An electrician installed a Tesla wall charger with a 60A breaker. I've added a NEMA 14-50 receptacle to the circuit behind a toggle switch (either the wall charger is powered or the plug, not both). The question is: do I need a 50A breaker between the switch and the 14-50?
This thread seems to emphatically say "YES: You must use a 50A breaker", the logic being that
The outlet is rated for 50a. If something goes wrong in the WC and pulls > 50a the outlet is not safe. The breaker wouldn’t trip until 60a [with the implication that the plug could melt before the breaker tripped].
Essentially, this falls into a philosophy of "the breaker protects the wires and the receptacle."
However, as has been pointed out many times on DIY (e.g., here), it's standard practice to install multiple NEMA 5-15 outlets on a 20A breaker, with roughly the reasoning that "devcies with a 5-15 plug are designed not to pull more than 15A; anything else is a short which will quickly exceed 20A and will therefore trip the breaker". This philosophy is that the breaker protects the wires only, and the end device itself protects the receptacle [the device is designed to pull <15A, so a single device cannot be in the 15-20A gray area that could potentially melt the outlet without tripping the breaker].
Which philosophy is correct? Is there something more subtle going on here where 5-15s are a special case, or is it fine (according to NEC) to use a 14-50 on a 60A circuit?
(Throughout, I'm assuming wires are of an appropriate size: this question is about the receptacles.)
crockeea
  • 253
    What kind of **toggle switch** are you using? A 2-pole 50A switch is usually not a simple thing. – manassehkatz-Moving 2 Codidact Jul 13 '20 at 16:10
  • well written for a first post here! – FreeMan Jul 13 '20 at 16:11
  • @manassehkatz-Moving2Codidact https://www.amazon.com/Baomain-Universal-Changeover-SZW26-63-D303-3/dp/B07H5GZ53G/ref=sr_1_2?dchild=1&keywords=Baomain+Universal+Rotary+Changeover+Switch+SZW26-63%2FD303.3+with+Master+Switch+Exterior+Box+LW28-63%2F4+660V+63A+3+Position+3+Phase&qid=1594657048&sr=8-2 I was surprised to see how few options there were: *why* is this such a hard thing? – crockeea Jul 13 '20 at 16:13
    Lack of mass market need for it. ...and shopping at Amazon, not an electrical supply house. Without looking at the link I'm guessing Chinese product - North American (or European in Europe) product would be easy to find via industrial supply or electrical supply, but not at your local hardware store unless it's unusual - though having one at all is becoming unusual... – Ecnerwal Jul 13 '20 at 16:20
  • The key in your question is " install **multiple** NEMA 5-15 outlets on a 20A breaker" - you're installing only one. This would also not be legal with only 1 15A recep on a 20A breaker. – PhilippNagel Jul 13 '20 at 16:27
  • For something like this (a) you **definitely** want to see a UL or comparable listing - 120V 15A is bad enough, at 240V 50A you are playing with some seriously dangerous (electrocution) power; (b) while if UL (or comparable) listed with a plastic box would be OK, metal would be inherently safer because a lose wire would be more likely to hard short and pop the breaker instead of flopping around making sparks, plus metal would contain sparks if it did. – manassehkatz-Moving 2 Codidact Jul 13 '20 at 16:37
  • @PhilippNagel Yes, I saw that. But it is still confusing why that would be the case. There seems to be an implicit assumption that tripping the 20A breaker must be caused by the sum of currents over multiple receptacles, but it's not clear why this assumption matters. Anything that can go wrong with a single 5-15 on a 20A could also go wrong with multiple 5-15 on a 20A. – crockeea Jul 13 '20 at 16:54
  • @crockeea, you have to keep in mind, the number one rule in the electrical code is that you MUST follow the manufacturer's instructions when installing anything, and so in effect those instructions (which are regulated as part of the device's UL listing process) become part of the code. So it can often be confusing to figure out the "why" of code until you also find and read the instructions of the particular device that that code section had in mind when written. – Nate S. Jul 13 '20 at 18:05
    Because Amazon is a lousy place to buy electrical gear, for a litany of reasons. 1) being absolutely flooded with cheap Chinese junk, which they pay extra to SEO-boost in search results, crowding out any listings for proper electrical gear. And 2) Proper gear sellers dislike mail-order because most gear is low-value but rather heavy. Mail-order is not a good business model. A *proper* DPDT center off 60A switch costs a fortune. – Harper - Reinstate Monica Jul 13 '20 at 18:23
No philosophy: Code is data-driven
Code is the result of analysis of systematically collected data about actual electrical accidents as they happened in the field. It’s the nature of science that you must take the field data as it comes, and not try to force it to conform to some notion of what it should be.
In the case of 15/20A, the data has shown that there’s no problem there. Keep in mind, UL was a partner in developing that use-case in the first place, by requiring as a condition of UL listing that everything from receptacles to appliances all play nice on a 20A breaker, unless they are on a dedicated circuit. In that case UL needs the breaker to conform to the device ampacity.
In particular, UL requires that every 15A receptacle be rated for 20A internally. And obviously 15A appliances must show they fail safe on a 20A breaker.
Conversely, data has shown that when “the big stuff” (40-60A) is mis-fused, trouble follows. The closest thing I can see to a “philosophy” is “little things have little trouble; big things have big trouble.”
Another aspect often overlooked is how NEC 110.2 (must use approved devices, i.e. UL) and 110.3(B) (must install the device according to its instructions) intersect with UL’s listing standards. UL approves the instructions as part of the product’s listing, hence 110.3(B), and those instructions are the scope of the design review and testing. When you misuse a device off-label, you’re in uncharted territory. No one can vouch for the safety of that device.
By the way, the cheap Chinese switch you linked violates NEC 110.2 right out of the box, since it does not meet the basic standard of “Approved” — it lacks a UL listing, or any competent NRTL competitor like ETL or CSA. It is illegal for stores to sell such a thing at retail; Amazon exploits loopholes in our consumer protection laws to sell it. Send it back as defective; the lack of a UL mark, a thing required on anything sold in the US, makes it defective.
Amazon denies responsibility because they say they’re only a “platform” connecting independent sellers to buyers, and the sellers also use Amazon’s billing, warehousing and shipping system. This is hollow, as far as I’m concerned.
Our best advice is to never buy AC mains equipment on Amazon. It’s either unlisted junk, or wildly overpriced because of the realities of how Prime shipping is paid for, and the fact that most electrical gear is both low value and quite heavy. Just work with your local electrical supply or home store, many do curbside pickup.
It isn’t constructive to “overthink” Code like this. What possible endgame is there to that, except deciding to ignore Code because the reasons are stupid? That’s a mistake because its premise is wrong: the premise is that the Codebook is full of rules both smart and stupid, and that it’s worth figuring out which is which, and that a novice is capable of this distinction. Every aspect of that premise is wrong.
I can tell you that everytime I’ve looked deeply into the reasons for a particular rule, I’ve seen several of them, and they interlock with other aspects of Code to provide multi-layered protection. A Code deviation will have unexpected side-effects.
The right way is easy and cheap
The easiest/cheapest way to implement that is actually a subpanel - $20 panel, two $9 breakers (50A and 60A) and you’re Code legal and done.
You’re not actually required at that point to interlock both loads, but if you really feel the need, you can choose your brands carefully to find one that has a $25 generator interlock in a box size you like. If I was min-maxing for price, I’d look at Eaton, as Square D “QO” is pricey and Siemens’ cheap interlock requires a 12+ space panel (which might be a virtue of its own actually, because you can put other loads there, heck you could power a whole wood shop, presuming the Tesla is out of the garage when you’re making sawdust).
My advice is send that switch back, and slap a subpanel there with or without interlock, and with or without extra space for other loads (not to be used concurrently with the charger, of course).
    @crockeea -- the thing is that 15A and 20A receptacles are really the same on the inside, something that's *not* true for the higher amperage receptacles – ThreePhaseEel Jul 13 '20 at 17:03
    @ThreePhaseEel Very helpful! However that still doesn't explain why a single 5-15 is not permitted on a 20A breaker, as PhillipNagel pointed out above.I accept that that is the code, but what is the reasoning behind it if the outlet is rated for 20A? – crockeea Jul 13 '20 at 17:07
    I don't know why none of the big-3 here have chimed in about the PURPOSE of the different configurations of outlets. They are all configured differently to insure that whatever device is plugged into the outlet gets the correct voltage and amperage connection, assuming overcurrent protection is provided at the breaker supplying the outlet. The device plugged in may or may not provide it's own over-current protection, most large tools do. I wouldn't supply my 3 hp table saw at any more than a 20 amp 240v circuit. The motor has internal thermal protection, but a 20a brkr doubles that safety. – George Anderson Jul 13 '20 at 17:27
    @Harper-ReinstateMonica This is pretty hostile, especially to a new user. I'm not challenging the code, I'm trying to understand 1) what the code says, and 2) why. I have two seemingly conflicting answers, neither of which is the definitive code, so I'm asking for clarification. I'm not proposing ignoring code, and I certainly don't claim to be smarter on this topic that those who wrote it. – crockeea Jul 13 '20 at 17:45
  • @crockeea, when you have a single plug on a circuit, it's a dedicated circuit, and no one puts those in unless they have something that needs it. And a device that calls for a dedicated circuit is allowed to rely on the breaker matching what they specify. So, for example, if you have a window AC that calls for its own 15A circuit, then it needs a 15A breaker and single 5-15 plug. – Nate S. Jul 13 '20 at 18:01
    This is a **frame challenge**. You *asked* a very specific question. But the background raises bigger questions - **why** are you switching, **why** are you using a non-listed switch, etc. - to which @Harper is responding to the *implied* question of "I have a big charger. I want to have other electrical stuff. How can I make it all safely coexist?" And he answered *that* question. – manassehkatz-Moving 2 Codidact Jul 13 '20 at 18:03
    @crockeea you know, on further thinking, I realize you are right. I’ve dealt with so many of these I see the glass as half empty. But here you are *asking* about what Code is, and taking an interest, and that puts you far above most. I’m sorry for being snippy. – Harper - Reinstate Monica Jul 13 '20 at 18:10
    When thinking about code, remember this: The code is written (metaphorically) in blood. Literally would mostly be smoke inhalation/asphyxiation, the common cause of deaths in fires. It's not written by some sort of electrical group - it's written by the National Fire Prevention Association. – Ecnerwal Jul 13 '20 at 23:52