I have an existing 50A circuit for an induction cooktop wired with 6/3 stranded Romex. It runs through the finished basement ceiling bulkhead and at some point near a rim joist where it feeds to 1st level kitchen. I am thinking of adding a junction box to feed a second 14-50R in the garage (1st level).
The j-box will be recessed and it's on the hidden side of the bulkhead anyway so visually it's a perfect spot. I am thinking of running a 6/3 wire from here, through the plate in the rim-joist and out to the other side of the (attached) garage wall.
The charge will be limited to 32 amp draw (14-50P). I will not be using both circuits at the same time as EV charge will be a scheduled one only at night/early morning hours. The cooktop is a multi-zone and specifies 12,000W (50a circuit). The maximum a single zone can draw in boost mode is 3,600W (15A).
Would branching out this circuit be to the code (KY USA)? And if so, what kind of box, and splicing hardware will I need? Other option is to run a whole new circuitry from the primary panel to a new garage sub-panel but at the moment I have no need, and the run from this projected J-box is only a few feet, which saves on cabling. Anything else I need to be watching out for as far as going through the interior wall to the attached garage? Presumably, that's an insulated wall.
Thanks! enter image description here
David
  • 1,047
  • 34
    A junction box cannot be behind drywall, can be behind a access door. I think you would need a device that shares the circuit by cutting off the EV when the stove is on. Been some talk on here about them. Depending on your location, a receptacle in a garage must be on/protected by a GFCI(that size means a breaker). Usually recommended to hardwire the EV charger, not use a plug. – crip659 Oct 26 '23 at 16:10
  • It won't be behind drywall. It will be recessed with the plate cover flash with drywall. I am familiar with power-sharing devices but they are nearly $700 so I am looking for a lower cost code-compliant way. 32A EV charger doesn't require hardwiring and the one that came wih my vehicle is a portable with 14-50P that cannot be hardwired but draws 32A max. – David Oct 26 '23 at 16:19
  • The lower cost code compliant method is to use an existing circuit that is in the garage, like a regular wall outlet with a granny cord. Properly installing higher power EV charging requires either a dedicated outlet with a GFCI on a new circuit, or a hardwired circuit of the appropriate size for the EVSE. – KMJ Oct 26 '23 at 17:00
  • IDK if this is of any use to you: https://diy.stackexchange.com/questions/136377/i-need-to-switch-between-two-240v-30a-loads – Huesmann Oct 26 '23 at 22:45
Every EV novice seems to inherit the exact same pack of misconceptions about home charging, largely fueled by the dubious economy of using the travel unit as the daily home charger. I get you may be at sixes and sevens about the whole "EV thing" and are poised to return the EV to the lessor if it doesn't work out for you, so you want to make bare minimum investment in infrastructure. But you're mistaken. EVs are here to stay and it's silly to scrimp only to have a worse overall experience.
It's one circuit. But the thing you're trying to do isn't allowed. That circuit is dedicated to range/oven per NEC 220.55. The EVSE requires a dedicated circuit per 625.40.
Generally, the idea of a "pinky promise" to be careful not to operate conflicting things at once is not recognized in NEC - e.g. the requirement for a generator interlock.
Alright. See where you plan to put that box? Stick a Siemens 8-space subpanel instead. ($55) (does not work with a 4-space due to Siemens oddities with breaker spacing).
Two 50A breakers ($15 and $83 per you) in the subpanel with an $30 ECSBPK02 interlock between them. I'm picking Siemens brand because the ECSPBK01 interlock makes this easy. You can do the same thing with Square QO2DTI or Eaton CHML, but CH and QO panel lines are not cheap, and cheap is a parameter here.
You'll have to switch it manually but it's code legal. Hey, you wanted the cheapest rig possible. This is it.
I can purchase a 50A GFCI Siemens breaker for $83 - not a big deal.
Because your panel is Siemens legacy? Breakers don't cross-fit, even though they seem to.
The EVSE breaker will need to be GFCI, which is unfortunate, because it brings nothing to EV charging. But hey, you wanted the socket.
Oh, and long experience of the EV community is that the Leviton, Legrand and Eaton sockets (all the cheapies) tend to melt down under EV loads. the community universally recommends the $80-ish Hubbell or Bryant.
One of my frustrations with the "money-scrimping" philosophy is that it seems to save so little. subpanels, Hubbell sockets, GFCI breakers... doesn't sound great.
I would run a plain, $15, 240V/20A breaker using 12/2 Romex (or whatever I had lying around) -- hardwired to a $450 Wallbox (CostCo). Yes, it's more. But not a lot more, and it will improve the experience all around. When nightly charging is easier, you'll charge nightly. Untangling that travel unit is a drag, and that encourages less frequent charging (which requires larger circuit).
4kW charge rate (20A circuit @ 240V) is plenty for home charging, and will provide 100-150 miles a night depending on the car and the night. Feel free to use fatter wire if your panel's Load Calc can support it.
And, because it's a Wallbox, I can add-on EVEMS load management, solar capture to export into the car rather than to the utility, or Power Sharing among multiple EVs.
  • Great answer, and no, I am not trying to cheap out. Was just seeing if existing circuit can be used to the code as this was the easiest. If I am going the sub-panel route, will be running a 90A or a 125A circuit. I have an electrician who would do load calc and final connections/torquing but I am researching what I need so that I can do most of the wiring work. If I go this route, 1/0 AL SAE with 125A breaker protected sub-panel is what I am thinking. Just need to figure out a proper way to breach the firewall between garage and interior. Any tips? Will be coming up rim joist & out to garage – David Oct 27 '23 at 13:11
  • One other thing, I see that KY USA hasn't adopted the 2020 NEC code. As I understand the GFCI requirement came with that year's changes. Am I mistaken? https://www.nfpa.org/NEC/NEC-adoption-and-use/NEC-adoption-maps – David Oct 27 '23 at 13:27
There are a bunch of other issues - how do you safely manage the load (what about the night before Thanksgiving when you decide to cook a bunch of stuff while the car is charging), EVSE ("charger") should really be hardwired rather than plug-in, you don't actually need 50A for charging in most cases, etc.
But the biggest issue is that an electric cooktop normally requires a dedicated circuit. If it is hardwired then it has to be dedicated anyway (can't have receptacles on a circuit with > 50% of capacity used by hardwired equipment) but even with a plug/receptacle connection this is not allowed.
    Likewise, using a receptacle in the garage then requires GFCI protection (which using the EVSE would avoid.) That's an expensive breaker, on top of the other issues you mention. – Ecnerwal Oct 26 '23 at 16:17
  • It may or may not require GFCI, as 240V GFCI is a relatively new requirement so it depends on local NEC year. – manassehkatz-Moving 2 Codidact Oct 26 '23 at 16:19
  • 32A EV charger doesn't require hardwiring and the one that came with my vehicle is a portable with 14-50P that cannot be hardwired but draws 32A max. I can purchase a 50A GFCI Siemens breaker for $83 - not a big deal. So sounds like your second paragraph makes it a hard "no". Do yo mind citing the code? – David Oct 26 '23 at 16:27
  • I don't mind citing the code. Just haven't found it yet and don't have time to search more right now. But I'm pretty sure of it. If Harper doesn't add a lengthy answer (or just a code citation) by the time I have a chance later, I'll look for it. – manassehkatz-Moving 2 Codidact Oct 26 '23 at 16:29
  • @manassehkatz-Moving2Codidact as far as Thanksgiving, in the rare cases where both circuits are used AND maxed to 50A, wouldn't the main breaker provide the protection? I can disconnect the EV and keep cooking happily – David Oct 26 '23 at 16:34
  • The problem is the in-between, and a *lot* of code is about the in-betweens. In particular, large loads are based on *continuous* @ 80% (a.k.a., derate 125%). So a 32A charger is supposed to be on a 40A (or larger) circuit. (There is no 14-40 so the plug is the same for 40 and 50). Breakers generally don't trip quickly until at least 110% of load (to avoid nuisance trips, motor startup, etc.) and sometimes a bit more (see "trip curve"). So you could have EV going strong at 32A and cooktop draw 20A = 52A total. That by itself on 50A circuit is marginal but OK but *not* for long periods of time – manassehkatz-Moving 2 Codidact Oct 26 '23 at 16:44
  • ("continuous usage"). Bump it a bit more on the cooktop and you could be in a real danger zone where breaker doesn't trip but wire overheats. – manassehkatz-Moving 2 Codidact Oct 26 '23 at 16:45
  • @manassehkatz-Moving2Codidact it's worse than that, a typical breaker will take a half hour to trip at 150% load, at which point the wire might be toasty warm depending on the scenario. Also the code cite is almost always 110.3(B) as the dedicated requirement will be in the installation instructions for the cooktop. For example GE says to use 'an individual, properly grounded branch circuit'. – KMJ Oct 26 '23 at 16:58
  • So if I wire for the new sub-panel (thinking 125a 1/0- 1/0- 1/0-2 AL SER cable) for future expansion. How would I route it from the basement to the garage? 2" conduit and sealed at the vapor barrier after breaching it? – David Oct 26 '23 at 19:29
  • Be careful with a new panel. Don't oversize it too much, because you need to have enough excess capacity in the main panel. A typical decent choice is to use 2/2/2/4 AL as that tends to be priced relatively low (due to popularity) and is good for up to 90A. Feed that from a 60A, 70A, 80A, etc. breaker based on available capacity after a **load calculation** of your main panel. Feed that into as big a panel as you like - 125A is fine, so is 200A, because the main breaker in that subpanel is simply a disconnect and can be any size you want. – manassehkatz-Moving 2 Codidact Oct 26 '23 at 23:02
  • As far as conduit, if you use *cable* then you don't need conduit, with the exception of to get through the firewall as you describe. – manassehkatz-Moving 2 Codidact Oct 26 '23 at 23:02
  • @manassehkatz-Moving2Codidact -- it's the EVSE that drives the dedicated circuit bus in this case, *not* the cooktop -- most cooktops are quite happy sharing a circuit with other cooking appliances, as permitted by Table 220.55 Note 4 – ThreePhaseEel Oct 27 '23 at 00:30
  • @ThreePhaseEel That's with other cooking appliances. So arguably "dedicated to cooking appliances" means "can't *add* an EV". This is starting as a cooking circuit. – manassehkatz-Moving 2 Codidact Oct 27 '23 at 00:37
  • @manassehkatz-Moving2Codidact -- it's more that the EVSE itself needs to be on a dedicated circuit (NEC 625.40) – ThreePhaseEel Oct 27 '23 at 00:43
  • How you route the wiring, @David, should be a whole new question - no room down here in comments to answer something like that. Provide a drawing and some pictures and a couple of options that you've come up with and ask for pros/cons of each possible route. Don't ask for "best" because that'll get closed as opinion based. – FreeMan Oct 27 '23 at 13:22
  • @FreeMan fair enough. Thanks for the tip – David Oct 27 '23 at 13:27