Wow, many violations at once. But I'll start with what you're asking about.

Tight grouping of wires will cause thermal problems. I see two bundles of (edit:) 12-22 wires, which are treated particularly harshly by 310.15(B)(3)(a) in terms of wire derate.
- #12 is 15A
- #10 is 20A
- #8 is 27.5A
- and above that you're going to want aluminum
Now you can quibble that it's less than 2 feet, but (edit) look what's happening on the right side. The GFCIs alone contribute 10 wires, which run from the top of the GFCIs to the top of the panel. And even if you could whip out your ruler and slide in on a technicality, that misses the point - you don't want to defeat convection wire cooling without a really good reason and this "OCD done wrong" neatness is not a good reason at all.
If they did this in the panel, they may have done it in the walls, which is much worse because you have 2 wires instead of 1 in a given cable.
Theft of copper. Not an NEC violation but a violation of your state's licensure. Spare length really helps later (i.e. some time in the next 50 years of the panel) when you need to move things around, to add things or correct error. So nipping off every spare bit of length mostly just serves the electrician, who can take the cut ends home and get $3/lb for shiny copper scrap. Generator interlock and surge suppressors must go at the top, and emerging smart breakers sometimes need an extra space for the electronics. So over time, this will turn this formerly neat panel into a ruckus of wire nuts... which defeats the "claimed" purpose of doing this in the first place!
Obviously this isn't a concern if you're not looking any farther past getting the closing papers signed. Then the neatness helps by tricking the home inspector into confusing neatness and code compliance.
White wires not identified to be hot wires on the left side.
Cable clamps look sketch.
Guard covers on the utility side of the main breaker terminals, a NEC 2020 thing IIRC. Another NEC 2020 violation is lack of surge protector, which then segues back into the copper theft.
Running the panel without its deadfront cover installed or with a non-approved clear glass cover. Now maybe the person is not doing that, but if they aren't, then there's no earthly reason to create the thermal problem.