I have an older General Electric panel that I need to install a 30-amp tandem circuit breaker to create
2 240 volt circuits. The GE panel accepts TQL-AC, TQAL-AC, THQL-AC, THQA, TXQL, type breakers. What brands are interchangable that would fit the GE panel.
    Why are you looking for an alternative? All those GE breakers you listed are widely available at reasonable prices. – Nate S. Feb 12 '21 at 21:49
  • If you're hoping to use half-width tandem breakers to get a 240V circuit in a 1" slot, it looks like you're probably out of luck -- GE's tandem breakers are called THQP, which your panel does not list, and GE uses a different connection mechanism for these than any other manufacturer, so there are no substitutes available. – Nate S. Feb 12 '21 at 21:57
  • Can we have a photo of the panel and the panel labeling? You can [edit] this into your question. – Harper - Reinstate Monica Feb 12 '21 at 22:46
  • Yes, can we have photos of your panel, including clear shots of the labeling on the inside of the door please? – ThreePhaseEel Feb 13 '21 at 00:04
Short version: you can't cross breaker brands. You cannot put a competitor breaker type in this panel.
A "tandem" breaker is not what you want. Here is an article about those.
What you're hoping to use is a THQP or TQP breaker, which appears very similar to a tandem breaker, however, is actually a 2-pole breaker that is half-height. On certain GE panels, GE has a system that uses 1/2" tall (half-height) breakers, 2 per breaker space. Their 2-pole breakers in that system are 1" tall and straddle 2 breaker spaces, with a 1/2" breaker above and below them.
You can't use them. Those half-width breakers clip onto a special "cruciform" cross-bars added to the bus stabs, and your bus stabs don't have them. You can see the cross-bars in the lower 5 rows of this panel here:
  • The "H" in a GE breaker part number just means HACR. So with and without the H is ok. – Bryce Oct 23 '23 at 01:05
  • @Bryce interesting, I've never seen them on shelves without the "H". And for the record I just did an edit to add the word "cruciform" so I have a chance of ever finding this photo again. It's very helpful when explaining GE thins. – Harper - Reinstate Monica Oct 23 '23 at 19:07