14
My house just went through a flood and there was 7 feet of muddy water on the first floor, so all the AC outlets were underwater. After the water receded, all the unprotected outlets continued to work just fine. But 4 out of 5 GFCI outlets no longer work and cannot be reset. Can GFCI outlets be taken apart and cleaned/fixed or is there something inside that fails permanently?
Also, all the GFCI outlets are at the ends of their lines. In other words, there is only one wire connected to each LINE terminal and no wires connected to the LOAD terminals. So they only seem to be protecting themselves. But if they failed once they got wet and all the non-GFCI outlets survived, can I just replace them with non-GFCI outlets?
Patrick
  • 143
    You should probably replace *all* the outlets that were underwater, whether or not they are working *now*. – chepner Apr 02 '19 at 19:09
    All this flood remediation work should be covered by insurance, no? Cost shouldn't be a consideration here. – Criggie Apr 02 '19 at 19:31
    Good point, Criggie. I will check with my landlady re: her policy coverage. Thanks! – Patrick Apr 02 '19 at 19:43
    Wait a minute, landlady? Why are *you* repairing/replacing anything? – Nuclear Hoagie Apr 02 '19 at 19:45
    Just to answer your question, I do repair and maintenance work here in exchange for reduced rent. Thanks to everyone but I think I've gotten lots of good suggestions and advice and have all the info I need at this point. You folks are the best! :-) – Patrick Apr 02 '19 at 19:53
    @Criggie Floods are a crazy thing. In many areas floods are specifically **not** covered by regular insurance unless you specifically opt-in (and pay extra) for flood insurance. Which of course is crazy because floods are one of the most obvious (to most people) situations where insurance **should** be the answer. – manassehkatz-Moving 2 Codidact Apr 02 '19 at 20:00
    @manassehkatz Having been through an 8 year insurance nightmare due to quake damage, I am convinced insurance is the single most unethical industry that is still "legal" If OP did the replacement and 20 years away there was an electrical fire, an insurer may refuse to cover that event as well. – Criggie Apr 03 '19 at 00:06
    @Patrick Not sure how the laws apply in your location, but here in NZ one is barred from doing electrical work for reward (ie pay) unless you're certified and qualified. The only things a non-certified person can do is replace lamps and fuses. Replacing a face plate could only be done if you are the home owner, under a DIY exemption. Since you're working on this for reduced rent, it could be taken as working for reward. Be careful. – Criggie Apr 03 '19 at 00:09
    @manassehkatz Basically it's to discourage people from building homes in stupid locations by rivers that flood every other year. Unfortunately, because insurers won't cover it, the government felt responsible to cover and now taxpayers get to rebuild people's homes every few years instead of them moving. – user71659 Apr 03 '19 at 04:13
    @user71659 But I've also seen it used by insurers in areas that don't flood (probably rated "100 year") so people don't buy the extra flood insurance, so the insurers try to use that to deny payment floods from totally UNnatural causes - e.g., broken pipes. It has become a $emantic game. – manassehkatz-Moving 2 Codidact Apr 03 '19 at 04:21
    A GFCI is a safety device. This is like trying to "fix" a bicycle helment after you've had a crash in it. It has done its duty - time to get a new one. – J... Apr 03 '19 at 16:49
6 Answers6
28
Not worth the risk
GFCI (whether in receptacles or breakers) are sensitive, life safety electronic items. As such, you don't want to mess with them. In fact, the whole purpose of the TEST/RESET buttons is because they can fail, even without obvious problems such as a flood. Newer models even test automatically.
Is it possible that there is simply still water inside the GFCIs so that disassemble, dry, reassemble will work? Yes. Is it a good idea to try that? ABSOLUTELY NOT!
New basic GFCI receptacles are in the $15 - $20 range (varies depending on brand, 15A vs. 20A and other features). Not as cheap as plain receptacles, but not that big in the grand scheme of things.
Presumably the GFCI receptacles were installed because the particular locations - basement, bathroom, laundry room, etc. required them. Assuming that is the case, replacement with plain receptacles would be a code violation. In most places you are not required to upgrade to GFCI unless you are making changes, but downgrading doesn't make sense and is likely a code violation.
Panel Alternative
An alternative is to install GFCI breakers in the main panel. This has the disadvantage that your panel may not have room for GFCI, or if you have a very old panel or fuses instead of breakers then that is not even an option. These breakers also typically cost more than "ordinary breaker" + "GFCI receptacle" so this change would be for practical reasons (e.g., protect outside circuits where a GFCI receptacle would be subject to severe weather) or as part of a panel upgrade. If you are looking at simple cost, replacing the GFCI receptacles where they are currently located will almost certainly be the way to go.
Check Out Everything Else
As Harper noted, there are plenty of other concerns as well. This is one situation where DIY may really not be enough. You could have hidden damage that can come back to burn you (literally) when you least expect it. Professional evaluation of the entire electrical system that was underwater is worthwhile.
    Thanks for the quick reply and helpful information about GFCI breakers, manassehkatz. There are 3 circuits involved so it sounds like just replacing the receptacles will be the way to go! – Patrick Apr 02 '19 at 17:43
    @Patrick To be clear, even if it were 300 replacing would be the way to go. These devices aren't here for fun. Do it right. (And if you value your time at all, there's about a 0% chance doing anything but replacing broken receptacles would be cheaper.) – GManNickG Apr 02 '19 at 20:33
  • @GManNickG Correct. The # of circuits actually has no bearing on this equation. What could have bearing on the equation would be if you had 5 GFCI receptacles **on a single circuit** because nobody knew how to use LINE/LOAD correctly. Then replacing all 5 with a single GFCI breaker and 5 regular receptacles would likely be cheaper. But that's not a typical situation. – manassehkatz-Moving 2 Codidact Apr 02 '19 at 20:36
  • Beware of GFCI breakers in panel. Computers don't like GFCI much. – Joshua Apr 02 '19 at 20:59
    @Joshua Computers - or almost any **properly functioning** equipment - should not care whether it is on a GFCI or now. I'm sitting in my basement right now with my computer on a GFCI receptacle. Never a problem. There **might** be issues in some circumstances with equipment causing problems for **A**FCI, but even then computers should not be the problem. – manassehkatz-Moving 2 Codidact Apr 02 '19 at 21:04
    @manassehkatz: It's an energy management problem. The data lines leak tiny amounts of power through the pull-up or pull-down resistors. We found that as little as two ethernet cables in use will reliably trip a GFCI due to the carrier sense circuit alone. Fundamentally, if you induce a voltage difference between the neutral and ground wires, the GFCI will trip. – Joshua Apr 02 '19 at 21:38
    @Joshua I've never had a problem. Most of my customers' computers are not on GFCI, but I haven't seen this at all. Are these servers, desktop computers or specialized equipment? What kind of power supplies? – manassehkatz-Moving 2 Codidact Apr 02 '19 at 21:41
  • @manassehkatz: Intel gigabit Ethernet adapters. Common HP and Dell computers. Off the shelf two-wire switches (no ground line). It's really easy to prove that the circuit that does not fault does not exist once you look at the actual wiring diagrams for Ethernet. – Joshua Apr 02 '19 at 21:44
    @Joshua Well, I've never seen a problem myself. I can see issues with powerline networking not getting past GFCI of AFCI. I can see why AFCI would be extra sensitive to a lot of things. But I don't quite get why GFCI would have a problem as long as the computer (or router or whatever) power supply is functioning properly. – manassehkatz-Moving 2 Codidact Apr 02 '19 at 21:57
  • @manassehkatz: Joshua's right, computer data cables will form a circuit through which small amounts of current flow, and if not every single computer and device on the network is on the same circuit, and you don't have perfect isolation transformers, you've just broken the GFCI assumption that line current = return current on neutral. – Ben Voigt Apr 03 '19 at 00:46
    @BenVoigt Well, I have yet to see this problem. Which may be because most (not all) of my customers with real networks are in offices which don't have GFCI-protected circuits. If/when I see this happen, I'll know what to look for. – manassehkatz-Moving 2 Codidact Apr 03 '19 at 01:03
    @BenVoigt The data cable should be isolated from ground. Ethernet in particular is supposed to be transformer-isolated. And balanced. You might notice the wires are paired up and the current on one wire of a pair is supposed to cancel out the current on the other wire of the pair - this is to reduce interference but it also means there's no net current. (There can't be a net current anyway because of the transformers) – user253751 Apr 03 '19 at 01:20
  • @immibis: The isolation from ground blocks only DC. And with PoE, not even that. The twisted loop is supposed to block net current at other frequencies, but that's always imperfect too. – Ben Voigt Apr 03 '19 at 01:23
    @BenVoigt Desktop computers (and laptops) don't use PoE. How much stray coupling do you need to get more than microamps of AC? – user253751 Apr 03 '19 at 02:49
    @Joshua and others -- I've put a question on this up on [EE.SE](https://electronics.stackexchange.com/questions/430425/how-much-mains-leakage-does-an-ethernet-connection-to-a-pc-induce-and-what-is-t), hopefully, the answers there shed more light on this problem. – ThreePhaseEel Apr 03 '19 at 02:54
    @Joshua, light bulbs lose power through heat and light. Why don't they trip GFCIs? – The Photon Apr 03 '19 at 03:02
  • @ThePhoton: Power transfer doesn't imply current imbalance. Just that the voltage and current are not exactly orthogonal in phase. – Ben Voigt Apr 03 '19 at 03:27
    @BenVoigt, was responding to the comment that said the problem was that "the data lines leak tiny amounts of power through the pull-up or pull-down resistors." – The Photon Apr 03 '19 at 03:31
    @BenVoigt, as for voltage and current out of phase, I've never had a problem running my power tools off of GFCI outlets outdoors. That includes a 50-year-old Shopsmith that was surely not designed with any kind of power factor correction. – The Photon Apr 03 '19 at 03:35
    @ThePhoton: You're right that Joshua's comment about "leaking power" is not an accurate description, but I think both you and I know what was meant: creation of parasitic circuits. – Ben Voigt Apr 03 '19 at 03:39
  • @BenVoigt, OK, sorry I misread your comment about phase of voltage and current. Deleting my response now. – The Photon Apr 03 '19 at 03:41
22
It's worse than that. The cables are done too.
Most houses are wired with Romex (NM) cable. That's not rated for getting wet. It has paper packing inside the sheath that just wicks water like crazy.
If the people who built the house were flood savvy, they built with UF cable, which is wet-rated and notably does not have that paper packing. It will be fine. Or they built with conduit and use THWN or THWN-2 individual wires. Those are also wet-rated and work fine even if the conduit is full of water, which is the normal expectation outdoors.
All the switches and outlets are done
Flood damage destroys everything, becuase it's not just water, it's a lot of crud too. Flood cars are finished. Some of that crud is electrically conductive, and it has gunked up each of the receptacles with it. Also, the crud is corrosive, so anything in that receptacle that could corrode, is right now.
For all those reasons (electronics are extra sensitive to corrosion), the GFCIs are all finished and must be replaced.
The service panel is also done
Service panels, even outdoor rated ones, are not rated to go for a swim. The crud is also inside the breakers laying conductive tracks and doing corrosion damage. These breakers will no longer be reliable. It might be possible to pull the buses out of the service panel and clean them, you'd have to see.
If you look at news footage of Houston's recent flood, you see lots of 2-storey apartments, 1st floors flooded out, and 2nd floors with the lights on and the A/C running. Flood-savvy builders take their power from overhead lines not underground, and put the service panel on the 2nd floor. They put 1st floor circuits on GFCI breakers so they don't electrify the water and drown people. A GFCI breaker protects the entire circuit and makes GFCI receptacles unnecessary.
All GFCI devices can protect downline loads if wired correctly. You are correct that a GFCI receptacle on the end of a circuit is a bit of a waste.
(Usually) you can't work on rental properties
Most areas have a law that only licensed electricians can do work on rental properties. That is to prevent landlords from doing shoddy work on the cheap and killing their tenants.
Check with your local authority (the department in City Hall you go to pull permits). They will tell you what a handyman can and cannot do with electrical in rental units. If they allow you to do anything at all, it would be limited to changing receptacles, switches or lights. GFCI receptacle changes could be included in that.
    The silver lining is that since the walls need to be torn apart to eradicate mold, getting access to the ruined electrical cables will not be difficult. – Ben Voigt Apr 03 '19 at 00:44
  1. It's not practically feasible to clean and repair a GFCI outlet. They're fairly elaborate and sensitive gizmos, and they're not designed to be disassembled. Could you pull it off? Probably. Would I want to? Nope. Would it void the UL listing? Yup.
  2. Whether GFCI outlets are needed at the end of a circuit depends almost entirely on where they're located. The fact that they're the last in a string of outlets is inconsequential. Are they in locations normally exposed to water, such as kitchens and bathrooms? If so, they need to stay.
  • Comments are not for extended discussion; this conversation has been [moved to chat](https://chat.stackexchange.com/rooms/91890/discussion-on-answer-by-isherwood-gfci-outlets-can-they-be-repaired-are-they). – Michael Karas Apr 03 '19 at 04:05
A GFCI protects you by using a circuit board to watch the current flowing out of the hot and coming back into the neutral. If it reaches around 5mA imbalance, the breaker trips. You said yours were submerged in a flood. Just like your cell phone or computer, the flood ruined the circuitry inside. You cannot repair it yourself (assuming anyone can repair it).
Replacing them is not terribly expensive, and the newer ones have a self-test mechanism.
As a homeowner, an electrical engineer, and a fair tinkerer, I would not attempt to repair a GFCI unless I was desperate.
However, if I absolutely had to, what I would try is first rinsing with plain water and a few drops of dish detergent, then rinsing in distilled water with a few drops of dishwasher "rinse agent" added, then rinsing in plain rubbing alcohol. Do all these rinses thoroughly, so that the fluid is swished through the fixture. Then shake dry the best you can and put in a 100 degree oven (no warmer!) for an hour or two. If that doesn't fix it, toss it in the trash!
It would be interesting to take one of the things apart to see how it's made, but I'm guessing it would be impossible to get back together again. To be successful you'd have to sacrifice one or two units to help you design assembly jigs of some sort, and you'd probably have to find some replacement rivets from somewhere.
With regard to the wiring, it's kinda iffy. You especially want to make sure the GFCIs are replaced, and that, when reinstalled, they are properly grounded. (Check the continuity of the ground wire!) Any cabling that looks suspicious (especially scummy or "burned looking", eg) should be replaced. And any regular outlets in, eg, nursery areas, where gerfingerpokin is apt to be going on should be replaced.
Hot Licks
  • 2,083
    You are right about having much difficulty putting them back together, as most safety devices are constructed in a tamper-proof way, having no serviceable parts inside. If they look like they have been messed with, they should be tossed out as nobody with any authority will approve them. "Insurance void if opened". – sleblanc Apr 03 '19 at 04:05
To separately answer the "end of the line" question re GFCIs, no, placing them at the end of a sequence of daisy-chained outlets is not in any way required by code, and it provides no protection to the rest of the circuit.
One wonders if the previous occupant replaced standard outlets in these locations with the GFCIs, under the mistaken impression that the would protect the entire chain.
Now might be a good time to reassess the situation (especially given the possible unseen water damage to the wiring) and install daisy-chained GFCIs as the first outlet of the circuits, or at least those circuits that are closest to humans.
Hot Licks