39
I keep hearing about tandem breakers, and how they won't work with 240V loads and how they should never be used for a multi-wire branch circuit. Aside from those issues...
What is a tandem breaker?
(note: they can be thrown independently).
    tandem breakers are usually on the same pole 120v where double pole breakers are 240v. I know it is splitting hairs with wording, but I have been called to a home the dryer did not work after a tandem 30 amp breaker was installed DIY. The drum would turn but no heat because it was only 120v. As far as I know all mfg's call there 240 breakers double pole, and tandem or double stuff are on the same pole. With tandem breakers they Cannot be used with a multi wire branch circuit because that would overload the neutral. A double pole,common trip, or 2 adjacent full sized breakers with handle ties – Ed Beal Feb 26 '18 at 15:10
It starts with spaces in the panel
A service panel has a basic unit I call a space. That's apparent when you look at the "knockouts" on the cover.
Electrical power in North America delivers split-phase power. Meaning there are two "legs" or "poles" - L1 and L2 - both 120V from neutral, and opposite-phased so they add up to 240V.
Pic: X-ray of service panel showing bus-bars alternating rows
Here's an X-ray of a service panel cover. See the trick? The buses are arranged in alternating rows. Every other row is a different pole on both sides. Any single-space breaker gets only one pole and 120V (its circuit also attaches to the neutral bar, not shown) -- but a 2-space breaker has access to both poles and 240V.
A single-space breaker cannot get 240V. That's very important when we get to duplex breakers. Now let's fit some breakers.
Pic: striped for legs with breakers in
On the upper right you see a single breaker. This occupies one space and serves one circuit.
On the upper left, you see a 2-pole breaker: this occupies two spaces, and can access both poles L1 and L2. Both sides will trip together if either side overloads. This is used for 240V loads, or for multi-wire branch circuits (MWBC).
Backside of a 2-pole or quad breaker. Note the 2 clips grabbing 2 different poles.
Duplex and friend
On the lower right is the star of the show: the duplex/tandem breaker. This occupies a single space and can only access a single pole. The sides will not trip together. It cannot power 240V loads, it must not power MWBCs, and it is generally used for two unrelated circuits. The entire point of the duplex is to save space in the box. We often call that a "double-stuff" for obvious reasons, and to emphasize how it's different from a 2-pole.
Back of a duplex breaker. Only one clip to grab one pole.
Lower left is the quad breaker, a 2-pole duplex breaker. Again the purpose is to save space. It's just what it looks like, 2 duplexes, except it can access both poles L1 and L2, and it has handle-ties so the inner pair will trip together on overload. That makes it suitable for a 240V load or MWBC. On this model, the outside pair is also tied together with common trip and can serve 240V loads or MWBC. Or, you can get these breakers with outer breakers independent.
General Electric's Q-line panels take a different approach to the problem, and you will never find a quadplex in Q-line.
No substitute for spaces
Most panels only allow these double-stuff breakers in certain positions. Some only forbid it in their labeling, while others actually key the buses so duplex breakers won't fit. Don't force them.
Nowadays in new or remodel work, most circuits must be GFCI and/or AFCI. Here's the trick: for most panels, GFCI/AFCI breakers are not available in duplex/tandem/double-stuff. This is why you can no longer add circuits by switching to these, and why being low on breaker spaces is kind of a big deal. Which is why many of us recommend quite large panels.
The 12-space panel featured here for illustration is terribly small, more befitting a shed than a house. They are made as large as 60 or even 84 space. Many will say "40 circuits/30 spaces" meaning they can accommodate double-stuff's in 10 spaces, but only have 30 total. Watch out for that.
    Very nice visuals. A great representation and explanation. – Speedy Petey Mar 12 '17 at 13:23
    Also worth noting is that the modern standards for panels that ALLOW "tandem" breakers is for them to be "CTL" listed, meaning "Circuit Total Limitation". Per this standard, the bus bars in the panel are designed such that only a FEW of the spaces will allow tandem breakers, which ensures that users don't try to exceed the total number of possible circuits. Older panels, now referred to as "Non-CTL" had no restrictions, but the breakers for them have slightly altered mounting arrangements and will not work on newer CTL panels. – JRaef Feb 13 '18 at 22:04
    I would fully agree with the exception tandem breakers are usually on the same pole 120v where double pole breakers are for 240v. I know it is splitting hairs with wording, but I have been called to a home the dryer did not work after a tandem 30 amp breaker was installed DIY. The drum would turn but no heat because it was only 120v. As far as I know all mfg's call there 240 breakers double pole, and tandem or double stuff are on the same pole. – Ed Beal Feb 26 '18 at 15:01
    Can you elaborate on GE's Q-line and what they do differently, or point to some resource that explains it? – Moshe Katz Oct 31 '18 at 18:14
  • I don't get the reason for quad breakers. I think I have some in my square d panel. I had a new panel put in and it has handle ties across spaces that are weird and unrelated. I have a handle between my basement lights and boiler. Both 15 amp circuits that used to have their own independent breaker, now they are tandem-ized, why? What is the benefit? – jmichas Dec 05 '19 at 03:11
  • @jmichas Most likely because they are a type of configuration called a "multi-wire branch circuit" *which is actually one circuit with two hots sharing a neutral*. This allows you to run two *effective* circuits on one /3 cable. But it requires a handle-tie, since it is one circuit. If you want more info, ask a question with some photos of your panel. – Harper - Reinstate Monica Dec 05 '19 at 03:17
  • @Harper-ReinstateMonica You nailed it. I figured that out today, I guess in my old panel the circuits weren't handle tied so it was confusing. I took the cover off the panel to look and found all the handle tied pairs that I had were indeed 12 or 14/3. It came into play more when I was backfeeding the panel during a power outage and found out I couldn't power both legs of the MWBC from a single phase 120 generator. Anyway, thanks for your input. – jmichas Dec 06 '19 at 04:46
  • @jmichas [This question](https://diy.stackexchange.com/questions/179894/why-are-adjacent-breakers-for-unrelated-circuits-ganged) just came up, which is on-point to your query. – Harper - Reinstate Monica Dec 07 '19 at 20:12
    @jmichas please tell me you turned off your main breaker when you were backfeeding? If not, you could be powering your entire block, and deliver a very unpleasant (read: possibly lethal) surprise to a lineman working on what they *believe to be* a de-energized line. – Doktor J Feb 06 '20 at 16:57
    @DoktorJ More than that; an interlock is required. Cheapest way to get one of those (and a lot more panel spaces) is a subpanel. – Harper - Reinstate Monica Feb 06 '20 at 18:56
    @DoktorJ Yeah, I was sure to turn off my main and I know I should have an interlock but this was an emergency situation and I needed to power my boiler to prevent pipes from freezing. – jmichas Feb 08 '20 at 15:59
The lowdown is panels are sometimes better compact and squeezed down for minimal space saving features. To achieve this, panel manufacturers use what is called tandem breakers.
Most panels have a maximum allocation for tandem breakers and is abbreviated with a ratio. For example 12/24 ( 12 space / 24 circuits ).
Kris
  • 4,813