I tested the water pressure last month and it came up at 89psi. My old pressure regulating valve said it would only go to 75psi and turning the bolt didn't change the pressure, so I assumed it was shot and replaced it. No leaks and the new valve appears to be installed correctly according to the arrows on the housing.

I also removed what I would best call an S-curve in the copper pipe after the pressure regulator and before entering the house. I had googled it and couldn't find anything about why it was there but maybe it acted as an air chamber - not sure. I removed it since it seemed unnecessary and only there to line up the pipes. This then let me put the whole unsightly assembly in a valve box underground. Here's a pic of the before:

enter image description here

And after:

enter image description here

Water comes up on the right, into a ball valve, into the pressure regulating valve (PRV), then tees up to the house via ball valve, and down to my yard's irrigation / hose system after a dual check valve. There are pressure vacuum breakers before the sprinklers.

enter image description here

Now, when either the master shower is turned on on the second floor or the hose is run from the end of my irrigation line, the pipes in the opposite end of the house on the first floor (near where the water enters the house) start to vibrate / chatter and make a lot of noise. I have just discovered that the noise seems to be coming from where the main takes a 90-degree elbow and moves into my main shutoff valve and the PRV. Please see the Youtube video of the vibrating here and see it in more of a closeup with a focus on the the vibrating stopping and starting here.

Video 1 Link

Video 2 Link

As soon as the master shower stops or the hose is turned off, the vibrating / chattering stops. Sometimes if I open any faucet in the house, even for a second, the vibrating / chattering can stop. These vibrations can't be good, especially for the Sharkbite fittings.

As suggested below, I tried slightly closing the valves, but that didn't seem to do much. I then tried to adjust the pressure bolt on the PRV and it seemed to work for when the hose was on. I tightened the bolt until the vibrating stopped, but then when the irrigation kicked on it starting vibrating again. So, I adjusted it again and this setting only stopped the vibrating when both the hose and irrigation were on. I found something else my experimenting: when I turn off the valve to the house, there is no vibration at all.

I would have to guess that either the new pressure regulator valve or the removal of the S-curve is causing this. I can't tell if this qualifies as water hammer. Does that sound right and how could I stop this from happening? Would I have to re-add the S-curve and remove the valve box? Add an expansion tank? Remove the dual check valve? Better secure the pipes in the wall?

Any help would be greatly appreciated!

pennstump
  • 223
  • 6
  • 23
  • [Edit] in a pic of the current plumbing, as that would probably help. Also, it could be water hammer, which means that a hammer arrestor would help. – FreeMan Mar 07 '22 at 17:11
  • No need to tell us the question has been updated. There are date stamps for that and it pops the question to the top of the list (default sort order). Also, your "updated" tag was somewhat misleading because there were very few updates in the paragraph that seemed to be marked as having been updated - all the changes were much farther down. If you want to see what changed, click the "edited – FreeMan Apr 07 '22 at 16:55
  • I replaced the PRV with a higher-flow unit and this seems to have stopped this condition. I'm attributing it to either a bad PRV unit (even though it was new) or like stated below, there may have been the perfectly imperfect amount of pipe between the 90 from the main and the PRV causing this resonance, and therefore causing the vibrations / chattering. – pennstump Apr 13 '22 at 18:11

3 Answers3

2

The effect you observe is likely not water hammer.

Water hammer occurs when a traveling column of water (in a pipe) is abruptly stopped, e.g. when a solenoid valve shuts. The weight and velocity of the water act like a hammer that is abruptly stopped when it for instance hits a nail. The kinetic energy is partially absorbed by a brief expansion of the pipes and partially it is reflected as a pressure wave. Hammering is usually lead by a strong bang followed by weaker hammering tailings that rapidly die down.

What you are observing is a resonant oscillation started and maintained by the mechanical turbulence in flowing water.

Any mechanical interconnection of springs and weights has the potential of forming a resonant system. (Electrical systems are similar, with capacitance and inductance.)

With such a system in place you need just a small amount of mechanical agitation (a.k.a. "excitation") for the resonance to build up.

Depending on the "damping factor" of the resonant system, the oscillation can even be unstable and reach ever greater amplitudes until the components breaks.

This is how bridges and buildings collapse from vibration in high winds.

In your case it seems that the resonant system is formed by the weight of the water and/or possibly the reflection of pressure waves in long runs of rigid pipe. Shutting sections off changes the resonant frequency and the damping of the system, which is why the oscillations occur in certain configurations (this valve open, other valve closed etc...). A soft hose buried in soil can work as a damper, the free elastic expansion of a hose above ground can work as a spring, a loosely mounted pipe can buckle, a water column forms a mass, a firmly encased column of water can work as a wave guide for pressure waves etc..

The excitation that starts it all and keeps it going is caused from turbulence that occurs in the piping when water flows. Turbulence occurs where piping changes diameter, takes a corner, splits etc...

The resonant system is further refined by the addition of non-linear elements, e.g. the turn-around delay in a check valve can exacerbate vibrations, insufficient valve force in a PRV can cause it flutter etc...

It's possible you just have a bad combination of some of the above.

What's hard or nearly impossible to change are the lengths of pipe or their configuration (trunk/star vs daisy chain).

What you can easily change is the model of the PRV and the check valve.

It's not necessarily the case that you have a bad model, but more that the specific characteristics of the model you have might be forming a resonant system with the rest of your plumbing.

A few steps you can take:

  • replace the PRV with one designed for more flow or more primary (supply side) pressure. Your PRV may be undersized.
  • replace the garden check valve with a larger model (or temporarily remove it to experiment)
  • measure and reduce the water pressure on the secondary side of the PRV. You have measured it with the old PRV, what is it with the current one? Aim for well below 60psi.
P2000
  • 15,754
  • 28
  • 51
  • Replacing the PRV removed the vibrations from the system, but any water running on the system causes some substantial noise inside the house where the water line enters. I think it's concentrated at the T split in the box underground. Is there anything you can think of that I can do to reduce this noise? Can a T joint be somehow baffled? – pennstump Aug 16 '22 at 20:10
1

Water hammer is a common cause of noise complaints and even damage in water supply plumbing. It occurs when the velocity of water traveling through a pipe is high and a valve is suddenly closed. The mass of water moving at high speed presses against the suddenly-closed valve causing a spike in pressure.

It doesn't sound like that's what is happening here. You've described a noise that happens for as long as the master shower valve is open and water is flowing -- conditions opposite of those in a water hammer case.

I think somewhere you have a valve fluttering: rapidly opening and closing, but perhaps not closing all the way. It might be oscillating between "more open" and "less open" and just happens to resonate in your system. The new regulator seems likely to play a part but I'm not sure this means the regulator is faulty per se.

If the master shower valve supports it, try setting the water to a lower flow rate. Also try easing the valve open slowly. Does the character of the vibrations change?

Does your system have a working expansion tank? If you have a tank-style water heater then an expansion tank provides essential elasticity in the system. Without it the expansion of cold water being heated in the heater can cause a dangerous increase of pressure in the system. An expansion tank can also provide a buffer to smooth out changes of pressure of the kind that might be causing the noises you hear.

Expansion tanks can fail, and they also can require maintenance. Generally an expansion tank has an air bladder which must be maintained within a certain range of pressure (it varies depending on the pressure of the water system). If the pressure in the air bladder leaks down, or if the bladder fails and becomes filled with water, then the tank won't operate properly. Repair or replacement could be needed (and there are probably other questions on DIY focused on that topic!).

Edit after addition of photos and videos

That's definitely not a water hammer situation -- those are characterized by the bang of a sudden impulse followed by a decaying ringing effect. In your video the pipe is at rest and then we actually see the oscillations grow over a half-second or so. It looks quite smooth; my earlier guess of valve chatter might manifest more harshly. This looks like resonance -- the mechanical equivalent of a standing wave oscillation in an electric circuit.

A technique in circuits (transmission lines in particular) to tune or de-tune so that resonance will or won't occur is to add "matching stubs" to the line. An article at WaterWorld about acoustical resonance in pipes suggests this technique can be appropriate for hydraulic (water) systems too. An attempt to calculate the length of a stub for your application is far beyond the scope of an answer. I would guess that if there's a place you can easily add a tee indoors or outdoors then you could add an arbitrary-length pipe stub and see what happens. It's entirely experimental -- if I were doing it I'd start with something long, say 7 feet or so. If it doesn't have a positive effect then cut off several inches, re-cap, and test again.

The S-curve you removed might have been helping to suppress this condition. Whether it was just dumb luck or was an intentional fix is impossible for us to say.

Greg Hill
  • 27,924
  • 31
  • 75
  • The master shower valve is unfortunately on/off only. What kind of valve might be fluttering? There is no expansion tank and I only just now learned what one is. We do have a tank water heater: 40 gallons. Would there be a problem in not having an expansion tank brought on by only changing the pressure regulator? – pennstump Mar 09 '22 at 16:31
  • @pennstump A properly-functioning PRV might or might not allow backflow (see discussion [there](https://www.physicsforums.com/threads/why-pressure-reducing-valve-doesnt-prevent-backflow.822366/)). If it prevents backflow then pressure buildup could occur absent an expansion tank, and thus the tank is added as a good practice. I'm thinking the valve inside the regulator might flutter or oscillate: it is spring operated after all. The shower valve might be quick-acting but surely it doesn't snap open. Maybe you can ease it to full-open by moving the lever more slowly. – Greg Hill Mar 09 '22 at 18:05
  • Would you please be so kind as to watch the 2 short Youtube videos that I've added links to in the question? – pennstump Apr 07 '22 at 16:53
  • @pennstump It's fascinating to watch the oscillation build in those videos. At least, to one who doesn't have to deal with it every day it is fascinating! I added further remarks to the answer. – Greg Hill Apr 08 '22 at 16:35
0

Consider this example. In electronics resistance and capacitance are used to filter out voltage spikes. It could be that your s-curve was functioning as a resistor. Also a pressure tank is basically a capacitor. Another thought is your new regulator looks smaller in diameter. This might result in a hysteresis in the way it functions. A difference (gap) in the opening and closing pressure that makes it open and close rapidly. If you touch it during the "flutter" does it feel like it might be the source? Try running the shower and then slowly closed the ball valve next to the regulator until you see a slight decrease in flow. Leave it that way and see if the problem goes away. Not a real fix but you might learn something about the problem.

jasowiii
  • 19
  • 2