I was installing new LED lamps on my kitchen, which seemed to be functioning well. After turning off the lights, the newly installed lamps still had a dim light, that kept itself for quite long.
I've measured around 60VAC on the OFF switch for these lamps and 110VAC for the OFF switch attached to another lamp.
After lots of head scratching, I've tried to plug just one leg of the LED lamp into a plug hole, result on the picture below.
One leg connected, but partially ON
Why does this happen? How can I prevent it? Does it take a toll on my electrical bill?
Mefitico
  • 123
    What kind of switches do you have? – manassehkatz-Moving 2 Codidact Mar 19 '19 at 17:38
  • Yea, smart switches, three way, switches with lights on them, motion detector, etc. – JPhi1618 Mar 19 '19 at 17:40
  • @manassehkatz A simple on/off switch. No fancy stuff, no dimmer, nothing fancy at all. – Mefitico Mar 19 '19 at 17:55
  • What you describe sounds like volt leakage. Some cheaper switches allow small amounts of current through. Your volt meter may not go to that low of a volt level to detect a reading – Eric F Mar 19 '19 at 18:38
    @EricF, you have a citation for that? I can't imagine an ordinary switch that isn't totally on or off. I'm not even sure how something can physically "leak a little voltage". – JPhi1618 Mar 19 '19 at 18:42
    no, it doesn't cost you anything. the power comes from EMI leaking into the wires. This is what causes false positives on non-contact voltage detection sticks. Even a few microamps can produce (faintly) visible light from LEDs. you could use a bleeder resistor or dummy load to snub the glow, but does it really hurt anything? – dandavis Mar 19 '19 at 18:45
  • 3 way switches allow a small voltage through. I am unsure if OP is using a 3 way or not so just a suggestion. Sources = many but here is one: https://diy.stackexchange.com/questions/10933/why-does-voltage-still-exists-when-a-circuit-is-broken-by-a-3-way-switch – Eric F Mar 19 '19 at 18:46
    @EricF: no, they don't. You might be thinking of active switches like motion detectors, smart switches, solid-state dimmers, or digital timers, but regular 3-way switches physically break the connection. – dandavis Mar 19 '19 at 18:47
  • @EricF : That would have justified the lamps off in the ceiling light, but wouldn't really explain the light being on on my hand. (I took notice not to touch the other leg, as indeed the light would not be so dim if connected to my finger). – Mefitico Mar 19 '19 at 18:48
  • Also, I'm not using a 3 way switch. – Mefitico Mar 19 '19 at 18:48
    @EricF, I think [this article](https://en.wikipedia.org/wiki/Stray_voltage#Coupled_voltages) should clear it up for you. It's not a cheap switch "leaking", it's a byproduct of AC wiring and the tools used to measure "voltage". – JPhi1618 Mar 19 '19 at 19:00
  • What exactly are you touching to the bulb in that image? Is it a jumper wire sticking into the bulb fixture? – JPhi1618 Mar 19 '19 at 19:06
  • @JPhi1618 : It's the probe of a multimeter I had laying around. I noticed the other end would go into the plug hole. – Mefitico Mar 20 '19 at 12:40
What you are seeing is the effect of Stray Voltage caused by capacitive coupling. Electricians refer to this sometimes as Phantom Voltage.
Ungrounded metal objects close to electric field sources such as neon signs or conductors carrying alternating currents can have measurable voltage levels caused by capacitive coupling. Since voltages detected by high-impedance instruments disappear or become greatly reduced when a low impedance is substituted, the effect is sometimes called phantom voltage (or ghost voltage). The term is often used by electricians, and might be seen, for example, when measuring the voltage at a lighting fixture after removing the bulb. It is not unusual to measure phantom voltages of 50–90 volts when testing the wiring of ordinary 120 V circuits with a high-impedance instrument.
Sections bolded by me
The voltage you read with a common multimeter can change depending on how the wire is run, how long it is, etc, but you will usually be able to measure some voltage even when a light switch is turned off. If you connect even a tiny resistor between the phantom hot and neutral, the voltage will disappear. It is very, very low amperage and can't be felt or do any work.
Very simple LED bulbs that have the bare minimum of driver components can be illuminated by this voltage because they are very low power devices. LED bulbs that look more like regular light bulbs from major manufacturers have complex circuits to drive them and they typically will not show any glow.
JPhi1618
  • 27,679
  • 52
  • As for the second part of your question, it doesn't cost enough to matter. LEDs are very efficient, which is why they're able to light from phantom power. The solution is to add a resistor, which doesn't increase the efficiency any. The only reason to bother with it is if you actually want it to be dark when you turn off the switch. (Which is the case sometimes.) – user3757614 Oct 16 '19 at 17:55
As mentioned above, the cause is phantom (ghost) voltage most likely caused by using a twin active cable from the light to the switch. This can be fixed by either by replacing the cable with two sdi (single double insulated) cables or burning ghost voltage by adding a small load such as an iron core transformer in parallel with the light fitting.
Ben Davis
  • Hello, and welcome to Home Improvement. Thanks for the answer; keep 'em coming. And, you should probably [take our tour](//diy.stackexchange.com/tour) so you'll know how best to contribute here. – Daniel Griscom Oct 16 '19 at 17:55
  • North America doesn't have a concept in wiring equivalent to the SDI cables you're talking about, best I can tell... – ThreePhaseEel Oct 16 '19 at 23:37