I live on a farm, with an overhead line coming in, a transformer on a pole, and a line to the meter. My main panel has 200A breaker, that's split between house, pole barn, and ag barn.

We have regular outages, restorations, and surges so, I've already purchased a Siemens FS140.

I would prefer to have the entire farm protected but with no room for an additional breaker I'm considering installing the FS140 without a breaker. The installation instructions as well as other online info does not give instructions for installing without a breaker. While I realize the breaker is preferred, it doesn't seem to be absolutely required.

Best path forward?

What is the risk or lack of protection am I exposed to with a breakerless install?
If minimal, or acceptable, how to install without breaker?

Suggestions for panel mods add or replace panel,subpanel creating room for a breaker?

Return the FS140 and buy a different surge protector?

Here's a pic of my main panel. enter image description here

bsd
  • 156
  • 8
  • 3
    You mention three things fed from this panel (house and two barns) but there are three breakers plus a fourth set of wires connected to the through-lugs at the bottom of the bus (that look probably too small for 200A). What’s the fourth load, or is one unused? – nobody Jun 29 '23 at 12:59
  • That's likely input from solar panel – bsd Jun 30 '23 at 06:48

2 Answers2

7

That panel there is something some of us call a "Ranch Panel". It has a (typically) 200A main breaker, 4-12 breaker spaces, and then "Thru Lugs" onward to allow the full breaker ampacity to be carried onward to other points of use.

Must be installed past the main disconnect

To install it before the main disconnect, two things would need to be true: First, your panel would need to provide auxiliary lugs for that. I can't see for sure, but since this is a recent feature, I think yours does not. And second, your SPD would need to be a Type 1, designed to be installed like that.

That one is is a Type 2, which can only be installed after the main disconnect. And the panel doesn't appear to provide special lugs for that. Those bolts connecting the main breaker adapter to the main bus are not suitable unless the panel instructions and labeling say otherwise - which I doubt.

The surge can share a breaker, though

And this may be an answer here. You need to use a legal method to tap or splice: don't "slip the extra wire under the lug", don't piggyback terminals contrary to instructions, and definitely don't do this LOL

enter image description here

You better be laughing.

Given what's in your panel, I would get some black #6 THWN wire and pigtail onto one of the 60A breakers. Two #6 and a #12 should fit fine onto one of those very large wire nuts.

Is this really the right place for a surge suppressor, though?

Most people, if their radon detector goes off, they say "I must have radon" (reasonable). But if their GFCI trips, they say "My GFCI must be broken!" (say what??) It's true, you know I'm right. In a similar vein, people think "all surges come from a distant outside place and therefore I must fortify the point where power comes into my home".

Well, as Pogo says, "We have met the enemy and he is us!"

Your own appliances are probably responsible for a great deal of the surges you face. So there's a lot of logic to putting surge suppressors closer to the appliances that need protecting. E.G. my first choice of location would be the panel in the residence. Then also any outbuildings with sensitive electronics.

Let's clean up that panel.

First, that deadfront cover. It needs to be installed. The debris is getting in there either because you're running it with the deadfront cover off, or there are additional twist-outs that have been removed. Any empty twist-outs need to either be covered with an approved blank cover (though, they are flimsy) or rivet on steel of the same thickness. I suppose you could tack weld some steel (tack welding is fine; the twist-outs are meant to twist out) but the work needs to be "Neat and Workmanlike" and then you need to paint it. The panel interior paint is weird, it's similar to Glyptal. Glyptal would be fine, actually.

If the deadfront cover is missing, contact Siemens with the model number of the panel and see if they have a deadfront to sell you. Otherwise the panel will need to be replaced. Now there is a "Hail Mary" play that is sometimes possible: Panels have 3 parts: the deadfront cover, the steel box, and that huge plastic thing with everything else mounted on it called the interior. The interior attaches with 2-3 bolts (sometimes one is behind the main breaker). Search the panel for a "Box Number" - on the box or "use with box number ___" sticker on the interior. Then hit Siemens' catalog and see if they still make any "ranch panels" with that same box number. I know Siemens makes a 12-space ranch panel - wouldn't that be nice! If they do, buy it and have your electrician swap interiors next time they visit. The new cover will fit the new interior.

Could you manufacture a deadfront cover? Sure, if it looks professional. Again NEC 110.12 "Neat and workmanlike". The critical dimensions are that it needs to lay reasonably tight against the terraced part of the branch circuit breakers, and catch the outer edge on the left or right side of the breaker. That is the only thing that keeps the breaker from tipping out when you forcefully shut it off.

Next, take a look at that wire going into the 150A breaker. If it is 4/0 aluminum or 2/0 copper, it belongs on the bottom "thru lugs" - the ones currently occupied by that skinny #4 or #2 aluminum. Then the 150A breaker goes away and you have 4 spaces free to a) attach that #4 or #2 aluminum to a 70A or 90A breaker... and b) attach a breaker for the surge.

I can't tell from all the spider condominiums, but it looks like the aluminum cable has strands broken off to fit on those terminals. That is a big, big NO. There is no earthly reason not to put 4/0 aluminum feeder on the bottom lugs. That is specifically what they are for, and yes, they are protected by the 200A breaker up top.

If it is smaller than 4/0 or 2/0, does it go directly into a panel that immediately has an appropriately sized e.g. 150A main breaker? Because I'm not a fan of this, but in that case you can do the same thing, moving it to the "Thru Lugs" and again deleting that 150A breaker to free up 4 breaker spaces. It's not a perfect solution but having 150A wire fused 200A is certainly less bad than having 65-90A wire fused 200A, since 150A wire will endure the overload - 65-90A wire will burn up.

The 4 breaker spaces can be used a) to land that thin #4Al or #2Al wire on a 70A or 90A breaker. And to give 2 breaker spaces dedicated to the surge suppressor. However I'd be more inclined to share the surge onto one of the 60A breakers, and then reserve the last 2 spaces for generator interlock, solar, or whatever comes up.

Harper - Reinstate Monica
  • 295,284
  • 26
  • 275
  • 720
  • 1
    We just bought this place a year ago, so we're learning about the place everyday. I'm going to hire help and do everything "the right way". I'm going to accept this answer as install the FS140 at the house subpanel, and buy another SPD (if/when needed) for each barn. BTW: This is my retirement project, so budget is open to intelligent solutions. I'm open to buying a new "ranch panel" and tidying things up. Suggestions for replacement panel designed to support Type 1 SPD? – bsd Jun 30 '23 at 09:21
  • 1
    @bsd I would talk to authorized dealers (electrical supply houses). The rules changed quite recently to *require* surge suppressors on most installs, and the industry is still adapting to suit. Siemens calls ranch panels "trailer panels". One manufacturer makes a 12-space ranch panel with the thru-lugs, which moots the point by giving you more spaces lol. – Harper - Reinstate Monica Jun 30 '23 at 17:57
  • But might still need a type 1, no? – bsd Jun 30 '23 at 18:21
  • 1
    @bsd you only need type 1 if it will be installed where it has no breaker protection. A type 2 can share a breaker with a feeder or branch circuit load. Some panels provide auxiliary surge protector lugs on the utility side, others on the breaker protected side. Honestly the second one makes more sense since it doesn't force you into a Type 1. – Harper - Reinstate Monica Jun 30 '23 at 18:57
6

The installation instructions as well as other online info does not give instructions for installing without a breaker. While I realize the breaker is preferred, it doesn't seem to be absolutely required.

Following manufacturer instructions is a part of code. So if the instructions say to install it with a breaker, that's absolutely required.

Your best path forward is probably to put in a surge protector at the (I would assume, but it might make a donkey out of me) sub-panel at each of the 3 buildings served from your "ranch panel" at the power pole.