33
So, weird stuff is afoot and even my electrician is lost. All my HDMIs are hot, as well as my COAX coming from the cable company.
Details of what is going on.
  • Internet & cable went out, called service repair, cable guys noticed the HDMI & COAX were hot (22-62v)
  • house lights and appliance started to act up - lights dimming or brightening when other lights or appliances in use, built in microwave stopped even heating, bathroom light flickering (old school tube lights)
  • Called 311, city came out, found something wrong on their end, fixed that = still hot HDMI & COAX
  • electrician came out, discovered by ground was cut when I recently had whole house re-pipe with flex, fixed that, re-grounding the electrical, added new grounding(?) connector for cable COAX incoming to house, BUT HDMI still hot on every TV or connection, new or old wiring. checked all outlets, all 'correct' 120v reading. COAX may still be hot, hard to tell, but seemed fine, reading nothing from outside connection. HDMI hot no matter where TV or modem or cable box or PS4 is connected to in the house.
I'm super scared and don't know WHY this is happening and if it's a problem. I even checked my electricity 'pen' reader on an HDMI at work to see if it was the reader. It's not the pen. It's my wires.
Any help on diagnosing what the heck is going on or who to contact about this would be great.
  • To add to this story, I had a new outlet installed by a different electrician/general contractor and when they first tried to connect it, the contractor connected it to the wrong wire somehow and lightening came out of my socket that my TV, cable, and modem are connected to. It also blew out my outdoor lights out front. It was intense. It was later fixed by their electrician. Could this have caused something, destroyed my TV/Modem/Cable box, etc? It was all connected to a surge protector, but it was intense. –  Mar 02 '23 at 16:09
  • Also, my son's TV upstairs also has a hot wire and was not an issue with the bad wiring incident, that I know of. –  Mar 02 '23 at 16:12
  • Suggest migration to diy stack exchange. In the meantime, get the electrician back out there to troubleshoot. You may have an open ground from that branch that needs to be chased down. – hacktastical Mar 02 '23 at 16:15
  • @AlexiaWilson additional info belongs in the question ... it does not belong in a comment ... please use the `edit` button – jsotola Mar 02 '23 at 16:23
    what do you mean with "hot"? How did you you determine that? Please be specific and add a picture of how you measured this. – P2000 Mar 02 '23 at 16:37
  • Probably not destroyed the box if everything still works, but might have caused enough damage to cause hot wires. I would try to have the box/es exchanged for new ones, besides having the electrician check things. – crip659 Mar 02 '23 at 16:37
    "lights dimming or brightening when other lights or appliances in use" -> is this a case of https://diy.stackexchange.com/questions/184016/half-my-power-out-but-firing-up-an-appliance-turns-it-back-on/184022#184022 ? – user253751 Mar 02 '23 at 16:38
    Have you disconnected your TV, cable modem, and router and still observing the same? It's quite possible these were destroyed in the arc flash "lightening" and are now pushing voltage to the coaxial/HDMI lines. This should be checked regardless of what else you do. – Fredric Shope Mar 02 '23 at 16:47
    Please explain how you are measuring "HDMI voltage". Add detail to your question. Exactly where are you attaching each of your two meter probes? If you are attaching to pins of an HDMI cable, where is that cable connected at the other end? Same with Coax. And when you say "Coax may be hot, hard to tell" it makes me wonder even more about what you mean by "hot" because it's not hard to tell, you can easily measure it with a meter. Please explain! – jay613 Mar 02 '23 at 16:49
  • I'm *guessing* that you're measuring the HDMI head shell and the coax braiding both compared to ground, and on that basis I attempted an answer. – jay613 Mar 02 '23 at 17:01
    FWIW coax is supposed to be "hot" at 24 up to 60 volts... – jesse_b Mar 03 '23 at 13:12
  • I had a weird issue with a cable modem, with an issue in the power supply. The result was making the incoming cable sheath hot, pushing multiple amps down the sheath to ground. The main symptom was the cable isolater on the input was getting too hot to touch, since it was not made to have all that current coming back down the sheath. Similar issues with weird stuff in the house, since there was now a weird ground/neutral loop going on. Check your cable isolator, unplug and remove wires from your cable modem, see if that helps... – Jon Custer Mar 03 '23 at 19:08
TLDR: Forget the networking stuff, that's only a symptom. Call the power company and report a power outage, tell them "Lost Neutral". When they ask, don't talk about other symptoms other than "my appliances keep frying". DO NOT tell them a story. They will tell you to call an electrician, which won't work, you tried it.
You have a lost neutral on your AC power! Get it fixed for free!
The reason everyone's missing it is that they're focusing on your networking and not your AC power supply. From here on out, forget the networking. Focus on your broken AC power.
In the USA, we get 2 hot wires and a neutral. The 2 hot wires are 240V apart. The neutral is in the middle (or it's supposed to be) giving us 120V, twice, in two "poles". When the neutral wire breaks, we still get 240V, but the poles are not 120V anymore. Neutral starts wandering all over the place. So it might be 100V/140V, 90V/150V, 60V/180V, it varies.
The insidious thing about Lost Neutral is that usually, the voltage deviations aren't that bad. So everything still works. It just becomes subtle gremlins.
Yeah. "or brightening". That's what we're talking about.
Normally, this doesn't get too extreme, because neutral current has a couple of alternate paths. Each of yours had a problem, though!
First, at your house's main panel, neutral is bonded to ground which is wired to a Grounding Electrode System (GES, i.e. water pipe clamp or grounding rods) which ties to the actual dirt. So neutral current will try to go out your GES, through the actual dirt, to a neighbor or transformer's GES and then back to neutral. Dirt isn't a very good conductor (that's why we bother to mine copper), so it still allows a fair bit of wobble. Now you were mentioning
Right. You had a water pipe GES, which was broken when converted to plastic pipe - common problem but still negligent. The electrician fixed you up with a different type of GES, probably ground rods and advised you to "mumble mumble" lost in the noise.
The second path is cable TV, typically grounded at both ends for safety. Neutral current will try to seek through that. Of course it's not rated to return 20 or 30 amps of current, so this happens
Varying, huh? That's typical of Lost Neutral.
Right. Because the cable guy gave up on you ever fixing your Lost Neutral problem, and simply disconnected your cable TV cable from ground on your house's end. You do not have their permission to use their cable jacket as a substitute for your AC power neutral.
You are saying "the cable TV wire is hot" - probably not. Probably, the cable TV wire is properly grounded. Your house's grounds are hot because of the Lost Neutral.
"Correct"? So you're using a dumb "pass/fail" tester that doesn't actually give you a voltage number. It just says "In the neighborhood of 120V" or "not". So it will read "correct" even if your house has a Lost Neutral. We need to get you a better tester. An excellent tester for all sorts of things, way beyond voltage - is the "Kill-A-Watt" home energy monitor. About $25 and Walmart stocks it. Just plug it into any outlet and it will readout the voltage. Now check several outlets and watch for that "high/low voltage" symptom. 100/140V etc.
What actually happened
If you look at an electric line from the poletop to your house, you will see an aluminum carrier wire with 2 insulated wires wrapped around it. That stuff is triplex. The bare wire is the physical carrier wire that carries the weight of all the wires. Unfortunately, it's also neutral. It whips in the wind for 30 years, and aluminum has no fatigue limit. SNAP! This is often (but not always) seen by an obvious gap and the cable hanging by the 2 insulated wires. That's a hard failure, and it's more likely on the neutral than the hots. (unlike an underground installation where it's equal chance).
Get it fixed for free today
Anyway, 95% of the time, a Lost Neutral occurs in the zone that the power company is responsible for maintaining. That overhead line wire. You call them up and report an outage, they send an insulated boom truck and it's fixed in a jiffy once the lineworker spots it.
When I called to have ours fixed, on a Sunday, they were out in an hour. They identified a neighbor's lost "hot" and fixed that too.
    "weird unrelated symptoms" -->> lost neutral just-about all the time, at least from the number of posts on SE about it. – Criggie Mar 03 '23 at 03:13
    Our aluminum carrier wire / neutral whipped around in a storm and broke at the weatherhead a couple years ago. Lights in the house got brighter and brighter and brighter and... I flipped the main switch in the breaker box & called the power company, which - yes - came out & fixed it for free – G. Ann - SonarSource Team Mar 03 '23 at 18:37
    @Criggie And always answered by "Harper - Reinstate Neutral" – user253751 Mar 03 '23 at 18:37
    Rule of thumb: If it seems like you have a poltergeist that only appears in the form of electricity, suspect an open neutral. – Chris Parker Mar 04 '23 at 15:20
  • @Harper - Reinstate Monica , Can you expound on this further: "So neutral current will try to go out your GES, through the actual dirt, to a neighbor or transformer's GES and then back to neutral" What does "...transformer's GES and then back to neutral" mean? – OpenCoderX Mar 05 '23 at 06:56
  • @OpenCoderX Like other houses, the utility's transformer also has its very own neutral-ground bond, and GES (wire down the pole to ground rods in the dirt). – Harper - Reinstate Monica Mar 05 '23 at 07:31
  • @Harper - Reinstate Monica Is the implication here that the current will flow back to the transformer and back into the grid? – OpenCoderX Mar 05 '23 at 23:15
  • @OpenCoderX yes, current flows in loops. For movement on the hot wire to occur, a corresponding movement on neutral must also occur. – Harper - Reinstate Monica Mar 05 '23 at 23:32
13
Everything you are describing could be explained by a disconnected neutral that might be within your premises or outside. You should start by calling your power company and suggesting they come look for that specific problem. You could also call an electrician to look for it.
With this problem:
  • Some devices will not work sometimes, or will work partially or poorly with fluctuating supply voltage when other devices are turned on. The connection between devices will appear random.
  • Devices with metal housings (including the metal housings on HDMI cable ends and the ground shield on coax cables), where those housings should normally be at ground potential, may come up to various voltages. The effect gets worse if the building's grounding is poor or doesn't exist.
jay613
  • 34,254
  • 136
    OP said "electrician came out, discovered my ground was cut...." This certainly confused the symptoms too. – Criggie Mar 03 '23 at 03:14
When you say the HDMI and Coax are hot (22 V - 60 V), I assume you're talking about the outer metal shell on those cables? If that's the case, it means that all your metal chassis/boxes are hot, which is bad.
Since those metal boxes/chassis should be connected, eventually, back to earth ground, that indicates there may be a problem back in your circuit breaker (or fuse) panel. Like maybe the neutral and earth ground have been reversed, or one of them is no longer connected.
Unless you have some experience in this area (these kinds of problems can be tricky to track down the root cause of), you need a good electrician.
SteveSh
  • 6,765
  1. Disconnect all items that have coax and/or HDMI from AC power/Wall AC adapters and from the wall's coax plate(s).
  2. Now, measure the voltage from pin to shell on the closest-to-cable-provider/utility-plate. If it is not 0VDC and 0VAC, call your cable provider.
  3. One-by-one start re-connecting your items to the coax/hdmi. Measure the voltages. If OK, re-connect their power source. Re-measure the voltages. If good, repeat this step for all of your items, one-by-one. I'm guessing that the culprit(s) can be quickly determined in this fashion. Given your 'lightning' incident, it could very easily be that all of your devices will have to be replaced.