I have a question that is more theoretical in nature. I know that when you have 14/2 cable and put it in a 1/2 conduit you are above fill (or just at max fill). The NEC cites that this is in part due to heat dissipation.
300.17 Number and Size of Conductors in Raceway. The number and size of conductors in any raceway shall not be more than will permit dissipation of the heat and ready installation or withdrawal of the conductors without damage to the conductors or to their insulation.
Consider a close-celled foam installation:
The cables are usually entirely encased in the stud-bays (even less clearance than in 1/2 conduit), and while foam is a good insulator it is a bad heat-sink; it doesn't allow good heat-dissipation due to there being little to no air.
Since I've seen a few foam installations where the cable is completely covered there must not be a code regarding it, and I was just wondering why? Doesn't the foam pose an issue for heat dissipation?
Please when answering cite official sources if at all possible and don't rely on conjecture.
Additional section of interest:
310.15.3
(3) The rate at which generated heat dissipates into the ambient medium. Thermal insulation that covers or surrounds conductors affects the rate of heat dissipation. (4) Adjacent load-carrying conductors — adjacent conductors have the dual effect of raising the ambient temperature and impeding heat dissipation.
Alex
  • 628
    Do you have a solid source saying that fill calculations take heat dissipation into account? I always assumed it was so you could safely pull cable without damaging it. I tried to find a source but only found some contentious forum posts about heat. It's not like the conduit gives any air circulation which is how air is normally used to remove heat. – JPhi1618 May 01 '19 at 19:46
  • Are the cables being packed together tightly, or spaced apart within the foam? – ThreePhaseEel May 01 '19 at 23:41
  • @ThreePhaseEel assume a normal installation, in some cases 1 cable per hole, in others the max of 2-4 depending. this is all theoretical anyways. – Alex May 02 '19 at 00:34
  • @JPhi1618 i haven't found a study but it is part of the NEC (added above), both heat dissipation and protecting sheathing seems to be the reasoning. and although a conduit doesn't have air circulation, it does have "free-air" which seems to be an important term used quite often in the NEC. – Alex May 02 '19 at 00:35
  • Well, it’s that “seems to be” that I’m asking about. I’m not saying you’re wrong, I’m just curious if it ever specifically sites heat as a reason for some aspect of fill calculations. – JPhi1618 May 02 '19 at 00:38
  • sorry if i wasn't clear it is explicitly stated (see quote). by saying "seems" i just mean i haven't seen any study or raw data on it so i have to take the nec on their word as to the reasoning. i guess the real question is: is this because of "free-air" or is this because of "mutual heating", that the NEC isn't very clear on. – Alex May 02 '19 at 00:39
The foam isn't the issue, but a lack of spacing can be
Foaming NM cables into a wall (or otherwise burying them in thermal insulation) isn't considered to be an issue, provided that the cables were originally run in a manner that maintains proper spacing between them. However, not all installers are that careful, and for those who aren't, they find themselves staring at the third paragraph of NEC 334.80:
Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(3)(a).
This covers the issues with mutual heating that you allude to when the current-carrying conductors are actually adjacent to each other, such as when a bunch of NM cables are run together. However, with the cables spaced out properly, they will sit separated by thermal insulation, which prevents the cables from heating each other up.
ThreePhaseEel
  • 81,744
  • 227
  • So to help me understand, when considering cables in a conduit, you aren't so much worried about the heat dissipation by air, but rather the effect of mutual heating? – Alex May 02 '19 at 01:47
    @Alex -- yeah, when dealing with wires in conduit, the 310.15(B)(3)(a) derates are what deal with mutual heating effects – ThreePhaseEel May 02 '19 at 01:55
  • i guess i just find it weird that a romex wire sleeved in a form-perfect conduit would be illegal, however a romex sleeved in foam isn't. i guess it comes down to romex shouldn't ever really be run in conduit, and nec just added that section regarding calculating the fill for romex to cover their bases so that people don't try and shove 2 romex cables in a 1/2 pvc conduit. – Alex May 02 '19 at 02:28
    @Alex -- yeah, shoving NM down conduit is a bad idea simply for the amount of *grief* you'll experience in the process of pulling it. Also, there are cables that are intended to be run in conduits and other such raceways, such as the *tray cables* often used in industrial environments as well as communications-type cables, and the NEC needs to supply *some* way of handling them in fill calculations.... – ThreePhaseEel May 02 '19 at 02:43
    @Alex both. You also have to consider the effects of all the conductors being fully used, i.e. 9 #12 conductors going full-tilt at 16A, powering lighting in a big box store. The conduit must dissipate the sum of that heat, and its surface area is limited. – Harper - Reinstate Monica May 02 '19 at 13:51
The limitations on cable in conduit have a whole lot more to do with the risk of physical damage to the cable. This is really hard to understand for Romex people, because they only know Romex and they've never experienced the pleasure of working with stranded THHN with that nice slick nylon outer coating.
By contrast, wrestling cable in conduit is a nightmare. No nylon coating, and it's stiff as hell. It's also fragile and vulnerable to damage, since it's not made for conduit. And it's very likely to jam, which means it gets tugged on hard because people are people, and that means damage.
Oval cable needs the same conduit space as a circular wire of the large dimension. That's because the cable doesn't obediently lay flat, it gets twisted in handling, and that behaves worse than a circular wire of the large dimension, more likely to jam and snag.
Two is the worst case; effectively the pipe needs to be wider than the wide dimensions of both cables side by side. Because in the course of pulling, that will happen.
One thing that took me years to understand is that the ability to shed heat defines wire, cable and conduit ampacity. The thickness (cross-section) of a conductor decides how much heat it makes in the first place, and that is proportional to cross-section, which is the second-order of diameter - double diameter, quadruple cross section. However, ability to shed heat is proportional to surface area, which is the first order of diameter - double diameter, only double surface area.
That is why if you look at the ampacity tables, they don't ramp up as much as you'd expect to at the larger sizes -- doubling wire cross-section (going up 4 AWG sizes) doesn't double ampacity because it only increases the surface area (ability to shed heat) by sqrt(2).
That is also why the conduit-fill derate tables are so punishing above 9 wires. A 3" conduit has 16x the space of a 3/4" conduit, but only 4x the surface area (heat shed).
Anyway, in foam insulation, you have the same problem. A wire pair can radiate heat through insulation, not efficiently of course. Two wire pairs means it has twice the heat to radiate through the same inefficient media. More than two pairs, moreso; and at that point 310.15b7 is brought to bear. Spread the wires out and they are propagating heat through different media.
  • The paragraph with the bolded sentence could use some clarification. The part about heat production makes sense (it's related to cross-sectional area, which defines resistance per unit length, and is pi*R^2) though it's a little awkward to read. The bolded sentence might use a wrong term: surface area (per unit length) is pi*D, so doubling diameter doubles not cross-section, but rather surface area or circumference? I think it's the blending of "cross-section[al area]" and "surface area" terms that makes the paragraph confusing. – Greg Hill May 02 '19 at 19:48
  • If you could make a connection with foam insulation that would be great. I appreciate your thorough remarks on conduits. – Alex May 02 '19 at 21:52