3

This is a follow up to a question I asked recently about a subpanel that was not wired properly. I'm working on an extremely bizarre situation with the electrical system of an old house that predates electricity and originally had knob and tube. There are lots of issues with it, but this one is about the service.

This house has a 200 amp service that comes in via an overhead drop line. This will be a bit difficult to expain, and I apologize, but I do not have any more photos at the moment than are posted here, but I am trying my best. The electric meter is then connected to two adjacent meter boxes to the left with what I'm pretty sure are metal bars, not fuses, across the terminals. All three of these boxes each subsequently feed a 125 amp panel located directly below (I'll call these the main panels to avoid confusion) and each of these panels also further feed a subpanel (including the one I asked about in my previous question). There is no main shut off for the entire system or the subpanels fed by the main panels located directly below the meter boxes. Instead, the shutoff breakers in the main panels are located on the branch circuit bus, and the service wires to the subpanels are wired to the main bus, where the service wires feeding the main panels should come in. So, to put it in Layman's terms, there is no shutoff for the entire system or the subpanels; just the three main panels.

I have never heard of a situation like this before and have no idea why it would have been wired this way. Is this a unique situation here? I was thinking of just taking out the three panels and two extra meter boxes and replacing with a 200 amp panel with shutoff breakers for each subpanel, as well as moving all the additional circuits in the three main panels here. I guess I could just get a 200 amp disconnect box for the entire system, though, and rewire the main panels to include a shutoff for the subpanels. But I'm not sure that would be consistent with code. Here are the three main panels, as they are located from right to left. In each of these panels, the two hots connected to the main terminals actually service a subpanel, while the service wires for each of these panels are connected to the 125 amp breakers on the top. The meter boxes are located directly above the panels. Note that I am aware that there are lots of other problems with these panels that I didn't mention, and plan to fix them too.

EDIT: Here is a photo of one of the labels. enter image description here

EDIT: Here is a sketch of the layout of the system. Note that I have omitted the neutrals and grounds for simplicity's sake. The subpanels are also not located anywhere near the meter boxes and mains; they are included for explanation purposes. I was also unable to provide a photo of the entire setup due to the fact that I am away from this location at the present time. enter image description here

Sagierian
  • 191
  • 1
  • 6
  • 2
    Is it possible that this property was either *subdivided* or *subdividable* into apartments? Because this setup would make perfect sense there was a plan to break the space into apartments (or if this had been done and later reverted). I suspect the busbar area you speak of may be swappable for some kit that would let them put individual meters, one per panel. It appears the main breakers are back-fed, which is normal enough. – Harper - Reinstate Monica Mar 17 '20 at 07:33
  • 1
    That is possible. There may have been a plan for that at one time, but I'm pretty sure that's never been done. It's in a large house (about 7,500 square feet). However, there doesn't need to be three separate meters now. Also, mains are back fed, but the issue is that there isn't one single main or a shut off for the subpanels. Pretty sure there needs to be a main since there's only one meter. – Sagierian Mar 17 '20 at 07:39
  • 1
    Yeah, 7500sf screams "subdivide me". If you shut off those three 125A breakers, everything should be dead. Is that not the case? It's not weird to have 2-3 main breakers on a building. Last time I had to shut one down for the lineman, there were two, one for the main house and one for the in-law. – Harper - Reinstate Monica Mar 17 '20 at 07:49
  • 1
    Yes, those three mains shut off the entire house. Is not having a single main breaker for one meter not a code violation, though? Because that's the situation here. – Sagierian Mar 17 '20 at 10:59
  • 1
    Are the three main panels next to each other? Also, are you saying that the second and third meter boxes are fed from the first meter box? – ThreePhaseEel Mar 17 '20 at 11:47
  • 1
    @ThreePhaseEel Yes and yes. The three meter boxes are right next to each other and the three main panels are right below the meter boxes that they are connected to. – Sagierian Mar 17 '20 at 13:25
  • 4
    According to NEC 230 you can have up to 6 disconnects per service as long as they are located together (not sure if that means the same panel or just co-located). So there isn't a code requirement that the power can be cut off to the entire house with just one disconnect. – George Anderson Mar 17 '20 at 14:27
  • 2
    They use to allow the rule of six inside a single service panel. The reason was large breakers (100A+) were hard to make and prohibitively expensive, and six smaller breakers (20-60A) provided most of the protection. Given your vintage, raw cost of a 200A master may have been a factor. – Harper - Reinstate Monica Mar 17 '20 at 17:09
  • 1
    Not to mention, if subdivided, you want the ability to shut off each unit independently. You don't want to lose your power when your neighbor is doing something that requires their power be turned off. It's split up among living spaces not the building as a whole. – Ack Mar 17 '20 at 18:32
  • Harper - Reinstate Monica; you keep saying "used to", has the 6 hand rule changed recently? (By way of clarification, it's called the "6 hand rule" because the idea is that a fire fighter need not make more than 6 hand movements to kill all power to a building.) – JRaef Mar 17 '20 at 22:58
  • @JRaef -- it's going away with the 2020 NEC – ThreePhaseEel Mar 17 '20 at 23:32
  • @Sagierian can you call your utility up on their customer service number during business hours and ask them to cut power to your house, then once they kill the power, check for voltage at all three main breakers? We need to make sure that there isn't flat tapped power here, as while the Code doesn't care, your utility *most definitely* does... – ThreePhaseEel Mar 18 '20 at 00:08
  • Well, we just finally adopted the 2017 code, so I'm a long way from needing to know anything about 2020... – JRaef Mar 19 '20 at 00:22
  • @ThreePhaseEel Done. Those are indeed the main breakers. – Sagierian Mar 19 '20 at 03:36
  • @Sagierian -- I take it power went away at all three main breakers when the utility cut the power? – ThreePhaseEel Mar 19 '20 at 03:40
  • @ThreePhaseEel That's right. – Sagierian Mar 19 '20 at 10:39
  • @JRaef -- actually, a clarification: split-bus six-hand-rule panels were banished from new production a while ago. the rest of the six-hand-rule is what's going away with the 2020 NEC – ThreePhaseEel Mar 20 '20 at 01:24
  • @Sagierian -- who's your utility? – ThreePhaseEel Mar 22 '20 at 04:43
  • @Sagierian -- also, where do your Grounding Electrode Conductors connect into this mess at? – ThreePhaseEel Mar 22 '20 at 04:51
  • @Sagierian -- one more thing: can you post a close-up (with the main breaker off) of one of the labels on the inside right-hand side of the main panels? – ThreePhaseEel Mar 22 '20 at 14:15
  • @ThreePhaseEel - the utility is Entergy, and the neutrals and grounds are incorrectly connected in the subpanels. Most of the circuits in this house don't have grounds, though. The ground rod connects to the meter box, I think. I'll get a photo of the label soon. – Sagierian Mar 23 '20 at 19:46
  • @Sagierian which state are you in BTW? seems like Entergy has different rules depending on where you're at – ThreePhaseEel Mar 23 '20 at 23:02
  • @ThreePhaseEel I don't want to publicly disclose the exact location, but I will say that it is in the south. What are the rules that you are referring to, BTW? – Sagierian Mar 24 '20 at 04:04
  • @Sagierian -- utilities are free to make their own *service rules* governing (within the limits of convention) what voltages they supply, what current ratings of service they provide, how they set their metering up to work, and so on -- they're critically important as metering hardware often has to follow utility-specific requirements. Just what state you're in is fine, by the way -- no need to disclose any more than that – ThreePhaseEel Mar 24 '20 at 04:05
  • 1
    @Sagierian also, can you get us some photos of the overall setup of the metering equipment please, or a sketch of the physical layout of the metering equipment and main panels for that matter? – ThreePhaseEel Mar 24 '20 at 04:10
  • @ThreePhaseEel Thanks. I don't know what their rules are, but I would assume it's not any different than in most places. Pretty sure they've installed auto meters in the last year or so; I remember they were still manually reading the meter less than two years ago. – Sagierian Mar 24 '20 at 04:10
  • @Sagierian -- Entergy's rules, as far as I can tell, are rather conventional, yes (although there is no _single_ convention for this sort of thing -- in particular, ring-type vs. ringless meter mounting is a common point of contention for North American utilities, and there can be other issues as well) – ThreePhaseEel Mar 24 '20 at 04:12
  • @ThreePhaseEel - I have posted a sketch of the system above. Note that I am unable to provide photos at the moment as I am away from this location (it is actually located very far from where I live) and probably won't be back for a month or so. If you have any questions about it please let me know. – Sagierian Mar 24 '20 at 04:19
  • @Sagierian not to be picky, but if you say "I'm in Florida, or "I'm in Mississippi", you're not giving away a _ton_ of info. There are a lot of people living in each of those states. That much "detail" might help someone figure out what rules apply to you without them being able to locate your house... Just a thought. ;) – FreeMan Mar 27 '20 at 15:08
  • @Sagierian What did you end up doing here? I wondered if some of the down-stream issues mentioned would self-resolve once this part got fixed. – Criggie Dec 07 '21 at 02:28

1 Answers1

7

This was a triplex at one point in time

What you are seeing here is an electrical system that was originally built-out for a separately metered triplex (or a duplex with commons/"house" loads) that has then been converted, along with the building, to single-family residential duty. Originally, there were separate meters in all three meter sockets, and each meter needed its own set of panels in order to keep tenants' loads from getting mixed up, which'd violate NEC 210.25:

210.25 Branch Circuits in Buildings with More Than One Occupancy.

(A) Dwelling Unit Branch Circuits. Branch circuits in each dwelling unit shall supply only loads within that dwelling unit or loads associated only with that dwelling unit.

(B) Common Area Branch Circuits. Branch circuits installed for the purpose of lighting, central alarm, signal, communications, or other purposes for public or common areas of a two- family dwelling, a multifamily dwelling, or a multi-occupancy building shall not be supplied from equipment that supplies an individual dwelling unit or tenant space.

As a result of this, you now have a single-family house with three sets of panels in it, all with their own main breakers. This is fine, at least as of the 2017 code (albeit not in the 2020 NEC), due to what is called the "rule of six" or "six throw rule" given in NEC 230.71(A), paragraph 1:

230.71 Maximum Number of Disconnects.

(A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard or in switchgear. There shall be not more than six sets of disconnects per service grouped in any one location.

Someone was lazy, and probably created a Code vio in the process of being lazy

However, when your house was converted to a single-family dwelling, whoever did the retrofit took the lazy way out. Instead of ripping out the metering hardware and replacing it with a single meter socket, they left the existing hardware intact and rewired/jumpered it for use with a single meter. This creates an issue, though, as you're most likely overloading the remaining meter socket by pulling the full rating of your utility service through it. This is because while you have a 200A service, the individual meter bases are likely only rated for 125A.

Fixing this issue will require converting this mess to use a single-position, 200A meter main. The good news is your utility does not seem to be picky, as their service requirements permit either ring-type or ringless meter mounting for residential services, 200A and below. (They require lever bypasses for larger or commercial services, which forces those to use ringless meter sockets, but that's not a concern for your situation.)

However, there are three pieces of bad news here. The first issue is that a single meter must be between 5' and 6' from grade level, so that it can be read & serviced without the use of a ladder. Worse yet, the service mast is on the right-hand side of this all, which is quite constraining as many combination overhead/underground meter-mains have their utility wireway on the left, meaning customer wires can't be routed out that side of the box. Finally, any changes to this arrangement will mean cleaning the whole thing up, since your utility forbids both double-lugging of meter sockets and the use of metering cabinets as junction boxes.

Given the physical constraints involved, our options for converting this mess to a single main breaker configuration are severely limited by available hardware, and to a lesser extent by space issues. However, there are still a couple of paths available to us if we do not wish to rip out all the hardware here and replace it, as the existing QO panels still appear to be mostly usable once the grounding and bonding is corrected.

Tap-dancing our way around these constraints

While replacing the existing "200A" meter-socket with a meter-main that has a 200A socket/main breaker and three 125A feeder-breakers in it seems like the most obvious way to fix this issue, the difficulty with that is that there isn't enough space above the right-hand panel to fit a full-sized meter-loadcenter combination without putting the meter well above the 6' maximum your utility permits for single meters.

This doesn't mean that we can't swap a 200A meter-main in for that socket while leaving the existing panels largely untouched, though. What we can do is take advantage of the NEC's feeder tap rules to use a 200A meter-main breaker combination to feed the 3 125A panels without having to mount 125A breakers in the meter-main. This allows us to use a smaller meter-main, and also gives us more flexibility as to what hardware layouts are available to us.

In particular, Square-D makes a suitable meter-main in the CQRA200 (one can also use a CM200S or RC200S with a QOM2200VH field-fitted, although the CQRA200 is a cheaper/easier-to-find solution). This part is a 200A, ring-style, single-breaker meter-main with enough neutral terminations for our 3 neutrals as well as the grounding electrode conductor to the meter base, and more importantly, it puts the breaker on the left and the meter on the right, unlike most other meter-mains and meter-loadcenters which have the meter on top or on the left. (There are some underground-only units with the meter on the bottom, but we can ignore these here since you have overhead service.) This replaces the right-most meter-base, where the existing 200A meter is located.

Now that we have overcurrent protection and metering handled, it's time to invoke the feeder tap rules in NEC 240.21(B), which is what allows us to connect 3 125A feeder wires to a 200A breaker without providing overcurrent protection at the point of origin. In order to do this, though, we have a few constraints we have to follow:

  • The tap conductors must be protected from physical damage, which we can accomplish by running them in metal conduit
  • They must not be too small (no less than one-third the size of the upstream breaker, to be safe in all cases where tap rules can be applied), which is satisfied here as we have 125A taps from a 200A main
  • And they must terminate at an overcurrent protective device, such as the existing main breakers in your panels

With those rules in mind, we can specify the wires as 1/0 aluminum XHHW-2 single conductors in 1.25" rigid conduit, replacing the hubs atop the existing panels with Square-D B125s (unless they're that size already, of course). A T body takes the place of the center meter socket then, with the left-hand meter socket being replaced by a LR. The wires to the right-hand panel exit out the bottom of the meter-main to the hub atop that panel, while the wires to the center and left panels exit out the left side of the meter-main to said T body, where they go their separate ways.

Inside the customer area of the meter-main, we then make our splices. The neutral wires are handled in a normal fashion, landing on neutral/ground lugs in the meter-main. The hot wires, though, will require a different strategy; one could use a pair of insulated setscrew-type mechanical lug connectors to splice the feeder tap wires together, but that'd take up quite a bit of valuable box real estate. Instead, we use what's called a power distribution block, mounted into the meter-main cabinet, to make these connections; this is permitted by NEC 312.8(A) in conjunction with the rules in NEC 314.28(E). In particular, a Mersen MPDB67142 with a pair of MPDBC6667 covers snapped onto it can be used here, mounted in the top right corner with the "line" (large holes) side pointed upwards. The hot conductors from the panels are connected up into the "load" (small holes) side, one wire per hole with each leg having its own pole on the block, with a 2/0 copper THHN jumper running from each PDB pole to its corresponding hot lug on the CQRA200's main breaker.

Consolidating with a trade-in

If the tap-conductor route is not acceptable to you, the alternative would be to replace the far right-hand panel with a 200A, overhead-feed, surface-mount meter-loadcenter and use some 1.25" rigid nipples to carry the triplets of 1/0 Al feeder wires off to the other two panels through the side knockouts, replacing the hubs in those panels with Square-D blank-out plates (order a pair of BCAPs).

However, most overhead-feed meter-loadcenters cannot be used, due to the fact they use a utility wireway or tunnel run up the left-hand side of the customer space to permit underground feed as well; as a result of this, we are limited to models that support only overhead feeds, not underground service, and this is quite a stringent constraint indeed, limiting us to a handful of models. In fact, the only model in Square-D's entire lineup that supports this is the SO2040M200S, and we can't use it here as it cannot accept 125A breakers. (It's Homeline, not QO, as well, but that doesn't matter since we can't use it anyway.)

The remaining options, then, are the Siemens MC2040B1200S(Z) and the Eaton MBE2040B200TS. They are both ringstyle meter-loadcenters without bypass features, with 20-space, 200A interiors, and having no documented stab limits I can find. With either of these, you'll want to use appropriate 125A breakers to protect the feeders to the other three panels (two outside, one inside), as well as a 2-pole 20A breaker to replace the existing branch breaker in the far-right panel, and an extra neutral lug kit so that you can land all the feeder neutrals on the meter-loadcenter's neutral bar. The good news is that the new feeder wires can land where the existing service wires landed, or you can have them switch places with the existing outgoing feeders if you want the downstream subpanels inside to have their own disconnects.

Things to remember in any case

With either approach, you may have to do some jiggering of alignment of parts in order to get things to fit together; the worst-case is having to bend the service mast itself in order to get it to line up with the meter-main's hub fitting, although that may not be needed, depending on how the existing meter socket's hub is positioned.

You'll also need to ensure that all the various lug- or set-screw type connections are torqued to specification with an inch-pound torque wrench or torque screwdriver; this is required by NEC 110.14(D) these days, and is a good idea even if your AHJ has not adopted the 2017 NEC yet, lest your electrical system give you the loose lugnut!

Finally, the existing grounding electrode conductor will need to be routed into the new meter-main. An Arlington GC50 or equivalent grounding conductor connector is helpful for getting it into the meter-main box, and you'll also need to fit an Intersystem Bonding Termination device to the grounding electrode conductor at this point so that the cable TV installer, etc have places to land their ground wires.

ThreePhaseEel
  • 81,744
  • 29
  • 133
  • 227
  • Thanks. However, this was never a triplex, the owner has confirmed that to me. I personally like the idea of a meter main, and would honestly like to get rid of all three of the main panels completely, placing a cutoff for all three subpanels here and the other remaining breakers in the main panels (some of them aren't supposed to be there anyway). – Sagierian Mar 29 '20 at 04:11
  • @Sagierian -- the multiple meters make it very strange indeed, then. Can you get photos and measurements of the main-service hardware (meter bases and panels) next time you're out that way, please? – ThreePhaseEel Mar 29 '20 at 06:39
  • I can. But it will probably be at least a month. This is a long term process, and there are plenty of other issues with this electrical system I am trying to fix. – Sagierian Apr 01 '20 at 02:41
  • 1
    @Sagierian -- no worries, just get back to me here when you have the info :) and yes, it seems like the prior installers left you with a real piece of work to untangle! – ThreePhaseEel Apr 01 '20 at 02:52