18
I'm located in France.
For a house (built over 30 years ago) I have to pull new cables through the garden (about 20 m - 30 m). The cable has to avoid certain trees, bushes, obstacles and arrive at a certain point.
Earth is rather hard (clay) and I considered renting a tiny soil trencher.
There are existing electricity cables in conduits, telephone cables in a conduit and water pipes (non metal).
Electricity counter is at the border of the garden. Water counter a few hundred meters away near the public street. The house is accessible via a private street with right of use).
The conduits are over 30 years old and broken and destroyed. The service trying to add a fiber connection to the house tried to use the existing phone line conduit, just to find out, that the probe wire (don't know the correct term) went in 5 meters and came then out in the the garden. So it seems the conduit is no more in a decent state.
I don't have any confidence that the previous owner respected the 'officially' required depths and that he used marker tapes, which should normally be placed a few centimeters above the actual cables / pipes to avoid digging in to them by accident.
I know where each one arrives at the house (so I know the starting point), but I do not know where exactly they are going.
Is there any equipment (to buy / to rent), or are there any specialists who can help locating the existing wires / pipes?
Are metal detectors good enough for thin electricity cables / phone wires? How can I detect water pipes without metal?
Are there other tricks and recommendations of how to avoid breaking the existing 'connections'?
gelonida
  • 311
    The _Dig Safe_ service that @manassehkatz-Moving2Codidact is referring to is great for identifying underground utilities that the utilities know about. They don't track the ones that below to the residence owner. But, they will help you figure out where the ones that terminate in your house. – Flydog57 Jul 07 '21 at 03:57
France founded a centralized bureau to manage nation-wide location of public utilities in 2011, so you're in luck. You can find them here : Téléservice "réseaux-et-canalisations"
Vous êtes une collectivité territoriale, un maître d’ouvrage, un maître d'œuvre, un exploitant de réseaux, une entreprise du bâtiment ou de travaux publics, un agriculteur, un particulier… et vous avez des projets de travaux de terrassement, de sondage, de génie agricole…, le téléservice reseaux-et-canalisations.gouv.fr vous permet alors d’identifier gratuitement les exploitants de réseaux concernés par vos travaux et auprès desquels vous devez déclarer vos travaux.
You probably want the section for private individuals : Particulier.
The site above services all types of clients, including contractors, commercial, etc. It would seem that for private individuals you ultimately end up directed here : https://www.declarermonchantier.fr/
Note that this is not an optional step - if you dig and you cause damage you will be liable. The location service is free, so don't try to DIY this.
Attention : L’absence de déclaration fait courir des risques à vous-même, à votre entourage et à l’environnement. En cas de manquement, des sanctions sont prévues.
This service will not locate any private cables, pipes, conduit, etc, that were installed by previous owners, however. These would be connections from your main residence to things like pools, sheds, outdoor lights, or other things that are entirely your property - those would be your responsibility to locate.
The service will locate public utilities, however; electricity, gas, and water lines upstream of their respective meters, telephone and fiber before the demarc, sewer lines, etc, that are the property of the public utility.
J...
  • 1,383
    Thanks a lot this is very good to know. What I'm worried most about are however the pipes and conduits installed by the previous owner. I will still contact this service to be sure, there are no other connections, that I should be aware of. – gelonida Jul 07 '21 at 21:46
  • contacting the service might also help me to locate the 'entry points' of phone, electricity and water – gelonida Jul 07 '21 at 22:16
    @gelonida They will do more than help - they will come to your property and they will mark the locations of the phone, electricity, water, etc, in your yard. These will definitely not have been installed by the previous owner because they belong to the public utility. Anything the previous owner installed would be things *leaving* your house and going out to endpoints in the yard. Do you know what is in the conduits the previous owner installed? How do you know he installed them? Do you know where they go? It should be obvious if you have things in your back yard that require power... – J... Jul 07 '21 at 22:21
  • Yep. I will definitely contact them. Considering the internal lines. I know of electricity and water going from the house to a shed and to the garage and electricity only to the pump of a well. I also know that there are various water pipes going from the well to some spots for irrigation. – gelonida Jul 07 '21 at 22:24
  • @gelonida Ah, ok - those they will not locate for you, only the public infrastructure, but you *really* don't want to damage public utilities so it's very helpful to at least have those marked out. – J... Jul 07 '21 at 22:33
    The link, that you posted leads ultimately to https://www.declarermonchantier.fr/ This is where I declared the works. Let's see how it goes. Thanks again. – gelonida Jul 09 '21 at 09:29
  • @gelonida Thanks, that's good to know. I've updated the answer to include that link. – J... Jul 09 '21 at 12:43
  • Thanks for adding the link. Just for information: I made the declaration. which results in the creation of four documents (in my case) for four different authorities. I already got the first answer of one authority that none of their networks is close to my place (et least over 50 m away) Waiting for the other answers. – gelonida Jul 09 '21 at 12:53
  • @gelonida Yes, that's pretty normal. I'm in Canada and it works the same way here - the request goes out to all utilities and they independently must make inspections and report back. I just did this a month ago, actually, and it took 2-3 weeks for all of the reports to come in - that's longer than typical, but covid has left some backlog, it would seem. – J... Jul 09 '21 at 13:03
  • Created my own answer where I keep track of progress ( https://diy.stackexchange.com/a/228785/129268 ) Rereading your answer I'm worried that the final feedback might help me less than anticipated as the water and electricity counters are not in the house but at the border or even further away of/from the garden. – gelonida Jul 09 '21 at 13:14
16
In most parts of the world, official utility connections will be marked if you contact a "call before you dig" number that coordinates contacting all the utilities that might have buried service lines under your lawn/garden.
I don't know if France has that, or not.
Those services do NOT mark/locate private utility lines (i.e. if you have a line running from your house to an outbuilding/shed/garage.) They only mark service lines and underground distribution lines if they pass through your property.
There are locator services that can be contracted with (possibly the very same ones hired by the utilities in the above scenario) and there are also tools that can typically be rented through a tool rental store/service.
Standard "metal detectors" do not normally work well, you want a specialist tool for locating wires/cables/pipes.
    *Standard "metal detectors" do not normally work well* They used to work better, but now water is often PVC and electric, while still always metal wires, can be in PVC as well. – manassehkatz-Moving 2 Codidact Jul 06 '21 at 19:36
    Most "metal detectors" also lack the depth ability that proper locaters have. Great for finding metal trash at the beach an inch or two down in the belief that you'll find lots of lost jewelry, not so great for finding anything 12"/30 cm or more deep. – Ecnerwal Jul 06 '21 at 19:39
    Just a Suggestion: When you put in the new cable put it in PVC condulet. Be sure it is large enough with a bit of room to spare. It is not that expensive. Also route it around the edge of the garden where there is less chance of digging. When the utility sends a tec out, ask if he can do the other cables and that you are willing to pay cash. – Gil Jul 06 '21 at 19:51
  • "In most parts of the world" yet not France? – CGCampbell Jul 07 '21 at 16:13
    You can detect any underground lines that you can run a current through using the right equipment. HDPE piping is supposed to have a tracer wire installed with it since its not metallic so that it can be traced. Even knowing where things are, you can still damage lines with a shovel, especially if they are not in PVC. – rtaft Jul 07 '21 at 17:44
    @CGCampbell In most parts of the world and (as clearly stated) I did not know if France did, or not. According to *J...'s* answer, they do, in fact have that service. I try not to assume that what I know locally applies to any random location I'm not familiar with the details for. – Ecnerwal Jul 07 '21 at 18:19
  • @rtaft - "is supposed to" >> "probably doesn't" – Vikki Jul 07 '21 at 19:48
    @Vikki Oh I know, my gas line didn't have a tracer, thought I was clear of where it would be and hit it with a backhoe, it wasn't that deep or with the electrical. It didn't rupture thankfully. – rtaft Jul 07 '21 at 21:19
  • Thanks that's good to know. The exact contact address will as you stated depend on the country. But I didn't even think that something like this should exist in most countries. (It's the first time I have to deal with something like this) – gelonida Jul 07 '21 at 22:12
13
There do exist instruments for locating buried utilities. Vivax, Radiodetection, Leica, and Greenlee/Textron are names of manufacturers I'm aware of. This equipment operates on the principle of connecting a transmitter to a conductor (a metallic wire or pipe, or a wire buried alongside plastic pipe) and using a receiver to detect the electric fields radiating from that conductor.
I recently noticed one such kit offered for rent at an irrigation supply specialty store -- if ordinary tool rental stores near you don't offer a locator, you might inquire at supply houses for irrigation, plumbing, or electrical contractors.
If you're unable to get a utility operator to mark the lines (perhaps because they're private lines) and unable to perform locating on your own, the next best thing is to make an educated guess about where the buried lines are likely to be. You can then arrange the trenching project to avoid those zones, work shallow in those zones, or hand-dig the trench for a meter or two where you anticipate a crossing. When hand digging, orient the blade of the shovel so that it is parallel to the suspected utility. This minimizes the probability that you'll strike and slice through it, especially for small cables like telephone, TV, or fiber optic.
You know where the buried utilities connect at the house. Do a little more work to figure out where they connect out in the garden, street/alley, or neighboring properties. There will be tell-tale signs: an access vault for a water meter or shutoff valve, a splicing point for electrical or other cables, and so on. One can't be certain that the services to the house run in a straight line across the garden, but such is common.
Greg Hill
  • 27,924
    Vacuum/compressed-air excavation and water/slurry are good excavation techniques for not damaging unknown utilities. Dislodge dirt with an air-jet or stream of water, remove it with a vacuum at the working point, or a "mud pump" at the low point of the trench, respectively. Don't get too high-pressure on the water (*i.e.* pressure washers) or you may damage the cables after all. Large truck-vacuum services can be hired for the job, normally. DIY tends to be a rather smaller undertaking with a wet-dry shop-vac. – Ecnerwal Jul 06 '21 at 21:38
  • I don't know what france is like, but I'm pretty sure here in the UK electric service cables are usually just jointed underground onto the main cable down the street without anything visible on the surface. – Peter Green Jul 07 '21 at 01:21
  • Yeah will try to find tell tale signs for the end points. Will be tricky though. The water counter is several hundred meters away from the actual property. Electricity is probably coming from an overland line near the border of the property and phone line might be near as well. But there will be also power lines and water lines from the house to a shed and a garage which were added years after the initial construction – gelonida Jul 07 '21 at 21:58
  • So if I understand well, such equipment will not work for water pipes, that are not made of metal. Will check, now that I know that the concept of tracing wires exist, whether these plastic pipes have a tracing wire added. Contrary to electircity and phone line the water pipes don't seem to be in a conduit – gelonida Jul 07 '21 at 22:15
  • @gelonida That's right, locating equipment works only with things that conduct electric current -- not plastic pipes. You can take a calculated risk with your own private wires/pipes: find the disconnect/shutoff for each, confirm it works, then start digging. Plan on making repairs to any of your private wires/pipes if you should happen to damage one of them. – Greg Hill Jul 08 '21 at 03:02
  • @Ecnerwal hydro-excavation or water-digging is worthy of an answer by itself. Its an excellent way of moving material, specially if it has embedded rock to turn a shovel. – Criggie Jul 08 '21 at 19:58
    @Criggie There's an answer I wrote about DIY hydro/air/vacuum excavation [there](https://diy.stackexchange.com/a/221712/45928). – Greg Hill Jul 08 '21 at 20:13
  • Does it really make sense to suggest OP _buy_ this stuff, rather than find a contractor who does this to do the scanning for OP? – einpoklum Jul 09 '21 at 20:17
If the natural ground is very hard, you can try an archaeological approach.
Remove the top soil in a wider strip than you actually need to be able to detect different colours of the ground. If the top soil is deep, then remove it in 5cm layers until you hit the natural clay. Change in colour from the top soil or natural clay indicates that something was dug here before.
To make it easier for the next cable, put yours in a pipe (conduit) with some wire running through it so that you don't have to dig up the garden next time. The next cable than then just be pulled through the pipe by the wires.
Surt
  • 171
  • This sounds like too much effort, unless you have a class full of archeology students with a lot of spare time. :-( – einpoklum Jul 09 '21 at 20:18
I will enhance this answer over time to indicate what helped me and how I solved the issue.
There's multiple good answers each addressing another aspect of my question, so I had difficulties marking one answer as 'the correct' answer.
So far:
How to obtain information about existing cables and tubes for France:
Thanks to J...'s answer I went to www.reseaux-et-canalisations.ineris.fr which ultimately led to following link https://www.declarermonchantier.fr/
I created an account and declared that I want to do works, which resulted in four documents that were sent to four different potentially concerned authorities.
Will now see when and how I receive the information about the official pipes and cables, that are in my garden.
Within the hour I already got a first answer of one authority stating, that none of their cables is 50m near my garden.
Having reread J...'s answer
I'm not sure that the feedback will help in my particular case as the electric counter is at the border of the garden and the water counter even a few hundred meters down the street away from the garden.
For others who have the counters in their house, this will however be very useful.
2021-07-13: Enedis seems to provide information of their wires up to the electricity counter Just got feedback from Enedis concerning electricity. Information goes up to the counter. In my case I'm out of luck as the counter is at the border of the garden.
gelonida
  • 311
  • The proper thing to do here at [diy.se], would be to click the check mark next to J...'s answer - that's all it takes to let people know you found it to be the _most_ useful answer and have followed the advice there. It's also appropriate to click the up-arrow next to any and all answers that you found helpful. – FreeMan Jul 09 '21 at 12:08
    @freeman This is what I would normally do. However, J... s answer covers only one part of my question. (How to locate 'official' power / water phone lines). The answer does not address the aspect of how to locate lines that were placed by the previous owner. For this Greg Hill's answer is more relevant. As I don't know how to mark multiple answers as right anwsers I upvoted and commented all answers that were helpful to me and I thought, that I will add my own answer, that I will enhance over time with all the contributions of the others. – gelonida Jul 09 '21 at 12:34
  • @FreeMan I intend to enhance my own answer over time (with feedback of how things went, which equipment I finally used or how I finally solved the issue, but only after having validated the various suggestions for my special case. I'm open to suggestions how to better handle such a situation. – gelonida Jul 09 '21 at 12:36
  • That sounds reasonable. You may want to mention that in your answer so others will know, as well. Also, you cannot accept 2 answers, so up votes are the best you can do. – FreeMan Jul 09 '21 at 12:53
  • @FreeMan Updated my answer. Hope things are clearer now – gelonida Jul 09 '21 at 13:01
  • "water counter even a few hundred meters down the street away from the garden" - Maybe it's different in France, but I'm sure *you* don't own the pipes under the public streets if your meter is really that far away. What they will locate is pipes/cables/etc that *belong to the utility*. In North America the meter generally demarcates the ownership change where the input side is owned by the utility and the output side owned by the homeowner. This may be different where you are, I'm not sure. – J... Jul 09 '21 at 13:21
  • The water counter is at the public street, the rest of the pipes probably going along the private street with right to use (over 30 years old) that I need to access the house, I am curious what information I'll finally get. Everything is still possible. – gelonida Jul 09 '21 at 13:38
    @J... at least in the U.K. (where it’s still pretty common to not have a meter) the demarcation tends to either be the property boundary, or the output of the first external stopcock inside your property (if you have one). So definitely there is variation. – Tim Jul 09 '21 at 16:33
  • in my case Enedis provides information for electricity just till the Electric counter. I just got a pdf which is not that precise. but gives me a rough idea. – gelonida Jul 13 '21 at 12:02