I live on Vancouver Island. My house is less than 10 years old. It is equipped with Siemens QT circuit breakers. I could not find a specific breaker so I intentionally shorted the circuit at the outlet but no breakers tripped. I did the same with another circuit and again no breakers tripped. I did a third circuit with the same results. I used an old extension cord and cut off one end and bared the wires. Plugged it into the socket and got the expected result, a large flash. I touched the wires again with the same result. Surely at this point the breakers should trip. I think this is weired.
Any help would be appreciated.
I now feel that my house is not properly protected
Keith
    Quite a few possibilities. How about a clear, bright photo of the panel interior? – isherwood Dec 09 '15 at 20:48
    Did you then check one of the outlets you shorted to see if it was still live (using a regular lamp or outlet tester)? – bib Dec 09 '15 at 21:14
    I wouldn't re-use the outlet where you plugged in the shorted extension cable, arcing may have damaged the contacts in the outlet. – Johnny Dec 10 '15 at 00:07
  • As others have said, shorting the outlets is a bad idea. But since you did put a dead short on the outlets without tripping the breakers, I'd start looking at every junction in the wires from the panel to the outlet you're testing -- every junction box, every outlet connection, etc. Keep in mind that not all outlet boxes may be easily visible and could be in a crawl space or attic. If you have a bad connection anywhere, it will get extremely hot during a short (hot enough to melt insulation and make things worse) and may keep current low enough to keep the breaker from tripping immediately. – Johnny Dec 10 '15 at 00:14
    There are tools such as [this](http://www.amazon.com/Klein-Tools-ET300-Digital-Circuit/dp/B003LHJSY8) which are much easier for figuring out which circuit breaker it is without turning anything off or trying force the breaker to pop. –  Dec 10 '15 at 03:51
Standard circuit breakers are not designed to trip instantaneously for all loads. Breakers are designed with time curves they must meet, and for anything but the highest currents there is a noticeable delay from seconds to hours.
Schneider Electric PDF: Your brand/type of breakers could differ from this chart, but the concepts are largely the same for most magnetic circuit breakers.
Here's some math provided by Tester101 in the comments below:
14 gauge solid uncoated copper is 0.00307 ohms per foot. A 100 ft. run of #14 would be 0.614 ohms (200 ft. * 0.00307 = 0.614 ohms). According to Mr. Ohm, Current (I) = Volts (V) / Resistance (R). Therefore a direct short would be 195.44 amperes (120 V / 0.614 = 195.44 A). Which is 13 times a 15 ampere circuit, so it should trip within 2-3 seconds. Even with a 200 ft. 20 ampere circuit, it would be 310.88 amperes (200 * 0.00193 = 0.386 120 / 0.386 = 310.88) . Which is 15 times rated current, and again 2-3 seconds to trip. However, that's based on the trip curve in the posted link, which may be different than the trip curve of the breakers in question.
I've marked an example on the chart which shows that at a current of 15 times the rated current, it can take up to 2 seconds to trip (download the PDF and zoom in so you can actually read all the numbers). For a 15 amp breaker, that's over 200amps for almost 2 seconds. That's enough power to melt strands of your extension cord and possibly damage whatever you used to short the first two outlets.
When you touch two wires, only a small area of the wire touches, and explosively heats and melts (the POP and spark). I suspect if you stripped the extension cord and used a proper wire clamp on the ends to make a good connection, you might be able to pull enough current to quickly trip the breaker, assuming the outlet doesn't internally melt from arcing when you plug it in.
The main point is that this IS NOT a good thing to do. Tripping a breaker to find it with a short is pretty dangerous, and you can damage outlets or other wire junctions in the process. If there's a wire nut in an adjacent outlet that's not making the best connection, it could melt. Then you have to find and fix that which could be a challenge unless smoke and fire direct you to the problem area.
Plug in a radio, turn it up, and start manually throwing breakers. When the music stops, you found the right breaker. Don't purposely short wires.
JPhi1618
  • 27,679
  • 52
    That bears repeating: ___This IS NOT a good thing to do. Tripping a breaker to find it with a short is pretty dangerous, and you can damage outlets or other wire junctions in the process. Don't purposely short wires.___ – keshlam Dec 09 '15 at 21:56
    Alternative to the radio: Get a tracer. US$12 or so will get you a transmitter that plugs into an outlet, and a matched detector that can be used to find the breaker supplying that outlet. That doesn't require that you be able to hear the radio. – keshlam Dec 09 '15 at 21:59
  • @keshlam Yea I added the radio tip because I've lost my mind trying to use a tracer. Maybe the one I had wasn't very good, but I never could find any breakers. They keep selling them, so they must work - just not for me. – JPhi1618 Dec 09 '15 at 22:01
  • @Tester101, I was thinking that the very small section of wire that actually touches would pop and melt before "crap ton" was reached. I would expect the small amount of copper to melt, therefore breaking the connection before significant current is drawn, but maybe it's more current than I expect? – JPhi1618 Dec 09 '15 at 22:43
  • @JPhi1618: It is equally likely the wires will weld themselves to each other. Maybe more likely. Either way , ___bad idea___. – keshlam Dec 09 '15 at 23:41
  • @JPhi1618: Using the tracer takes a bit of practice. The trick is dialing the sensitivity down until it indicates only a single breaker, but does indicate on that one. It also works better on fullsize breakers than on the double breakers. – keshlam Dec 09 '15 at 23:53
  • Doing the math on a 100 foot run (round trip) of #14 yields a short circuit current of 400 amps at 120 volts. That would be more like 27 times the rated breaker current so should be around .025 seconds or just over one cycle on the posted let-through chart. Dead shorting breakers is a bad idea but they should trip instantly if dead shorted. An old corroded breaker may never trip so they should at least be exercised and possibly replaced. – ArchonOSX Dec 10 '15 at 03:44
  • I take back what I said about the crap ton of current. After doing some math, it looks like the current isn't that high. #14 solid uncoated copper is 0.00307 ohms per foot. A 100 ft. run of #14 would be 0.614 ohms (`200 ft. * 0.00307 = 0.614 ohms`). According to Mr. Ohm, Current (I) = Volts (V) / Resistance (R). Therefore a direct short would be 195.44 amperes (`120 V / 0.614 = 195.44 A`). Which is 13 times a 15 ampere circuit, so it should trip within 2-3 seconds. (Continued...) – Tester101 Dec 10 '15 at 14:07
  • (...Continued) Even with a 200 ft. 20 ampere circuit, it would be 310.88 amperes (`200 * 0.00193 = 0.386` `120 / 0.386 = 310.88`) . Which is 15 times rated current, and again 2-3 seconds to trip. However, that's based on the trip curve in the posted link, which may be different than the trip curve of the breakers in question. – Tester101 Dec 10 '15 at 14:10
  • @Tester101, very interesting addition with the math. I admittedly didn't know how much current a short could draw so it's very useful to know there's real calculations to figure it out. – JPhi1618 Dec 10 '15 at 14:13
  • @JPhi1618 for my tracer to work, I have to sweep it up and down the rows of breakers. When I first turn it on, it will beep on nearly every breaker in the panel. I'm not sure why that is, but I eventually always find the correct one. – Jason Hutchinson Dec 16 '15 at 20:46
  • @JPhi1618: I designed one of the popular tracers on the market. It beeps whenever it picks up a signal that's close to the maximum signal it has heard since the last reset. There's a lot of variability in how strong a signal it will receive from the "right breaker" or from other breakers, but the right breaker will generally produce a signal that's more than twice as strong as any other. Until you find the right breaker, the device may yield many false detects, but once you find the right breaker that will be the only one that will make it beep until the next reset. – supercat Jun 19 '17 at 23:20
i actually built a device that tests breakers, it has 3 switches on it, two are in series between hot and neutral. one is a safety the other is the shunt that when closed after the safety is closed shorts line to neutral, the second switch is wired between ground and neutral when closed it creates an imbalance that will trip the protective systems of gfci breakers and outlets and test the ground fault section of the new afci breakers. it is hooked up using a heavy duty #10 3 wire cord with a small sub panel breaker box in line with a 40 amp breaker in it. i found that it works well and if the circuit being tested fails to open it opens the inline breaker in the test set. not recommended but it is a lot safer than simply shorting two wires together.. and any such a device is at best to be used as a last option dont just reach for the proverbial dead short in a can without first exhausting all other options because as others have said you run the risk of burning the house down.
This article: https://inspectapedia.com/electric/Circuit_Breaker_Failures.php
shows how unreliable circuit breakers can be, with significant numbers not tripping even at 200% of rated current.
More info here: https://inspectapedia.com/electric/Circuit-Breaker-Defects-Aronstein-IEEE-2018.pdf
Some brands have some 50% failure rates.
Finding breakers by shorting the outlet may be a good way to burn your house down.
Sherwood Botsford
  • 3,644
MCB's were designed to replace the regular wire fuses with the ability to reset a switch instead of replacing a wire fuse. Given that fact, a current over draw needs to be detected with requisite action. The rating of the MCB shows the amount of load possible on the MCB without tripping.
A short circuit is exactly what it is, it will trip even if the current drawn is within the load limit. If that does not happen, please replace the MCB's in question.
Cheers
    Welcome to the site. As this is read by people of all experience levels, please always expand abbreviations such as MCB - [Magnetic circuit breakers](https://en.wikipedia.org/wiki/Circuit_breaker#Magnetic_circuit_breakers). – JPhi1618 Dec 10 '15 at 13:10
    I'm not sure I agree with "it will trip even if the current drawn is within the load limit" - a MCB should only trip when the current exceeds the stated limit for the time specified by the manufacturer. You can even overcurrent a breaker within it's trip time without it tripping. Further, you could have a situation where a short circuit wouldn't generate sufficient current to cause a MCB to disconnect (eg a very long extension lead). – John Dec 11 '15 at 08:53
    @JPhi1618 I think it's worth adding that MCB in the UK (particularly when referencing domestic electric installations) usually stands for Miniature Circuit Breaker rather than Magnetic (even though they may have electromagnetic operation...). – John Dec 11 '15 at 08:59