13
I'm using a basic outlet tester like the one from picture below. Let's say someone wired the ground to the neutral in some outlet, to provide a fake ground. What would the tester report? Would it be "CORRECT" or would it be something else?
In case it reports "CORRECT" (wrongly, of course), is there some easy way to test that the ground is fake? By easy I mean not having to open the outlet...
Wiring tester
fernacolo
  • 331
    put a heavy load on the power outlet ... measure the voltage between neutral and ground ... zero voltage indicates that the two are shorted at the plug – jsotola Aug 12 '19 at 00:02
    A receptacle tester is a pretty simple device, not a tricorder capable of checking all the wiring in your house. Since ground and neutral are connected (hopefully only once at the box), it can only do so much. – Jon Custer Aug 13 '19 at 13:48
The tester can't tell the difference. One way to look at is that electrically, since neutral and ground are already bonded at one location (normally the main panel), the electrons don't know the difference. But the other way to think about it is to look at what the tester is actually doing.
What do the Lights Indicate?
These testers are actually 3 simple lights connected as follows (left to right on your particular tester, others may vary):
  • Hot to Ground
    This will light up provided that Hot is indeed Hot (and not Neutral) and Ground is functional.
    Note that Ground being functional in this context does not mean "connected to a water pipe or rebar or a ground rod", though that alone might be enough. It means "ground connected to neutral in the main panel".
    That also means that if Ground is connected directly to neutral in this receptacle box, the tester does not see that as a problem.
  • Hot to Neutral
    This will light up provided that Hot is indeed Hot (and not Neutral) and Neutral is functional.
  • Neutral to Ground
    Since Neutral and Ground are bonded in the main panel, this light is normally off. Connecting them inside the receptacle box won't make any difference. Where this does light up is if something else is really messed up so that current flows between neutral and ground. The most likely scenarios are Hot swapped with either Neutral or Ground, so the tester "identifies" those conditions but those are really not guarantees as there are other possible situations.
What do the Light Combinations Mean?
There are 8 possible combinations. But "all on" would be really strange (but possible if someone wires a 120V receptacle to a 240V breaker) so that is not included. The other combination not included is Off, Off, On. That would mean current flowing only between Ground and Neutral (the exact opposite of this question), and no current flowing between Hot & Neutral or between Hot & Ground, which would be pretty hard to do (Open Hot + Hot/Neutral swapped?)
Just remember, the titles assigned are based on the most common scenarios but are not the only possible problems.
  • Off, On, Off = Open Ground - Hot to Neutral but no Hot to Ground
  • On, Off, Off = Open Neutral - Hot to Ground but no Hot to Neutral
  • Off, Off, Off = Open Hot - But really means "nothing at all" - e.g., could be "Open Ground + Open Neutral but Hot OK" - so don't assume this means there is no hot wire present - that could be a deadly mistake!
  • On, Off, On = Hot/Ground Reverse - Hot to Ground OK, but not Hot to Neutral, so the likely situation is that the Hot & Ground wires are reversed but it could be something else.
  • Off, On, On = Hot/Neutral Reverse - Hot to Neutral OK, but not Hot to Ground, so the likely situation is that the Hot & Neutral wires are reversed but it could be something else.
  • On, On, Off = Correct - Except, it really only tells you that Hot is in the right place and that all Ground & Neutral are, collectively, correct. It does not tell you, for example, if Ground & Neutral are reversed or, as originally asked, if Ground & Neutral are combined.
Could Such a Tester Be Made?
The one possibility I can think of is based on any wire (ignoring superconductors - we are talking about normal residential copper wires) having some resistance. So a "normal" neutral to ground path (i.e., round-trip to main panel) would have some resistance - a quick search showing 2.525 Ohms/1,000 feet) on 14 AWG - you could measure that resistance. If you have 50' of neutral in one direction and 50' of ground in the other direction, that would be a total of 0.2525 Ohms - small but measurable, compared to essentially 0 Ohms if ground & neutral are connected in the receptacle. But this would require some pretty careful measurements that you simply aren't going to get from a $10 receptacle tester. Plus it would need even higher accuracy to work on 20' length of 12 AWG wire. Just open the receptacle and check it out...
    You could capacatively couple neutral and ground in the tester and then send pulses down the ground line and measure the phase shift (or delay) at the neutral line. This would give you an idea of how far away you were from the point at which neutral and ground are connected together. It could probably be made to work reliably if nothing else was connected to the circuit, but it would definitely cost a lot more than $10. – David Schwartz Aug 12 '19 at 15:21
    You could also measure the voltage between the ground and neutral, near the socket, after you connect a device that draws some power like a light bulb. If the voltage keeps exactly 0, a wrongly terminated ground is likely – Ferrybig Aug 12 '19 at 17:56
  • My ground and neutral are bonded in the box (easily verified) but the outlets have .1V between neutral and ground. I think the bond has a high resistance. – Joshua Aug 12 '19 at 19:21
    @Joshua the 0.1 V you report between neutral and ground does *not* indicate that you have a high resistance bond so there's no need to be pulling the front off your panel. The neutral may be carrying current (the ground will not be). This current will cause a voltage across the length of the neutral conductor between this receptacle and the bond in the panel, e.g., 1 A of current and 0.1 Ohm of resistance would give 0.1 V difference between neutral and ground. – Jim Stewart Aug 12 '19 at 20:51
12
Yes, it will misread. Because magic-8-ball testers are built for one thing: a quick pass/fail test for brand new wiring you just installed.
Obviously, in new wiring, you don't have a bunch of the kinds of problems you have in old wiring, like people bootlegging ground off neutral. The device is simply not made to solve those problems.
So if you misuse the tool to test old wiring, the reports (what it says on the label) will often be misleading, and will send you on wild goose chases. That's why I call it a magic 8-ball tester! An actual magic-8-ball would be about as reliable. It is useful in two ways:
  • The lights themselves can give you hints (provided you know how they are connected, see manassehkatz's discussion)
  • The "GFCI test" button can be helpful when testing downline receptacles fed off a GFCI elsewhere.
With old wiring there's no substitute for opening it up and having a look.
  • Open up, take a look, use a proper voltage meter before you touch any bare wire. +1 – Mast Aug 12 '19 at 17:37
    And test your meter on a known-hot circuit (more important, perhaps, on an analog meter, but still a good idea on a digital one, IMO.) – Dennis Williamson Aug 12 '19 at 21:03
    A common use is in fact to test old wiring. If I am buying a house, then I (or the "home inspector" I hire) may use one to see if there are obvious issues with the wiring. This is not so bad, since the unsubtle issues do show up and usually do give a good general indication of what to expect. If I see issues in multiple places, I know I'm more likely to have a major re-wiring ahead. – MickeyfAgain_BeforeExitOfSO Aug 13 '19 at 11:45
  • I didn't say it wasn't common. I said it was misuse. A plain case of "if all you have is a hammer..." Because the specialty tool would be pretty esoteric. The home inspector's job isn't to troubleshoot electrical, it's to inspect everything and write up a spiff report in a nice clean binder and collect his money. It's not a good indicator because the seller *also* owns one of those, and can easily go through in advance and rig every outlet to pass. – Harper - Reinstate Monica Aug 13 '19 at 16:35
  • @Harper-ReinstateMonica Sorry to comment on an old post, but a quick question: So we shouldn't trust one of these testers on old wiring if it says everything is okay; what if the tester shows that something is _wrong_? Assume that something is in fact wrong, but not necessarily what the tester indicates? – Kevin May 13 '21 at 19:17
    @Kevin Yes, any indication other than 2-yellow indicates *something* is wrong; I'm just saying the label on the device *that tells you what the colors mean* will be unhelpful and misleading. – Harper - Reinstate Monica May 13 '21 at 19:39
  • @Harper-ReinstateMonica Thanks! Out of curiosity, will a multimeter tell you anything that a 3-light tester doesn't (besides specific numbers for voltage & resistance)? I'm not suggesting it as a substitute for examining the wiring, just curious. – Kevin May 13 '21 at 19:55
    @Kevin Yeah, it can give you hints about things like lost neutrals. – Harper - Reinstate Monica May 13 '21 at 20:04
The tester will show "correct". Opening the outlet is the only way to check it that I know of.
JACK
  • 78,739
  • 72
  • 188