I have a situation where my oven and counter-top range are split up, but fall within spec of being able to utilize one 50a breaker on the panel.
My plan is to pull a single 6/3 cable to a large junction box, inside which I’d splice the two sets of 8/3 wires from the oven and range with the 6/3 cable (hots and neutrals, the grounds are skinny enough to use a twist-connector). Because the all the cables combine to be pretty thick, I am not sure a twist-connector on the hots/neutrals would be a good choice (previous owner had it that way, but even with smaller cables it felt a bit sketchy).
With NEC 2017 in mind, what type of connectors can I use? In the automotive world I’m used to things like a multi-terminal connector/distribution block. Is there something like this in the home-owner world?
Tried searching and found some split-bolt suggestions - do I just wrap it with lots rubber tape to insulate? Can a split bolt be used to connect three wires (one 6ga and two 8ga or even just 3 6ga if a future oven has that)?
Another option I found are Polaris connectors. Expensive but seem straightforward. Would they or the split bolts need to be secured to the inside of the box, if used?
Any additional suggestions or recommendations are welcome.
ThreePhaseEel
  • 81,744
  • 227
sil80
  • 567
    Why are you using #8 onward to the oven and range? Would #10 (30A) suffice? – Harper - Reinstate Monica Aug 13 '20 at 03:48
    What kW rating are the oven and cooktop in question? – ThreePhaseEel Aug 13 '20 at 03:54
  • The range is 7.5KW @ 240V (so 31.25A) an the oven is I believe 4KW (16.7A). But they have their own wiring coming out and it's smaller than 8ga, I was just using 8ga for relative sizing of the connector. Seems like they just make it under 50A, right? – sil80 Aug 13 '20 at 12:52
    If lowest cost is not an object (and it may be) I'd consider using a small subpanel here, even though it's not required by code (it's OK to exceed code requirements.) I've personally ***Not*** enjoyed the experience of hearing and then seeing an oven element fail, and proceed to spew a volcano of molten stuff while it happily arced away and the 50A breaker said "Hey man, not my job, this arc is *way* under 50A" until I shut the oven off myself. – Ecnerwal Aug 14 '20 at 01:16
  • Space and cost are a bit of an object, although I am with ya on that. Don't most modern ovens have protection against this? My equipment is probably less than 10 years old, I guess I should try to find the literature on it online to see if it will shut itself off. Cooktop is a glass top and oven is a smaller bosch unit. – sil80 Aug 14 '20 at 11:36
I use Polaris and other brands for this, in the past I used to use cambric , linerless and super88 to insulate the split bolts the cost of the Polaris style pays the first time you reuse them and are much easier to use. I use a size 4-14 rated alcu Home Depot actually had a good price on these and I usually put tape on to hold the plugs in place but nothing is required to hold them in the box. Their are 2 lug 3 that I think you want up to 6 I have purchased all 600v rated and UL approved.
There's a neater way to do this
While Ed Beal's suggestion of "Polaris" type insulated mechanical lug connectors will work, it's a bit ugly to have big honking connectors flopping about in a box. Fortunately, there is an analog in the mains world to the distribution blocks you're used to in the automotive world. What you're looking for is also, aptly enough, called a power distribution block; however, in mains-wiring-land, you need to be careful not to confuse them with power terminal blocks, as you must use a part tested and listed to UL 1953 (QPQS category code in the UL database), not a part that's only been component recognized under UL 1059 (XCFR2 category code in the UL database).
Under these constraints, the cheapest option would likely be a Mersen/Ferraz MPDB63163 with a trio of MPDBC6263 covers; depending on where you shop, you'll be looking at about $40-$50 for that, which takes care of both hots and the neutral in one go. This compares favorably to having to get three insulated mechanical connectors at around $20/piece at the time of this writing, and also provides a neater installation as the PDB gets fastened to the back of the box so that nothing can flop about.
You'll want a big box in any case
The other factor in play here is that with either route you take, you'll want to use something larger than a typical 4 or 5" square junction box to house the splices. For starters, "Polaris" type connectors are fairly chunky creatures, with a 3-port, 4-14AWG splice taking up over 2.5 in3, far more than a wirenut or even a push-in type splicing device would use. Furthermore, the rules in NEC 314.28(E) regarding the use of power distribution blocks only permit their use in boxes upwards of 100 in3 in size, and also require NEC 312.6 compliant wire-bending space at the power distribution block's terminals.
As a result of this, I would recommend that you make these connections in a NEMA 1 pull box instead of an ordinary junction box. A 6"x6"x4" box with a matching flush cover will provide enough space for all of your splicing needs, and costs only about $20 at your local electrical supply house. (It also fits within a standard 2x4 stud wall, if only barely.) You'll want to use an appropriately threaded machine screw into the grounding hole on the box with a 10AWG solid copper pigtail to connect the box to the incoming ground wires, by the way, and don't forget to use NM clamps in the knockouts, just as you would with a regular junction box.
ThreePhaseEel
  • 81,744
  • 227
  • The size of 1 block appears to be 1.5 length of the Polaris connector. Considering 3 Polaris connectors are needed to be equivalent to the block plus wire routing, that will end up with a noticeable increase in free space. – Kendrick Sep 16 '22 at 04:57
If you have a circuit rated for 50A using that sized breaker and 6/3 cable to distribute to the load then ALL wiring on that circuit must be rated for 50A. You may not splice in smaller gauge wires because they would not be rated to carry the full capacity of the circuit.
On the other hand you may use larger sized wiring to distribute to the loads receptacles as long as the circuit breaker rating does not exceed the current rating of the smallest gauge wire used in the circuit.
If you do use mixed gauge wiring in a circuit make sure to provide marking and tagging, especially in the main distribution panel, that such usage is being done so that someone in the future does not see large sized wire going to a circuit breaker and think that the breaker can be upgraded to a higher capacity.
Michael Karas
  • 64,093
  • 63
  • 142
    Wrong here -- the OP's configuration is expressly permitted by NEC 210.19(A)(3) Ex. 1 – ThreePhaseEel Aug 13 '20 at 03:53
    Fascinating! I've used the "tap rule" before, but it was to power a smallish sub-panel and I had over-current protection in the receiving sub-panel and all wiring installed in a raceway and didn't exceed the length restrictions. What a great catch, 3ph! – George Anderson Aug 13 '20 at 12:08
    Just found this fantastic video diving into the math of NEC 210.19(A)(3) Ex. 1, the diff between NEC 2017 and 2020, multi-appliance branching, and what types of conductors can be used for these situations. Thank you again, ThreePhaseEel for pointing out exactly what portion of the code addresses this situation. https://www.youtube.com/watch?v=g36INO3rxEw – sil80 Aug 13 '20 at 15:46