Question

I bought a new three pronged cable from home depot. Can I put that cable into this dryer and simple connect it to the wall? Is that safe? Will it work? If so, what do I do about the spot for the grounding wire? I would love to see a video/image of this being done.

In the past I've replaced a three pronged cable with a four pronged cable in a dryer and successfully connected it. But this time I'm trying to do the reverse..


I've fixed and already washed one round of clothes. Hopefully all is well :)

Harper - Reinstate Monica
  • 295,284
  • 26
  • 275
  • 720
Omnipresent
  • 385
  • 4
  • 8
  • 14
  • On a side note, that receptacle looks like a NEMA 10-50R which is rated for 50A and is typically used for electric ranges. You might have trouble finding a "dryer" cord that fits, since dryers typically use NEMA 10-30 (14-30 for 4 prong) (rated for 30A). – Tester101 Feb 25 '13 at 16:08
  • So you guys are saying that I can just hook a 3 prong cord up, bing bang boom and be done with it? It's already got a ground inside the dryer? –  Oct 14 '15 at 06:23
  • Heck no, it's a terrible idea. Hooking up a dryer or range with no ground is asking for trouble. The 3-prong style is obsolete and it's easy and legal to retrofit just a ground wire. – Harper - Reinstate Monica Jun 17 '17 at 23:17

4 Answers4

14

What you are doing is done all the time, and there is no problem with it, if done properly. The fact is these 3 prong receptacles still exists in many older homes, and there is no requirement to upgrade an entire circuit simply to plug in a device. If you go out and purchase a new electric dryer, the seller will ask if you have a 3 or 4 prong receptacle. They will then sell you the appropriate cord, based on your answer (if you don't know, they'll probably sell you both and tell you to return the one you don't need, or offer their instillation services).

RTFM

If you check the manufacturers installation instructions, there should be a procedure for connecting the dryer to a 3 prong receptacle. The procedure can very from manufacturer to manufacturer, so make sure you check the documentation for your specific dryer.

From a random whirlpool manual:

This dryer is manufactured ready to install with a 3-wire electrical supply connection. The neutral ground conductor is permanently connected to the neutral conductor (white wire) within the dryer. If the dryer is installed with a 4-wire electrical supply connection, the neutral ground conductor must be removed from the external ground connector (green screw), and secured under the neutral terminal (center or white wire) of the terminal block. When the neutral ground conductor is secured under the neutral terminal (center or white wire) of the terminal block, the dryer cabinet is isolated from the neutral conductor.

enter image description here
Click for larger view
enter image description here
Click for larger view

Tester101
  • 131,097
  • 78
  • 316
  • 608
1

Here is the applicable code section:

2011 NEC Article 250 Grounding and Bonding

VII. Methods of Equipment Grounding

250.140 Frames of Ranges and Clothes Dryers

Frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be connected to the equipment grounding conductor in the manner specified by 250.134 or 250.138.

Exception: For existing branch-circuit installations only where an equipment grounding conductor is not present in the outlet or junction box, the frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be permitted to be connected to the grounded circuit conductor if all the following conditions are met.

  • The supply circuit is 120/240-volt, single-phase, 3-wire; or 208Y/120-volt derived from a 3-phase, 4-wire, wye-connected system.

  • The grounded conductor is not smaller than 10 AWG copper or 8 AWG aluminum.

  • The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service-entrance cable and the branch circuit originates at the service equipment.

  • Grounding contacts of receptacles furnished as part of the equipment are bonded to the equipment.

Here is the handbook commentary:

The exception to 250.140 applies only to existing branch circuits supplying the appliances specified in 250.140. The grounded conductor (neutral) of newly installed branch circuits supplying ranges and clothes dryers is not permitted to be used for grounding the non–current-carrying metal parts of the appliances. Branch circuits installed for new appliance installations are required to provide an equipment grounding conductor sized in accordance with 250.122 for grounding the non–current-carrying metal parts.

Prior to the 1996 Code, use of the grounded circuit conductor as a grounding conductor was permitted for all installations. In many instances, the wiring method was service-entrance cable with an uninsulated neutral conductor covered by the cable jacket. Where Type SE cable was used to supply ranges and dryers, the branch circuit was required to originate at the service equipment to avoid neutral current from downstream panelboards being imposed on metal objects, such as pipes or ducts.

Caution should be exercised to ensure that new appliances connected to an existing branch circuit are properly grounded. An older appliance connected to a new branch circuit must have its 3-wire cord and plug replaced with a 4-conductor cord, with one of those conductors being an equipment grounding conductor. The bonding jumper between the neutral and the frame of the appliance must be removed. Where a new range or clothes dryer is connected to an existing branch circuit without an equipment grounding conductor, in which the neutral conductor is used for grounding the appliance frame, it must be ensured that a bonding jumper is in place between the neutral terminal of the appliance and the frame of the appliance.

The grounded circuit conductor of an existing branch circuit is permitted to be used to ground the frame of an electric range, wall-mounted oven, or counter-mounted cooking unit, provided all four conditions of 250.140, Exception, are met. The exception can be applied only where the existing branch-circuit wiring method does not provide an equipment grounding conductor. There are many existing branch circuits in which nonmetallic sheath cable with three insulated circuit conductors and a bare equipment grounding conductor was used to supply a range or clothes dryer. The bare equipment grounding conductor was simply not used because it was permitted to ground the equipment with the insulated neutral conductor of the NM cable. This “extra” conductor results because the bare conductor in a Type NM cable is to be used only as an equipment grounding conductor and cannot be used as a grounded (neutral) conductor in the same manner as is permitted for the uninsulated conductor in Type SE cable.

In addition to grounding the frame of the range or clothes dryer, the grounded circuit conductor of these existing branch circuits is also permitted to be used to ground any junction boxes in the circuit supplying the appliance, and a 3-wire pigtail and range receptacle are permitted to be used.

Exhibit 250.55 shows two examples of existing installations in which Type SE service-entrance cable is used to supply ranges, dryers, wall-mounted ovens, and counter-mounted cooking units. Junction boxes in the supply circuit are also permitted to be grounded from the grounded neutral conductor. In the bottom diagram the service-entrance cable installed from the feeder panelboard to the range or clothes dryer outlet contains an insulated grounded conductor to prevent incidental contact between the conductor and metal enclosures. Such contact could result in current being introduced onto circuit paths other than on the intended path, which is the grounded (neutral) conductor.**

nobody
  • 5,770
  • 3
  • 27
  • 37
Speedy Petey
  • 16,388
  • 2
  • 27
  • 50
-3

I know that this is an old post - but I have been working a similar issue using my 3 pin older 10-30R dryer outlet for my electric 240Volt Car (Chevy Volt) charger. The only difference between the new standard (1996 to present) receptacle which is a 14-30R - 4 wire 30amp/240 volt and the 10-30R - 3 wire 30amp/240 volt receptacle is the missing ground pin. THAT DOES NOT MEAN there is no ground wire hidden inside the junction box containing the receptacle - it is there 99.9% of the time unless someone cut it off the cable. The Electrical Cable whether ROMEX or old fashioned Metal covered BX has a GROUND wire (the metal shield if BX or a bare ground wire if Romex) - just move it from wherever it is connected (usually to the metal junction box mounting screw) and extend it to the NEW REPLACEMENT 14-30R Receptacle that you should have purchased from wherever you bought the dryer (or you can get it at Lowes or Home Depot) - we are talking about $11 bucks, there about - this will give you your 4 wire/4 pin connection (Hot - black, Hot - Red, Neutral - White and bare copper- Ground) right at your outlet - no need to run an extra wire from inside the box to the dryer. Put back the 4 Prong cord that came with the dryer - make sure no bond from white to ground and be done with it - cost is minimal and a much neater and safer way to do it. What am I missing? Also - your receptacle is either 240 or 120 cannot have both in the same box. Maybe I did not understand what you meant by that statement.

Chris

Chris
  • 1
  • These circuits were originally wired with SE-type cable using the bare wire for the neutral and the insulated wires for the two hots, as NM and AC weren't available in such heavy gauges at the time. So, you shouldn't expect a ground to be there. – ThreePhaseEel May 17 '15 at 19:46
  • But you can now retrofit one, just get some 10 or 8 AWG ground wire and use any viable route. If the neutral wire in the SE cable is bare, wrap it thoroughly with tape so it can't short against the ground. Neutral is not ground. – Harper - Reinstate Monica Jun 17 '17 at 23:18
-4

I have Moved a dryer with a four conductor cord into my home that has a 3 prong outlet. The outlet provides 240V and 120V. The house wiring for the circuit provides the two hots, the neutral, and a ground wire. the ground wire is bonded to the outlet box. I replaced the cord with a 3 prong plug and attached an external ground wire to the connection of the fourth cord wire (ground) and bonded the other end of the external ground wire to the ground wire in the outlet box. I left the internal bond wire where it was for the four wire cord. This installation IS directly equivalent to the four prong installation.

As you can see, these two circuits are the same.

enter image description here

  • This installation is definitely NOT "directly equivalent to the four prong installation". Also, you DO NOT "connect an external ground wire"! The neutral in the 3-wire cord also serves as the ground since you must leave the bond in p0lace inside the dryer. – Speedy Petey Jun 02 '14 at 10:38
  • 1
    NO SIR. Neutral and ground are not same thing. They may be connected at the main breaker box, but they serve two different purposes. Neutral is the designated return path for the hot wires, while ground is fail safe return path for stray current in the event that a hot makes contact with the frame of metal appliance. The four wire installation has a ground wire integral to the cord, while the 3 wire with external ground supplies the exact same thing. The picture provided in the post above shows how to do this. (H+H+N+G) = (H+H+N)+(G) simple math! Always bond appliances to a good ground. – Posted by another Tim Jun 08 '14 at 03:09
  • 1
    Tim, please do NOT explain this to me. I am WELL aware of how it works and you are wrong. A 3-wire dryer cord DOES NOT use or require an "external ground". This may have been acceptable for a while many years ago but it is NOT acceptable now. A 3-wire dryer cord has the neutral bonded to the dryer case internally. The neutral DOES/DID serve both purposes. This exception was removed from the code several cycles ago which is why 4-wire dryer cords, with a dedicated equipment ground, are now required. – Speedy Petey Jun 08 '14 at 12:26
  • See post above for proof. – Speedy Petey Jun 08 '14 at 12:38
  • @SpeedyPetey I have read the above and totally agree. What I have done is the equivalent of a four wire system. I have used a three wire cord for the current carrying and have an external ground wire. It is wired exactly like it has a four wire cord attached. the ground wire is bonded to the ground wire present in the outlet box and connects to ground wire on the frame as per instruction manual. I am not using the neutral as the ground. How is it any different? – Posted by another Tim Jun 08 '14 at 21:24
  • @SpeedyPetey I think we are on the same page, we just dont know it. I edited my original post for clarity. I am trying to show that I am using the four wire system. I believe that it is a safer system. I am just doing it with a ground wire that is not integrated into the cord. Sorry for the confusion. – Posted by another Tim Jun 08 '14 at 21:55
  • Sorry, but this is NOT safer, NOR is it the same thing. Whatever though, you are free to do as you wish. Just please do not suggest to others that this is an appropriate or safe alternative. – Speedy Petey Jun 08 '14 at 22:47
  • There. As you can see, this installation conforms to all the NEC stuff you have shown. This is a safe installation and is equivalent to using a four wire cord. – Posted by another Tim Jun 08 '14 at 23:55
  • You keep telling yourself that Tim. It is NOT complaint and NOT the same thing. You keep posting and editing just so you can convince everyone you are right. You are NOT. – Speedy Petey Jun 09 '14 at 09:33
  • The drawing was my final edit. The electronic circuit is exactly the same. Electrons cannot tell the difference. If someone, including you, can explain to me why this is not electrically the same as using a cord with 4 wires, then I will retract it. If your reason is that the ground conductor is separate from the cord, say so! That is the only difference. Stop with the "You're wrong" stuff and give an actual reason. – Posted by another Tim Jun 10 '14 at 00:14
  • Tim you are incorrect, it is not NEC-compliant to have a bare THHN wire coming out of the outlet like in your left-drawing. It is of course electrically-equivalent, but it looks extremely unprofessional _(which is a large part of the NEC - it's not **only** about safety)_. If you already have a dedicated ground coming to the outlet _(which is the hard part)_, you should just replace the dryer-cable and outlet with a 4-pronged connection _(the easy part)_. – BlueRaja - Danny Pflughoeft Sep 03 '15 at 16:46
  • I would say Tim's separate grounding strap (with bootleg strap removed from the dryer) is certainly better than no ground at all or a "legal" bootleg ground which is what a 3-prong plug is. But it is not code. The Code way is to use a 4-wire cable and fit a 14-30 receptacle which uses that existing ground, then gather some hobbits and elves and toss the 10-30 receptacle into the fires of Mount Doom from whence it came. – Harper - Reinstate Monica Jun 17 '17 at 23:24