26
Summary
The question pretty much says it all. It's probably a ridiculously easy one to answer. It's cool outside but I know that my house is heating up because my AC kicks on periodically. I've had this experience in multiple houses, so I presume it's not just caused by some sort of one-off issue with an AC or thermostat. It seems strange and I'd like to understand why it happens so that perhaps in the future I can make my house more energy efficient.
More Details
I'm a life-long Florida resident and have had this experience in a few houses. I've noticed that even when it is cooler outside than in (say the AC is set to 80°F (27°C) and the weather is 76-78°F (24–26°C) outside), my AC still runs periodically throughout the day. Note that the obvious answer is "Just open the windows", but for those not familiar it is usually 80%-90% humidity outside, and even 76°F (24°C) isn't pleasant at 80% humidity (it's also a recipe for mold, which has been a problem for me). Basically, there are only 1 or 2 months of the year when it is both cool and dry enough to open your windows in Florida (IMO).
In that sense having the AC run periodically is not actually crazy, mainly just to keep the humidity down. However, it still seems strange to me that if the AC should kick on (aka the house is warming up) at all if it is 2-5°F (1-3°C) cooler outside than the temperature I have the AC set to.
I realize this is likely house-dependent, but I've lived in more or less the same "kind" of house for the past decade or so: wood frame, insulation-in-attic, single pane windows, and a few trees around providing shade for the house (although certainly not enough to shade the entire roof).
I presume this is a sign of some general inefficiencies in my house's thermal-insulation-design. Why might my house be heating up even when its cool outside?
conman
  • 756
  • 37
    Your thermostat (which controls the AC) doesn't know what the *outside* temperature is, it only knows what the *inside* temperature is at the specific location where it is installed. If the temperature it measures is higher than the setpoint you've selected, then it commands the AC to run to reduce the temperature *inside*. – brhans Aug 19 '19 at 12:45
  • @brhans Well, certainly. But presumably the biggest influence on the temperature inside my house is the temperature outside my house. If it's cooler outside then presumably my house should be cooling during the day, not getting warmer, and therefore my AC should have no reason to run. – conman Aug 19 '19 at 12:51
    My personal suspicion is that direct solar flux on my roof is heating up the attic (reference: attics are hot) and therefore what is going on is that poor insulation in the attic is allowing the heat from my attic to warm up the house faster than cool air from outside leaks in though my windows/walls. – conman Aug 19 '19 at 12:53
    That may or may not be true - but either way it's irrelevant. Your thermostat does not 'know' what the outside temperature is.. All it 'knows' is that the temperature it's measuring is higher than the setpoint you've set it to, so it runs the AC. – brhans Aug 19 '19 at 12:53
    @brhans lol, yes, indeed - I am well aware of how an AC works. I'm not literally asking why my AC is turning on. I'm asking why my house is heating up even when its cool outside. – conman Aug 19 '19 at 12:55
    Seems like you'd want to tell us something about your insulation (type, quantity) and other aspects of your home if you're seeking opinions on that. What you describe is perfectly normal and expected, laws of physics being what they are. If you're looking for ways to improve the situation, please revise to add detail. – isherwood Aug 19 '19 at 12:56
    @isherwood Currently I'm just trying to figure out what is warming up my house when it's cool out. There seem to be a couple suggestions that it is the attic. That was my guess as well, and while in retrospect that seems like the only possible answer, I wasn't really sure, hence this question. I certainly don't expect you to make any guesses about my attic without further details, but "Your attic is heating up your house" (aka what Jack said) is certainly a helpful answer to my question. – conman Aug 19 '19 at 12:59
    @conman Last year I installed a whole house fan. It vents into the attic so when it does get cool out, I open windows and turn on the fan. It sucks air into the house and cools off the attic. I had to install 13 additional soffits in the eves but it was well worth it. – JACK Aug 19 '19 at 13:26
    In addition to the answers that note that the interior may legit be getting hot, consider also that the *hysteresis management* hardware/software in your control system may be misconfigured. – Eric Lippert Aug 19 '19 at 22:15
  • [It's called an ***economizer***](https://diy.stackexchange.com/questions/71980/hvac-system-that-pulls-in-cold-air-from-outside)... no one has them. It's an automated fresh air intake for exactly what you describe; pulls in outside air when it's economic to do so. – Mazura Aug 19 '19 at 23:37
  • @Kat Thanks, that's a good suggestion. There is still some mention of the AC simply because that is how I know my house is heating up, but indeed the house heating up when it's cool out is the part of the question I'm interested in. – conman Aug 20 '19 at 12:10
    @Mazura That duplicate question doesn't help me at all, unfortunately. As I mentioned in the question, I'm not interested in pulling in outside air due to high humidity. I suspect an economizer would be nearly useless in Florida. – conman Aug 20 '19 at 12:11
  • There's nothing to 'do' here; it's a physics question. VTC retracted for changing the title, but no +1 because there's no objective. – Mazura Aug 21 '19 at 01:30
    Easy: Because you are sitting in front of the computer all day, reading StackOverflow. – Peter - Reinstate Monica Aug 21 '19 at 10:18
  • You may have noticed a giant thermonuclear explosion in the sky above us... about 150 million km away... – J... Aug 21 '19 at 17:41
  • "I presume this is a sign of some general inefficiencies in my house's thermal-insulation-design. Why might my house be heating up even when its cool outside?" It could actually be a sign of the opposite, your house is well insulated, and internal heat sources, computers, lights, coffee makers, people, etc are heating up the interior. Perhaps if your house were less well insulated and leaky it would stay cooler on cool days. – Glen Yates Aug 21 '19 at 17:56
  • @conman: Does this only happen during the day for you, or have you seen your AC kick in at night? Because I've seen the latter, so I don't buy the solar gain explanation. – user541686 Dec 14 '20 at 00:15
9 Answers9
64
Meet solar gain
For the most vivid example of solar gain, sit in your car with everything off - A/C off, blower off, windows rolled up tight, doors shut tight. You can't. Your body will force you to open a door or something because it will become unbearably hot within minutes.
If it were always night, or if your house were entirely in shade, this would not be an issue. However, your house is in sun, and that means it is being actively heated by about 100 watts (300 BTU/hr) per square foot (around 1 KW/m²).
That's really a square foot directly facing the sun, so it'll be less if you're not at the equator at noon... but walls count too, so that's kind of a wash. The reflectivity of the roof and walls help. So let's say all in all, 50% gets through.
This is why a car with 48 square feet (4.5 m²) of cabin gets so hot so fast - it's intaking 2400 watts/8000 BTU/hr of heat. That's the heating power of an oven. This is why leaving a baby in a car is so serious. I'm not equating a house to a car, just pointing out that solar gain is not to be armwaved or ignored, and is definitely your #1 load by a wide margin, maybe even by an order of magnitude.
So, your 1000sf (93 m²) house, is absorbing 50,000 watts of heat, or about 150,000 BTU/hr, from solar gain.
Yes, this is a stupidly large amount of energy. Too bad we can't harness it for something, eh? :)
Insulation slows it down. But only slows it. Given enough time, it still gets through.
Thermal "mass" works both for and against you. The thermal mass inside the insulation envelope helps your house resist changes in temperature. However the thermal mass outside the insulation envelope (roof, joists etc.) has been warmed by the sun all day, has reached 120-140F (50–60°C), and holds that heat for a few hours after sunset. That means its high heat is still trying to push through the insulation even after the sun has gone down. Conversely in the morning, even with full sun, you get some relief before the roof and joists heat up.
At least it's more efficient...
Your A/C unit interchanges with air, and in your case, you are saying the ultimate heat sink is cooler than the thing it's cooling. That gives a heat pump an advantage; it is pushing heat "downhill". You can check it with a load monitor (if the cycle length doesn't make it obvious), but you probably aren't using near as much power as on a hot-air day.
It's even better, of course, to interchange heat with groundwater. But that is a more specialty unit.
    To add to the AC unit running when it's cooler outside, this is actually really the way heat sinks want to work. They want to move heat to a colder location, so they can cool the refrigerant more. When it's hot out, the refrigerant can't get as cool, so it's not removing as much heat from your house as when it's colder outside. – computercarguy Aug 19 '19 at 22:39
    This is very misleading. Sure, every square foot of your house is receiving a ton of heat from the sun — so is every *other* square foot of the daylit side of the earth. They don't heat up to oven-like temperatures because they're also radiating heat *away* at pretty close to the same rate, and the net heating power is very much smaller (or negative, in the late afternoon). In the absence of other effects that *capture* heat, the sun would heat the inside of the house to the same exact temperature as the outside. – hobbs Aug 19 '19 at 23:45
    @hobbs so according to your theory, *earth sheltering* a home shouldn't do much since roofs and earth should be equivalent. That's not true. Also many soils *do* get very hot. Examples are the desert, roadway surfaces, etc. What helps most other surfaces is deep mass: nobody cares if the road and 2 feet of mass under the road gets hot. Also, where soil is vegetation covered and watered, the dirt can do two things roofs cannot: absorb energy via photosynthesis, and use latent heat of vaporization of water. Your comparison of "roofs" to "every other square foot of earth" doesn't hold up. – Harper - Reinstate Monica Aug 20 '19 at 00:03
    Insulation does more than slow the heat - due to daily temperature cycles, that slowing also results in redirecting the heat. During the day, you might have a house temperature of 75F, roof temperature at 120F and an outdoor temperature of 95F - heat from the roof will flow indoors more easily than out. When the sun sets, your house is still at 75F, the roof now at 110F, and outdoors now at 60F - heat from the roof moves outside more easily than in. Insulation reduces the total amount of heat energy entering the building, it doesn't just slow it down. – Nuclear Hoagie Aug 20 '19 at 12:54
    I agree this is misleading...your car is very close to a greenhouse, your house is hopefully not. – user3067860 Aug 20 '19 at 13:30
    I've often wondered if having a 'double-roof' would be worth it in places like Florida. By that I mean having a second layer of sheathing separated from the home by a an inch or so with a ridge vent and soffit vents. The solar gain on the top roof should then cause air to flow between the two layers and help keep it away from the structure. – JimmyJames Aug 20 '19 at 13:32
    @user3067860 Not misleading at all. Most houses have windows and any light rays that enter the house are captured and mostly converted to heat. This is in addition to the heat radiating off the structure. Many homes are not designed with the passive heating from the sun in mind: the developer doesn't pay the AC bill and many/most home buyers don't understand the impact. – JimmyJames Aug 20 '19 at 13:42
  • @Harper I quibble with the last section. If the AC is running when it's cool outside, it must be working hard when it's hot outside. I'm also going to guess that opening the windows will cool things more quickly (for free) especially if there are windows low and high on the structure. Humidity is the downside with that. – JimmyJames Aug 20 '19 at 13:46
    @hobbs "In the absence of other effects that capture heat" And that's exactly what a home does. Take, for example, a large picture window on the south side of a home that is not shaded from the sun. On the inside, you have bright light streaming in but if you are standing outside, the inside looks dark. The reason is that almost none of the rays that enter are being reflected back. It's almost a perfect capture. The cavity of the home acts like a [black body](https://en.wikipedia.org/wiki/Black_body). In cold climates, this effect is used to heat homes in the winter using the sun. – JimmyJames Aug 20 '19 at 13:53
  • @hobbs [More on passive solar heating.](https://en.wikipedia.org/wiki/Passive_solar_building_design) – JimmyJames Aug 20 '19 at 13:58
  • As a Floridian, I don't need passive solar heating. Where's my passive solar cooling :p (yes, I know that's a contradiction of terms). I'd be tempted to build a house just so I can have it built with a more energy efficient design that self-cools on summer days... – conman Aug 20 '19 at 14:14
    @conman Designing things so you avoid solar gain in the summer is the main goal in Florida e.g. large overhangs on the roof to shade windows. The second image in [this article](https://www.wbdg.org/resources/passive-solar-heating) shows a home somewhere where palm trees grow with an example design using plants. Solar energy can be used to create a chimney effect or [stack effect](https://en.wikipedia.org/wiki/Stack_effect) which can draw cool air up through the home but with the humidity in FL, solar panels driving AC might be the way to go. – JimmyJames Aug 20 '19 at 14:30
    I think the point @hobbs tried to make is that there is *some* radiative cooling from every exterior surface, via blackbody radiation. Calculating *only* the incoming power per area without looking at the energy balance is misleading. Light that hits the outside of a house will heat up the outside, and that heat can radiate and conduct and convect away without most of it conducting to the inside. Things get hot, but not as hot as an oven. Yes it makes sense to be aware of the large amounts of energy that come in (or could come in through windows), and thus why windows are such a big deal. – Peter Cordes Aug 20 '19 at 14:37
  • @PeterCordes Nowhere in the answer is a house compared with an oven. A car is compared with an oven in a 'vivid example of solar gain'. The answer doesn't claim cars and homes are the same. – JimmyJames Aug 20 '19 at 14:41
  • Exactly, I present the car example only to illustrate the fearsome power of solar gain, that it's not to be trifled with or armwaved or dismissed, and is actually an order of magnitude higher than the other gains one normally thinks about. I live in a temperate but desertine clime with a western exposure and a whole-house power budget of 3600W, so my summers and falls are a daily, pitched battle with solar gain. [This guy gets it](https://diy.stackexchange.com/questions/171669/storing-comsumable-dry-goods-in-your-car-in-the-summer)... – Harper - Reinstate Monica Aug 20 '19 at 15:59
  • @hobbs obviously also the sun is heating inside air in the house, which, contrary to outside air, has nowhere to go, especially if windows are closed due to AC – Gnudiff Aug 21 '19 at 07:46
    I'm going to accept the wisdom of the internet here (aka most upvotes), although to be fair I'm not sure if I would say that it's not worth worrying about. It may be the norm, and the AC is obviously meant for it, but considering how much that solar gain probably contributes to the cost of my electricity every summer... – conman Aug 21 '19 at 17:50
  • @hobbs Actually I think a big part of why they don't heat up to oven-like temperatures is convection... the main think I recall from my intro meteorology class in college is that all other things being equal, the temperature on a windy day will be lower (at a ground station) as air heated near the ground mixes with upper air. – Michael Aug 22 '19 at 15:47
  • @conman good point, edited. I didn't mean it was trivial, just not as bad as pushing heat uphill into air that's hotter than your home. – Harper - Reinstate Monica Aug 22 '19 at 16:18
  • "So let's say all in all, 50% gets through." I'd be interested in seeing evidence to support that estimate. Why 50%, not 5% or 0.5%? – Nate Eldredge Sep 09 '19 at 16:58
  • **I don't think this answer is correct.** I've literally seen the AC turn on *at night* (like 2am) despite any obvious heat sources inside the home, when it's cooler outside. – user541686 Dec 14 '20 at 00:09
37
Because you have indoor heat sources
There's a lot of reasons your house will get warmer than the outside temp, but this is the single largest one.
  • The human body produces as much as 400 BTU (422 kJ) per hour at any given time, equivalent to 117 W.
  • Your refrigerator can give off close to 500 BTUs (528 kJ) per hour (147 W).
  • A TV can use about 20-30 watts, or about 70-100 BTUs per hour
  • Stoves and ovens add varying BTUs, but don't constantly run either
Add all these up and you'll find your house reaches the necessary temp to kick on, even if it is cooler outside
    I'm not sure why neither the fridge nor myself occurred to me, lol! I work from home and we homeschool, so there are literally 7 people home all day long... in retrospect it may not even be my house's fault... – conman Aug 19 '19 at 13:10
    I have a hard time with the notion that a few bodies and appliances contributes anything near the heat that solar gain does. Surely it's a factor, but a minor one. – isherwood Aug 19 '19 at 15:38
    @isherwood My thoughts exactly. Simply closing the blinds during the day can have a huge impact. A lot depends on the position/size of the windows and whether the roof has a major overhang but it's a likely source of the problem. – JimmyJames Aug 19 '19 at 20:55
  • These are all true, but likely tiny contributors in comparison to the sun. – R.. GitHub STOP HELPING ICE Aug 20 '19 at 01:05
    BTUs per what ? – user253751 Aug 20 '19 at 02:29
    Don't forget the washer and dryer, anyone who takes a hot shower, any *other* electronics you have sitting around, etc. It does really add up. – user3067860 Aug 20 '19 at 13:28
    I looked up this strange BTU unit and it doesn't make sense here. – Nobody Aug 20 '19 at 13:53
  • @Nobody I don't get what you're saying. Can you clarify? – Machavity Aug 20 '19 at 13:57
    isn't BTU a measure of energy, not power? – Vaelus Aug 20 '19 at 14:11
  • @Vaelus Yes, but I'm trying to make an apples-to-apples comparison here as well. [Air conditioners are rated in BTUs.](https://www.consumerreports.org/window-air-conditioners/how-to-size-a-window-air-conditioner/) I'm trying to offer an approximate amount of BTUs in AC you need to offset that. – Machavity Aug 20 '19 at 14:13
    That can't be done without considering how long it took to produce that much energy. I suspect air conditioners are abusing notation, and instead mean BTU per some unspecified standard unit of time. Since humans and appliances are continuously making heat, you'd have to compare units of power, like watts or BTU per h. – Vaelus Aug 20 '19 at 14:18
    @Vaelus, Per https://en.wikipedia.org/wiki/British_thermal_unit#As_a_unit_of_power: When used as a unit of power for heating and cooling systems, Btu per hour (Btu/h) is the correct unit, though this is often abbreviated to just "Btu". – BowlOfRed Aug 20 '19 at 15:55
    @Machavity The proper unit for what you are describing is the Watt with abbreviation W, which is a unit of power. BTU is some historical unit for energy, not power. As was already described in some other comments since my original one. – Nobody Aug 20 '19 at 18:46
  • @isherwood Some anecdotal experience here, but 2 persons in a single room with 2 computers (4 monitors), and all the fixins (mouse, keyboard, etc) can heat up our room to about 83-84 degrees, despite a window open to pleasant 72 weather. – Anoplexian Aug 20 '19 at 22:16
    Agreed. In my 'home office' I have 4 monitors, 2 computers, 2 external hard drives, powered speakers, a router, myself, and plus or minus 2 cats. Even when running just one window unit *in that room*, it's hotter than the rest of my house by no less than a few degrees. I think what the OP is missing is **the inefficiency of electrical appliances to do more work than they produce heat**. - Anyway, tl;dr: the plot of *The Matrix*, +1 – Mazura Aug 21 '19 at 01:17
  • @isherwood Passive houses rely entirely on heating of bodies and appliances; that's how they stay warm without active heating throughout a central European winter night. – gerrit Aug 21 '19 at 08:09
    Sure, but they're very different from this scenario, and probably include significantly more insulation, heat reflection technology, purpose-built windows, outdoor exposure engineering, etc. In a typical "this looks nice so let's build it" home, no way. – isherwood Aug 21 '19 at 12:48
  • @isherwood It's not insignificant at all. I have a "cold room" in my house where I keep the heat off because I don't really use it. The fridge is in there, and in winter it barely needs to run because the temperature in that room gets as low as 7-8°C at night. Well, in summer that room becomes one of the hottest rooms in the house, even with the window open, despite facing north. – Demonblack Aug 26 '19 at 10:34
  • I don't think I used that word, and your room may be getting hot for other reasons, such as heat soak through the attic. We agree that _some_ heat comes from those sources, but it isn't much. – isherwood Aug 27 '19 at 13:15
  • I don't think 117W is anywhere near enough to heat up a home like this? Otherwise you could take a space heater, put it on low, leave it running in your room for a day, and have the whole house heat up a few degrees. Does this sound plausible? – user541686 Dec 14 '20 at 00:13
12
In addition to the other answers that address your question for the most part, there is one more possibility I can think of. It is possible that your AC is not only trying to get the inside temperature to the target,but also the humidity.
Some high-end thermostats will have a humidistat built in, while it is a separate unit in other cases. Regardless, some AC systems are setup to also run when the humidity inside is too high. Some systems have special modes for this, that somehow don't cool as much, but pull more humidity out of the air they handle (probably at a loss in efficiency, but I don't know for sure how this works), while others just run like normal, causing it to get colder than your target temp inside. In US brands, I think one that I've seen the built in de-humidifcation feature a lot is Trane, but others may have it also.
PhilippNagel
  • 4,947
  • 39
  • That's helpful to know. I own my current house (which needs a new AC soon), but my previous houses were rentals and definitely did *not* have high-end thermostats. That may be of interest to me in the future though! – conman Aug 19 '19 at 14:02
  • Do you know keywords to search for to buy such a thermostat? I've considered rigging one up just to avoid having to constantly adjust the setting to ensure that the AC runs sufficiently often to eliminate humidity without wasting lots of energy midday on hot days. – R.. GitHub STOP HELPING ICE Aug 20 '19 at 01:44
  • There are stand-alone units you could probably wire in parallel with your regular thermostat (search dehumidistat). I've seen thermostats with this function that are usually made to work with a specific air handler/furnace/AC unit, that has the aforementioned functionality. This would supposedly avoid overcooling, while still maintaining the desired humidity. But there maybe also regular thermostats that just run the AC with lower fan speed or something, maybe search for thermostat with dehumidification control ( I found a Honeywell one with that term, for example). – PhilippNagel Aug 20 '19 at 02:23
  • @R.. Indeed, during cool whether I adjust my thermostat up and down during the day, not because the temperature is too hot or too cold, but simply because the humidity is too high and I need the AC to run for that reason alone. I basically have to overcool my home, just a little. – conman Aug 20 '19 at 12:50
Because an Air Conditioner doesn't give any airflow between inside and outside. An AC is essentially a refrigerator. Inside is the conditioned space, and outside is the heat dump (i.e. the back of the fridge where it's hot) The heat is transferred from inside to outside via the liquid coolant - it evaporates inside, collecting heat due to the latent heat of vapourization, and compresses outside, giving off this heat. This is a closed system, contained almost entirely in sealed copper pipe.
There is no air transfer between outside and inside. So, if your inside temperature is higher than the thermostat set point, the AC will run -- regardless of the outside temperature. If you want to take advantage of the lower outside temperatures, then you need to bring outside air in. i.e. Open a window, which you have good reason NOT to do given the humidity.
As a simple thought experiment, we could remove all insulation from the house, and then your internal temperature would be a better match to the outside, as the purpose of insulation is to significantly reduce heat transfer through the walls and roof. However, this plan would be advantageous for only a few days of the year.
In addition to Machavity's answer, I'd also like to comment on solar warming. The sun hits your roof, and adds heat. This heat transfer is mitigated by the roof insulation, but not eliminated. Another source is the sun hitting the windows. Even if you have curtains or internal blinds, a lot of heat enters the house this way. The best way to mitigate this is with external blinds or shutters. These stop the sun from hitting the glass and causing a greenhouse effect.
Chris Cudmore
  • 14,089
  • 59
There's nothing wrong with your thermal insulation design. Insulation is designed to isolate your inside temperature from the outside temperature. So your a.c. is set to 80°F (27°C), then at 3am the temp outside slowly drops to 76°F (24°C)... it will take hours for your inside temp to see the difference because you attic is still going to be hot. By the time it could see the difference, the outside weather is heating up. The same happens in the winter. Your inside temp is at 78°F (26°C), we have a cold snap (yes, I live in Fl too) and the temp drops down to 40°F (4°C), your inside pretty much stays the same. Hope this helps.
Last year I installed a whole house fan similar to the one below. It vents into the attic so when it does get cool out, I open windows and turn on the fan. It sucks air into the house and cools off the attic. I had to install 13 additional soffits in the eves but it was well worth it.
gerrit
  • 243
JACK
  • 78,739
  • 72
  • 188
  • While I mostly agree, we can't say that there's nothing wrong with the insulation because we know nothing about it. There may be gains to be had by modernizing, especially in the attic. – isherwood Aug 19 '19 at 12:54
  • This largely conforms to my suspicions. In other words, this is likely a sign that my house heats up a lot due to the heat in my attic. i.e. better *something* in the attic may help with my overall AC usage. – conman Aug 19 '19 at 12:54
There are a lot of answers that address why it can be hotter inside than outside. But to your point, "it still seems strange to me that if the AC should kick on at all if it is 2-5 degrees cooler outside than the temperature I have the AC set to." The thermostat is inside and has no idea what the outside temperature is. It turns the AC on when the inside temperature is above its set point.
The outside temperature has very little instantaneous effect on the inside temperature. As Jack describes, the house insulation creates a long delay between changes in outside temperature affecting the inside temperature. So in terms of the thermostat turning the AC on and off, the outside temperature at the time is basically irrelevant.
fixer1234
  • 6,068
  • The question is "Why might my house be heating up even when its cool outside?". Do you answer that? – Astor Florida Aug 21 '19 at 12:19
  • @axsvl77, I state in the answer that that was not the aspect I was answering. The question is now displaying the 7th revision. I answered before revision 5, when the relevant wording was changed. At that time, the wording suggested an additional question that was not being addressed. I quoted the exact wording I was responding to. It appears that the OP didn't realize that the original wording was ambiguous and could be understood in different ways, and added clarification after seeing this answer. – fixer1234 Aug 21 '19 at 15:26
Check your thermostat is in 'cold only' mode in summer and 'heat only' mode in winter (not in AUTO mode). If in AUTO it could be starting the furnace if temperature goes under the setpoint then kicking in the AC when it goes over
DDS
  • 2,377
Insulation "mass" heats up during the day heating the attic to very high temperatures, such as 110 or 120. Then in the evening when it's cooled down outside the insulation mass is still very warm and is radiating heat, some of which goes through the attic vents but also through the ceilings into the living spaces below. Increasing the attic ventilation by having a ridge vent and wide open soffit vents, not blocked by insulation and using the correct baffles to give the cool outside air free passage from the soffits to the ridge vent, should expedite the cooling of the insulation and lessen the heat transfer to the living space. Also, it's important to block the gable vents because they shortcut the ridge vent-soffit air flow greatly reducing it. It's really that simple.
steve
I totally resonate with Steve's answer! In hot summer and cold winter climates one needs to provide attic ventilation that can be opened or turned on in summer and closed or turned off in winter. Like up where I live in Alberta Canada.
  • Hi - this is more of a comment than an answer. Once you have enough site reputation, you can freely comment on other answers. – KMJ Oct 31 '22 at 03:35
  • This does not provide an answer to the question. Once you have sufficient [reputation](https://diy.stackexchange.com/help/whats-reputation) you will be able to [comment on any post](https://diy.stackexchange.com/help/privileges/comment); instead, [provide answers that don't require clarification from the asker](https://meta.stackexchange.com/questions/214173/why-do-i-need-50-reputation-to-comment-what-can-i-do-instead). - [From Review](/review/late-answers/152313) – FreeMan Oct 31 '22 at 11:28