I am trying to wire an outbuilding with the equivalent of a 15-A circuit from 300-400 ft (90 - 120 m) away.
What gauge wire do I need? Also, does the full length need to be a constant gauge or can the thickness of the wire taper at it approaches the load? For example, 100 ft (30 m) of 10-gauge wire from the source leading to 100 ft 12-gauge leading to 100 ft 14-gauge, etc.
Peter Mortensen
  • 329
gothicsurf
  • 51
  • How much voltage drop are you willing to accept at the remote end when a full 15 A is drawn? What is the source voltage? – jonk Jul 04 '21 at 05:07
  • Can you buy tapered wire? Ie starts one size and finishes another? – Solar Mike Jul 04 '21 at 05:44
    The 15 A requirement isn't sufficient to determine what's appropriate -- at least in the US. A difference is made between feeder circuits and branch circuits. If this is a single 15 A circuit with the only breaker at the home site then it is a branch circuit. If, on the other hand, this is has a separate sub-panel, then it is a feeder circuit and the rules change. If there are animals, like horses or milk cows involved with four feet on the ground, then again different rules apply. So is this a technical "copper wire" question only? Or is safety involved? – jonk Jul 04 '21 at 05:50
    This should be migrated to diy.stackexchange. The short answer is, use a wire size that drops less than 6V total (3V each leg) at max current, or whatever your local electrical codes require. Not sure? Consult an electrician. –  Jul 04 '21 at 06:17
    Tapering the wire does not make sense and is not common practice. – mkeith Jul 04 '21 at 07:26
    You don't say where you are or your system voltage, but if it's a 110V circuit you might consider transmitting 220V and fitting a 220:110V transformer at the far end. The savings in cable might just about pay for the transformer. – user_1818839 Jul 04 '21 at 11:36
    @user_1818839 Or even kick it up to 480V. It's just jumping the same transformer differently. – Harper - Reinstate Monica Jul 04 '21 at 14:09
  • What loads are you actually trying to run at the outbuilding? Lights? Small equipment (battery charger, fencer, or so on)? Power tools? Motors? – ThreePhaseEel Jul 04 '21 at 15:36
  • To calculate you need actual maximum load, minimum acceptable voltage under load, initial measured voltage, and the actual length. – NoSparksPlease Jul 05 '21 at 03:34
  • @NoSparksPlease A 15A circuit tells you what the actual maximum load is. The maximum acceptable voltage drop is 3% (per NEC recommendations), the input voltage is dictated by the utility and is guaranteed to be within a known range. OP has told us how long the run is - we have everything we need to provide an answer. – J... Jul 05 '21 at 13:13
  • @J... no, they haven't told us where they are. The top answer assumes a location where aluminium wiring is available for domestic jobs, but the US isn't the only country that measures in feet (in practice). The biggest hint that they probably are in or near the US comes from the use of wire gauge, but it is only a hint – Chris H Jul 05 '21 at 14:04
  • @ChrisH 15A circuit, AWG, feet... I mean, if it looks like a duck... If you're holding out hope that Americans, particularly on this stack, are going to realize that other countries exist in the world you'll be waiting a long time. – J... Jul 05 '21 at 14:13
  • @J... "gauge" not "AWG", and feet/inches are common here in the UK (to the extent that I tend to buy my measuring kit in Europe to avoid having that useless scale). We'd normally use 5/16/30A circuits, but 15A circuits were common when we had fuses instead of MCBs. Your guess is probably right, but it's still a guess. – Chris H Jul 05 '21 at 14:19
  • @ChrisH At the same time, anyone in the UK rich enough to own 400ft of back garden isn't bothering to DIY their own electrics... – J... Jul 05 '21 at 14:23
  • @J... you'd be surprised, though I've only got <1/10th of that – Chris H Jul 05 '21 at 15:50
  • @J... 15A tells me to expect he probably knows that is the smallest US circuit size, but didn't exclude other possibilities including 240v or 230v outside of North America. He may be expecting to power a specific piece of equipment at lower draw. According to ANSI C84.1 the guaranteed Range B voltage supplied by utility could be as low as 110/220v. Voltage drop of 3% is only part of the NEC recommendation, and is only a recommendation, and NEMA design tolerance is +/-10% of 115/230v. The difference between 300 and 400ft could easily cause one wire size difference. – NoSparksPlease Jul 05 '21 at 17:20
  • The idea that tapering of an electrical conductor could achieve a beneficial result springs from analogy with water flow in open aqueducts and closed pipes. Imagine a farm is right at the base of a mesa rising steeply up to a plateau which gradually slopes up to a spring. To supply the farm from this spring, it would make sense to start from the spring with a larger pipe to the edge and transition to a smaller pipe down the steep slope. The situation is different for electric current in a wire. – Jim Stewart Jul 05 '21 at 17:30
6 Answers6
14
You'd use aluminum
That is the main takeaway. Continuing to "bump" copper wire larger and larger and larger is just crazy. Because there are 2 costs to wire: the insulation and jacketing which is complicated stuff, especially for outdoor wire; and the metal of the wire. Above about #12, the biggest part of wire cost becomes the metal, and that's where aluminum's 12:1 cost advantage over copper really comes into play.
You can buy #2 aluminum (90A nominal) for the same price as #10 copper (30A nominal).
In 120V-land it would be wise to bring a fourth conductor
It will cost 33% more at most, but give 4 times the practical power. It will allow you to bring over both poles (phases) of 120V power, giving 240V also. Instead of 15A@120V you have 30A@240V. Keeping the neutral wire allows you to place loads on either phase, and if you balance them, you could run four 15A@120V loads for the same voltage drop as 1.
Alternately, use transformers
If aluminum wire doesn't bring price into line, you would be better off using 2 transformers to step up the voltage to the highest the wires will permit for the long-distance transmission. For instance, bumping 120V to 600V (5x) will result in 25x improvement on voltage drop, i.e. 1/25 the conductor cross section will provide the same drop.
Also, because you are carrying only one phase, you only need 2 conductors + safety ground. That allows you to derive 120V and 240V at the far end, since the transformer can be tapped for that.
Crunch the numbers, sometimes this makes sense.
And you bet you can taper.
You'll have to, because the switches, receptacles and breakers intended for 15-20A circuits will not take #2 or #4 wire, and many are not rated for aluminum either. So you will need to splice down to smaller wires as appropriate. If you are computing voltage drop, you need to then compute voltage drop on each segment individually, although very short runs under 10' aren't worth calculating.
For splices up to #6 wire size, use "MAC Block Connectors". Above that you need to move into the more expensive Polaris connectors.
  • By “above that” do you mean larger diameter (smaller number) or vice versus? – Tim Jul 04 '21 at 17:26
    If one is using isolating transformers at either end of a run, and nothing connects to the loop between them other than the transformers themselves, would one need a safety ground connection between them? I would think some form of device to pull the loop *weakly* toward a ground-referenced potential at the source and sense the current required to do so would be cheaper and more effective at detecting faults. – supercat Jul 04 '21 at 19:05
    @supercat yes, I've always wondered that, but haven't found any clear references. – Harper - Reinstate Monica Jul 04 '21 at 19:26
  • Is aluminum wire available in individual wires that can be pulled through conduit? (My house is wired with aluminum, but it is all in non-metalic sheathed multi-conductor cables. – Jim Stewart Jul 04 '21 at 21:04
  • Re *"result in 25x improvement on voltage drop"*: Don't you mean *"result in 25x improvement in power loss"* (or similar)? – Peter Mortensen Jul 05 '21 at 06:56
  • Are you sure it's 30A@240V? I think it should be 30A@120V (if used split-phase) or 15A@240V (if used together) – user253751 Jul 05 '21 at 10:50
  • @JimStewart Of course - aluminum wire is available in all sizes and is particularly common in larger gauges and as service feeders for the cost reasons here. – J... Jul 05 '21 at 12:29
  • Is aluminum wire available in individual wires in solid AWG 14, 12, and 10 THHN? – Jim Stewart Jul 05 '21 at 12:34
    @JimStewart Not easily, but yes - it's the 21st century, you can get anything you want if you look hard enough, but no those gauges of aluminum are not commonly used, nor are they being suggested for use here, so I don't see what the question is getting at. Aluminum stops being commonly available below 6AWG or 8AWG. – J... Jul 05 '21 at 12:39
    @JimStewart Also note that 14AWG aluminum is too small for even a 15A branch circuit, so you're not likely to find that size of wire for any electrical use as there are generally no common circuits with a low enough ampacity for such a wire to be usable. – J... Jul 05 '21 at 12:51
Answering one part of your question:
... can the thickness of the wire taper at it approaches the load?
The same current runs the full length of the wire. If you had tapered wire it wouldn't matter which way around the tapered end was connected. You would just get most of the voltage drop at the end with the smaller wire gauge. The load end voltage would be the same no matter which end was fatter.
You would only reduce wire gauge if the cable was powering loads along its length - say various houses on a street. The further down the street you go the less current will be required beyond that point and a smaller wire gauge would suffice.
schematic
Figure 1. The voltage drop will be the same regardless of the order of the resistances in the circuit.
Transistor
  • 864
  • The voltage drop is equal to the current multiplied by the resistance of the wire (V=IR). If you have fat wire for most of the run, and thin wire for some of it, the resistance will be lower, so the voltage drop *will* be lower for the same current. (Of course, this applies whether the thinner wire is at the start middle or end of the run.) – psmears Jul 05 '21 at 11:53
  • That's what I said. Regarding your comment, "*If you have fat wire for most of the run, and thin wire for some of it, the resistance will be lower **[than if you used thin wire for the whole run]**, so the voltage drop will be lower for the same current.*" – Transistor Jul 06 '21 at 15:46
  • Your answer currently says "If you had tapered wire ... the load end voltage would be the same." Having read it again I can see what you actually mean, but it's ambiguous - it sounds like you're saying "the same \[as if you had the same thickness wire all the way]". Would be worth clarifying. – psmears Jul 06 '21 at 21:36
4 gauge aluminum. Or larger gauge, if local odd market forces make some larger size less expensive (i.e. 2-2-2-4 "mobile home feeder cable" is sometimes stupid cheap due to volume.)
Or, a pair of transformers and smaller wire (but you are probably not quite at a distance where that pays off.)
  • Can you pull 2-2-2-4 mobil home feeder cable through conduit? The new installations of underground distribution and service I see around here are in heat bendable conduit (PVC?). Is that what you would recommend for this case? – Jim Stewart Jul 06 '21 at 16:17
As noted in other answers, going with large aluminum wires can make a lot of sense compared with smaller, "just big enough" copper wires. That takes care of the voltage drop. But two more things to consider:
Conduit vs. Cable
Inside buildings we (most of us DIY that is, as opposed to professionals) normally think "cable". But you can't use the usual cable (NM, aka Romex) for connections between buildings. You have to use more expensive cable rated for buried (and wet) locations. Plus once you are burying cable, you have to bury it deep to protect it.
The alternative is conduit. With conduit, you don't need to dig as deep (varies depending on the type of conduit), and you have the possibility to upgrade by adding wires (if you originally ran 3 (hot/neutral/ground), you can add a 4th (2nd hot for 240V)) or upgrading wires (replace 12 AWG with 10 AWG, or whatever). So running conduit may give you more options later, if you don't make exactly the "right" choice now for wire size.
Subpanel
It sounds like you want just one circuit - 15A for lights/convenience receptacles. That may be fine now. But what if you later want to have a separate circuit for high power tools? Or an electric vehicle charger? Or HVAC? If you use large enough wires now (e.g., 2-2-2-4 aluminum as suggested by others, based on pricing) or can upgrade later via conduit, then you have the option of switching from a single circuit to a subpanel. That will allow unlimited possibilities, up to the total power available.
There are some additional requirements, particularly in terms of separate grounding (typically two ground rods) at the outbuilding, but the costs will likely be less (especially with a 300' run) than adding an additional separate circuit the full distance. The "taper" issue goes away - you need to use the "big" wires the entire distance, including the last foot, because you are relying on the full capacity available end-to-end, but the connections are not a problem because the breaker in the main panel and the subpanel will both be able to handle the large wire size and aluminum (unlike a typical 15A receptacle that can't handle either the large size or aluminum).
There are three things you have to take into account, and not necessarily in this order.
  1. Heat due to I²R
    Every part of the wire has to be of sufficient gauge so as not to overheat with the current. If you wire some parts of the run in heavier gauge, you gain no benefit, it won't stop the thinner parts overheating.
  2. Voltage drop due to IR
    The total run has to have sufficiently low resistance so that you don't have an excessive voltage drop at the end. If you wire some parts of the run in heavier gauge wire, this will reduce the total voltage drop, so is beneficial. If you are buying new wire, then you get the lowest voltage drop per cost by using the same gauge for the whole run. If you happen to have some heavy gauge wire for free, then go ahead and use it for part of the run.
  3. Local regulations
    These vary with locale, purpose, and from decade to decade. Install something non-conforming, and it would likely invalidate your insurance, which could make for a very expensive problem if you need to claim, even for something unrelated to your outbuilding.
Pete Kirkham
  • 195
Neil_UK
  • 584
It's all about resistance and it depends on the voltage drop you can withstand. If you are starting devices that have a large starting current like a compressor motor, you'll need larger gauge wire as the motor may stall while starting. The following graph will give you an idea of voltage drop versus wire diameter. Conductor resistivity is for annealed copper wire.