I am doing some wiring from a subpanel. The main panel is sending power via 3-way wiring (3 plus a ground) to the subpanel. This subpanel is intended for both 220 and 110 volt add-ons. I have a 110 line from the subpanel via a 15-amp breaker switch. It is a very short wire from the subpanel--maybe 3 feet away to an electrical outlet.
I have thus far installed (1) a small radio to test the circuit; it ran fine for 10 minutes, then burned out and started smoking. Then, (2) I tried a lamp to test the circuit; the bulb lit up and immediately blew.
Is there too much voltage/amperage going through this circuit? How? Shouldnt the 15-amp breaker switch keep this from happening?
Roger Roots
  • 71
    Have you used a meter to confirm the 110v? – BrownRedHawk Jun 19 '17 at 19:59
    It sounds like you wired it 240 instead 120. Re-check your wiring. Please research your subject more and be careful. – ArchonOSX Jun 19 '17 at 20:11
    As a side note, circuit breakers are overcurrent protection. They have a voltage *rating* for safety and to ensure that the breaker operates properly at expected voltages. Also note that, for a given load, doubling the voltage will result in half the current. So providing excessive voltage to a device will likely cause problems with the device, but at only half the current it's unlikely you'll trip the breaker unless your device fails in a short-circuit. – Chris M. Jun 19 '17 at 20:35
  • Yep, you somehow miswired. The cable from the breaker panel should have two wires (black and white) and a bare copper ground. The black should be attached to the only terminal on the 120v breaker, and the white should be attached to the *neutral bus bar*, where all the other whites are attached. – Hot Licks Jun 19 '17 at 21:46
    @ChrisM.- your statement about voltage & current is only true for a *very* limited set of circumstances. For the vast majority of 'dumb' electrical loads, doubling the voltage will double the current and quadruple the power - followed shortly by all the magic smoke leaking out. – brhans Jun 19 '17 at 22:03
  • The devices that you plug into an outlet determine how much current is drawn (inversely proportional to impedence/resistance of the device). So plugging a normally working device into an outlet won't cause too much current to flow (assuming that aren't other devices already plugged in on that circuit). On the other hand the voltage at an outlet is determined upstream (often by transformers). So in some sense voltage "pushes", and current is "pulled". So, simplistically, if the fault isn't in the device the fault must be upstream, namely the voltage. – Χpẘ Jun 19 '17 at 22:53
    I would strongly agree with the advice to leave this to a professional, but at an absolute minimum, get yourself the proper test equipment instead of destroying random equipment, which could prove rather dangerous. – Zach Lipton Jun 20 '17 at 04:44
    You are doing this wrong enough to both burn down your house and kill people. Turn the power off and call in an electrician. – Eric Lippert Jun 20 '17 at 04:48
  • Did you install the subpanel? Did you install a single pole or double pole breaker in the panel for the 15 ampere circuit? When you wired the 15 ampere circuit, did you connect both wires to breakers, or one to a breaker and one to the neutral bus? Can you post some photos? Do you have a volt/multimeter? – Tester101 Jun 20 '17 at 11:00
  • If nothing else, next time start your tests with the lamp first. You won't have to wait 10 minutes to see the results, and it's cheaper to replace a bulb than radio! – Mohair Jun 20 '17 at 18:56
  • @HotLicks For reference, an Arc-fault breaker should have terminal screw for the neutral and it's own white wire that connects to the neutral bar. – JimmyJames Jun 20 '17 at 20:19
  • Can we see a picture of how the line is connected to the sub-panel. I'll bet dollars to donuts the problem will be quite obvious from the picture. (A 110 volt line should only be connected to one side of a 220 volt panel. Otherwise, it's a 220-volt line.) – David Schwartz Jun 20 '17 at 20:33
  • Given that there have been no replies by OP since the initial question, am I the only one who's worried that OP might be dead already? – R.. GitHub STOP HELPING ICE Jun 20 '17 at 23:30
    I signed up for an account just to upvote the remark by @EricLippert. Please don't work on house wiring until you have a *much* deeper understanding of circuit theory. Electricity is *not* a field you can safely cut your teeth on without solid knowledge of the theory, except maybe small battery powered circuits. – Kevin Jun 21 '17 at 06:29
There is most likely too much voltage, as ArchonOSX commented.
How?
You miswired it and got 240V. You can check this using a voltage tester.
No, the job of the breaker is not to block too much voltage but to disconnect the circuit when too much current is flowing. This is mostly to protect the wiring in the wall from overheating and setting fire to your home. It won't protect a 100W incandescent bulb or anything similar. Those normally draw less than 1 Amp - far below the 15A breaker rating.
In the case of overvoltage, a higher current may briefly flow through your appliance/lamp but the appliance dies before the current reaches the breaker's limit.
Sorry to be a killjoy but I suggest you don't. At least until you have gained a higher level of understanding of household electricity. Since the higher voltage can fairly easily kill you, a family member or a visitor, you might want to pay an electrician to fix this for you properly and then consider taking some evening classes in the subject (if available in your part of the world).
Useful links
RedGrittyBrick
  • 24,201
  • 47
You may also have a problem with your neutral wire. In any sort of split-phase 120/240V wiring, if the neutral is loose or poorly connected, it can cause the two 120V sides to have wild voltages between 0 and 240V. The dead giveaway is that they will still add up to 240V, so one will be higher than 120 and the other lower.
So if your careful rechecking reveals that you did not mix up any wires, take a hard look at the neutral wire connectioms.
Only expanding on the breaker issue.
The breaker/fuse is connected in series and is designed to break when current through it reaches the specified value. Period.
Breakers use the relationship between current in the coil and intensity of the magnetic field it generates; fuses use the relationship between current and power dissipation.
If we know what the mains voltage is, we can estimate what power must be consumed in the circuit to cause the breaker/fuse to open. What power is needed to burn the fuse is a completely different story.
If you have a 15A fuse protecting 110V mains the faulty device will consume 1,65 kW and I think the fuse itself will draw around 10 W to heat and burn.
If you use the very same fuse to protect 12V mains in your car the faulty device must consume 180 W to break the fuse.
If you have accidentally used 220V mains instead of 110V the device must consume 3,3kW to burn the fuse!
In your case, say you have used 100W/110V lamp. In normal opperation it draws 0,9 A. If you connect it to 220V mains it dissipates 400 W. If I use a 50% safety margin in the lamp design it will withstand a 150 W load which is way too small to sustain the accidental load. The current of 1.8 A is way too small to trigger the 15A fuse...
To your question: I will repeat what has been already suggested. Get this work done by qualified electrician. Do not do it yourself, unless you are damn sure what you are doing. And get yourself a multimeter.
psmears
  • 178
Crowley
  • 1,377
In an electrical circuit, voltage is "pushed" through the lines and current is "pulled" by any device drawing power from the lines. This means that at your wall outlet you are providing a constant 120 volts (push) and no amps (pull), assuming nothing is connected. If you connected a 120-watt bulb the break-down is that you are "pushing" 120 volts (constant) and you are "pulling" 1 amp. The pull is determined by the resistance of the device drawing the power. The equation to determine amps drawn is:
v=I*r (where v=volts, I=amps, r=resistance (ohms))
therefore,
I = v / r
Just to add, the maybe not so obvious, is that you cannot force more amps into the connected devices. You cannot control the amps at all, actually (from a wall outlet). The amps "pulled" are purely determined by the devices internal resistance.
To answer your question it doesn't sound like your breaker is the issue. I think the other responders got it right by suggesting your voltage is high.
twegner
  • 111
As others have noted, breaker is for amps rather than volts, and volts is your problem.
You should have a multi meter set to ac voltage 220v+ setting in order to test. You should know what you are doing or get someone to help you who does before playing with electrical stuff because it is dangerous.