16
I'm about to install several Hunter ceiling fans. The instructions that came with the fan show three wires coming from the ceiling box for a single switch light. When I remove the light, there are only two wires leading to it. And the wires are old, cloth covered. (House was built in '50.) Why two rather than three and what the heck do I do now?
Rap
user13891
  • 163
The 3 wires are normally hot, neutral, and ground. It sounds like your home doesn't have a ground wire.
From Wikipedia:
Equipment earthing conductors provide an electrical connection between non-current-carrying metallic parts of equipment and the earth. The reason for doing this according to the U.S. National Electrical Code (NEC), is to limit the voltage imposed by lightning, line surges, and contact with higher voltage lines. The equipment earthing conductor is usually also used as the equipment bonding conductor (see below).
Equipment bonding conductors provide a low impedance path between non-current-carrying metallic parts of equipment and one of the conductors of that electrical system's source, so that if a part becomes energized for any reason, such as a frayed or damaged conductor, a short circuit will occur and operate a circuit breaker or fuse to disconnect the faulted circuit. By bonding (interconnecting) all exposed non-current carrying metal objects together, they should remain near the same potential thus reducing the chance of a shock. This is especially important in bathrooms where one may be in contact with several different metallic systems such as supply and drain pipes and appliance frames. The equipment bonding conductor is usually also used as the equipment earthing conductor (see above).
If the box is metallic, there's a chance it may still be grounded, even though there is no wire. There's an answer to a similar question that describes how to check if a box is grounded.
If the box is grounded..
If the box is grounded, then you can connect the ground wire from the fan directly to the box, and the fan will be grounded.
If not..
If the box is not grounded, you have two choices:
  • Run a ground to the box. This would mean running a new wire back to the panel (could be bare copper, but if you're doing the work may be better just to run a new wire - 14/3 would be the best), which could mean opening up drywall.
  • Wire the fan without ground. This is slightly dangerous, but not moreso than the when the previous fixture was there -- except that people do touch fans to control them. If something ever happens to cause the fixture to become energized (eg a frayed wire inside), someone who touches it will likely be shocked (which can cause serious injuries and even death).
Personally, if I was unable to get a ground to the box, I'd probably use a fan that was remote controlled so no one ever has a need to touch it (get a fan either with no pull strings/controls, or cut the cords off so no one is tempted to touch them). The wall switch can be left in to control overall power, and the remote used to switch light/fan speed, or the wall switch can be removed so the power is permanently on and the remote is used for everything.
In any case, you should connect the fan's ground wire to the box, so that at least the fan body and box are bonded (at the same electrical potential).
Bootleg Ground
DO NOT CONNECT GROUND AND NEUTRAL in the box. This is sometimes called a "bootleg ground" and is not only pointless, but actually very dangerous. If the neutral wire ever has a fault ANYWHERE, in addition to the fixture simply not working, it becomes energized and you can be shocked if you touch it (as you likely would to, say, check if the light bulb was burnt out).
gregmac
  • 28,910
  • 84
    Get the remote control as gregmac suggests. This is the safest way and will give you switching for light and fan separately and fan speed, all without touching the device. – bib Jul 09 '13 at 23:26
  • If the fan is a primary light, especially for a kitchen, dependency on the remote control to turn the light on may not be in compliance with electrical code. A wall switch may be required (at each entrance) at least for turning on the light (maybe regardless of saved remote control setting). If other lights are around that wall switches can turn on, then not a worry. – Skaperen Oct 06 '13 at 17:44
    Sorry but your answer is misleading. If you have ever wired a ceiling fan before, what the OP says is correct, the fan has 3 wires, with the Blue being power for the fan. If the house isn't wired with 14/3 to the ceiling box, then his only options are to either rewire with 14/3, where the red wire would provide constant power (for the fan) and the other would be switched, for the light. To use the existing 14/2, then you need to connect the blue and black from the fan together with the black in the ceiling box. This would have the switch control power to the fan and light both, forcing you to –  Oct 06 '13 at 17:19
    @Chris The OP doesn't have 14/2: he has a white and black, with no ground wire. My answer was more concerned with how to safely wire and use the fan, not how to control the light and fan separately, though I've edited it because if you're going to rewire at all, it's worthwhile to run 14/3 to give you that option. – gregmac Oct 06 '13 at 19:12
  • @Skaperen code citation? – gregmac Oct 06 '13 at 19:18
    @Skaperen -- all you need is a means of turning on and off the light at each entrance, whether it be a hard-wired switch or a wall-mounted remote. (210.70 is the NEC cite btw) – ThreePhaseEel May 12 '15 at 22:30
  • Is the warning against a "bootlog" ground true for the reverse direction as well? That is, if connecting a device with only hot and neutral to the power source which has three wires, don't connect the neutral on the device to the main ground? (In this case it appears to go directly to a 120VAC to 24VAC transformer in the device) – Michael May 01 '16 at 17:00
  • Suggestion: If you're going to run the fan un-grounded, see if it's possibe lto add a GFCI. A GFCI should keep you safe even if the fan body gets connected to hot. – derobert Apr 13 '17 at 20:05
Two is "normal". Black for hot and white for neutral.
Your fan has 3 wires (4 counting the green ground). You will have a white which you will connect to your neutral and you will have power for light and power for fan. Both of the power lines will be capped with your "black"/hot wire coming in.
To have the light and fan controlled independently you would need to rewire from fan to switch with 12-3 (or 14-3). An alternative is to install a remote that has sensor sitting in fan unit (or buy a fan with it built in).
DMoore
  • 47,764
  • 190
Your wiring is an ungrounded system, possibly what was called "knob and tube", which refers to the ceramic insulators used. Be very careful with the cloth-covered insulation, as age will make it quite brittle and easily damaged. Most of the times with wiring this old, both appear the same color, making your install more time-consuming determining hot from neutral. I have used heat-shrink tubing in the past to ensure the old cloth insulation remained intact during fixture replacement, as well as for color coding the existing wires. You only have to sleeve it over the existing wire, no need to shrink-fit it as it is just to prevent shorts and aid in wire identification. Determining which is the hot (black) and which functions as the return (white) is where you have to take your time and be careful due to holding your meter to see as well as holding your tester leads. If wired backwards, everything will still function, but your chances of electrical shock greatly increase. Grounding the fan green wire to the box will not help in preventing electrical shock in an ungrounded system. A remote control unit is probably the safest option besides an entire wiring upgrade.
Ceiling Fan and Light wall switch. Look with a flashlight into the back of the plastic box. That is were you may find the bare cooper ground lead for the replacement wall switch (4th wire). If the original fan light switch did not use the ground (3 wire) then the electrician would just shove the ground wire deep back in the box. Pull it out and ground the new wall switch. It could be safer.