I am upgrading some 15A outlets on a 15A circuit. Can I install 20A outlets instead of 15A outlets? If not, why not?
Will a 20A outlet on a 15A circuit pass a home inspection? Or, is it not allowed?
I'm going to be plugging in a 14000 BTU portable air conditioner and it just seems like a good idea to have a 20A outlet to reduce heating in the outlet, even if the circuit is rated only for 15A.
NOT a duplicate of Would there be a problem installing 20A switches on a 15A circuit?, because I'm asking about outlets, NOT switches.
I don't want to violate any laws either or have problems when I go to sell the house. I am located in California, in the United States. The house is an HOA-controlled condo, but I own the condo. The outlets I'm adding will be in the garage, likely on a NON-GFCI line--I'll be tapping a new outlet off of the house's interior hallway, through the wall, into the garage for a single new receptacle in the garage. The circuit is rated at 15A. I was thinking of putting a 20A outlet. I'm not sure, but maybe this is supposed to be a GFCI-outlet too, since it's in the garage--not sure.
Update:
This Amazon product review seems relevant: it indicates putting a 20A outlet on a 15A circuit is a code violation (emphasis added):
This was titled and advertised as a 15 amp device, but is actually a 20 amp device. As such, it's against safety code to use if you are on a 15A circuit. I had to return this item and purchase a 15 amp version, as installation of this would have caused me to fail inspection.
19 May 2021: I just saw this related question too:
  1. Is it OK to have a 20 Amp receptacle on a circuit with 12 AWG wiring and a 15 Amp breaker?
    if you want to reduce heating install a better outlet instead of a budget one. – Jasen May 19 '21 at 04:50
    Agree with @Jasen. 15 amp outlets are designed to function on 20 amp circuits. In most cases, there is little difference between a 15 amp outlet and a 20 amp outlet of the same grade other than the prong configuration. If you want to avoid heating, put in a $10 or $5 outlet instead of a $0.89 outlet. – DoxyLover May 19 '21 at 05:12
  • @DoxyLover, I just added two $14 USB-capable outlets, and neither work. I found some replacements with high ratings but they are 20A outlets. Will a 20A outlet on a 15A circuit pass a home inspection? Both USB outlets I just installed, which don't work, have prong receptacles apparently that aren't properly pinched together (ie: not tight enough), so the prongs don't make contact. Seems odd a $14 brand-new outlet doesn't work (though its USB power outlets do). – Gabriel Staples May 19 '21 at 05:28
    Are these $14 usb outlets name brand with UL listing? – manassehkatz-Moving 2 Codidact May 19 '21 at 06:29
That won't have any effect. The internals of both 15A and 20A outlets are made of exactly the same stuff.
That's due to a UL requirement that 15A receps must be able to carry 20A internally, so they can be used in 20A circuits per 210.21.
If anything, 20A outlets are a bit worse, because the neutral wiper cannot be ful-width, since it must have a notch in it for the 20A sideways neutral. Of course many 15A receptacles use the same stampings.
Putting a 20A recep on a 15A breaker would defeat the entire purpose of 20A plugs being a different shape. So obviously that has to be a code violation. You don't want to plug a 20A-requiring appliance into a 15A circuit, because it would definitely overload, and ALL safety margin would rest on the breaker tripping.
If you wonder why a "single point of failure" is a bad safety strategy, watch aviation accident investigation videos.
No 20A receptacle on a 15A circuit allowed.
15A receptacles can safely take a 20A current, so in terms of heat development in the outlet or receptacle, it's the same anyway.
P2000
  • 15,754
  • 51
  • Then why are 20A outlets made at all if 15A outlets already take 20A? Certainly 20A outlets can take more load than 15A outlets, no? Maybe they take 25A then? – Gabriel Staples May 19 '21 at 05:26
    @GabrielStaples 20-amp outlets are designed to accept either 15-amp (NEMA 5-15) and 20-amp (NEMA 5-20) plugs. They differ in that the 20-amp plug has one prong turned 90 degrees. Therefore, the 20-amp outlet has a T-shaped slot to accept either. – DoxyLover May 19 '21 at 05:39
    @GabrielStaples the 20A T-slot is allowed if the breaker is 20A. A 20A device has a plug and chord rated for 20A (fryer, toaster, hair dryer..). It's not for the receptacle's protection. The T-slot prevents plugging a 20A device into a 15A circuit and rendering it thus inoperable. – P2000 May 19 '21 at 14:35