Condition: My house is 37 years old and our kitchen remodeler (not an electrician) did the following. He tapped into one of the oven’s 120 volt legs to power a 120 volt duplex receptacle. There is no neutral wire back to the panel for this duplex receptacle’s circuit, instead the remodeler used the ground wire connected to the oven’s 3-prong receptacle. The duplex receptacle is used to power the microwave and the warming drawer. All appliances are independent of each other. At times about 20 amps flowed to the microwave and the warming drawer. When using both of these appliances, touching their metal surfaces was required.
Remedy: We used the oven and warming drawer for some time before identifying the problems and having them rectified by licensed electricians and inspected by our city.
Question: While we never felt a shock, my conclusion is that because the oven’s ground wire was used as a neutral wire, the ground wire energized the metal on the oven and the microwave when the duplex receptacle returned current to the panel. We did not feel a shock because in our instance, the voltage was very low on the duplex receptacle’s neutral wire. Are these conclusions correct?