1

Does adding a horizontal pipe, say 6in, in between the two S elbows convert a S-trap into a P-trap? Is it code?

See picture

S-trap to P-trap

isherwood
  • 129,178
  • 7
  • 160
  • 386
Max
  • 643
  • 4
  • 17
  • Oh for Pete's sake. Now I have to be careful about VtC on plumbing, too, huh. Well, in this case, I'm certain of the "it's precisely a duplicate, not just related" but I am not a fan of the "1-vote close" in general. – Ecnerwal Dec 05 '22 at 03:20

1 Answers1

3

If you add a vent at least two pipe diameters (4" since this is 2" pipe) away from the exit of the P-trap on the left, then it's to code.

If not, it's still an S trap.

Ecnerwal
  • 201,085
  • 10
  • 245