I have a 12'x16' shed which has been leveled using concrete blocks but otherwise sits on the grass/dirt. It's about 100' from the house. I live in Georgia. I'd love to add some lights and outlets to it.
Can I run an underground electrical wire to it, ending in a 60 amp sub-panel? Or does the shed need to be more permanent with, perhaps, a poured concrete foundation in order to do that?
Sam Washburn
    I'm not sure about code, but I've done just that with two sheds over the last 20 years. Unless you expect the shed to move it's not an issue, in my opinion. – isherwood Oct 20 '20 at 12:44
    I just built a 10'x14' foot shed in IN this past summer and did exactly what you're asking. Well almost - I only ran one circuit. You can check out my questions from earlier this summer to get some details about wiring and conduit. – FreeMan Oct 20 '20 at 12:53
  • Do you really need 60A? That's enough to charge a Tesla and still have spare for both table saw and dust collector. Put another way, you have 2 banks of 120V @ 60A each, so 120 amps worth of 120V gear all running at once. Grow house? Bitcoin miner farm? – Harper - Reinstate Monica Oct 20 '20 at 16:27
    @Harper-ReinstateMonica Aren't you one of the lead preachers for "provide overhead now for expansion later"? (Yeah, I get that 60A seems like quite a lot, but...) – FreeMan Oct 20 '20 at 17:07
  • @FreeMan I am trying to head off the common error of "I need 2x 20A circuits, 20+20=40 and 60A is a nice round up, therefore 60A sub"... given OP's statement a 120/20A circuit may suffice, or perhaps a 20A MWBC. – Harper - Reinstate Monica Oct 20 '20 at 18:31
  • Fair enough, @Harper-ReinstateMonica – FreeMan Oct 20 '20 at 18:34
  • FYI, there was [this question](https://diy.stackexchange.com/questions/196522/is-this-plan-for-running-a-circuit-in-buried-conduit-correct) and also [this one](https://diy.stackexchange.com/questions/196670/should-i-use-a-gfci-breaker-or-receptacles-for-my-shed-run). – FreeMan Oct 20 '20 at 18:47
  • @Harper-ReinstateMonica I'm renovating it into a tech workshop. Adding insulation, several outlets on a tech bench, two computer stations, a spilt-a/c unit and a dozen or so LED light fixtures. I also want to leave some overhead for if/when I sell the place in case they want to do something else with it. – Sam Washburn Oct 21 '20 at 01:23
    @SamWashburn You had me at "mini-split" :) If you're fully finishing it with insulation and therefore doing HVAC there, yeah, I agree 60A is a good call. Just wouldn't be doing my job if I didn't raise the issue :) – Harper - Reinstate Monica Oct 21 '20 at 03:01
Yes, the national electric code allows wiring in structures like your shed.
If you plan on using UF wire for the run buried 24” deep you need to bring the wire up in conduit so the wire is protected. If you run conduit, the conduit only has to be buried 18” for PVC. If you run rigid or intermediate metal it can be buried 6”. Burial depths are listed in the NEC 300.5.
With the conduit option, we normally pull thhn as it is dual rated as thwn. (Conduit in ground is considered a wet location.) You would not want to pull UF wire in conduit, and Romex or NMB is not allowed. You might consider aluminum wire at that distance for the feeder depending on what your load is.
Anything more than a 20 amp multiwire branch circuit will require a panel in the shed. There are very small panels that will provide 4-6 circuits but these may be undersized: if you want lights on 1 circuit, outlets a second circuit, possibly a welder or air compressor a double pole circuit... and you are out of room for breakers. So it ends up being better to go with a larger panel (100 amp 20+ circuits). The cost will be close to the same as the smaller panel but you can feed it with 60 or 40; that is fine.
Remember your receptacles in your shed require GFCI protection--even light circuits in the ceiling--if plugs are used. However, lighting circuits that are hard-wired do not require GFCI protection.
With more information, we can help with the wire size or provide additional information.
Mathieu K.
  • 115
    doesnt code already require a GFCI breaker in the panel for a new installation? – Richie Frame Oct 20 '20 at 23:52
    The protection can be by a breaker, GFCI receptacle or a GFCI device made for use in a device box I use these for kitchens and garden tubs so the protection is closer to the area that is being protected. But code doesn’t specify a location like the service panel it just requires listed protection. – Ed Beal Oct 21 '20 at 00:23
It is advisable to use a slip joint [expansion coupling] on the conduit stub up, otherwise nothing out of the ordinary. Around here, that's not out of the ordinary even with a poured foundation.
Assuming PVC conduit, 18" cover to the top of the conduit, minimum. Warning tape above. Stub-ups (what sticks out of the ground) need to be schedule 80, and it's advisable to just use schedule 80 for the whole run, as it's a lot tougher than schedule 40. Toss an extra conduit in the trench (trenches are expensive, conduit is cheap) in case you ever want network/phone/intercom/whatever out there.
If you want to spend a lot more on conduit, rigid galvanized steel only needs 6" of cover and serves as the grounding conductor.
A brief word about direct burial cable .vs. conduit: direct burial may look less expensive the first time you do it. It's more prone to fail than wires in conduit are, and it looks rather expensive the second time you do it (trenches are expensive, conduit is cheap.)
    Second what you're saying about the cost of trenches. If you're going to dig a trench you should do what you reasonably can to ensure you never need to dig it up. – Loren Pechtel Oct 21 '20 at 01:53