35
I read an opinion somewhere that almost all mobile air-conditioning systems are "working against themselves". An A/C whose motor and compressor is inside the house as opposed to being mounted on the outer wall is inherently "flawed". I am talking about an A/C with a single outgoing exhaust hose:
I remember the argument only vaguely, but there are three main points:
  1. By pumping the hot air out, the A/C creates an under-pressure in the house which sucks in more hot air from outside
  2. The heat of the motor and compressor stay inside the house
  3. It is impossible to engineer the compressor to be quiet enough for a bedroom
I would like to know if these points are legitimate and if there are perhaps some advantages of mobile A/Cs that make up for these flaws. For instance, the first point seems to be equally true for any A/C unit, even the ones that have an outdoor unit. The air has to come from somewhere, right?
Martin Drozdik
  • 639
    Re: "the first point seems to be equally true for any A/C unit", most other types have a barrier between the condenser and evaporator and recirculate only interior air past the evaporator not causing a need for make-up air. – NoSparksPlease Jun 13 '21 at 14:56
    3. "…impossible to engineer the compressor to be quiet enough for a bedroom" will always be a matter of opinion, unless you explicitly define what you are using to declare it "quiet enough". How loud it is is primarily a matter of engineering (i.e. units *could be* made quieter, but that usually involves other trade-offs, commonly size, weight, and money). Also of note is that the airflow is going to cause noise too, which may be more than the compressor. But, basically, "quiet enough" comes down to some people being comfortable with fairly loud noise levels, while others need ultra-quiet. – Makyen Jun 14 '21 at 01:29
  • If you're extra stupid, and don't vent the hot air outside, these portable machines become heaters. I walked into an electronics store where the staff was a bit less smart than the average person, and used these things all over the store. At night time, outside was a comfortable 20 Celsius. Inside was a balmy 30+. – Nelson Jun 14 '21 at 04:03
    Here is a great explainer, https://youtu.be/_-mBeYC2KGc – mcfedr Jun 14 '21 at 07:50
    *The air has to come from somewhere, right?* - warm air in a room, circulated over the surfaces of a matrix containing very cold fluid, and discharged into a room has the net effect of loading heat from the room into the fluid. The fluid can then be transported outside the room taking the heat, but not the air, with it. The room can be completely sealed and still cooled and all the air stays within the room. Such devices are typically called refrigerators (infiltration caused by pressure reduction caused by cooling is omitted for clarity) – Caius Jard Jun 14 '21 at 11:20
  • Don't forget that people often use portable air con units to blow cold air on themselves regardless of the overall effect on room temperature - the personal perception being more important than the actuality – Caius Jard Jun 14 '21 at 11:24
  • Huh, I have seen these in big box stores but funnily enough they *never* show a hose connected to the outside on the packaging/box. Glad I never thought to get one and try it out... – TylerH Jun 14 '21 at 14:38
  • This brings up a question, what happens to the condensation? Isn't this just a dehumidifier with a hose to vent the heated air outside? Where does the water go? I've never had a dehumidifier last more than a year or two, and their compact design makes them more prone to fires. – rtaft Jun 14 '21 at 14:39
  • @rtaft The condensate water is sprayed onto the hot side coil, so that it vaporizes and exits with the heated exhaust air. If this process doesn't keep up with the accumulation in a humid climate, you have to empty the collection sump just like in a dehumidifier. – Kevin Reid Jun 14 '21 at 17:25
    Just to be clear about "the first point seems to be equally true for any A/C unit" - NO, this is not true for typical 'split system' AC units. These operate as a closed system, there is no exchange of air between indoors and outdoors. "The air has to come from somewhere", yes, it comes from the 'return' duct where your air filter is. – Glen Yates Jun 14 '21 at 19:05
  • As a clarification are you looking at if these units will make a single room comfortable or if these units are comparable to other AC units? This question seems phrased to make a case that they are worse than having no AC at all and that is not the case. – Myles Jun 16 '21 at 14:24
  • @Myles comparable to other units. I did not want to make the case you mention, sorry if it seems so. – Martin Drozdik Jun 17 '21 at 20:27
6 Answers6
44
As has already been mentioned, “dual hose” “portable” AC units do exist. So, we need to consider two separate questions: are single-hose ACs bad, and are portable ACs bad?
Single hose operation
Yes, but a conventional household window or "split" air conditioner has two independent air flow paths. Air is taken from inside, passed over the evaporator coil, and sent back into the room, colder and dryer. Separately, air is taken from outside, passed over the condenser coil, and sent back outside, warmer. (Or, exactly the same but warm inside and cold outside, for a reversible ("heat pump") system in heating mode.)
A dual-hose portable AC has the same refrigeration apparatus and the same separated air flow paths, but the outside air, inflow and outflow, passes through hoses instead of just grilles on the sides of the unit.
A single-hose portable AC just leaves off the outside air intake hose, so it is taking inside air and blowing it outside carrying heat.
The air that is being sent outside is coming from inside the room. Thus, some conditioned air is being wasted, and replaced with (warmer, wetter) unconditioned air coming in through building leaks and open doors. So, single-hose portable ACs are less efficient. (We can confirm this from the big-picture perspective of thermodynamics, which tells us that any time we take substances of two different temperatures and mix them (here, the cooled air and the leaked-in air), we are discarding the energy that went into creating that temperature difference.)
There's a secondary problem: The negative pressure extends to adjacent rooms (unless you have unusually airtight doors). As a consequence, running a portable AC in one room will tend to make other rooms warmer because they're experiencing the warming effect of pulling in more leaked outside air all over, but not as much the cooling effect of the AC's output (unless you have fans to blow it all around).
Neither of these is a problem in a dual-hose AC — theoretically. (In practice, users have found that some dual-hose units have poor construction such that the "outside air" side of the machine is not very airtight, and thus tends to pull in some inside air.)
Machinery inside the house
There are disadvantages of the portable form factor:
  • In a window or split air conditioner, the noise and waste heat of the compressor (and fan for the condenser coil) can be kept outside the building. In a portable AC, they are inside.
  • As the hot exhaust air (and somewhat less hot intake air, if applicable) pass through the hoses, the hoses heat up and pass some air back to the room. They may also have leaks at their ends, in cheap plastic poorly-sealed fittings. Thus, some heat that should have gone inside is transferred back into the room. (It is possible to make or buy a insulation wrap for the hose, which will reduce this effect.)
Both of these can be thought of as inefficiencies that are incidental rather than fundamental — if we put in lots more insulation and sealing against noise and heat, then it would be less noisy and more efficient. But then you'd have a much bulkier, more expensive unit.
Point by point
This section will reiterate what I said above, but in context of your questions.
True, because almost all mobile air-conditioning systems are single-hose units. (Why? I don't know. Probably because they are cheaper to make and look less bulky, and only recently did (USA) efficiency ratings start requiring accounting for the inefficiency due to the outside air brought in, if I remember correctly.)
The inherent flaw is in units with a single hose, but it is possible to have the compressor inside the house with a dual-hose system, which is still less efficient but not “flawed”.
True.
  1. The heat of the motor and compressor stay inside the house
This issue is mostly noise, not heat. The compressor can live in the exhaust air-flow path, so it is cooled by ordinary “fan blowing air over the equipment” and does not consume any of the heat-moving capacity of the refrigeration system per se — in this regard, portable ACs are the same as window or split ACs.
  1. It is impossible to engineer the compressor to be quiet enough for a bedroom
I don't care to comment on claims of impossibility, but I haven't heard of this problem being solved in practice.
Kevin Reid
  • 4,044
    Inefficient for sure; but, I've used portable air conditioners to spot cool rooms with problamatic ducts and compared to the costs of a split-system, seems like the best bang for your buck (technically, a window air conditioner is more efficient but for ease of setup and aesthetics the portable is hard to beat). – Leroy105 Jun 13 '21 at 20:44
    re: *quiet enough for a bedroom*, it's clearly possible as they exist. My parents have a unit that looks pretty much like the OP's picture in their bedroom (couldn't tell you the exact brand name or model), and they've been able to sleep with it in the room for years (I would say its noise level is about on par with a regular box floor fan on high, so not silent, but not so loud it keeps you up at night either.) – Darrel Hoffman Jun 14 '21 at 19:06
  • @DarrelHoffman I'd like to know what unit that is, because every one I've ever looked at and used generates noise in excess of 50dbA even at its lowest speed, which is incredibly loud. In contrast, pedestal fans at their lowest speed are easily under 40dbA. The difference is massive and the only time I sleep with my portable AC running is when the heat would otherwise make sleep impossible, and due to the noise my rest is always poor on such nights. – Ian Kemp Jun 15 '21 at 23:08
  • Portable units also have the advantage that they are invisible from the outside--something that can be important in places where there are rules about the appearance of your house. CC&Rs for our subdivision prohibit window mounted units (but there's no HOA, someone would have to go to court to enforce it) but the portable behind me isn't an ugly hunk sticking out. – Loren Pechtel Jun 16 '21 at 02:46
  • @IanKemp Unfortunately, I don't live near them right now so I can't check easily. (I could call and ask, but that'd be a weird conversation: "Hey, somebody on the internet wants to know what brand your AC unit is...") To be fair, my dad also sleeps with a CPAP machine, so if *that* isn't keeping them up, the AC unit isn't gonna make much difference. But I've heard the unit while it's on, and it didn't seem overly loud to me (especially compared to a CPAP). – Darrel Hoffman Jun 16 '21 at 13:45
    @DarrelHoffman My CPAP, 2 years old, is quieter than my outside central air unit *as heard from inside the bedroom*. If your dad has a CPAP that is so loud it is louder than an *indoor* AC unit, it's time (past time, really) for him to get a new one. – Ross Presser Jun 16 '21 at 15:31
  • As for the sleep, it depends on circumstances. I can manage to sleep with somewhat loud mobile AC working, although I note I'm not as well rested compared to no noise environment - but *much better* then trying to sleep in high heat without AC! Then again, few times I've been able to sleep on floor between racks in server room (which are quite noisy compared to paltry mobile AC units) when properly exhausted (like 2-3 days without sleep). Not that I would recommend it :-) – Matija Nalis Jun 16 '21 at 19:58
17
It's true that portable AC units have some inefficiencies when compared to other styles of units (window, mini-split, conventional). At least in the US, this is apparent when you look at newer testing standards from the Department of Energy, which will sometimes list two BTU ratings on portable units: one for the capacity of the machine, and one that accounts for things like heat loss into the room from the compressor, and negative pressure effects (for single-hose units). On the basis of efficiency only, portable air conditioner units perform worse. However, that's not always the full story.
For example, let's say you have one of the following cases:
  • window doesn't fit an AC unit
  • fitting an AC unit in the window would impede an emergency exit
  • rental or HOA agreements forbid window AC units
  • you don't need air conditioning a majority of the year
  • you're not allowed the modify the building to install a conventional or mini-split unit
  • you are physically unable to perform the installation
In cases like these, a portable air conditioner unit may be your only option, in which case efficiency becomes.less of an issue.
CJC
  • 305
    Or, a lot of people, myself included, own one for emergency use during a central A/C breakdown, so efficiency is secondary to cost, ease of installation, and storage. – user71659 Jun 15 '21 at 21:01
Yes all your points are correct. The cheap portable single-hose AC units are all of that - I own one.
But mine cost about $100, whereas the cheapest installed system is over $2,000 here. For the 5~10 days a year where the air temp is excessive, I can put up with the downsides.
This unit only cools 35 degree C air to perhaps 30 in the room, so actual performance is woeful, as well as loud resonant vibrations solved by a large strategically-placed F clamp.
Criggie
  • 10,046
    I'm certain an engineer of your calibre could hack a hole in the device so as to fit an air draw inlet hose for the heat dumping circuit and conenct both to outside.. It's all a question of what one's time is worth – Caius Jard Jun 14 '21 at 11:34
    @CaiusJard and how much you want your home to look like Doc Brown's. (thank you for the compliment though :) – Criggie Jun 14 '21 at 12:07
    just think if you tripped on the second hose and hit your head on the sink tho'.. – Caius Jard Jun 14 '21 at 19:29
All three of the points you cite are indeed true.
The first point is not true of the other common A/C designs (i.e. central air, split unit, window mount). All these types dump the heat into the air outside the house and blow the heated air away. Only the mobile type dumps the heat into the air inside the house and then blows the heated air away.
The only advantage to the mobile type is that it can be used in places where no other type can be installed. If you don't have central air, don't know how to install a split unit, and can't fit a window mount into any of your windows, you may decide that a mobile A/C is better than nothing.
It is just another of life's little imponderable mysteries that there is no such thing as a mobile A/C unit with two hoses, that would draw in outside air to dump the heat into, and not create an under-pressure in the house which sucks in more hot air from outside.
A. I. Breveleri
  • 14,190
  • 44
    Dual hose portable units do exist, though, and some sources say that people who can't fit any other type of air conditioner, should seek them out specifically to avoid the "negative pressure" issue – CJC Jun 13 '21 at 14:44
    The 2.4 million search results here: https://www.google.com/search?q=dual+hose+portable+air+conditioner suggest that the mystery is not only *ponderable*, but has been *considerably pondered*. Granted, these units generally start about $300, with the "mid-range" closer to $5-600 in the US. – Lawnmower Man Jun 14 '21 at 03:37
    Thank you. I was wrong. The true imponderable question is: given that two-hose models are available, why do one-hose models exist? – A. I. Breveleri Jun 15 '21 at 13:26
  • Dual hose units are common at higher capacities, basically nonexistent at lower capacities. There's obviously some sort of tradeoff but I don't know what it is. – Loren Pechtel Jun 16 '21 at 02:48
  • @A. I. Breveleri They exist because they are easier to install, most customers are not engineers, the Internet is filled with false or non existent information about the negatives of portable units, and the federal government in the US won't have efficiency requirements on portable units until the year 2025. – Alex Cannon Jun 19 '21 at 15:49
  • @Alex Cannon: I was about to respond but I was fatally distracted by your assertion that "the Internet is filled with...non existent information about the negatives..." – A. I. Breveleri Jun 20 '21 at 00:08
  • It is! Try searching for the negatives of portable air conditioners and when you think you're going to get something good you find that the web page completely ignores the fundamental flaw that they suck in cool indoor air to blow out the vent and it usually tells you the pros of a portable AC. I still like how it is worded even if it doesn't technically make sense. – Alex Cannon Jun 20 '21 at 04:32
Here is a shorter version of what the issues are regarding a single pipe or vent portable air conditioning unit. Issue 1 is the most important.
Issue 1: Does the exhaust vent (on a single vent unit) suck hot outdoor air back in the building? Yes it absolutely does. The negative effect of this depends on the difference between the indoor and outdoor air temperatures. It also depends on the air flow rate of the exhaust vent. If the outside temperature is 40C, and the temperature in the building is 39C, then the effect of sucking outdoor air in to the building is negligible. If the outside air is 40C, and the indoor air is 30C, then the effect of sucking 40C air in to the building through every crack and unsealed window will have a noticeable negative effect on cooling capacity. As the temperature difference increases, the efficiency and cooling capacity drops. Eventually it will reach a point where no matter how well insulated the building is, the effect of sucking in hot outside air counteracts the cold air coming out of the unit and it becomes impossible to cool the building any further.
It is possible to design a single vent unit to work better by reducing the air flow rate going out the vent pipe, and therefore increase the temperature of the hot side condenser radiator. Increasing the condenser temperature makes the unit less efficient, and it is still sucking in cooled indoor air to blow out the vent, just less.
If you have a single vent unit you can observe the hot air outside coming in to the building by cracking open a window and holding an unfolded napkin or thin tissue paper up to it. The air coming in will blow the paper away. Now turn off the portable unit and try it again.
I wonder if there are any single vent outdoor portable units that would blow cold air in to the window? It would sort of be the same situation in reverse.
Issue 2: Does the heat of the motor and compressor stay inside the house? No, it can be vented out the vent pipe. The indoor air that's sucked in passes by the motor and then it is blown out by the fan through the condenser radiator and out the pipe. The same for the compressor, but it is mostly cooled by the refrigerant and its heat is put in to the condenser radiator.
Is it impossible to engineer the compressor to be quiet enough for a bedroom? It could be done, but it would be too expensive. Scroll compressors are quieter. A compressor can be covered with insulation, and the chassis of the unit can be insulated inside too. This would make it so much bigger and expensive that it wouldn't be worth it.
Points 1 and 3 are legitimate. There are not many advantages to a single vent portable unit compared to a window unit. One advantage is it does circulate air, so bad smells and cigarette smoke will be sucked out the vent pipe. Another is not having to clean out the condenser radiator all the time if you have a cottonwood tree by your window. I know someone who reversed the fan or bought a window unit that way so he could clean the cotton wood seeds off of the condenser without taking it apart.
The first point is not true for a window AC nor a dual pipe portable unit! A window AC unit uses outside air to cool the condenser. There is not supposed to be any air flow between the inside and outside sections of a window AC unit.
Alex Cannon
  • 119
I own a single-hose AC; it does create the negative pressure, and it's noisy. I would like to add to what to others said about the noise. In principle, one can blow the outgoing cold air via a duct from the portable AC placed in room 1 into room 2, thus reducing the noise in room 2. In practice, I've tried to attach a 5" duct to my cheap single-hose unit via a DIY plywood plenum, but the inner blower in the unit could not sustain the pressure in the 5" duct. I could probably boost the flow with a separate in-duct blower.
If ducting the cold air directly from the output from the AC unit does not work, one can run the unit in room 1 and then duct the cooler air from room 1 into room 2 with a separate blower. This is what I have at the moment. It's better than no AC at all, and the noise is essentially gone.
I am yet to find a two-hose portable AC that would reliably separate the outside air path from the inside air path, without creating negative pressure. If anyone knows of such a system, please share. Maybe such units are costly to produce, and with that money it's easier to install a regular split unit.