9

I was going to replace an old 3 prong dryer receptacle with a new one. It being an old townhouse built in the late 60's I assumed there wouldn't be a ground wire, but when I took the outlet out I noticed there was a metal electrical box with with the 2 hots, neutral, and an extra bare copper wire. The copper wire is pinched between the box and what looks like some kind of face plate. There is no ground screw, I assume they did it this way to ground the metal box. I confirmed the box is grounded with a multimeter reading 120v between one of the hots and the box.

I decided to upgrade to a 4 prong outlet and dryer cord. What would be the best way to go about grounding the box and outlet? I bought some 10 gauge wire, grounding wire connectors, grounding screws and clips. All the research I've done says to ground the box first then the outlet, using either a ground screw or grounding clip. If using the grounding screw, if the copper wire coming from the bundle is long enough, wrap around the screw and then to the outlet. Other "proper" method is to grab 2 extra pieces of copper wire, and using a wire nut twist them together with the ground wire, with 1 scrap pigtailed to the ground screw and the other going to the outlet. I would have to cut the ground wire because I cannot get it out of it's current pinched/squeezed position. However this box is small and these are 10 gauge wires, I don't see how to squeeze all that in together with the outlet in this tiny box.

Some questions I have, can I leave the ground wire as is and just run a standalone pigtail from ground screw to the outlet since the box is already grounded or does the piece of copper wire going to the outlet have to be twisted together with the ground wire using a wire connector? If they must be twisted together, can I use a grounding wire connector with a hole and top and just have the pigtail from the screw go through the hole into the outlet while twisted together with the ground wire? I would save a little space at least. Also, since 10 gauge wire is thicker, it might be tougher to wrap around ground screw and read someone recommending using a yellow fork terminal connector, I thought those were only for stranded wires?

I am also not sure if the ground wire is connected to anything else below the box, although it's doubtful. The new outlet also has a grounding strip connecting it to the plate of the outlet, although some don't recommend relying on that to ground the outlet. Thank you.

Edit: to clarify, there is a threaded 10-32 in the box, which I plan to use with grounding screws I bought.

enter image description here

enter image description here

enter image description here

enter image description here

Update: Thank you all for the help. It did indeed have a mud plate, the opening was a bit too small for the new outlet to fit through, the previous 3 prong outlet did fit in there since it had a round body with only 3 connections. I went ahead and cut out some of the sheet rock to enlarge the hole and put in a new 2 gang mud plate. The box itself was not very deep, what I should have done was cut the wires for the hots and neutral short because they were a pain to twist around with them being 10 gauge. Probably not good to have that many twists I'd imagine.

enter image description here enter image description here enter image description here

I originally did all this because the terminal block and power cord connections had melted/sparked and tripped the breaker. Most likely the screws became loose over many years due to the vibrations.

enter image description here enter image description here

Voltages checked out OK with a multimeter on the outlet and the terminal connections on the dryer. So far dryer works and nothing has caught on fire or exploded lol. Seems every month I have to learn new things when fixing something else that breaks.

lxflr
  • 93
  • 1
  • 6
  • If you read 120 between hot and ground, you have good ground. A bad/broken ground will read 0v. – crip659 Sep 11 '22 at 23:14
  • @crip659 Yes, I was wondering if I can just leave the ground wire untouched and ground the outlet to the box since the box itself is grounded but it's probably not code compliant. – lxflr Sep 11 '22 at 23:53
  • 2
    If you're having trouble fitting everything in the box, there are surface-mounting "extenders" you can put on to give you a bit more room (at the expense of having the outlet protrude a bit from the wall). – brhans Sep 12 '22 at 00:33
  • 4
    Your new outlet looks like it might be too wide to fit in the existing box opening. If the main part of the box under the mud ring is wide enough, it might make sense to widen the opening in the wall to fully expose the width of the box, remove the mud ring and instead install either a 2-gang mud ring or box extender. That would deal with the issue of freeing up the ground wire as well. – Armand Sep 12 '22 at 02:07
  • 3
    Thx for posting the updated photos! – Armand Sep 13 '22 at 23:53
  • 3
    You are better off NOT cutting the wires short. You are supposed to have 6" wire length beyond the face of the box (so that things can be pulled out to rewire without disconnecting) and it doesn't matter if it's coiled up in there, so long as you don't replace the outlet every week. – Ecnerwal Sep 14 '22 at 01:29
  • @lxflr you might also check that the neutral and ground wires are both terminated on the appropriate bus in the panel. They should be since both were apparently being used, but with a 4-prong receptacle on what was a 3-wire circuit, if I were in your situation (as I recently was) _and_ felt totally comfortable opening the panel, I would check that. (Incidentally I think the wiring of the old receptacle was technically incorrect, because the third prong there is a ground not a neutral, but it was apparently connected to the neutral wire -- that's now moot with the 4-prong receptacle). – trawson Sep 14 '22 at 01:50

3 Answers3

8

The ground wire coming off the cable must go to the metal box first. That's a Code requirement.

If it is competently attached to the metal box using a feature intended for that purpose, you're all set there.

The new receptacle can pick up ground from the metal box one of three ways:

  • If the mud ring is clean bare metal, and the metal yoke of the socket bottoms out on it. This doesn't usually work when a box is inset somewhat into the drywall, like yours is.

  • If the socket is labeled "Self-Grounding", it will pick up ground off the mounting screws. (this is a special brush that assures good contact).

  • You run a wire from the ground terminal to a ground clip or ground screw in the box.

  • You replace the mud ring with a "domed cover" that has flattened corners, which make solid clean-metal contact with the box.

You might have bought the wrong receptacle for this application. That one is designed to fit a 2-gang box. Check its instructions for if it can be installed in a 1-gang box. Armand's guidance for replacing the 1-gang mud ring for a 2-gang is one way to solve that, but will require a 4x4 hole cut in the drywall. Make sure you get a cover plate that will cover it.

Harper - Reinstate Monica
  • 295,284
  • 26
  • 275
  • 720
  • Thank you, I did indeed have to replace the mud ring and widen the hole in the wall. I used a grounding screw to wrap the ground wire for the box and from there connected it to the outlet. – lxflr Sep 13 '22 at 23:26
  • Can you reference the code section that requires the EGC to go to the box _first_? That's new to me; I thought it was fine, for example, to attach two pigtails to the incoming ground wire, one to the box ground screw and one to the device. I know there's a requirement that all EGCs in the box that are not just passing through be connected to the box, and that it needs to be possible to remove a device from the box without breaking the continuity of the ground to another outlet downstream. But I can't find anything that says the EGCs have to be connected to the box first. – trawson Sep 14 '22 at 01:31
7

There should be (almost always is) a 10-32 threaded hole somewhere in the box. Normally it's the smallest hole. In newer boxes it's often in a "hump," which provides screw clearance if mounted to a hard surface, and makes it easier to find, but in old boxes, usually not.

If not, you can get self-threading grounding screws, drill the approriate size hole, and thread one in.

In either case, you connect the grounding wire to the box with the screw, and either extend it to connect to the receptacle, or join it to a pigtail to the receptacle. I'm personally dubious about depending on "self-grounding" of the receptacle metal parts to the metal box for 30A receptacles.

Ecnerwal
  • 201,085
  • 10
  • 245
  • 533
  • 1
    I'll edit my post to clarify that when I mention the ground screw, I am referencing a new ground screw that I bought to be used with the 10-32 threaded hole in the box. So in this case would you recommend cutting the ground wire from it's current location and try to wrap it around the ground screw? Space is a bit cramped in there, I figured it might be easier to twist a pig tail on the screw outside the box, then twisting it and the ground wire together with a a wire connector, something like this: https://imgur.com/2KvqTx2 – lxflr Sep 11 '22 at 23:52
  • 2
    You should be able to remove the grounding wire without cutting it. That may require loosening the mud ring (what you call "some kind of faceplate.") Cutting wires is a last resort, since they are difficult to make longer. – Ecnerwal Sep 12 '22 at 00:17
  • Perhaps use a split bolt rated for 3 conductors to join the existing ground wire without cutting it to a ground wire from the new outlet and a ground pigtail attached to a grounding screw in the metal box? – Armand Sep 12 '22 at 02:04
5

You may have a 4" wide box under the visible mud ring. Sample photo of 1 device mud ring which may be what you have:

enter image description here

Sample photo of 2 device mud ring replacement which would give you more room to work with, but require widening opening in wall:

enter image description here

Sample photo of 2-gang box extender to extend box more than just a mud ring would:

enter image description here

Armand
  • 4,356
  • 7
  • 26
  • 1
    You were correct, I upgraded the 1 device mud ring with a 2 device one, pictures in post added. – lxflr Sep 13 '22 at 23:12