If neutral is connected to ground and current desires ground then I would think it would go to ground. But my understanding is that it is kept off of ground until it's "upstream" of the breaker box, or unless a malfunctioning device shorts hot to ground. So what "prevents" the electricity from going to the ground that the neutral is connected to?

BMitch
  • 42,687
  • 14
  • 92
  • 197
Doug
  • 39
  • 1
  • 2
  • 4
  • 1
    Possible duplicate: [Why didn't homeowners get electrocuted when appliances were grounded through the neutral?](http://diy.stackexchange.com/q/35738/2196) – BMitch Dec 08 '13 at 14:27
  • 1
    I answered this exact question [here](http://diy.stackexchange.com/questions/31263/will-the-second-light-in-this-circuit-light-up/31272#31272), though the explanation is very technical. The short answer is, there *will* be current through you if you touch a neutral wire while grounded, but it will be so small you will barely feel it. – BlueRaja - Danny Pflughoeft Dec 08 '13 at 18:18

6 Answers6

4

Current doesn't want to return to ground, but rather it wants to return to the source. The ground isn't a great conductor and while it is in parallel with the service, the amount of current returning through the ground is so small it is effectively zero. However, if you lose your neutral then the ground becomes the only viable return path for the current to get to the source.

I replaced a residential service and the neutral on the service drop broke on the service drop-side of the point of attachment. The house still had power because the system was grounded and current was taking "plan B" of returning to source through the ground. Luckily the home owners just purchased the house and hadn't moved in yet.

Ian
  • 41
  • 2
-1

The short answer is resistance. Electricity will find the easiest path to ground. At the neutral-ground bonding in the breaker panel is a connection to the ground wire that goes to the actual ground. It's a heavy gauge, and connected to grounding bars deeply embedded in the ground to offer the least possible resistance.

For current to travel from the neutral back to the ground wires to where it can electrocute you, it needs:

  1. an imbalance in the house wiring (remember, there are two hots, and with a broken neutral it becomes a circuit with two loads in serial),
  2. a failed neutral since the neutral will be at the difference in current used by the two hots (by design of a center tapped transformer), and
  3. a better path to ground than the ground wire that is connected to the grounding rods.

As long as any one of those three conditions doesn't apply, you should not see any current on the ground wire.

BMitch
  • 42,687
  • 14
  • 92
  • 197
  • I doubt that you will ever see an installation where the two hot conductors are perfectly balanced. So you will see some current on the wires that go to the grounding rods. Which is the main reason they are 6 gauge wire, to help pull the voltage down. – Brad Gilbert Dec 09 '13 at 00:12
  • The imbalance will first go out the neutral. After that, it will appear as an increase in voltage on the lesser used hot. See [this question](http://diy.stackexchange.com/q/6351/2196) where using the microwave caused someone's lights to get brighter. – BMitch Dec 09 '13 at 00:20
  • If you have a multimeter capable of measuring milli-volts, and measured the AC voltage from the grounding rod to the dirt a few feet away; you would see that there is some voltage. See also [infinite resistor grid](https://www.google.com/search?q=infinite+resistor+grid). – Brad Gilbert Dec 09 '13 at 00:48
  • I was looking at the majority of the electricity flow, which is what I think most people are concerned about when wiring a home. The paranoia is from the hot having 120, the neutral on the other end of that 120, the ground connected to the neutral, so metal appliances should have 120 on their exterior ready to electrocute you. Sure, there's going to be some milli-volts from the slight resistance, and there could also be phantom induced voltage, but it's going to be much more like a 9v battery than the 120v hot. – BMitch Dec 09 '13 at 12:25
  • People are totally underestimating the amount of current that can flow on the grounding system. The ground path can have a VERY low resistance, for example where the GEC is attached to metal piping that in turn is connected to the GEC's (and therefore neutrals) of neighboring residences. I've seen as much as 40% of all 120V loads in a home flowing on its GEC and water service pipe, with no apparent problems, and going on for years. – kreemoweet Mar 16 '23 at 17:27
  • @kreemoweet I think we're saying the same thing. The grounding rod, service pipes, etc, are a very low resistance path to ground. Which means you're unlikely to see 120v and a hundred or so amps electrocute you when touching a grounded appliance. – BMitch Mar 17 '23 at 13:05
-1

A great question and it seems odd to have a ground and a neutral. We have a neutral to keep the ground from being loaded. We dont want the ground to be load, it doesnt have the capacity and its for back-up.

In AC systems, there is current on the "hot" leg and on the "reference" leg. We use a neutral leg for reference. In countries with 240v systems, there is no neutral, but two opposite legs of 120v that provide a reference for each other. You see in AC systems, the voltages are not constant - it alternates back forth +X volts and -X volts. + and - from what? voltage is just potential differences from the reference. In 120v systems, on leg will be -60v from the neutral and then switch to +60v from neutral 60 times a second. In a 240v systems with out neutral wire there is a perceived reference between the two 120v legs that are off opposite phase.

So, yes in theory, you could get the potential difference from a 120v "hot" leg and ground, BUT then your would be loading the ground and it would no longer serve a safety function. In practice when you load the ground, appliance panels and other things that are grounded out become will be loaded and can shock.

Tom
  • 123
  • 2
  • 1
    The grounding conductor should always have the capacity to carry the full load supplied by the ungrounded (hot) conductor, in a properly wired circuit. – Tester101 Dec 09 '13 at 12:01
-1

Because ground is not a return unless you bridge across from neutral, hot, or have a component short to frame ground.

It is a free standing wire/conduit network connected to earth that isn't a part of a circuit till a fault occurs.

Fiasco Labs
  • 11,280
  • 1
  • 27
  • 44
  • it is part of the circuit because the neutral is connected to it at the panel box. So it's a extension of the neutral wire. – Grasper Oct 07 '15 at 19:36
  • Ground is always one of the possible return paths for current (where neutrals are grounded) and it absolutely will and does carry current in proportion to its resistance. It's very common for residential ground systems to carry measurable current in normal use – kreemoweet Mar 16 '23 at 17:11
-2

The ground wire is for safety, it should be very close to the same potential as Earth. To that end, there is a legal limit of how much resistance there is from the ground at the service entrance to dirt outside. In the US it's 25Ω, or you can get away with just using two ground rods 6ft (or more) away from each other. (It's cheaper to install two ground rods than spend time and money on properly testing the resistance)

The reason the neutral and ground wires are connected at the service entrance, is to help keep the voltage potential of the neutral to Earth, as low as possible by keeping the resistance to Earth as low as possible.

To have absolutely no current on the grounding wire going to the ground rods, the nearest transformer would have to have equal current on both hot conductors. Since the transformer typically has it's neutral (center tap) grounded at the the same location as the higher voltage side, there would also have to have to be equal current on all of conductors on the high side as well.


So basically there is always some current going through the grounding system, at the service entrance. The main thing, is that the voltage is kept as low as possible; by keeping the resistance as low as possible.

If you want proof that there is some voltage, and therefore current, on the grounding system, measure the voltage from the grounding rod to a point in the dirt a few feet away. If you measure any voltage with a high-end multimeter of even a tenth of a volt (AC); then there is current on your grounding system.
You can even measure some voltage from the grounding rod to the point at which the neutral and grounding system are bonded. Although this will be far less than the other test, as copper and aluminum are better conductors than dirt.

Even if you turn off your power, you will still see some voltage with both of these tests. Assuming there is someone else connected to the same transformer as you, and your neutral and ground wires are still wired properly. The amount of wire the current would have to travel through before it got to your premises would be greater, so the amount of current/voltage would be greatly lessened.

Brad Gilbert
  • 553
  • 4
  • 9
-4

I admittedly know very little about AC wiring. It doesn't make a lot of sense to me. But here's my neophyte expalnation. Somebody please explain why this is not correct.

AC swings from positive to negative 60 times a second. As the black Hot wire goes positive, the white Neutral wire goes negative. When the Hot wire is +60V, the Neutral wire is -60V, and vice-versa, for a total voltage swing of 120V.

Another way of thinking about it is, positive voltage is pushing and negative voltage is pulling so there is a push me-pull you effect happening 60 times per second relative to the source (stepdown) transformer.

So, the reason current is not lost thru the Neutral wire to ground is because of potential. Ground is 0V potential. The positive voltage being supplied is +60V which is greater than 0V (ground) so you might think Ground is where the current would go. However, at the same time there is +60V on one wire, there is also -60V on the other. So, the +60V is actually being pulled back to the source transformer by the negative voltage (-60V) which is has a greater voltage potential than ground (0V). Throughout the sine wave cycle, the positive voltage has an equal negative voltage which keeps the current in the circuit. The potential difference swings from 0V to 120V 60 times per second.

  • 1
    I think you may be getting hot and neutral confused with the two opposite phase hot wires supplied in typical US residential connections. Neutral does remain neutral, but each hot cycles from positive to negative relative to the neutral. Each hot on average is 120V different from neutral (sometimes positive, sometimes negative) as measured by an averaging method known as root mean square or RMS. – Armand Mar 16 '23 at 08:12