the new conduits. (Adding the extra conduits doesn't change the grounding logic from above at all, by the way.)
ThreePhaseEel
  • 81,744
  • 227
  • Would it be okay to mount a junction box above and to the right of the main panel, move 8 branch circuits out of main panel and into junction box, then bring the NM-2 cables across ceiling and into top of middle panel? That way those 8, 16 current carrying conductors, will completely bypass the main and EMT connecting main and middle panels. I would also pull the grounds out of main and put through same path. Would that avoid the derating issues? – ptay Apr 28 '18 at 17:32
  • @ptay -- that'd work, yes. – ThreePhaseEel Apr 28 '18 at 18:46
  • @ptay -- however, you'd still need to use 10AWG between the middle panel and the new junction box unless you split the run across two conduits. – ThreePhaseEel Apr 28 '18 at 22:29
  • Would rerouting the 8 x 12/2 NM that currently goes into the top of main through a junction box require the use of conduit? At the top of the main panel I planned to simply pull out the existing 8 x 12/2 circuits and bend it to the right and terminate into junction box (~2" away). Then splice with longer 8 x 12/2 NM and run that across ceiling on running board (about 20 inches) then parallel with joists and straight down into top of middle panel. Could I mount the junction box on the ceiling to avoid conduit requirements? – ptay Apr 28 '18 at 23:51
  • @ptay -- if you're making the run from the j-box to the panel with NM, you don't need to use conduit for it, no – ThreePhaseEel Apr 29 '18 at 00:18
  • I heading to local hardware store to grab the stuff. Would a 8" x 8" x 4" junction box suffice (256 cu. in.)? – ptay Apr 29 '18 at 00:25
  • @ptay -- that would be ample space :) – ThreePhaseEel Apr 29 '18 at 00:51
You need a serious case of Harper's Junction Boxes
My panels are distinctive because all around them are junction boxes 6-18" away. And then, many circuits come into those junction boxes, get spliced in those boxes, and onto the main panel. I do that because breaker thieves cut all the wires at the edge of the panels, leaving every wire 2' short.
But I find it useful for lots of things. Want to add GFCI to a circuit? Don't spend $45 on a GFCI breaker, spend $16 on a GFCI deadfront and $1 for a receptacle cover for that box.
Anyway, in your case, you don't necessarily need to use EMT, but the general idea is the same: pull the cable out of the main panel, bring it to a right-positioned box, splice there, and onto the new panel. However if you do use EMT, that's your ground path. And you can make those junction boxes attached to the ground of the subpanel, where it belongs.
In retrofitting grounds, the ground must go back to the same panel as the conductors come out of. In a "network of EMT" like you have here where the whole works is the ground, it's almost moot... almost.
The thing to beware of is throwing a bunch of circuits down your 1-1/2" conduit - you have to watch out for the derate table. Because of the derates already present on 14, 12 and 10 AWG wire, that derate table has no effect with 4 or fewer cables in one conduit, raceway or bundle. However it does affect subpanel feeder more acutely, so watch out.
  • What do you mean by "breaker thieves"? Are they stealing the breakers or the copper wire? Is theft now so common that one has to design the wiring for easier repair after a theft? Could you post a picture of one of your panels with all these junction boxes around it? – Jim Stewart Apr 28 '18 at 08:38
  • @JimStewart The breakers. The $4 breakers. I have no idea why. It was a really old panel, maybe they thought the breakers were scarce, maybe they had no idea what to take. Given the stuff they *didn't* take, it's clear they weren't MIT graduates... – Harper - Reinstate Monica Apr 28 '18 at 13:25
  • @Harper Can I get one large junction box for the 8 circuits, install upper right of my main, then bring the 12/2 solid Romex NM-B from junction box into top of middle subpanel? I would save room in main, it would bypass the EMT between main and subpanel, and be grounded in subpanel. – ptay Apr 28 '18 at 17:47
  • Yes, you could have one big junction box. You need roughly 5 cubic inches per splice, plus 5 c.i. once. I used these lovely 6x6x10s (600c.i.) that I fed with 4-5 conduits to keep to the 4 circuit per conduit max. ( tge entire building was conduit ). Remember the 4-max rule also applies to closely bundled NM. – Harper - Reinstate Monica Apr 29 '18 at 13:00