What size wire would I need to run a 100 amp subpanel 28 feet away? I have 6/3 wire would that do it?
Asked
Active
Viewed 594 times
[This answer](http://diy.stackexchange.com/a/29077/33) might be helpful. – Tester101 Mar 19 '16 at 19:22
6 AWG copper is not large enough for 100 amperes. – Tester101 Mar 19 '16 at 19:23
This does seem like a duplicate question. Nothing against you Mel, it was cool to ask, it's a peculiarity of SE's format. – Harper - Reinstate Monica Mar 19 '16 at 20:16
You can feed a 100A panel with #6, you just cannot put that feeder on a 100A breaker. The panel size does NOT have to match the feeder/breaker size. What is this panel going to feed? – Speedy Petey Mar 20 '16 at 00:15
Just to answer the question..
You'd need 4 (Hot, Hot, Neutral, Ground) #1 AWG wires.
- 1 AWG supplies up to 110 amps
- 6 AWG supplies up to 55 amps
If you use the 6 AWG, you could only feed the subpanel with a 50A breaker. Essentially making it a 50A subpanel. It's best to go ahead and get the most out of it if you can by using #1 wire.