A single 12-3 cable was run to a double switch to control individual lights. The white is used as a hot, is this wiring correct/per NEC code?
1Why are you asking about this? Are you trying to put a smart-switch here? – ThreePhaseEel Nov 26 '18 at 04:49
back in the day, when you used a white in a switch loop, it was mandatory for it to be the always-hot, as it is here. That was so an electrician beeping out the wires would be more likely to notice the white is being used as a hot, since it's *always* hot. Also, that white wire needed to be marked with black paint or tape. Today, anywhere that would be legal is now required to bring an actual neutral to the switch, so white is used for the neutral and not for any hot. – Harper - Reinstate Monica Nov 26 '18 at 05:18
So it's no longer code, but no one is required to *change* existing wiring that once was code, right? That is, this is grandfathered, right? – Jim Stewart Nov 26 '18 at 11:31
The switches here have the ground connection and they are grounded. This is additional safety and code compliance. Lots of older houses still have ungrounded switches and this is a safety issue. AFIK this means the homeowner could use metal cover plates if desired. – Jim Stewart Nov 26 '18 at 11:54
1While you've got it open anyways you might put black tape on the white hot wire, to lessen any possible confusion of future homeowners who encounter this switch. – Eric Lippert Nov 26 '18 at 15:04
@UKMonkey OP specifically asks about NEC. – J... Nov 26 '18 at 15:13
1As an additional minor issue, it looks like the bonding wire is not actually secured to the box - it goes straight to the switches. I don't know that it was ever code to do it that way, but the ground wire should be screwed to the box first, then carry on to the devices in the box. – J... Nov 26 '18 at 16:06
Since the switches are grounded would the contacts of the switches with the box be sufficient to satisfy the code requirement to ground the box? – Jim Stewart Nov 26 '18 at 21:15
1@J... Except the metal surface of the fbox is flush with the wall, and the metal yoke of the switch appears able to bottom hard on it. That is an acceptable grounding path if that surface is clean bare metal with nothing in between. Would be better to ground the box rather than the yoke, though. – Harper - Reinstate Monica Nov 27 '18 at 00:37
1@ThreephaseEel - I just try to put a dimmer on it. This house had a lot of bx wires. I am curious even if you ground on the box, it won't actually grounded or trip the fuse. – Jemilianl Nov 27 '18 at 05:21
There is one safety issue here
It appears that the original installer took the ground wire from the 12/3 cable, looped it around one switch ground screw, then attached it to the other switch ground screw. This grounds the switch yokes fine, but leaves the (metal) box ungrounded save through screw threads. The solution to this is to cut off the existing ground wire with some slack left, then nut it to pigtails to the switch ground screws and a ground screw (10-32) into the provided hole in the back of the box.
While you're at it, you should wrap the white wire with black tape to make it crystal clear to the next bloke looking inside the box that it's hot and not neutral.
As to Code...this used to be OK, but not any longer
Back before the 2011 NEC, an "old style" switch loop like this was permitted by the Code -- a single pole switch only needs always-hot and switched-hot, so a 12/2 cable could be used for a single switch or a 12/3 for a pair of switches sharing a hot feed, as you see here.
However, due to the increasing prevalence of remote-controlled switches, motion sensors, timers, and advanced dimmers, all of which benefit from having a neutral at the switch box to provide power to the electronics inside, the 2011 NEC added 404.2(C) to ensure that the neutral was available for such devices, in lieu of them powering themselves via a hack such as using the ground wire as the return path or trickling their operating current through the load (quoted from the 2017 NEC, save for vernacular terms in [square brackets]):
(C) Switches Controlling Lighting Loads. The grounded circuit conductor [neutral] for the controlled lighting circuit shall be installed at the location where switches control lighting loads that are supplied by a grounded general-purpose branch circuit serving bathrooms, hallways, stairways, or rooms suitable for human habitation or occupancy as defined in the applicable building code. Where multiple switch locations control the same lighting load such that the entire floor area of the room or space is visible from the single or combined switch locations, the grounded circuit conductor [neutral] shall only be required at one location. A grounded conductor [neutral] shall not be required to be installed at lighting switch locations under any of the following conditions:
(1) Where conductors enter the box enclosing the switch through a raceway, provided that the raceway is large enough for all contained conductors, including a grounded conductor [neutral]
(2) Where the box enclosing the switch is accessible for the installation of an additional or replacement cable without removing finish materials
(3) Where snap switches with integral enclosures comply with 300.15(E)
(4) Where lighting in the area is controlled by automatic means
(5) Where a switch controls a receptacle load
The grounded conductor [neutral] shall be extended to any switch location as necessary and shall be connected to switching devices that require line-to-neutral voltage to operate the electronics of the switch in the standby mode and shall meet the requirements of 404.22.
Exception: The connection requirement shall become effective on January 1, 2020. It shall not apply to replacement or retrofit switches installed in locations prior to local adoption of 404.2(C) and where the grounded conductor [neutral] cannot be extended without removing finish materials. The number of electronic lighting control switches on a branch circuit shall not exceed five, and the number connected to any feeder on the load side of a system or main bonding jumper shall not exceed 25. For the purpose of this exception, a neutral busbar, in compliance with 200.2(B) and to which a main or system bonding jumper is connected shall not be limited as to the number of electronic lighting control switches connected.
Informational Note: The provision for a (future) grounded conductor [neutral] is to complete a circuit path for electronic lighting control devices.
and the 2017 NEC followed up on this with the addition of 404.22, which provides a phase-out for the hack of returning current via ground in lieu of neutral:
404.22 Electronic Lighting Control Switches. Electronic lighting control switches shall be listed. Electronic lighting control switches shall not introduce current on the equipment grounding conductor [ground] during normal operation. The requirement to not introduce current on the equipment grounding conductor [ground] shall take effect on January 1, 2020.
Exception: Electronic lighting control switches that introduce current on the equipment grounding conductor [ground] shall be permitted for applications covered by 404.2(C), Exception. Electronic lighting control switches that introduce current on the equipment grounding conductor [ground] shall be listed and marked for use in replacement or retrofit applications only.
- 81,744
- 29
- 133
- 227
4But this use of the 12/3 cable for two switches to power two independent lights is perfectly safe and is "grandfathered", right? The owner is under no obligation to bring the wiring up to current code, at least as far as old fashioned switch loops, right? – Jim Stewart Nov 26 '18 at 11:40
6@JimStewart -- it's safe and is grandfathered for existing installs, as long as you aren't trying to shove a smart switch in there :) – ThreePhaseEel Nov 26 '18 at 12:35
1ThreePhaseEel, I think this comment should be the first sentence in your answer. – Jim Stewart Nov 26 '18 at 13:04
@user12816, ungrounded switches used to be allowed by code, but changing to grounded switches *is* an improvement in safety. Of course it is easy to change the switches to grounded ones, but in general it is not easy to correct switch loops which have no neutral. Since the OP here asked about this, this raises the question: how would one bring a neutral into every switch box in a house wired in NM? – Jim Stewart Nov 26 '18 at 18:21
1The question asks about both safety and code-compliance, as individual factors, and this answer only addresses one of them. It *implies* that this is safe (since it used to be to code and the reason for the code change isn’t stated to have been an increase in safety standards or a discovery of a safety flaw in the approach), but it should be stated explicitly, particularly since your comment implies that in addition to concerns about smart switches, this way is also at least saf-*er*. – KRyan Nov 26 '18 at 18:49
@JimStewart: If a switch has no exposed metal, what purpose does grounding serve compared to designing things so there's no "drip path" between any electrical connections and any exposed components? – supercat Nov 26 '18 at 23:00
@supercat if a switch has no exposed metal, what do the cover plate screws go into? – Harper - Reinstate Monica Nov 27 '18 at 00:39
@Harper: Thermoplastic. I guess if someone used a metal cover plate there might be some advantage to having that cover plate grounded if there were any live conductors that might touch it or get connected via drip, but ensuring that there's nothing that could cause the cover to become live would seem safer. – supercat Nov 27 '18 at 00:44
1@supercat, this is one of those things that we don't have to speculate about. Press the sharp spikes of multimeter leads (in ohm mode) into the heads of the two screws of a switch with a plastic switch plate. I just did and got 1 ohm. This was a grounded switch I put in a few years ago.. – Jim Stewart Nov 27 '18 at 01:13
@JimStewart: It may be practice to ground the screws, but that seems to create the possibility of a shock risk in case of a ground wiring problem that wouldn't exist if the screws didn't connect to anything, and I'm not sure what risks it guards against that couldn't be mitigated just as well by ensuring there is no drip path to any live components. – supercat Nov 27 '18 at 01:26
1thanks for all the comments. I just try to put a dimmer switch on. This house was built in 1953, most of the wires are bx wire, the plastic of the wires start to fall off. The previous owner did some of the upgrade wiring, but not all. Most of the switches/box are metal. I am not sure if I ground it on the box, that will actually grounded. I am thinking to upgrade most of the wiring. – Jemilianl Nov 27 '18 at 05:17
@ ThreePhaseEel - if the electrician see this kind of connection, is he obligate to change it or upgrade to current code? – Jemilianl Nov 27 '18 at 05:27
@Jemilianl -- the problem right now isn't that the switches aren't grounded, it's that the box itself isn't grounded. Your electrician will be obligated to fix that, but the neutral issue shouldn't be an issue for an ordinary dimmer, only some fancy ones (with wifi/etc or designed for things more sophisticated than incandescent bulbs) – ThreePhaseEel Nov 27 '18 at 12:41