Recently renovated a kitchen, including adding 2 GFI outlets: one by the sink and one on the opposite wall near stove. City inspector ordered that the one by the sink be removed. What reason would the city have to require the expense of removing a GFI outlet?
2Did he mean remove it completely, or just replace it with a non-GFCI outlet? My guess is it's too close to the sink for any outlet. – SomeoneSomewhereSupportsMonica Apr 17 '16 at 00:29
1@SomeoneSomewhere, it could be behind the sink and still be code compliant. – Speedy Petey Apr 17 '16 at 01:09
2He should have given you the reason. "Just do it" is NOT a valid request by an inspector, especially when his request makes absolutely NO sense. .......... Your question needs to be posed to the inspector, NOT us or some internet forum. – Speedy Petey Apr 17 '16 at 01:10
Possible duplicate of [Which Kitchen outlets do NOT need GFCI?](http://diy.stackexchange.com/questions/9341/which-kitchen-outlets-do-not-need-gfci) – Mazura Apr 17 '16 at 01:56
Or this one: [Where *shouldn't* I use GFCI/AFCI?](http://diy.stackexchange.com/questions/75011/where-shouldnt-i-use-gfci-afci) – Mazura Apr 17 '16 at 01:57
1Can you post a photo of the device in question? – Tester101 Apr 17 '16 at 03:50
@SpeedyPetey That may depend on where you are. I don't know US code, but if the sink is within 150mm of the outlet, ASNZS 3000 would require any outlet to be both RCD(GFI)-protected and enclosed in a cupboard, or a shaver outlet (isolating transformer). Outlets in general must be RCD protected wherever they are, except in a few circumstances. – SomeoneSomewhereSupportsMonica Apr 17 '16 at 08:17
@SomeoneSomewhere, being in the US I am not familiar with those codes. Considering the OP is asking about GFI receptacles it is safe to assume he is at least in North America. And if you do not know US code I am wondering what you're basing your replies on? ........ The question at hand is not GFI or not (ALL counter receptacles in the US must be GFI protected), it's that the inspector is requesting a receptacle be removed. Unless I am reading it wrong. – Speedy Petey Apr 17 '16 at 12:12
**L. Lemon, PLEASE clarify whether this is about the receptacle itself, or the fact that it is a GFI receptacle.** – Speedy Petey Apr 17 '16 at 12:14
2011 code has nothing on the subject. However it is clear the purpose of the rules therein is to keep you from draping cords across sinks. That seems like a very good idea.
Code requires outlets anywhere there's a 12" or wider section of countertop - because that space will inevitably draw a coffeemaker or George Foreman. It's possible the inspector is seeing an outlet over a space less than 12" wide, and saying "Well, you'll never put anything there, you'll end up draping cords across the sink to another place (which might be shy of outlets)."
Code also requires a GFCI for any countertop outlet (210.8a6), and near any sink anywhere (210.8a7). That means he definitely does NOT mean to have an unprotected outlet there. If an outlet is allowed at all, it must be GFCI protected, whether by GFCI outlet, being daisy-chained from the LOAD terminals of another GFCI outlet, or a GFCI breaker in your service panel.
It's also possible he's telling you "dummy, this outlet feeds from the other one, just daisy chain it off the LOAD terminals of the first GFCI and no need for this one." But that is merely economy, and the inspector wouldn't have a stake in that.
- 295,284
- 26
- 275
- 720
If I were told that the countertop was too small for an outlet, I'd make the argument that the narrow counter space is where I'd charge my phone. – Johnny Apr 17 '16 at 01:35
@Johnny and there's a product for that. http://amzn.to/1XCBiSC – Harper - Reinstate Monica Apr 17 '16 at 09:24
@EdBeal, **code requires a receptacle within 2' of a sink**, and **ALL receptacles serving counter areas must be GFI protected.** ....... Where are you getting your code facts from? – Speedy Petey Apr 17 '16 at 12:16
I originally had 2' , then remembered 4' between. Code requires any outlet within 6' of a sink to be GFCI. My state only holds that requirement. Thanks for the correction my code book is at work. – Ed Beal Apr 17 '16 at 14:45
