The power to my master bedroom stopped working. I changed my light fixture first from a ceiling fan/light combo, I'm getting power in room from what volt meter says. I have also changed outlets out to three prong from the old 2 prongs. This house was built in 69 and never been rewired.
What I need to know is what my wiring should look like on first outlet in room that also joined by the outlet in my living room.
  • When you changed from 2-prong to 3-prong, how did you connect the grounds? – Cheery Sep 29 '23 at 01:54
  • you were changing the wiring and now nothing works – asinine Sep 29 '23 at 02:02
  • There is no ground wire at all – Gabrielle Hulsey Sep 29 '23 at 02:05
    @GabrielleHulsey Are you aware that you can’t just put in plain 3-prong outlets unless the breaker is GFCI? You need GFCI outlets (or just one if the others are chained off of the Load terminals of the GFCI) and have to be marked “no ground”. – DoxyLover Sep 29 '23 at 02:26
  • Well, you may be able to put in three-prong without a ground wire if the system was built using metallic conduit. But it the house was new in '69 that seems unlikely, so yes, GFCI would be absolutely necessary if you want three -prong outlets and even then you'd have to use the "no ground" sticker on all the outlets so I figured. – keshlam Sep 29 '23 at 02:50
    What does it look like now? What did it look like before you changed it? PHOTO, at least of the current situation, would be tremendously helpful. – keshlam Sep 29 '23 at 02:52
  • "I changed my light fixture first from a ceiling fan/light combo" - prob where everything comes to and goes from; the box in the ceiling. Pull the fan and show a pic of those wires. Yeah, I know, good times... – Mazura Sep 29 '23 at 05:24
  • The drawing does not show a wall switch for the "fan & light... now only light" in the master... – Jimmy Fix-it Sep 29 '23 at 05:35
  • Are you making changes because the power in your master stopped working, or did the power in your master stop working so you started making changes? – FreeMan Sep 29 '23 at 11:36
In order to do this, the ceiling junction box must be rated for a ceiling fan. Fans create vibration that will destroy non-fan-rated boxes, and may pry their nails out too! Revisit that issue and upgrade as necessary.
I have also changed outlets out to three prong from the old 2 prongs. This house was built in 69 and never been rewired. There is no ground wire at all...
Ground requirements were phased in from 1954 to 1965. By NEC 1965 they required grounding for every circuit that was not a dryer or range (sad story there).
If you do not see a ground WIRE, there's a significant possibility that you have metal boxes and the metal boxes are grounded... either a) by grounding sheaths on the type of wire used, or b) by use of metal conduit. Or there may be ground wires in the back of the box; it's very common for novices to not notice or state them.
Assuming your boxes are grounded... If the box is metal, you can ground the receptacles simply by using the better ($3) "spec grade" receptacles, which automatically pick up ground via contact blades on their mounting screws. The cheap ones will also pick it up if they have hard, clean, flush metal/metal contact with the metal box, however the little paper squares holding the screws on must be removed for that to work.
It should look exactly like you found it.
And, if "tabs" were broken off on the old receptacle, they need to be broken off on the new receptacle also. Failing to do so will either make light switches no longer work; or make a big spark and trip breaker(s).
If things simply stopped working, then look closely at the neutral wires (white, though not all whites are neutral) and make sure neutrals are exactly as you found them.