I am looking at the electrics in a house that a friend just bought, and it has one of the problematic "Stablok" Federal Pacific panels. Watching this video, made by a supposed master electrician who I find to generally be pretty good:
https://www.youtube.com/watch?v=tX-Ze8KhN10&t=540s
He talks about ways to determine if a Federal Pacific panel is really dangerous. This includes pulling the breakers to look for signs of overheating damage to the breakers and/or the bus bars.
But the part that gave me pause was where he talks about testing the actual breakers, to see if they trip properly when shorted. He first says to turn off a breaker, then short neutral to hot somewhere on the circuit, and then see if the breaker allows itself to be turned back on; seems reasonable. He then talks about shorting neutral to hot on a live circuit, disclaiming that you shouldn't try this unless you're very experienced.
I'm curious was the wiser people here think of these suggestions. To me, shorting a live circuit is crazy, mainly because you could cause overheating and/or wiring damage somewhere else (perhaps hidden) in the circuit, and never know it. Seems like even the technique of shorting a dead circuit and seeing if you can turn the breaker on, is suspect if you do it using the circuits conductors in the house - for the same reason.
But what about this? Turn off a breaker, disconnect its hot lead, and run a short jumper from the hot terminal to the neutral bar; then see if the breaker will turn on. This eliminates the possibility of doing any damage to installed wiring.
RustyShackleford
  • 2,411
    This question has a good write-up of the issues with the Stab-Lok system. TL;DR, the breakers can jam in the ON position, the breakers can fail to trip at the proper limits, the bus bars inside the panel have undersized components, and much more! I only know what I've read on this site, but it sounds like Stab-Look is widely considered something that needs replacing as soon as possible https://diy.stackexchange.com/questions/62320/should-all-federal-pacific-panels-be-replaced – maples Feb 20 '22 at 17:58
    At least one of those possible failures means that when you flip the breaker on to "test" it, **it might not be able to turn off** and something else will have to break the circuit, possibly your test wire exploding, or the bus bar connections catching fire. – maples Feb 20 '22 at 18:00
    I think you mean he's a pretty good *showman*. Because that's what it takes to succeed on Youtube. **Youtube does not select for expertise. It selects for being good at video production, business and "playing the Youtube game"**. Which means the videos can be as bad as the comments. This guy is better than any other electrician at gaming the Youtube search engine. That's hardly a recommendation. I can count *reliably accurate* Youtubers on the fingers of one hand. (Technology Connections and BlancoLirio, and *maybe* Drach.) – Harper - Reinstate Monica Feb 20 '22 at 18:17
  • You mentioned shorting neutral to ground. This will only affect a GFCI breaker. An ordinary breaker will ignore that. Was that a typo? – DoxyLover Feb 20 '22 at 18:20
    Think this through before committing an act of sheer idiocy because some dude on YouTube (that won't be buying your friend a replacement house after you burn their new house down by following his "advice" to test a freaking Stablok by shorting it) said so. Stabloks **fail to open when overloaded.** So if you short it and it fails to open, you're gong to watch stuff catch on fire, backed by the full power of the electric company. It needs to be replaced ASAP, and not overloaded in the meantime. – Ecnerwal Feb 20 '22 at 19:18
    Rusty, Rusty, Rusty, You've been around for a long time and have asked a lot of questions about electrical stuff. Heed the warnings of the pros here and don't mess with the panel. – JACK Feb 20 '22 at 19:52
    Intentionally shorting live conductors in a house is idiotic. If you want to play electrical engineer, replace the panel, take the old panel and breakers to an engineer and let them play with it in a controlled environment. Every single knowledgeable person I’ve spoken to, both here on the internet and two working electricians and an electrical inspector where I live have all said these panels and breakers are not reliable and should be replaced sooner rather than later. – RibaldEddie Feb 20 '22 at 20:17
    Testing a breaker installed in your house by intentionally shorting it out is a Bad Idea™. It's an _Especially Bad Idea™_ if it's an FPE panel. – FreeMan Feb 21 '22 at 14:22
    You guys have all been pretty clear on this; I tend to agree, as do a host of people commenting on the youtube video. I'd like them to replace the panel. Unfortunately, their attitude is that the house hasn't burned down in the 30+ it's stood. Which to me, makes about as much sense as saying "if I had not worn my seatbelt a single day of my life, I would not have sustained any injury, having never been in a serious car crash; so why should I wear it now ?" – RustyShackleford Feb 22 '22 at 03:07
Let me start by saying after replacing failed stablock/ Federated(FPE) panels in the US, I will not work on them with the exception of replacement.
Now you are considering creating a short on a breaker type known to cause catastrophic failures and have the panel go up in smoke. I would think about that first. Not only do the breakers fail to trip or open with an over current event, the “stab” design is also a failure point. Messing with a stablock panel is not wise, even for a pro. After they are replaced, the connection can still fail. This is why the design was abandoned.
I became very anti stablock after work both failure’s and service calls.
For grins I actually tested several panels worth (not the panels that burned up) with no visible damage. Quite a few of these breakers did not open at 500% until they started smoking (I was using a breaker test bed)
To your question
Have I ever shorted a line to test? Well yes I have a plug in unit that basically dose this and I would never use it on an FPE panel using the homes wiring, it could trip late after overheating the insulation and later finish off the job with a fire.
My professional opinion is it was irresponsible and foolish to create the video, but there are all kinds of Youtube videos on how to do almost anyything, safe or not. There were supposedly videos on eating tide pods, which I would also not recommend.
Really I would not do anything with a stablock other than recommended replacement.
    I fully endorse this answer. Ed Beal conforms with the majority of experts (and my view as well). But if you saw my comment to the question, Ed proves my point. This accurate, reliable viewpoint is not presented with the same "dazzle" as the *entirely wrong* Youtube guy with his good lighting and clickbait thumbnails. I call this Walter Cronkite Effect. Time was, TV was extremely hard to make (high barrier of entry) and required huge organizations, so anyone who made it onto TV was well-vetted. If Walter Cronkite said it, you believed it. *That is no longer valid*. – Harper - Reinstate Monica Feb 20 '22 at 18:36
    This answer totally sums up the issue. There's a subdivision close by me that utilized these panels and breakers. They have been a nightmare. Inspectors won't issues permits for additions or adding load unless the panels are changed out as part of the work. – JACK Feb 20 '22 at 20:39
    @jack I think these should have been recalled. but it got two political or that is my belief. Back in the late 90’s A home inspector stated they were illegal as part of a buyers inspection. the seller actually won a judgement because they were never recalled (the inspectors inaccurate statement that they were illegal caused the loss of a sale) inspectors can prevent modifications so they get replaced and I agree that is one legal way to get rid of them. So anyone out there doing inspections just make strong recommendations to upgrade and link the data online most that read it will update ASAP – Ed Beal Feb 21 '22 at 00:58
  • IMO this doesn't really answer the question. If those FPE breakers are so unsafe, then using them for normal household devices seems just as ill-adviced as a deliberate short. The more interesting question is whether a short circuit is a suitable way to make sure a breaker (that you reckon to be ok) actually does break as it should then. And this seems a _sensible_ thing to check IMO, though of course one should always ensure to terminate the short after half a second if the breaker hasn't done it by then. – leftaroundabout Feb 21 '22 at 16:21
  • ...An appropriate way would be to connect a thick graphite strip to neutral and touch it with a small ceramically isolated tungsten probe connected to live, making sure to pull the probe back again quickly regardless of what happens to minimise arcing. – leftaroundabout Feb 21 '22 at 16:27
  • @leftaroundabout, I do not think there is an appropriate way to test these in premises wiring. I do encourage the 12’ drop test or that is how far the drop is at my recycling center. – Ed Beal Feb 21 '22 at 16:59
  • @EdBeal well, again, if you don't trust the wiring to hold up to a controlled (albeit crude) test, why would you trust it at all? If the wiring doesn't hold up to currents that don't trip the breaker, then the breaker is useless (regardless of whether it's actually the breaker that's faulty, or the wiring itself). Better to set the house on fire whilst there's a professional around and everyone's awake. – leftaroundabout Feb 21 '22 at 17:18
    @leftaroundabout We don't trust it at all. Which is why we recommend replacement of the panels and breakers. – JACK Feb 21 '22 at 17:33
  • @leftaroundabout I trust the wire I do not trust the stablock breakers or the buss, I have seen 1/2 a panel every wire that crossed another melt down from a toaster, this was a legal load but the wiring may have already have had damage and now every breaker on that side of the panel was tested until the fuse on the service pole blew, everything inside the panel was damaged from the heat everything outside the panel was fine . 4 breakers did not function. Your advice wold be similar to: I have the covid vax so it’s ok to get infected since I work at a hospital. I am a pro and I would not do it – Ed Beal Feb 21 '22 at 17:42
  • Fair enough, but then the answer should start with the _comment_ that any house with Stablock be evacuated until they're replaced, and then proceed to answer in the context of a breaker that actually has a good probability of tripping as per spec. (And FWIW, regarding your analogy: here in Norway most people _do_ get Covid now, precisely because the combination of vaccine and less harmful omicron variant has made it safe enough. It's nice to avoid it, but not worth the continued restrictions, and in fact it's better to get it sooner than later when the vaccine protection will be weaker.) – leftaroundabout Feb 21 '22 at 17:54
  • @leftaroundabout if you read my answer it states the very first thing I won’t work on them and the second is about catastrophic failures, it’s hard to get any stronger than that when the actual question is is it safe to test them by shorting them out. I did not mention which strain BTW and delta is out there killing folks still today I think the medical center I work in has almost 90 inpatients and 34% were break through or they had the vax and still got it , to get hospitalized for days usually refers to life threatening or worse. – Ed Beal Feb 21 '22 at 20:14
He first says to turn off a breaker, then short neutral to ground somewhere on the circuit, and then see if the breaker allows itself to be turned back on; seems reasonable.
This not reasonable. It is a waste of time. We don't put overcurrent protection on neutral, so the breaker won't notice anything different.
If the breaker were a GFCI, it should trip that but using a purpose-built GFCI tester that leaks just enough current to ground to trip the GFCI (~6mA) is a far safer way to test a GFCI.
It would also detect reversed polarity - the breaker should trip if the white wire you shorted to ground was actually hot. But again, there are much safer ways to go about this - like a voltmeter or a lightbulb and a known-good neutral/ground reference.
This is a very bad idea. FPE breakers are known to jam on overload. You might be able to turn the breaker on and then not turn it off due to the defective FPE design.
But wait, there's more! There's a good chance the panel is either a "rule of six" panel with no main breaker, or whatever main it has between the meter and the breaker you're testing is also FPE and affected by the same "jams on overload" condition. Now you've got a piece of wire burning up in your panel with no way to turn it off.
FPE busses and breakers are fatally flawed. This is a settled topic. They should be replaced as soon as possible. Even if they seem to work today, that doesn't mean they won't fail tomorrow.
Leave the experimentation to the professionals. Don't listen to YouTubers.
nobody
  • 5,770
  • 27
  • 37
Besides the other excellent answers here, there's another way of thinking about this situation, which is that: Sometimes, empirical tests are a great way to learn things or solve problems, while other times, empirical tests are a really, really bad way.
I'm not an electrical engineer, but I work with them and one thing that drives me insane is when someone designs a circuit where a component is used slightly outside of its specification in some way. There's always some "good reason" for this (usually it's because no part with specifications meeting the circuit's crazy requirements is available), but it sets you up for miserable, frustrating, preventable disasters. Sometimes the circuit works — because you "get lucky" and the component in question magically performs properly outside its specification — and sometimes you don't. But circuits that randomly don't work are the worst! I've even heard of organizations that try to "solve" this problem by prequalifying the raw parts they buy, putting them through their own tests to determine which of the parts happen to exceed their specifications and can therefore be "safely" used in the circuit that requires them. This strategy helps somewhat, but it still seems to me like absolute madness.
But, now, to return to the question, what we have here is almost the reverse situation. We have some parts which are known, empirically, to not meet their original specifications at all. We might as well retroactively apply a new set of specifications to a Stab-Lok 20A breaker:
Voltage: 50 VAC
Trip current: 200 A
Interrupting rating: 21 A
And since these effective specifications do not meet the requirements of any electrical installation anywhere, the strong recommendation is to not use the damn things.
But you're proposing an empirical, "postqualification" acceptance test. You're proposing to test a single Stab-Lok breaker, to see if you get lucky, to see if it magically Just Happens to exceed its effective specifications and interrupt an actual short. But even if it does, so what? How many times are you going to repeat the test? What guarantee do you have that the breaker is going to behave the same way tomorrow? What guarantee do you have that, under the slightly different conditions of an actual fault, the breaker is going to trip properly? Do you really want to take that chance? Are you really going to place more faith in the result of your single little small-scale test, over the accumulated experience and wisdom of, basically, everybody? And when actual human lives could be on the line?
Steve Summit
  • 223
Testing a safety equipment is WAY more complex than simply trying a certain failure mode and seeing if the outcome is less than catastrophic.
This method has at least these problems:
  1. The failure may get way too expensive in terms of health or lives lost, as well as property damage. In some cases you may burn an appliance few homes away, as well as something belonging to your utility company. Up to and including a prolonged neighbourhood-wide blackout.
  2. I am sure there are legal obstacles as well. At least where I live, it is forbidden to connect to the utility grid an appliance that is known to malfunction.
1+2 can get you in the court and the expensive lawyers will not be on your side.
  1. The test is profoundly pointless. The test may show that the safety device in question works more or less as intended in your particular test case, once. It may happily fail in another, pretty much legitimate occasion. E.g. the breaker may trip when cold, but may fail when first preheated for an hour by 90% of its rated current. Or when the humidity is low. Or when the moon is in a specific phase and the breaker tripped more than 2 times the last month.
fraxinus
  • 3,009
NO.
Short circuiting neutral to ground will not trip a regular breaker. It will probablly trip a GFCI/RCD but it's not really a very meaningful test as the current flow is completely dependent on what loads are present at the time. If you want to test GFCIs/RCDs get the right tool for the job that can prsent a known test current and time to see of the GFCI/RCD trips in the appropriate time. Or just press the test button (which is not an ideal test, but much better than shorting neutral to earth).
Short circuiting live to neutral will result in dangerously high currents, if the breakers fail to do the job of breaking said currents you may have a very dangerous situation on your hands.
Peter Green
  • 4,998
  • It depends on the installation type: on TN it should trip the breaker (because neutral and PN are connected at main panel or are the same wire). On TT/IT setups you're right, an RCD should trip but a MCB probably wont (it depends on ground loop impedence). In any case The answer NO is correct because the short-circuit current is unknown and if it's bigger than breaker breaking power will damage it. – DDS Feb 21 '22 at 16:36
  • Short circuiting neutral to ground won't trip a normal breaker (unless it's a double pole one, but such would be abnormal at least in the UK) because neither the neutral or ground go through the breaker. – Peter Green Feb 21 '22 at 16:53
  • I misspoke (and edited correction) - didn't mean to say short neutral to ground. – RustyShackleford Feb 22 '22 at 01:31