20
I did this wiring in my bonus room years ago, and now I'm wondering if it is in fact legal and safe. This is a built-in book case that I built and installed myself. The bookshelf went in over a light switch box, so I moved the light switches with the boxes and cables you see here. I've removed the plastic blank faceplate for the picture. When the faceplate is installed, the two cables come out over the top of the faceplate. The two cables enter the top rear of the box through a cable clamp which you can't see in this picture.
I'm happy to go back and do it right if this doesn't pass muster. I guess my main question is whether the exposed cables are okay.
This is all in North Carolina, US.
picture of wiring in built in bookshelf
Update: here's a pic of the wiring in the wiremold tracks, before snapping on the elbow covers. I had to do quite a bit of hacksawing and grinding to shorten the elbows so they would fit. completed wiring before elbow covers
And here's the almost completed job. almost completed job
Thanks to all for the help!
TreyGuy
  • 203
    Is there anything that stops someone from shoving books into the exposed NM cables, thus pinching/crushing them? That's my prime concern with this setup.... – ThreePhaseEel May 27 '19 at 20:40
  • @ThreePhaseEel: no, there's nothing covering the exposed NM cables. Maybe I could add some plastic conduit from the left box to the wall? – TreyGuy May 27 '19 at 21:04
  • Can the conduit just stop at the hole in the wall? Is plastic conduit okay here? – TreyGuy May 27 '19 at 22:31
  • Wire looks uf to me nmb subject to book crushing ? Been that way for years..It is ugly most AHJ would have let that go to a home owner. With a little talk.. Nail you to the cross if you were electrician..Put a box over it done. –  May 28 '19 at 06:33
    @RobertMoody What do those abbreviations mean? – Omar and Lorraine May 28 '19 at 07:34
  • How about you simply install 5in of 3/4 pipe from side to wall. That would solve issues – Jason Lopez May 28 '19 at 11:58
    @Wilson, they are types of wire. UF is "underground feeder" rated for direct burial (usually not used inside), and NM-B is "Non-metallic" and is the proper term for common residential wire known by its brand name, "Romex". Lastly, AHJ is "Authority Having Jurisdiction" which is a generic term for whatever city or county or state entity is responsible for inspecting electrical (or plumbing or whatever) work in the area. – JPhi1618 May 28 '19 at 17:45
    Thanks @jphi1618. Turns out none of that applies in my country. Must be a US specific thing – Omar and Lorraine May 28 '19 at 19:05
  • @Wilson yeah -- NM is what folks in North America call UK/Commonwealth "twin and earth" type cables – ThreePhaseEel May 28 '19 at 23:42
  • BTW, am I correct in assuming that you have a ground clip present on the right side of the rear box? – ThreePhaseEel May 28 '19 at 23:43
    @RobertMoody nah nah nah, (*dodgey salesman voice*) he's missing a GST which was suppossed to be connected to the SPE but it can't beacuse the XYZ and ABC wires are crossing with the WRE – Emobe May 29 '19 at 07:01
    @ThreePhaseEel Yes, that is a ground clip in the original picture. Now the ground is attached at the rear of both boxes and on the switch in the right box. – TreyGuy Jun 03 '19 at 22:35
6 Answers6
28
My concern here would be for physical abuse
Right now, nothing stops those NM cables from getting whacked/pinched/crushed with books and such, especially if you have heavy tomes on your shelves. This could be considered a violation of NEC 334.15(A) or (B):
334.15 Exposed Work. In exposed work, except as provided in 300.11(A), cable shall be installed as specified in 334.15(A) through (C).
(A) To Follow Surface. Cable shall closely follow the surface of the building finish or of running boards.
(B) Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means extending at least 150 mm (6 in.) above the floor.
Type NMC cable installed in shallow chases or grooves in masonry, concrete, or adobe shall be protected in accordance with the requirements in 300.4(F) and covered with plaster, adobe, or similar finish.
You have two options to address this
There are two ways to address this issue: you can either replace the NM cables with a wiring method better suited to withstanding said reader-inflicted physical abuse, or you can put something in that will protect the boxes and cables from rough encounters with books while still allowing for access to them. We'll discuss these options in turn.
Making this more rugged
While the normal wiring methods that are used to withstand the NEC's definition of "physical damage" are the various flavors of heavy-duty rigid conduit (RMC, IMC, EMT, Schedule 80 PVC, and RTRC-XW), surface metal raceway is also rated for such a duty, and doesn't suffer from the bending radius issues that other wiring methods in this application would have to deal with.
If you're using Legrand's Wiremold line for this, you'll need:
  • Two BW17 right angle raceway-to-1/2" conduit fittings, attached with 1/2" chase nipples and locknuts
  • Two BWH6 flat elbows
  • A BWH7 inside elbow
  • A length of BWH1 raceway
  • And a two gang metal extension ring for the old switch box
The idea here is that you use the extension ring instead of the normal starter box (as they don't make one in two gang, and two-gang to one-gang mud rings stick out too far) along with one of the BW17 fittings and associated parts to get the raceway going upward from the gang furthest from the inside corner, then use the two flat elbows and the inside elbow to get around the bend and going back down. Then it's just a matter of using the other BW17 and its friends to transition the wires back into the box.
Once the raceway's in, then, you run individual THHN wires inside it to connect the circuits between the two boxes, just as if you were working in conduit. (The existing NM cables can be tossed, or shucked and their wires kept for pigtail duty, your choice.) Don't forget to plug the knockouts where the cables once entered/exited the boxes!
Using some cabinetry to box the boxes
If you feel yourself a better cabinetmaker than electrician, another option for this situation would be to put a cabinet divider wall in just to the right of this, and then add a cabinet door over the front, maintaining access while protecting the existing assembly from physical abuse or damage. This also has the advantage of being a more finished look, at the cost of having an "un-cabinet" in your house that you can't really use for anything at all. Making it match the existing built-in bookshelves may be a challenge, as well.
ThreePhaseEel
  • 81,744
  • 227
    Wow, thanks for the very detailed answer! Stay tuned for pics of the completed project. – TreyGuy May 27 '19 at 23:40
    @TreyGuy -- we upvote and/or accept folks' answers to show our thanks here :) – ThreePhaseEel May 27 '19 at 23:41
  • I tried upvoting, but it seems I don't have enough cred as a newbie member. I don't see an option for accepting your answer. – TreyGuy May 28 '19 at 01:07
    @TreyGuy -- it's the greyed check below the vote arrows – ThreePhaseEel May 28 '19 at 01:15
    I do love the box it part..And as long as it is easy to get at splice laying there not nailed .. –  May 28 '19 at 06:42
  • You do always seem to make great points..You know the trade you talk nm nmb it looks uf If you been in trade should pick that wright off ..Just question . Would you do that in sch 40 or 80 And explain if any physical abuse on sch 40 witch can go under ground be here . –  May 28 '19 at 06:55
    You can find/make fake book spines to cover up the lost space – ratchet freak May 28 '19 at 11:04
  • There's a minimum distance to maintain between the cabinet and the wires right? Otherwise you'd need some sort of metal plate to prevent errant fasteners, if I understand correctly. – JimmyJames May 28 '19 at 13:50
  • Totally agree with the boxing - add two sides and a top to make a step, and either put small books on top, or display a knick-nack there. Get fancy with a piece of glass as the top, and add an LED as an uplight inside the box switched by the room light switch and its extra-fancy. – Criggie May 28 '19 at 20:18
  • @JimmyJames 1.25", but that only applies to cables in walls, on furring strips, or the like – ThreePhaseEel May 28 '19 at 23:41
  • I updated the original post with pictures of the wiremold in place. Thanks @ThreePhaseEel for the suggestion... I never would have thought of wiremold. I barely even knew it existed, even though it's right there in Home Depot. I did have to modify the elbows quite a bit to get them to fit in the space. – TreyGuy Jun 03 '19 at 03:19
I would go a different way here.
First, the original light switch junction box belongs in the actual wall, not pulled out into the cabinets which themselves could pull out of the wall. I would leave a nice big hole in the cabinet which aligns with the switch box.
They make blank steel cover plates for 2-gang boxes... They are fairly small dimensionally, and they have a 1/2" knockout on their face. I'd come out of that into flexible metal conduit, then the FMC into the back of that 2-gang handy-box you nicely installed.
I'd run 5 individual wires - stranded THHN will handle quite nicely, and one color will suffice since they're all hot (I recommend yellow since it takes colored sharpie well)... plus one green ground. Mark both ends with colored electrical tape or a Sharpie so you can distinguish them.
Wire nut them on to the matching wires inside the wall, send them through the tube, and mount the faceplate on the box that is in the actual wall. Then inside your new box, attach the THHN to switches. The ground goes to the ground screw on the handy-box and that's done. If you use stranded you must not use backstabs! Attaching to screws takes a knack; the best option is a "screw-to-clamp" type switch, where you tighten the screw to attach a back wire.
  • I considered the FMC route, actually -- I felt that the surface metal raceway would offer better protection against damage for this, and I don't think built-in units are going to detach from the wall any time soon if at all adequately fitted... – ThreePhaseEel May 28 '19 at 00:31
    I've lived in earthquake country, built-ins anchored into drywall, that would not surprise me. I actually searched the NEMA plugs for an obscure but available xx-15 /3+gnd socket to make a way for it to plug in... But could not find a plug-socket set that was sanely priced. – Harper - Reinstate Monica May 28 '19 at 01:08
    The cabinets are screwed to the studs, so I really don't think they're going anywhere. – TreyGuy May 28 '19 at 01:10
  • @Harper -- yeah, the NEMA 14 line starts at 14-20 and goes up from there (and yeah, anchoring built-ins to drywall is a fool's errand in earthquake country IMO) – ThreePhaseEel May 28 '19 at 01:17
  • Yes I was looking at NEMA 18, 20, odd stuff like 480 wye....That nobody would mistake for residential service... – Harper - Reinstate Monica May 28 '19 at 12:23
Another option would eminate the wiring altogether! Goconex (now Nevven) makes a wireless system that would give you all you space back. Two small controllers, actually small receiver/relay units, are wired into the circuits in the ganged box, the romex to the handy box pulled and discarded. The handy box can stay or not, as you wish, but if pulled a plain plate can cover the hole. Finally, two transmitter switches can be mounted in the same place as were the old switches. These appear to be standard Decora rocker switches, same mounting format, but have ZERO rear protrusion, can mount on a box or completely surface mounted. The entire switch unit fits behind a standard switchplate and is still flush with the wall. You can mount the switches anywhere within 100' (maybe you really never wanted them there?) Or add another switch? One switch can discriminately operate an infinite number of relays or one relay can be controlled by up to five switches.Batteries in the remote switches are said to last 10-15 yrs.
    I have this type of switch (although a different brand), and batteries only last around a year of bathroom type of use. They also use more expensive 12V batteries. – George Y. May 28 '19 at 19:15
    MK make a [wireless battery-less switch](https://www.mkelectric.com/en-gb/Products/WD/Echo/Pages/default.aspx) which is piezo-powered. But it needs specialist receiver equipment and is quite expensive. This answer may be describing something similar for the US market. – Andrew Leach May 28 '19 at 19:30
  • Great suggestion. Electricians don't usually think of, let alone consider, wireless solutions. (Errr, does "eminate" mean "eliminate"?) – wallyk May 29 '19 at 16:46
I'm not sure why almost everyone is wanting to make your solution be expensive. Do a Google search for 2 gang electrical extension ring. Very simple to install. Keeps everything contained in your original wall box, but provides you the ability to extend the box into the bookcase.
Side note bookcase must be secured to the structure to be legal. Even though you didn't have to use the UF cable it can still be used in this application. You just turn OFF POWER, pull switches out, label wires with masking tape,( S1U, S1L,S2U, S-- switch, 1 or 2- left or right switch your choice, U,L- upper or lower power connection screws on the switches. Remove wires from the switches. Then remove the box that you used in the bookcase, get all wiring to come back into the original wall box. Use push plugs to close any holes in the wall box that are not being utilized for the incoming original wiring. Push all wiring back into original wall box to ensure safety of existing wire from damage, make sure hole in bookcase is aligned with original wall box, Install extension ring into hole in bookcase, push bookcase into place, attach extension ring to original wall box and then resecure bookcase to the structure, pull all wire back out through the extension ring, re-install wiring to the switches, add electrical tape around exterior of each switch, covering the power connection screws,. (Safety). Attach switches to extension ring, and reinstall wall plate. Ensure both switches are in the off position, turn power back on from source. Turn each switch on individually.
Everything should work as intended, but by turning each one on individually, if there is an issue, it will be easier to deduce if a problem exists. The most important thing to remember is to never work on a live circuit unless it is absolutely necessary. Any good electrical tradesman will express the same sentiments. We know how to work on live circuitry but try our best not to if possible. No reason to be another accident statistic when it's preventable. Leviton 42777-2WB is one example of an extension ring that could be used in this application
donjuedo
    Hello, and welcome to Home Improvement. This is interesting, but is hard to read as a long Wall 'O' Text. You might want to edit it to make it clearer; please [take our tour](//diy.stackexchange.com/tour) so you'll know how better to contribute here. – Daniel Griscom May 29 '19 at 14:19
Any exposed wire need to be covered or inclosed, wood box and slid it over the wires. I am more concerned with grounding in the metal box without a ground screw in the box you run the risk of electrocution.
Use wire mold and come out of the top, go to the right, around the corner and back down. Drill a hole in the center of the faceplate (maybe get a metal faceplate if you need it) and use a 90° wiremold connector or use a 4" surface mount box (the kind that is made to use with wire mold) and come in to the top. Or do the same thing but with MC cable. You may need 12/3 or 12/4 depending on how many conductors you need. If it's just 1 switch you can use 12/2 and use the white as your switch leg but new code says you're not supposed to do that. You could always box in that corner but technically the "junction box" needs to be accessible. But if you're not getting an inspection then it's up to you. Ground those metal boxes!
