7

I've just moved house and my clothes dryer has a four prong plug but on the wall there's a three prong socket. Do adapters exist for this? Or do I need to get a new cord for my dryer? Or is there another solution?

Tester101
  • 131,097
  • 78
  • 316
  • 608
Guy
  • 2,063
  • 11
  • 33
  • 44
  • This is an electric dryer or a gas dryer? – The Evil Greebo May 25 '12 at 11:34
  • @TheEvilGreebo Must be electric. Gas dryer wouldn't have 4 prong plug. – Tester101 May 25 '12 at 11:35
  • Oops, yeah reversed that. Ok - describe the 3 prong plug - does it look like a typical 3 prong plug or is it "unusual" - bigger, with oddly slanted openings? – The Evil Greebo May 25 '12 at 11:37
  • Do you know the make and model number of the dryer? – Tester101 May 25 '12 at 13:59
  • 2
    Can you post a picture of the plug and receptacle so we can answer this question without guessing? – SteveR May 25 '12 at 14:03
  • If you know how to test the outlet for whether it's hot/hot/ground or hot/hot/neutral, do so. If not, you should consider hiring an electrician to ensure that the outlet is wired correctly and safely as a 3 prong and change the plug on your dryer, or upgrade the outlet to 4 prong which may take rewiring to the panel. – The Evil Greebo May 25 '12 at 14:20
  • 2
    @guy recently had this issue, check the back of your dryer, there might be instructions right on the dryer for switching to a 3 prong cord. – wax eagle May 25 '12 at 15:06
  • A big thank you to all the answers and comments! @waxeagle - Great idea - found instructions there. TheEvilGreebo - yes, electic. SteveR, Tester101 - Apologies, I should have done that at the outset, photo and make/model would have helped. – Guy May 25 '12 at 21:32

6 Answers6

5

You could replace the cord on the dryer, but you'd have to bond the chassis of the dryer to make that acceptable to current NEC codes (Article 250.140). This can be a safety hazard if done incorrectly, and it may or may not void the warranty on the dryer.

Since your dryer is set up to use a 4 prong receptacle, the optimal solution would be to update the receptacle to a 4 prong (NEMA 14-30R if I remember correctly). However, this will require you to run new cable to the receptacle, since you'll need a cable with a ground. Depending on the draw of the dryer and the length of the run, you'll either have to pull new 10-3 /w ground or 8-3 /w ground cable.

EDIT:

As @TheEvilGreebo pointed out, you may be able to simply swap out the cord on the dryer for a 3 prong version. Check the manufacturers documentation to verify the procedure, and to make sure your model supports this.

EDIT:

This schematic for an electric dryer might help you understand how the dryer could be wired (depending on make/model/manufacture date).

enter image description here

Tester101
  • 131,097
  • 78
  • 316
  • 608
  • Actually, Tester, many modern electric dryers are built to be convertible between 3 prong and 4 prong 220. You can buy both styles of cord easily at Home Depot and swap them out with a screw driver and a hex bolt driver - 1/4 or 3/8 as I recall. – The Evil Greebo May 25 '12 at 12:37
  • @TheEvilGreebo Good to know. I haven't bought an electric dryer since 3 prong was all the rage. I knew electric ranges were this way, but didn't know dryers were too (I guess it makes sense though). – Tester101 May 25 '12 at 12:40
  • 1
    As to your edit: To give advice to the OP to wire the dryer in this this way is irresponsible and dangerous! The only correct answer is to replace the receptacle with the correct four prong outlet! – SteveR May 25 '12 at 14:15
  • 1
    @SteveR It's only dangerous if the dryer does not have the ability to use a 3 prong cord, if it can use either there is no problem. – Tester101 May 25 '12 at 14:24
  • See my edit quoting Wiki article. – SteveR May 25 '12 at 16:32
  • 2
    @SteveR [WikiHow](http://www.wikihow.com) is **not** an authoritative resource, and they fail to site the NEC article they are referencing. I'm giving you the NEC article number **250.140**. – Tester101 May 25 '12 at 16:40
  • @SteveR You can read the NEC section yourself in [Chat](http://chat.stackexchange.com/transcript/message/4722229#4722229). Just don't get *Grounded Conductor* (neutral), confused with *Equipment Grounding Conductor* (Ground). – Tester101 May 25 '12 at 16:43
  • [This answer](http://diy.stackexchange.com/a/14457/33) might also be helpful. – Tester101 May 25 '12 at 17:40
  • Thanks everyone! Turned out there were instructions on the back of the dryer to convert it (kudos to wax eagle for diplomatically saying the equivalent of RTFM). Home Depot had the cable with 3 prong plug for around $17. Clothes are now tumbling in the dryer thanks to the help you provided. – Guy May 25 '12 at 21:38
  • 1
    @Guy The three-prong dryer plug is not grounded. That is [not safe](http://diy.stackexchange.com/a/31494/2865). You should update it to a 4-prong outlet instead. – BlueRaja - Danny Pflughoeft Sep 07 '13 at 06:36
0

For those who say this can't be done it is possible that at some point the wiring may be set up for a 220v thirty amp system, and then down graded to a 120v 20 amp circuit. See what wires are in the box after assuring there is no power. If you have the heavier wire in the right array, you lucked out.

  • Welcome to DIY.SE! This may be more appropriate as a comment to Tester101 or amphibient's answers, since it is essentially the same advice to rewire the outlet – mmathis Oct 24 '16 at 21:55
0

There are two options.

1) You either have to update the outlet on the wall to a 4-prong and the wiring that runs to it from the breaker panel. 4-prong outlets have two hot wires, a neutral, and ground.

OR

2) You install a 3-prong plug on your dryer.

The cheaper option would be to replace the plug on the dryer. 4-prong plug is the current standard, so if you do upgrade the outlet, you'll be set for future.

almostengr
  • 76
  • 3
0

the easiest thing to do is to replace the outlet, wire a new outlet in, assuming they both use the same type of cable (typically 10-3). you flip the circuit off before you do it, of course. much simpler than looking for an adapter (and probably safer)

amphibient
  • 7,357
  • 47
  • 122
  • 194
  • downvoter, explanation? – amphibient Jun 06 '13 at 18:21
  • Not the down voter; but you took a year old question and made an answer that adds nothing of value not already in an existing answer. – Dan Is Fiddling By Firelight Jun 07 '13 at 14:37
  • See this [suggested edit](http://diy.stackexchange.com/review/suggested-edits/13961) for some more commentary. – Niall C. Apr 10 '14 at 16:19
  • 1
    Sorry, I disagree. I believe @amphibient had the correct answer here. Never alter the appliance. You'll not only void the warranty, if new, you could seriously mess up the machine or kill someone using the machine. I don't care that the answer was a year old. Someone will come along and think that fiddling with the appliance is a-ok. Be safe. Run a new wire and hook up the appliance as it was designed to be used. – Robert Achmann Dec 23 '14 at 03:46
0

Dryer cords are designed to be replaced. It's apparently even common for them to ship without a cord so that you can install the appropriate cord for your outlet. Houses built before 1996 typically need a 3-wire cord with a NEMA 10-30 connector. Houses built after 1996 (in the US) typically have a NEMA 14-30 outlet, and will require a 4-wire cord. (FWIW, a new cord seems to run around $11-$25 (as of 2015), depending on how long you need it and where you buy it.)

Whirlpool has detailed wiring instructions so you can make sure you are wiring it properly. Other manufacturers will likely have similar instructions.

Home Depot has some generic wiring instructions. Contrary to people here, they recommend not updating the outlet to NEMA 14 yourself, but having a licensed electrician do it if that's the way you want to go.

Having a separate ground sounds like a good idea at first, but if your dryer is like mine, it's not going to make a lot of difference. Mine came with a 4-wire cord, but ground and neutral were wired to the same terminal internally. I first thought that was crazy, but it is consistent with the installation instructions (although it is possible to keep them separate). So, depending on your dryer, you may not get a separate ground even with a 14-30 connector.

aij
  • 101
  • 1
-2

EDITED for clarification:

The three prong plug has two hot legs for the two bus voltages to add up to 220 volts, plus a neutral wire. Prior to 1998 the neutral was also grounded to the dryer case. A four prong plug has the two bus connections, a ground, and a neutral return. Often these are used if the dryer circuit requires 120 volts at some point, the current would flow from one bus and return through the neutral. If you were to change from a four prong to a three prong and your dryer is designed to use 120 volts at some point, then that current will have to be returned on the ground leg. This is not acceptable by NEC code, nor is it safe. If the 120 Volt circuit were to short, the full 120 volt potential could be present on the dryer case! Imagine touching the dryer at that time, and maybe on a wet floor!

If you can determine that the dryer does not require 120 volts, and that no current is returned on a neutral leg, then I see no reason not to use the three prong (although why does it have a neutral leg at all?). I would ONLY do the conversion if it is recomended by the manufacture. With todays economy I don't think that a manufacture would go to the expense of a four prong plug if it was not required.

The conversion kits mentioned by others may be to convert from a three prong dryer to a four prong receptacle. That is okay, being that the neutral wire is not used.

EDIT:

Wiki tells it like it is. "Modern appliances require 4 conductor cordsets (separate conductors or wires for line 1, line 2, ground and neutral). Generally, this setup is safer, because the current-carrying neutral is not connected to the dryer case. However, it is useless if the wall receptacle does not have a separate ground slot. In that case, you'll have to do the very simple procedure of converting a 4-wire dryer to a 3-wire setup. Conversion of these appliances in the U.S. is prohibited by the NEC (National Electric Code). The receptacle and wiring should be modernized to a 4 conductor arrangement instead."

SteveR
  • 3,869
  • 1
  • 17
  • 17
  • The third pin is neutral, not ground. Old dryers use [NEMA 10-30](http://en.wikipedia.org/wiki/NEMA_connector#NEMA_10) receptacles, which is hot, hot, neutral. They would be wired with 10/3 or 8/3 cable. The chassis of the machine would be bonded to neutral, which basically means the neutral is also a ground, however, the wire would be insulated. – Tester101 May 25 '12 at 13:45
  • What Tester said. Third pins on 220 plugs are never ground. The options are hot/hot/neutral (3 pin) and hot/hot/neutral/ground (4 pin). – The Evil Greebo May 25 '12 at 13:48
  • @TheEvilGreebo That is not entirely true. NEMA 6-30 is hot, hot, ground. It's used if 120V is not required. – Tester101 May 25 '12 at 13:53
  • Did you read the link? "This was a legal grounding method under the National Electrical Code for electric ranges and electric clothes dryers from the 1947 to the 1996" If I am to offer advice it won't be on how it was done wrong in the old days, but how to do it safely today. The practice of using the neutral as ground is no longer used, and that is why he has the correct four prong plug! – SteveR May 25 '12 at 14:00
  • @SteveR You're right it's not done this way anymore (in new construction), but the third prong was never *ground*. It was always neutral, it just happened that they bonded the chassis of the dryers to neutral. There was always the potential for current on the third wire; if the dryer used 120V, so it is not a ground. – Tester101 May 25 '12 at 14:07
  • @SteveR Go read NEC article 250.140, this practice is still acceptable "For existing branch-circuit installations only" given specific conditions are met. – Tester101 May 25 '12 at 14:14
  • @Tester101- I'm not saying it was not done years ago, I'm saying it is not done today. To give advice to the OP to wire the dryer in this this way is irresponsible and dangerous! The only correct answer is to replace the receptacle with the correct four prong outlet! – SteveR May 25 '12 at 14:15
  • First, I stand corrected on the above. Second - They still sell three prong outlets today. They still sell four prong outlets today. They still sell three prong plugs today. They still sell four prong plugs today. We - NONE of us - really KNOW whether his 3 prong is HHN or HHG. The 3 prong plug may be perfectly safe as H/H/N as long as the 3 prong wire is connected correctly. – The Evil Greebo May 25 '12 at 14:18
  • I think at this point the best option for us is to rescind our answers pending more information about the existing setup. – The Evil Greebo May 25 '12 at 14:19
  • @TheEvilGreebo Dryers use either NEMA 10-30 (3 prong) or NEMA 14-30 (4 prong), which are h/h/n and h/h/n/g respectively. – Tester101 May 25 '12 at 14:22
  • Yes, but we don't know how his house is *wired*. His 3 prong outlet may have been WIRED h/h/g. – The Evil Greebo May 25 '12 at 14:28