14

I have been in the house for about a year and the toilet has always had poor drainage. It doesn't overflow but there's hardly any suction at all when you flush it. The tub next to the toilet drains very slowly and will gradually fill up when using the faucet but just running the shower head it drains fast enough to keep up. Both are tied to the same drain line and I figure maybe there's a blockage somewhere. Btw, I replaced the toilet a few weeks ago and it made no difference. (reasons other than just drainage)

I had a plumber come out and they think that the venting was done improperly. The pipe on the left coming off the T is the vent and goes straight up through the roof. To the right, tying in just in front of the vent, goes to the bathtub.

I was quoted at $1200 plus materials to rearrange this. I'd prefer to keep that money in my pocket to fix other things and have no problem crawling in there myself to do the work. I'm just not sure exactly what their plan was to correct the placement of the pipes.

Here's what they wrote on the invoice:

Remove a section of the four inch main drain line into the crawl space area and tie in the drain and the vent line separately so that it is no longer wet vented and. This conclusion was found due to having the customer flush the toilet while I was on the roof to see what/ if any air was pushed through and it was minimal.

enter image description here

isherwood
  • 129,178
  • 7
  • 160
  • 386
Phaelax z
  • 608
  • 2
  • 5
  • 12
  • 3
    I don't have enough plumbing system design experience to answer with confidence, but this is a "wet vent" scenario. Unless your tub is actively draining when you flush it shouldn't be an issue. There's plenty of venting available there even if it isn't ideal or strictly legal. Have you checked that the vent is actually clear all the way through the roof? – isherwood Sep 23 '20 at 18:33
  • And what did your local plumber propose as a solution? – isherwood Sep 23 '20 at 18:34
  • I'm not sure of his exact solution, but basically wanted to move where things interconnect. I think remove the tub drain from the vent and move it further down the main pipe, he didn't get into specific detail on how he was going to change it. – Phaelax z Sep 23 '20 at 18:40
  • It’s hard to tell from 1 photo , how much drop and slope you have – Tony Stewart EE75 Sep 23 '20 at 18:42
  • 1
    I agree with Isherwood not a plumber but that vent is close enough where it should not be an issue when you flush the toilet is it sucking air through the tub drain if it is there may be a blockage in the vent line itself, I have found leaves a culprit several times in a 4” old home I even found a dead squirrel it doesn’t take a lot to block vents I would run a snake or garden hose down the vent from the roof. – Ed Beal Sep 23 '20 at 18:42
  • I've updated the original post under the pic with what was written on the estimate. – Phaelax z Sep 23 '20 at 18:43
  • 3
    Have someone drop some ice cubes into the vent while you listen for them to arrive in the crawl space. You'll know in a hurry if the vent is clear. – isherwood Sep 23 '20 at 18:47
  • Is the tub & vent 1.5" or 2" ? The vent (at least) should be 2" (since it's venting a 4" pipe, according to the plumber's estimate.) – Ecnerwal Sep 23 '20 at 19:34
  • 2
    get under threre and slap that pipe to see if it's full of water – Jasen Sep 24 '20 at 08:37
  • 4
    Stupid question: Did the plumber snake out the drain? – Hot Licks Sep 24 '20 at 22:18
  • @HotLicks Already answered in comments below - No, they did not. – Ecnerwal Sep 25 '20 at 12:55
  • I agree with the commentors & posters suggesting your company is not the best. First step would be to try snaking/rodding the drains with or without camera; you can try this yourself with a cheap solution, or ask a specialist or (competent) plumber. – user3445853 Sep 25 '20 at 15:09

5 Answers5

22

It's a common misconception, but blocked vents do not cause slow drains. If you Google it, you'll find lots of incorrect information that completely ignore the physical realities of how a vent operates. The purpose of a vent is to prevent the P-trap from being siphoned, it is not intended to help water go down the drain any faster - in fact, a properly vented fixture will actually drain somewhat slower than a fixture with no vent.

People often talk about a vent in the context of an inverted soda bottle analogy, likening the vent to putting a hole in the opposite side of the bottle so the liquid doesn't slowly "glug" out of the mouth of the bottle. That analogy is nonsense, because there is no such thing as a plumbing fixture with only one entrance/exit like a soda bottle - water going down your pipes does not need to "switch places" with the air ahead of it. Every plumbing fixture ever made has a separate inlet and outlet, and is already open to the air at the inlet side, allowing the air to follow the water down the pipes. Adding or removing a vent does not change that at all - it is not analogous to adding a second hole to a soda bottle, as it's actually adding a third opening to the already two-ended plumbing system. A blocked vent could potentially contribute to slow drainage if the inlet side is also blocked and cannot let air in, but in that case, it's really the blockage in the drainage pipe that's the issue, which is only exacerbated by the blocked vent. I can't imagine a situation where water can go down the drain, but air cannot.

As an experiment, you can pour water into a sloped pipe and watch it drain as fast as gravity will carry it. Now add a T and a vent somewhere along the pipe, pour the water in again, and see that the vent does not slow the water at all. In fact, plumbing without a vent will drain slightly faster, as water accelerating through the pipes "pulls" the water behind it. Although a vent slowing the drain may seem counterintuitive, it makes sense when you consider that the purpose of the vent in the first place to to prevent the pipes from emptying completely! You can watch a video of such an experiment here - in a realistic setup with a drain, trap, and vent, blocking the vent actually makes the basin drain faster.

Any air that needs to be pulled into the pipe can be pulled in from the inlet - a vent would only help in draining a toilet, for example, if the lid forms an airtight seal around the bowl. The vent is just there to prevent a suction effect that would siphon the P-trap. Your venting may be done improperly, and it may cause different problems with your plumbing, but it is not the primary culprit of a slow drain. If anything, a blocked vent would result in a drain that is faster and smellier (due to the siphoned P-trap). Look for a blockage in the drain pipe, not the vent.

Nuclear Hoagie
  • 982
  • 1
  • 5
  • 17
  • Hopefully someone will do this experiment and post in on youtube. – chicks Sep 24 '20 at 21:28
  • 2
    @chicks While it doesn't have a video of the side-by-side comparison, an experimental setup of testing vent/no vent is at the following link: https://www.startribune.com/why-houses-need-plumbing-vents-forget-the-soda-bottle-analogy/188978471/. The guy found that the no-vent plumbing actually drains *faster*, as water accelerating down the pipe "pulls" the water down the drain. This makes sense, as the whole purpose of the vent in the first place is to *prevent* all the water from going down the pipe. – Nuclear Hoagie Sep 25 '20 at 13:47
  • 1
    I struggle with this answer because I had a toilet that would not drain until a chimney sweep climbed up to my roof a clog from our stack vent. The toilet started draining moments after they removed the plug. Because of this experience I keep arguing with plumbers that stack vents can indeed cause clogs. Yet you seem to present a scientific argument why this is not possible. – Moby Disk Sep 25 '20 at 15:31
  • 1
    @MobyDisk Admittedly, I'm not a plumber, and there is such a widespread belief that a blocked vent can cause a slow drain that I've wondered if there's some practical effect I'm missing. But I can't articulate any reason why it would, and any explanation I've seen of how it could falls apart under scrutiny. In your case, I wonder if there was a clog where the vent meets the drain line? One could remove a drain line clog via the vent, which could make it seem like the vent was the issue. – Nuclear Hoagie Sep 25 '20 at 16:14
  • There IS a functional difference between a trapped fitting without a functional vent and an open pipe. – Ecnerwal Sep 25 '20 at 18:17
  • @Ecnerwal Not sure what you're getting at - why would the trap make any difference in whether the vent slows the drain? See the video link I added to the answer, which experimentally shows that an unvented fixture drains faster than a vented one, even with a trap in the drain line. – Nuclear Hoagie Sep 25 '20 at 18:36
  • That demonstration in the video is useful but flawed. The area above the water has to be filled from somewhere, and that air will have to come through the P-trap if there's no vent. But the demo uses too small a tube for the amount of water flowing through it. In a real plumbing system, you want the water to hug the sides, with a column of air in the middle. As soon as you get enough flow to completely fill the pipe, you'll get an air pressure differential, vented or not, which will slow the flow. At that point, the only place to get air is through your P-traps or the vent... – Bryce Wagner Sep 26 '20 at 15:56
  • (continued) But at that point, you've already exceeded your pipe capacity, and it's going to be slower no matter what. The key is to stay below full capacity. You have to account for the increased pressure from below, not just the vacuum from above. – Bryce Wagner Sep 26 '20 at 15:58
  • @BryceWagner Interesting point about the difference in between a completely full pipe (from draining a full tub, for example) and a partially full one (from running a sink slowly, for example). But I still don't see why the vent makes a difference in the partially full scenario - I'd think that if there's a column of air through the whole pipe, you don't really get any pressure differential that needs to be remedied by drawing air in through the drain pipe or the vent. – Nuclear Hoagie Oct 08 '20 at 18:14
  • @NuclearWang I've been thinking about it, and I think having a vent might prevent a full pipe scenario. This would require doing real world tests to prove, but my thought experiment says that with a vent, it will encourage air gaps in the water, which gives it room to spread out, and thus allow it to hug the walls. It's important to test with real pipe sizes, not little tubes, because the larger surface tension in a small tube is going to make it act different than a full size pipe. Surface tension is a pretty big factor, and suds can really screw up your drainage. – Bryce Wagner Oct 09 '20 at 01:38
  • @BryceWagner I've been thinking about it a little more, and it occurred to me that in any situation where you see a slow drain, the pipe must be full - water has completely filled from the blockage to the basin. If the pipe didn't fill up, you'd never notice that it was draining slowly. A blockage effectively narrows the pipe and reduces its capacity below normal flow from the supply. I think a full pipe is the only relevant scenario when discussing a slow drain. – Nuclear Hoagie Oct 13 '20 at 14:04
14

Unless something is clogged, this should work fine (assuming appropriate slope on all lines.) The vent should be 2" for a 4" line, and is only draining the tub (2DFUs) which is half the permitted load wet venting. The vent loading (shown) anyway) is at most 8 DFUs (depending on toilet flush size) and while that could (easily) use 1.5" on that basis, it can't wet vent more than 1 DFU at that size and it's also not "at least half the size of the drain pipe" so it would be undersized/illegal. There is an error which your plumber failed to mention, however.

When you are not showering or draining the tub, that is a dry vent (yes, it's technically a wet vent all the time, but in practice, it's dry except when the tub drain is flowing water.)

If you (or plumber) have not already snaked the tub drain all the way to the main line, do that. Snaking the vent is also advisable, as it may be clogged away from the tub connection or on it's way to the roof. Snaking the main line to whatever point it appears to work well is also advisable. Unless something was done that you/your plumber did not mention, I see no sign that it was actually checked to be clear in what you have reported - just that the plumber stood on the roof and observed it not working.

The thing that is VERY wrong with it (not mentioned in your quote) is that a sanitary TEE is being used incorrectly to join a horizontal drain - that should be a WYE, and if you are replumbing, you'll want to fix that. You can use a "combo WYE" or a "WYE and a 45" in that orientation, or you can use a wye in the normal (to the side) orientation for the drain connection.

Under IPC rules it's generally accepted (or not forbidden) to use a sanitary TEE that way FOR A DRY VENT ONLY. Some dispute that use being acceptable, and other codes may actually prohibit that use - IPC prohibits that use for a drain or wet vent connection. A WYE is always acceptable - for a dry vent, pull the WYE up to at least 45 degrees above centerline, or run it right out the top.

If you wanted to change this around and separate the functions as proposed (which I doubt will help, unless one of the pipes you cut and replace is full of gook that you should have gotten clear via snaking) you're in for a signficant bit of work - dropping a new fitting into a main line means getting upwards of two inches of motion on it, and under IPC rules "saddle tees" are illicit (don't know what rules you are under, code-wise) though you can use PVC repair couplings (and pray they don't stick before they are in the right place) or rubber couplings to have a "removable section" to give you the working room. Here you might just yank the toilet and unscrew its flange to get the working space you need.

The other distinct possibility is that the main line is not properly sloped all the way to wherever it goes off to the left side of the picture - a low (or high) spot in the line can cause all sorts of trouble with proper drainage. A competent plumber should have noticed that, but I question your plumber's competence (or perhaps honesty) if everything did not get verified as clear by some means (snake, drain camera, whatever...)


If seeking to "separate the functions" (or simply make it "correct to code", at least IPC) the most minimally invasive method I would envision is (after thorough pipe cleaning):

Cut off (leave stubs) the tub trap. Under IPC rules the distance from the fixture outlet to the trap weir "cannot exceed 24 inches" vertically, which means you can be that far, if needed. Extend the tub drain down to reposition its trap weir (the waterline in the trap) 1/4" per foot it's away from the main line higher than the centerline of the main line where you will connect it. It looks like you probably can do that within 24" vertically of the tub, by eyeball. You're looking to run it under the vent line, which you will leave alone other than throughly cleaning it.

Cut in a 4x2x4 WYE (i.e. a 2" sidearm from the 4" line) rolled just enough above centerline to meet that trap (ie, rather than set the WYE dead level, set it so that it connects at the right slope for the drain.) Connect a 2x2x2 (or 2x1.5x2 if the tub is 1.5") WYE "more than 4 pipe diameters downstream" (8" for 2" pipe) from the trap exit on the new drain line and plumb that to the (now dry-vent only) former tub entry to the dry vent line - that vents the tub trap directly, since you have the connection sitting there. Wet venting it via the main line back to the dry vent is likely acceptable, but this is better, and costs very little in time, effort, or parts.

Drain Reconfig

Ecnerwal
  • 201,085
  • 10
  • 245
  • 533
  • 1
    He did not attempt to snake anything, which I figured would be the first thing he'd do. No camera, he wanted to but did not have one. He's not a "drain guy", and only they get cameras at their job. I'm not sure what separates a drain guy from a plumber, but this is fairly large plumbing company in the area. I'm also almost 45min outside a major city in a corn field, not many will drive out here. I'll get a snake and attempt that first and see what happens. – Phaelax z Sep 23 '20 at 19:51
  • 21
    So you had **a drain problem** a 45 minute drive from the shop and they sent you "not a drain guy" - spread the bad word of mouth far and wide, that's a **lousy** company. – Ecnerwal Sep 23 '20 at 20:34
  • Maybe I haven't had enough coffee yet this morning, but I'm having a really hard time following your descriptions of the issue and the suggested repair. Would you consider a little MS Paint on the OPs picture to show the problems you've identified and the proposed fix? I'm not doubting you, just not following you... – FreeMan Sep 24 '20 at 11:53
  • 1
    I would never consider using MS Paint. I've hated MS since DOS was cutting edge. ;-) And I haven't had enough coffee yet myself. 1000+8 words as requested. A Sanitary Tee is only acceptable for entering a VERTICAL pipe if it's carrying waste-water. This use is forbidden. Stuff piles up on the uphill side of the tee where it "plops" out of the tee with no impetus down the drain line, as it would get coming from a combo- Wye. – Ecnerwal Sep 24 '20 at 12:50
  • 1
    Upvote for checking the fall on that horizontal line. OP should be able to check this themselves with a level. – alexw Sep 24 '20 at 18:53
  • I ran a 25' drain auger, didn't seem to have any issues, but also dumped a gallon of "Instant Power Main Line Cleaner". Wasn't sure if its safe to put that down the toilet, so I poured half through the shower drain and half down the vent pipe. After a few hours, didn't seem to make any difference. If there is a clog, I can't find it. I'll check the slop of the drain pipe next. – Phaelax z Sep 25 '20 at 17:28
  • Have you snaked everything (tub, vent, and main), or only the main line? – Ecnerwal Sep 25 '20 at 18:18
6

Run some water in the tub until the problem shows, then get under there and slap that pipe to see if it's full of water it should be mostly empty and sound hollow.

If it's full there's a blockage downstream somewhere.

Jasen
  • 19,044
  • 1
  • 20
  • 32
2

I see that nobody has bothered asking about the performance of your septic system. Do you have a gravity system, or do you have a lift pump? If you have a lift pump, that means there is a filter inside one of your main septic tanks, that is supposed to only permit grey water to pass through a horizontal pipe leading from your main septic tank to the smaller (typically 300 gal) lift station tank. At my place, that filter can get gunked up with long hair, just like a shower drain, and this leads to very slow flow of water from an overfilled main tank to the 300 gal lift station tank. This gets to a point where my downstairs toilet and tub drains too slow. If left unmaintained long enough, grey water will backup up into the downstairs shower.

Also, a friend of mine bought an older home, and the previous owner was in the practice of pouring bacon grease down the drain for years. Over time, this had the same effect as cholesterol in your arteries - the size of the 4 inch (gravity system) drain pipe going into the first septic tank shrank to about 2 inches before the new owner finally had a plumber out to his house that actually found the root cause for his slow-draining system. You could pour all kinds of liquid acids into his system, and would not have penetrated deeply enough, because by the time the acid reaches the blockage, it is too diluted. The fix estimates were crazy. He fixed it himself by digging down the side of his foundation wall to the pipe, and digging all of that out enough to go about cutting out a section of it to clean it all up and then ended up replacing that 4 inch pipe between the house and tank. A dirty, nasty time consuming job indeed which is why the estimate was so high. My point is, before you go about replacing pipes and rerouting, be sure that the real issue is not with the tanks and final lines. Prove that you have really good drain volume at another tub in the house first. It could take dumping 2 or 3 5-gal buckets of water into the pipe as fast as you can to discover if the problem is just an "almost full" tank, or clogged septic system filter.

Darrin
  • 121
  • 1
  • 3
    I should provide the disclaimer; do NOT cut into your septic line pipes unless you have had all of your septic tanks emptied to a point that is below the inlet hole inside the tank. If you don't you'll of course find yourself in a pond full of doodoo. ;-) – Darrin Sep 24 '20 at 17:01
  • 1
    This is useful information, _assuming_ the OP is on a septic system, not city sewer... – FreeMan Sep 24 '20 at 18:10
  • 2
    Did say "middle of a cornfield" which trends septic, but did not mention a problem affecting **all the house** or backing up out the lowest drain (so appealing, not.) Which makes this less likely to be the root cause.... – Ecnerwal Sep 24 '20 at 18:58
  • 2
    No septic, city sewage. Only 1 bathroom. Only the tub faucet and the toilet seem to create more water than the drain can handle. – Phaelax z Sep 24 '20 at 21:40
  • So, the clog is between the toilet/tub and the next thing on the line, (bathroom sink or whatever comes in next) evidently. – Ecnerwal Sep 25 '20 at 12:53
  • If snaking out everything still does not improve the situation, I would next have a good look at the trap installed onto the tub--not the PVC trap in the photo. It could just be fastened at an angle that is level or negatively sloped due to the spacing--such as being too close to a floor joist to make an ideal connection to the tub. The sink might be tied into the vertical PVC pipe in the wall (we can't see it here to know). – Darrin Oct 02 '20 at 18:17
  • If those things look okay--and you will know when it doesn't look right--then I agree with extending the drop of the vertical drain pipe of the tub, by lowering that trap, and tying it into a [new] santi-wye as suggested by @Ecnerwal. Especially if the tub is sitting right there only inches above that trap in the photo, and the sink is also wye'd into the vertical tub drain pipe--all in a tight place, or in less than ideal structural arrangement. – Darrin Oct 02 '20 at 18:17
  • Didn't catch my comment in time to change "sink" to "toilet". – Darrin Oct 02 '20 at 18:46
-2

Does my toilet drain poorly because of bad venting?

no

I replaced the toilet a few weeks ago and it made no difference.

remove toilet, place outside about a foot off the ground, with its drain unrestricted. Dump a 5 gallon pail of water into the bowl and observe the flush. If it's still terrible you purchased a terrible toilet... buy a toto. Otherwise your drain is blocked, get some FlowEasy cleaner from a plumbing store. For just that one 3" toilet drain I would get a quart and use the whole quart poured down the open drain when the toilet is off. Wear gloves and a long sleeve. Then replace the toilet. Maybe consider getting the gallon of Floweasy and do all your drains. Odds are your tub drain is also blocked which is why that is slow.

ron
  • 1,108
  • 6
  • 9