14

I am building a new home, and want to get fiber internet installed in it. In my current home, the fiber is wired externally on walls, above doors and finally into the living room through a drilled hole. I want this wire to be installed internally (inside walls like electric wires) so that I don't have to see it. As far as I understand, a fiber can't be bent too much, else it won't give required performance and signal speed. So CAN it be wired internally at all? Because as I imagine, internally there would be a lot more bends and curves the wire would have to go through. I tried finding the answer to this, but there doesn't seem to be one. Could someone explain?

So just to clarify: I'm just talking about the one fiber line that comes to a house and provides internet, not wiring all the rooms with it (I didn't even know that could be done or it would be feasible, thanks for informing me).

An update: So I understand now that it can be done using conduit generally, but can it be done with this kind of fiber (attaching a photo). Would I need a special kind of long conduit for it? The ISP's fiber line that comes from outside the house into my lobby

Johnnytest
  • 148
  • 1
  • 1
  • 8
  • 23
    Don't. There is a lot of downsides, and no upsides, to installing fiber inside your home past the first exterior wall. Put a small utility closet on an exterior wall, bring the fiber there, and from there to the rest of the house run regular ethernet. – whatsisname Apr 04 '22 at 03:43
  • 2
    Very little code(must do) concerning low voltage(less than 50 volts) wires/cables. You can usually do what you feel like with them. Types of cables might have some recommendations to bends and the like. – crip659 Apr 04 '22 at 15:47
  • Related : [Should an optical cable inside a house be run in conduit?](https://diy.stackexchange.com/q/198720/41369) – J... Apr 04 '22 at 15:52
  • How common is equipment for fiber + PoE? I would stick with copper for a home network. – erickson Apr 04 '22 at 16:33
  • omfg on some of these answers – ron Apr 04 '22 at 18:20
  • 4
    I'm confused, @whatsisname. I had fiber installed at my house a couple of months ago. They did horizontal boring to bring the drop to the house, installed a box on the outside of the house, then ran it inside to where I wanted the jack on the wall to be. From there it goes to the ONT which transitions to CAT5e/6 for distribution to the rest of the house. Why in the world you recommend this not be done with the walls open in new construction? It's _much_ easier to do this now than to fish it through the walls to install it later. – FreeMan Apr 04 '22 at 22:45
  • 2
    @whatsisname The upsides are that you can easily upgrade speeds later, don't have to worry about distance limitations, and interference is essentially impossible. I had the house I'm in now connected with fiber three years ago and it's been *way* better than Ethernet. When my provider offered Internet at >1Gbps, I was good to go with no fuss. – David Schwartz Apr 04 '22 at 23:11
  • 3
    This question would benefit from more detail: how much fiber do you want to run? (For example, just to the router, or to every room in the house, or something in between?) Do you also want to run ethernet? Etc – usul Apr 05 '22 at 00:35
  • @FreeMan: I'm arguing against using fiber within the house to go from room to room. Fiber from the ISP into the house is great, but after it's entered the house, use Ethernet for home networking. OP question to me sounded as though they wanted a 100% optical network in their house. – whatsisname Apr 05 '22 at 01:37
  • @DavidSchwartz: I'm talking about sticking to Ethernet for room to room connections. If someone has two rooms in a house that are more that 300 feet apart, well, they can afford pay someone to figure it out rather than posting on a volunteer website. – whatsisname Apr 05 '22 at 01:39
  • Hey guys thanks for your help, in my country the only fiber available is the one coming into the house, I've never heard of houses being _wired_ with fiber. And @whatsisname while I can afford to pay someone, I can't seem to find someone who knows about this. Only the isp deals with this, and they told me what I posted- that it can't be bent too much and therefore was unlikely to fit inside walls. – Johnnytest Apr 05 '22 at 05:12
  • @whatsisname Some "advanced users" might want room-to-room fiber for super-duper-fast networking (10Gbps or more) but it isn't normal, that's right – user253751 Apr 05 '22 at 09:03
  • My first employer ran fiber to the desktop in our new building back in 1994. It was fantastic speeds and fantastically expensive! Of course, it was simplex, so every desktop machine had a fiber NIC with 2 ports, one for Tx, one for Rx. However, just about any modern speed could have been pushed across that existing fiber, had the hardware at the ends been updated to support it. – FreeMan Apr 05 '22 at 11:09
  • @whatsisname If you're using mostly WiFi devices, your room-to-room connections are for switches or access points. Gigabit is already too slow for those with many Internet providers exceeding gigabit speeds and WiFi already exceeding gigabit speeds. Maybe my experiences are different from yours, by my room-to-room connections aren't for a single, slow device anymore. And that's today. House wiring should be built to last decades. – David Schwartz Apr 05 '22 at 20:15
  • @DavidSchwartz Right now you can run 2.5GE over 100m of Cat5e cabling that you installed 20 years ago for "Fast Ethernet". With some luck, you can also get 5GE over shorter distances (we're talking room-to-room after all), although Cat6 is strictly speaking required for guaranteed performance. All that with commodity hardware. There's no reason to believe technology will stop advancing, so we might live to see 40GE on the Cat6a copper that you install today. That's likely more than enough for the foreseeable future. – TooTea Apr 06 '22 at 18:40
  • @J... In my country this is what everyone gets when they get a fiber connection installed. It's not like it doesn't bend at all, when the tech brought it, he had it rolled up in a circle with a radius of about 0.5 meter, but I don't think it can bend more than that. – Johnnytest Apr 07 '22 at 04:15
  • @DavidSchwartz: When comparing laying fiber *today* with laying Cat *today*, we aren't talking Cat5e. I rennovated my house fourteen years ago and had Cat7 layed for the cables, with Cat6 connectors for downward compatibility. Got FTTH layed two years ago, and did exactly what whatsisname recommended -- fiber ends right after entering the house, which is (not so) incidentially right beside the switch serving all rooms (and the WiFi APs). – DevSolar Apr 07 '22 at 11:06

9 Answers9

20

So you want access behind the walls to upgrade your network wiring (since it changes really often compared to the lifetime of the house). But, you also want to seal the walls up in drywall, mud and paint like everyone else does. Common struggle.

The answer is conduit

This is pipe that is designed to interconnect electrical junction boxes.

It comes in a variety of forms: flexible, non-flexible, metal or plastic.

Most of them provide for curves called "Sweeps" - which provide an easy, at least 5" radius bend for all curves. Or they use a flexible conduit which naturally limits sharp turns.

I for one dislike plastic because it worsens the escape problem in house fires. Another argument in favor of metal conduit is RF shielding.

I caution against over-use of flexible conduit, because it is springy, and you'll be fighting that springiness while pushing a tape through or pulling a wire through.

Conduits can only have 360 degrees of bend between pulling points (but even that makes pulling difficult for a DIYer). A pulling point can be a junction box, or a "conduit body" - however conduit bodies require unusually tight bends - check whether that's OK for fiber. Such points must remain accessible forever without tools or damaging building surface.

Boxes

A proper junction box has sides and a back, with round knockouts which the conduit enters. That's intended for AC power wiring which must be enclosed, but you're welcome to use it for datacomm (and if metal, provides RF shielding).

Data cables only require a backless "non-box" such this minimalist one. (note swinging ears for clamping to drywall, a second-rate attachment method; this is a retrofit aka "old work" box).

enter image description here

What do you do to make sure the conduit ends are accessible? I suppose you could anchor the conduit firmly somehow to be within ready reach of the opening. Or here's a more robust "new work" box (requiring open studs to attach, but anchors much better) that provides attachment points for conduit.

enter image description here

Again, you're not required to use open boxes or "wish boxes" (wish it had a back), but you're allowed to for datacomm.

Oh wait. Maybe proper boxes are a good idea with fiber.

Because here's an interesting wrinkle with fiber. Fiber is allowed in power conduits provided it is entirely non-metallic. So if you build your conduit network fully NEC Chapter 3 shipshape and in Bristol fashion, you can use them for additional AC power circuits - up to four in fact.

For that matter, you could do a hybrid system where you use full and proper conduit for enough of your AC power that you can just toss fiber in there.

The downside of this "fiber+power" tactic is that you can't have any copper datacomm in there - not cable TV, not Ethernet and not PoE. So if "the next thing" comes out is fiber+copper for low voltage power, you'd be out of luck (since AC and low-voltage can't be mixed).

(because, it's presumed a wire meltdown may occur inside a junction box, with 120/230V live having contact with any other wires in the box. Low voltage wires typically go to places not insulated for that, like out of the wall on an Ethernet and into the back of a PC which connects to other peripherals).

Harper - Reinstate Monica
  • 295,284
  • 26
  • 275
  • 720
  • Fiber+copper for high speed POE hardware is plausible. If doing new work I'd run separate conduits. Installing 2 sets now would be far cheaper than having to retrofit a second set later. – Dan Is Fiddling By Firelight Apr 04 '22 at 21:19
  • @Dan Physically it would make sense - the fiber that AT&T installs looks like 2 fat wires. In fact the "wires" are fiberglass and are just there as a "damage shield" and to keep you from bending it too tight; the actual fiber is a tiny strand between them. Well, the "wires" *could be wires*. – Harper - Reinstate Monica Apr 05 '22 at 02:30
  • I didn't get the "you can't have any copper datacomm" versus the "fiber+2 copper for power" bit - one is "datacomm" and one is "power" – Caius Jard Apr 05 '22 at 09:01
  • @CaiusJard you're not allowed to mix high voltage wiring (wall power) and low voltage wiring (copper ethernet or POE wires bundled with fiber) in the same conduit because low voltage hardware isn't required to remain safe if shorted to a 15A 120V line. – Dan Is Fiddling By Firelight Apr 05 '22 at 11:00
  • Lots of home fiber installations use a fiber bundle that has a small "locate wire" in it, which is used strictly for attaching a signal generator to it so they can find where it's buried. – Tristan Apr 05 '22 at 13:50
  • 1
    Easy solution for pull boxes; don't turn corners at them. Put them in the middle of straight runs or just before a gradual bend. – Matthew Apr 05 '22 at 15:53
  • @Harper-ReinstateUkraine I understand that I can install conduit, I'm asking if the fiber wire I've shown can actually get through the conduit without breaking. It doesn't seem to bend very much. – Johnnytest May 27 '22 at 11:09
  • @Johnnytest Sorry. Yes when AT&T hooked me up with fiber, I had a very knowledgeable "old head" for an installer, and *you bet I asked*. Yes, their fiber can handle all the normal bends and turns found in electrical conduit installations. You would need to be careful about radius when exiting the box in a way that a cover plate manufacturer might not approve lol (Code doesn't care unless there's AC power in the box). And you need to have a way to coil up any excess length without exceeeding radius. – Harper - Reinstate Monica May 27 '22 at 17:31
13
  • Yes, fiber can be run internally as well as externally. Your vendor may not provide any way to hand off to internal fiber, though, and may prefer to keep their interface external so they don't have to get in the house to service it.
  • Reduced Bend Radius fiber exists, and is very commonly what is used for internal fiber runs. The vendors will demonstrate it working while wrapped around a pencil...but you can still break it if you mishandle it.
  • Conduit is truly the best idea for any sort of networking. Networking has a short life relative to house lifetimes. Conduit allows swapping it out painlessly when the next thing comes along.
  • At the present time most of your in-house networking conduit would likely be better stuffed with wire. The practical realities of POE for distribution to wireless access points and the lack of major advantages for fiber inside a building less than 100 meters in any dimension don't support fiber to every room as a sensible option right now. Fiber is the right way to go between buildings.
  • Do remember to provide ceiling boxes in all major rooms, since high-speed wireless works best without walls in the way of the signals, so an access point on the ceiling (tends to be the most visible) that your end-use device can see is a very good thing. They are generally easily mistaken for smoke detectors if well-designed (don't forget the wiring for smoke detectors, either.)
Ecnerwal
  • 201,085
  • 10
  • 245
  • 533
  • 3
    +1 *"but you can still break it if you mishandle it"* Technically, yes, but you can also break Romex if you mishandle it... or CAT5/6 cable. If you drop a circular saw on it from ten feet up or drive over it with a combine, sure, you can absolutely break it, but ruggedized fibre is really equally as tough as anything else you'll run in your house. You can staple it to studs, pull it around hard 90-deg bends... it's really [pretty tough stuff](https://youtu.be/UBt00CVvMBA) meant for contractors to install. – J... Apr 04 '22 at 15:23
  • 1
    @J...: Since the OP mentions building a new home, your argument about busting open walls does not apply in this case. – arne Apr 04 '22 at 16:35
  • 6
    Lots of good advice here about running fiber in a house but your question sounds like *it is the ISP's fiber* you want to run through your walls? If that's right, the most important point in this answer is the first one ... don't plan to run the ISP's fiber through your walls. Ideally plan to terminate it directly inside the wall where it enters the house. Later, when things go wrong, you will appreciate a clear delineation between ISP equipment and your own. If you make them run their fiber through your walls, they will blame you for all faults and you'll have no recourse. – jay613 Apr 04 '22 at 18:01
  • @jay613 Yes, that's exactly my question. Right now it enters the house through a hole that they drilled in my lobby, and it gets to that hole externally- over fences, walls and tiles. It looks really bad. I just want to know if it can be run to my lobby from _inside_ the walls so that it doesn't look bad. – Johnnytest Apr 05 '22 at 04:58
  • Microduct (the conduit used for buried fibre drops to consumers) is basically a kind of PEX tubing. using this enforces a bend radius. – Jasen Apr 05 '22 at 08:58
  • Now I'm quite confused. Fences? Is it the appearance of the cable *outside* your house that you have issue with? You want it run more attractively, maybe underground? That's do-able. Is it running along wall surfaces inside your house? That ugliness can be dealt with, but not, ideally, by running the ISP's cable through your interior walls. What exactly is the issue? – jay613 Apr 05 '22 at 12:03
  • Yes, it's the appearance outside (and to a very little extent, inside) that's the problem. I'm asking if the ISP's cable can be run _through_ the walls from outside to a point inside a room, where I can keep the modem and stuff. The overwhelming consensus here seems to be that yes it can, I'm still fuzzy on the details though. – Johnnytest Apr 05 '22 at 12:26
  • I think this answer and comments stand. You should not run ISP wire through interior walls. If you don't like the way it looks on the outside you should either ask the ISP to run it more professionally (underground, in conduit, under a soffit, whatever you like) or to put their termination at the earliest possible point along your wall, rather than running along it. From there, you take over and do whatever you want. – jay613 Apr 05 '22 at 13:44
  • @Johnnytest In that case install a box next to the mail box next to the road or something and have the fiber terminated there. From there you can run conduit with Ethernet into your house. That way you don't even need to let the ISP people into your house. – Nobody Apr 06 '22 at 19:40
  • @jay613 Asking the ISP to run it through conduit is the same thing as running it through interior walls (the walls have a conduit). It doesn't look like that's possible however, since the cable can't bend. I can look into taking over from the outside wall, but the distance from there to inside is pretty long, and to maintain speed I guess I would need a super expensive long ethernet cable. And I'm not even sure how that would go with the ISP, they may refuse to take responsibility for any issue that may come up. – Johnnytest Apr 07 '22 at 04:05
  • I meant, through conduit *outside* your house. They can do that and it remains their domain. If they want, which they don't, but you can ask. Get the handoff to as close as possible to where you want, remaining outside, in ISP control, using techniques like underground conduit that you request. You may need to pay for it. I agree, not conduit inside your house. I emphasize, handoff should be JUST Inside the wall from where the fiber enters, and from there YOU figure out how to get service where you want it. Combo of UTP cable, Mesh Nodes, WAPs, etc. – jay613 Apr 07 '22 at 13:19
  • @jay613 The point is to have no exterior wiring equipment at all. I checked with the isp, they don't have a problem with me putting the fiber inside the walls, but they don't know if it can be done at all. This cable doesn't seem very bendy. I just need to know if it can survive bends or not. As for converting it to ethernet, they don't allow that at all as they directly plug the fiber into their modem cum router. – Johnnytest May 27 '22 at 11:26
8

Yes

This is entirely possible to do. However:

  • You should do it in conduit, paying careful attention to the exact geometry of the conduit. This will let you run new cabling when standards eventually change and you want to upgrade.
  • You will probably need ‘reduced bend radius’ cabling. This is more expensive, but if handled properly can make absurdly tight bends.
  • While you could share the conduit with power lines, doing so would mean you could not ever use metal network cabling while still being in compliance with electrical code in most parts of the world.

However...

Fiber provides very specific advantages when you want extremely high speeds or have to transmit signals very long distances or have a specific reason to want no risk of EMI or corrosion.

But it’s got a major disadvantage right now: it’s actually pretty expensive for consumer usage. Pretty much nothing uses a direct fiber NIC, it’s all SFP derivatives. And that all gets expensive pretty fast. You’re looking at hundreds of USD each for each AP and switch, plus anywhere from 20 USD to a few hundred USD per fiber termination module, plus 20 USD each for media converters for each device you want to add to the wired network that doesn’t already have a SFP slot (assuming you don’t want a proper NIC in the system, which will run you hundreds of USD each).

And the reality is, none of those specific advantages of fiber actually provide any benefit in a building the size of a typical house (unless you do a really bad job with the wiring and live in a particularly humid climate) compared to running Cat6A twisted-pair cabling. Unless you are doing atypical things, your home network almost certainly does not need to be any faster than your internet uplink, and given that it’s home internet, you probably do not have access to any better than a symmetric gigabit uplink right now, and likely will not have access to any better than a symmetric 10GbE uplink for a very long time.

This means you can (probably) save a significant amount of money by just running Cat6A cabling instead, which is still good enough to do 10GbE, has the advantage that you can use it for PoE (which makes handling of things like wireless APs much easier), and does not require special hardware anywhere. By using good conduit with a smooth interior and paying proper attention to the conduit geometry, you can pretty easily make it even more future proof by simply making it easy to pull new cables.

  • Hey. So I understand that I'll need a conduit, but I have no choice over the type of cable. It's a not too thick black cable, provided by the isp. – Johnnytest Apr 05 '22 at 12:32
  • So I added the photo of the cable, if you can check and tell me if it can bend through walls it would be nice. – Johnnytest May 27 '22 at 11:17
6

So, if I understand correctly, you want the fiber to come into your house, then connect to the fiber router somewhere inside the house, without looking ugly on your walls. Then the rest of the house is wired with standard Cat5e or Cat6.

That's what I have done, so here we go.

The guy who will come to install fiber to your house will pull a rather thick fiber cable from the street. This contains a few very thin fibers, with a tough plastic protection sheath around them so it survives being pulled through underground conduits. This fiber cable doesn't have a connector at the end, because that would prevent it from being pulled through conduits. The installer routes this cable to a fiber junction box, then does the junctions, and the router is connected to this box with thinner optical cables. These cables are designed for interior use, so they are quite thin and flimsy.

In a multi-story building, there is usually one junction box per floor, and thin cables running to each apartment. In this case the thin cables can be routed through conduits and walls, because they don't have connectors attached. In houses, they usually put the junction box somewhere easy to install inside or outside the house, then they'll use a readymade patch cable with connectors attached. The connectors will not go through conduit, unless the conduit is huge, like 35mm, to let the connectors through. And they tend to get stuck, and the fiber is fragile, so it's a bad idea to pull these cables with connectors through conduits.

enter image description here

So, you should check how things are done in your jurisdiction. Look how it was done in your neighbor's houses, and call the installer. If they want the fiber junction box outside to be able to service it, then ask if they can route the fiber through conduits you provide, and make sure the installer will come with the necessary stuff, especially the kit to add another junction box at the end of the interior cable, what kind of conduit diameter you need to install, where it should exit the house, etc.

Then, all you need to do is make sure there is a conduit path from wherever the fiber will come from (on the street) to wherever you want to install it. The tough fiber cable doesn't bend well, it is quite rigid to protect the fiber inside. The flimsy cable breaks when it bends. So this conduit shouldn't have sharp angles.

I'd recommend 20mm or 25mm conduit, it's easier to pull through and harder to bend.

These conduits are usually delivered with a steel wire inside, which is mostly useless, it always gets stuck or breaks. So the first thing to do after laying the conduit is to attach a proper tough wire to it, or a tough PP string, and pull it through.

Then leave both ends accessible, and when the installer comes, just tell him to pull the fiber through it. This needs two people, one pulling on one end, and the other pushing the cable in at the other and making sure it doesn't make any knots, so you'll have to lend a hand.

Make sure you have a roll of PVC adhesive tape on hand.

bobflux
  • 8,767
  • 23
  • 29
  • 1
    And also tie another length of PP to the end (that you don't have in your hands) of the first, so you still have a pull cord in the conduit after you finished pulling the cable – Caius Jard Apr 05 '22 at 09:05
  • 1
    Fiber can be blown/sucked through too, don't forget – Caius Jard Apr 05 '22 at 09:06
  • *"and the fiber is fragile"* - No, it isn't, unless you buy entirely the wrong stuff. – J... Apr 05 '22 at 11:30
  • This sounds exactly like what the OP wants and needs. – Peter - Reinstate Monica Apr 07 '22 at 10:11
  • The fiber which the isp brings is shown in the photo, @bobflux. It doesn't seem like it will bend much, so I'm not too sure it will make it through the conduit. – Johnnytest May 27 '22 at 11:14
  • It looks like normal outdoors fiber with the super tough jacket, same stuff we got here. It went through my conduits just fine. It won't do sharp corners, but then again you're never supposed to lay out conduit with sharp corners... Have you put in the conduit yet? – bobflux May 27 '22 at 12:48
  • I would recommend 20mm diameter plastic conduit (as pictured in the answer). The smaller diameter, which is 16mm, is cheaper, but it's much easier to get stuck when drawing wires through it. The most important thing is to not make sharp bends, no kinks, don't step on it and squish it, don't attach it to the walls with a fastener that squeezes it, etc. – bobflux May 27 '22 at 12:53
5

We run fiber inside walls all the time. You can run it just like any other wire just be careful not to pull to hard and stretch it or get any kinks in it and you'll be fine. You can even use round staples to secure it and run it to where your modem is.

MagnumTech
  • 51
  • 1
  • Staples? Inside walls? – Johnnytest Apr 05 '22 at 12:30
  • Staples? On delicate fibre with a minimum bend radius? – qris Apr 05 '22 at 15:12
  • 2
    @qris YES - [Staples](https://youtu.be/UBt00CVvMBA?t=330). Doesn't even need to be round ones - good old fashioned flat staples right from a staple gun is fine. It's not the 1990s any more. Fiber technology has left the stone age. – J... Apr 05 '22 at 20:13
4

The newly-added photo shows a specific type of fiber cable. The legend on the cable isn't entirely legible but it looks like it says 4F SMF, which means 4 strands of single-mode fiber, and doesn't actually tell us anything about the bend characteristics of the cable.

It appears to be flat drop cable which has typical construction like the photo below: (credit novalight.com)

flat drop cable cross section

This type of cable doesn't bend very well -- it's somewhat easy to break those fiberglass dielectric strength members. The Commscope flat drop product I've worked with can be wrestled down to maybe a 6 inch bend radius (a 12 inch diameter coil of slack in a hand hole in the ground is how I experience it). This cable would go through an ordinary bend in EMT conduit if helped along with a pull string but would break if forced into the tight bend of a conduit body. It also really only bends in one axis: up and down as viewed in this photo; trying to bend this cable "in-plane"

NEC 770.48(A) pertains to "unlisted conductive and nonconductive outside plant optical cables" entering buildings. There's a limit of 50 feet, which may be extended by "continuously enclosing the entrance optical fiber cables in rigid metal conduit or intermediate metal condeuit to the point of emergence." In a single family detached home you'd be unlikely to hit the 50 foot limit, however.

Interestingly, 770.48(B) indicates unlisted nonconductive outside plant cables are permitted to be installed in IMC, RMC, rigid PVC, and EMT conduit. "Nonconductive" means there's no tracer wire conductor, no metallic armor, etc. The one pictured is almost certainly nonconductive. I'm surprised that ENT "smurf tube" suggested by others isn't permitted for outside plant cable too, but there you have it.. I suppose one would comply with 770.48(B) while using ENT by terminating the OSP cable on the exterior of the building and transitioning to some other non-OSP cable to enter through the ENT conduit.

A drop cable like this is going to have to be terminated in some kind of demarcation box, at which point it'll be connected to a patch cable of some sort or a pigtail for immediate connection to the ONU/ONT right there in the demarc box.

The long and short of it is this: Install a conduit. The fiber provider may or may not be willing to bring their outside plant cable through your conduit into the building. If they're unwilling, at least they may place their demarc box near your conduit so that you can run copper or optical cable from there into the house.

Greg Hill
  • 27,924
  • 31
  • 75
  • Ok, so I am installing a conduit anyway (for telephone and tv wires), but if this cable breaks, then I guess it's not much use. I don't see how I can run some other cable like copper through the conduit and connect it to the fiber. Also I'm pretty sure my speed will get impacted by this, and the isp won't do anything about that. – Johnnytest Apr 06 '22 at 09:16
  • @Johnnytest Maybe the ISP will be willing to run their cable through your conduit. If not, they might place their ONT/ONU fiber-to-copper converter outdoors and you can run CAT5/6/? through the conduit. If they terminate their fiber outdoors with say an SC/APC connector then you can buy a coupler and pre-terminated patch cable, push that through the conduit, and locate the ONT/ONU indoors closer to your equipment. In all cases there is a converter box that sits between the fiber and the copper 1/2.5/5/10G Ethernet port on your WiFi router. – Greg Hill Apr 06 '22 at 14:53
  • They may be willing to run it, but it doesn't look like this cable can fit through a conduit over multiple turns and bends (that's the vibe I'm understanding from this page after posting the photo). I can look into using copper or ethernet through the conduit, but the distance from outside to the inside is quite long, and I think it'll take a pretty expensive wire to maintain speeds for that distance comparable to the fiber. – Johnnytest Apr 07 '22 at 04:08
  • @Johnnytest As another answer mentioned it would be shocking if you're getting more than 10 Gbps residential service on the fiber. CAT6 copper cable can also manage 10 Gbps, and this cable is not expensive, so there's no obligatory loss of speed in a fiber-to-copper transition. If your conduit is minimum 3/4 or even 1 inch, has straight runs, minimizes the number of bends, and doesn't have any tight fittings (L body or outside corner body) a flat drop fiber cable will go through it fine. – Greg Hill Apr 07 '22 at 15:33
  • The distance from the outside wall to the inside of the room is quite large, and the conduit will inevitably have lots of bends, turns and such since it has to get through walls, under floors and between rooms. I guess a CAT 6A or CAT 7 cable that long would manage to avoid any speed loss, but my isp doesn't allow converting the signal from the fiber to ethernet, they put their fiber line directly into their modem cum router. – Johnnytest May 27 '22 at 11:02
2

It depends where you are in the world and what your local fibre-co can do.
Contact your area's fibre-provider/company and ask what is possible for new builds.

EXAMPLE: In New Zealand, there are government-backed fibre providers who are the sole incumbent in a region. They cannot retail services, they are mandated wholesale only. This lets anyone run a dedicated fibre ISP.

In my city, the local company Enable will pre-wire your half-built house with blowtube to the point inside where your fibre termination will be. This is normally scheduled before internal cladding goes in. Once things have progressed closer, they will blow fibre in from the local cabinet and terminate it. Then your ISP can commence service after that date.

Best of all, this is all free to the home owner.

Criggie
  • 10,046
  • 2
  • 24
  • 65
  • 1
    The company here installs these connections externally, the installers said they don't know if it can be done internally or not, they certainly hadn't done it and didn't know how either. That's what I'm trying to find out here if it is even possible or not. – Johnnytest Jun 27 '22 at 17:25
  • @Johnnytest then conduit / tube / pipe is your best answer for a clean install. Make sure you're at home when the installer comes to point them in the right direction. A new build like yours should be easier than a retrofit if serviced at the right time, Good luck ! – Criggie Jun 27 '22 at 20:54
  • The problem isn't the conduit or the tube, it's the fiber itself. It doesn't seem like it can bend enough without significant signal loss/damage to the glass. – Johnnytest Jun 28 '22 at 00:42
  • @Johnnytest noone uses glass fibres any more - its all optical-grade plastic and can handle insane bend radii . – Criggie Jun 28 '22 at 00:59
  • I've posted the photo above, this is glass. This is the only kind the isps have. And I can't even convert to ethernet because the isp plugs the fiber straight into the modem. – Johnnytest Jun 28 '22 at 06:15
0

Can an incoming optical fiber cable be wired internally in a house's walls?

  • the incoming fiber drop from the utility pole is outdoor rated cable; if that cable [jacket] rating meets the riser rating for cable then yes it could be run within walls
  • recognize the difference between riser rated and plenum rated cabling, as well as electrical cable which has a heating component to it that is the driving factor whereas fiber optic cable is light transmission and there is no heating component associated with it. does the nec (electric) apply to fiber optic cable when fiber has no electrical component, i don't know. probably NFPA and fire and cable jacket material.
  • the answer is not conduit
  • there is riser rated fiber optic cable, plenum rated fiber optic cable, and even armored (i.e. BX) rated fiber optic cable, use it appropriately but u as a residential home would not.
  • u would not run fiber optic all throughout your new house... to future proof it for when terabit speed happens in year 3000. the toolkit to terminate fiber optic is expensive as well has no mainstream network and pc/laptop hardware support fiber optic connectors such as TC or LC, you'll then need media converters at each fiber optic wall jack so running fiber makes no sense.
  • run cat 6 or cat 7 copper throughout your house, connecting to a central location where you have a gigabit unmananaged switch that costs less than $100, so that each room has an rj45 wall jack. Cat 6/7 within the home will support up to 10 gbps keeping any given run less than 100m or 300', if you get a 10 GbE switch. Otherwise 1gbps is fantastic given internet service is at most 2gbps currently with frontier fiber and nobody really needs more than the 500 mbps plan; xfinity was hot sh1t @ 200mbps; and plan for where a wifi router will transmit as all tv's now stream via wifi they don't even offer a hard lan connection.
  • the fiber drop from utility pole only needs to enter the house and be run far enough within to locate an ONT, optical network terminal, which needs 120vac and converts the light stream to electrical; the ONT has 1 input the fiber ST or LC connector and 1 output an rj45 so you are then on cat 6/7 at best anyway. Partial context of your question... you do not run fiber optic all through the house and anyone suggesting so has no clue, the outdoor rated fiber from the pole enters the house and is run to where you want the ONT which could be just inside the exterior wall, or can be run to the deepest depths of the home doesn't really matter.
  • the outdoor rated fiber can enter the house and have a bridge... a disconnect connector, and then some other length of [indoor] rated riser/plenum fiber could be run however within the house to locate the ONT in some preferable place; it would only be one single run of jacketed fiber optic, kinda similar to NM 14/2 and UF-B.
  • for a new home just plan on having a nice hole pre made in the exterior wall or foundation so the tech can feed the fiber or coax or any cable into your house rather than haphazardly drill based on time of day and previous installation difficulty and aggravation.
ron
  • 1,108
  • 6
  • 9
-1

Like posted above all of these answers are pretty dead on.

Running fiber to all locations in house would be top notch speed (which is super badass)...

However for MOST if not ALL of the devices you are looking to hook up to (wifi, tv, xbox, ps, computers etc..) RJ-45 connections are needed.

Like above $$$ you want to set up a household system for great fiber speeds. now that you have fiber at all the locations you want, now you need to use media converters that change from fiber to cat6. now this is just dumping even more money to bottleneck your speeds to devices that don't use the full potential anyways.

I wouldn't recommend wasting the money on fiber through the whole house just yet. The demand for that kind of speed to your devices isn't here yet.

I personally have Welink as an internet provider and I get about 600 up and 600 down; it's amazing. I have all my devices hardlined in with cat6 to an unmanaged 48 port gigabit switch (nothing fancy). I have 2 Google wifi devices (I do need an upgrade from these wifi 6 i.e. a faster connection which these don't provide).

I never have any down time or loading/waiting as long as I'm on the network streaming and downloading in the house is seamless. No need to spend big money for no reason.

Hope this helps.

I've been installing fiber infrastructure and devices for about 14 years now.

Glorfindel
  • 1,173
  • 2
  • 14
  • 20
  • How does your fiber come into the house? – Johnnytest Apr 06 '22 at 09:18
  • all the other answers are not dead on, they are clueless and is a perfect example why not to believe something on the internet because it has a bunch of upvotes – ron Apr 06 '22 at 18:19
  • 1