13
I'm trying to install AFCI breakers on my kitchen SABCs (2x 20A circuits), in my Square D Homeline panel. Unfortunately, the breakers trip whenever I try to do anything useful on those circuits.
I've spent hours going over all the wiring inside the boxes and making sure connections are tight, conductor wrapping is intact, and even taping around every outlet to avoid something accidentally making contact or arcing with ground when the receptacle is pushed back in. I'm at a point where the breakers don't trip if nothing is connected to the receptacles (tested for 24hr+), but plugging in and using almost any appliance trips them, including:
I've tried 3 different Homeline HOM120PCAFIC breakers (2 of the same batch from Amazon, and 1 of another batch from Home Depot). The latter was still in its manufacturer plastic wrapping that I had to cut with scissors, so I'm sure it was new. I got the same results on all of them.
I need to get these circuits inspected, since they were modified / re-routed (over 6') in a recent project with an associated permit. My state is on 2020 NEC and requires AFCI everywhere inside. AFCI breakers are the last thing blocking inspection.
Questions
Are Homeline AFCI breakers just known to nuisance trip often? I know Siemens had a class-action lawsuit against them for nuisance tripping at one point, but didn't think Square D had that too.
Are all my appliances just crappy and arcing all the time, and need to be replaced?
Are there any other options I haven't considered for getting this inspected?
peter
  • 1,381
    If you carefully switch the wire from another 20-amp circuit in the house to these AFCI breakers as a test, does the breaker trip? If it does not, do the kitchen appliances trip the breaker when they're plugged in on the other test circuit? If they do not also, then your kitchen may have arcing wires in the walls somewhere, with fire risk. – Triplefault May 05 '23 at 16:51
    I'd try taking a table lamp with an **INCANDESCENT** bulb of at least 100 watts and plug it into a kitchen outlet. If it trips the gfci then, you know you have a wiring problem, if not, your appliances are "leaking" electrons to ground....not safe, but do bear in mind it only takes about a 5 milliamp difference to trip a gfci. That said, whatever is causing regular gfci trips needs to be fixed. – George Anderson May 05 '23 at 17:10
3 different units, you haven't used AFCIs before, and any appliance does it, but it does not trip when nothing's plugged in:
Did you neglect to connect the circuit's Neutral wire to the matching breaker as is required for GFCI & AFCI breakers? Did you make sure it was the correct Neutral wire for the Hot?
Image removed for draconian attribution idiocy.
If your panel is not PON (Plug On Neutral, which the CAFCI part number implies it should be) you also need the "B" pigtail from the breaker to neutral.
Or do you have MWBC (multi-wire branch circuit) for kitchen outlet circuits running on 12/3 which you are trying to connect to single-pole AFCI units? That won't work. You need a double-pole unit to cover a MWBC (with the circuit neutral connected to it.)
  • Good catch on the neutral. – Chris O May 05 '23 at 19:54
    This was it! This was my first work with AFCI breakers and I didn't realize I had to connect the branch circuit neutral to the breaker too. After your answer I went and found the matching neutral and hooked it up to the breaker, and since then it no longer trips even with loads connected. Thank you! – peter May 05 '23 at 20:54
  • p.s. it wasn't a MWBC, these are two completely independent circuits each with their own breakers. I've installed a different CAFCI breaker for each of them now. – peter May 05 '23 at 20:55
    When shooting in the dark I try to cover many bases, since I don't know which one might be right until I have more information. Does the fridge work now? – Ecnerwal May 05 '23 at 20:56
    Yes! Fridge (and all other appliances) work perfectly fine. I feel like an idiot, but also, I've never been so glad to feel like an idiot in my life. I was in the process of returning the fridge and buying another one, and was considering some deeper investigation on the in-wall wiring. – peter May 05 '23 at 20:59
    Also for context, it's a plug-on neutral panel (as you noted). In hindsight, this probably contributed to misunderstanding it as "I don't need to worry about neutrals for AFCI breakers here". But I guess that's only for the pigtail, not the branch circuit neutral. – peter May 05 '23 at 21:01
15
There are 2 huge problems with AFCIs that blindside people new to them (and GFCIs as well).
Neutral to the breaker
If you're new to AFCIs, circuit neutral needs to go to the breaker, NOT the neutral bar. This is particularly nasty with Square D, because as you can plainly see, there is only one screw on the breaker. There actually is a second screw for the neutral, and it's hidden.
The concept is, the breaker must see all the wires in the circuit except safety ground so it can compare currents. That'll be important later.
Also note that per NEC 110.3, you are always required to follow instructions and labeling, which means "read them" :) Always; not just when you're stuck.
Neutral must be monogamous
That is, the neutral must only serve loads also served by its partner hot(s). In kitchens, the #1 place people get in trouble with this is "shared neutral" circuits with /3 cable with red and black hot sharing a neutral. It's a cheap way to save some wire, because you get two circuits' worth of power on 4 wires instead of 6. This is more formally called a Multi-Wire Branch Circuit or MWBC meaning it is 1 circuit with 2 hot wires. It IS NOT two circuits. Get that straight.
So remember the part where the breaker must see all the wires in the circuit (but ground)? If you're running MWBC/shared neutral, you must use a special AFCI breaker that takes two hots and 1 neutral. That is called a 2-pole AFCI. Something like a HOM220CAFIC.
"Neutral must only serve loads powered by the partner hot(s)" is a hard-and-fast rule in ALL electrical wiring, and has been since World War II. We often see installations where, let's say someone has a switch loop to a switch, and a receptacle near it that's on another circuit. So to run their smart switch they just poach neutral off the nearby receptacle - that neutral is now "sleeping around". Neutral is not "common". Historically, nobody stopped you from doing that so it would be easy to cultivate a bad habit. It was always illegal and unsafe. However, AFCIs and GFCIs "keep you honest" on this rule.
Note that it's more than just "neutral on the same circuit", it is "neutral in the same cable". NEC 300.3. If you put a clamp ammeter on any cable with loads running, it should show 0 amps, because all current going out on 1 wire in the cable should come back on another wire in that same cable. Thus the magnetic fields cancel each other out, and the clamp meter reads zero.
    This answer is spot on, I hadn't installed AFCI breakers before this and totally missed the fact that there was a second screw under there for the neutral! Connecting it fixed the issue on all my circuits. I definitely need to read the instructions next time I'm working with something new :) – peter May 05 '23 at 20:56
  • Will accept Ecnerwal's answer since he was first in suggesting this idea (which got me to go and fix it), but I upvoted your answer too since it's also spot on and has additional useful info – peter May 05 '23 at 20:58
  • What is done with the neutral pigtail when installing these in a PON loadcenter? Cut it off? Or just leave it hanging in case you later want to install the breaker in a non-PON loadcenter? – Jim Stewart Jul 06 '23 at 22:58
    @JimStewart For an xFCI to take advantage of a PoN panel, it must have a special neutral bus clip to clip onto the neutral bar. It will have that *instead of* a pigtail. If there's a pigtail the xFCI needs it wired to the neutral bar in the old-fashioned way. – Harper - Reinstate Monica Jul 06 '23 at 23:27
This is a comment under the accepted (and correct) answer
This really needs its own addendum answer because the industry is changing how these breakers work and it can be confusing.
In older panels, the neutral bus was simple a bar somewhere in the panel to connect all your neutrals to. This meant you often had the neutral somewhere far away and you had to fish wires around the box. Pigtails are for these older panels, but they work with any panel because you have a wire to run between the breaker and the neutral bus.
Every manufacturer is starting to make their own workarounds to the growing need for breakers to have a neutral connection (CAFCI, AFCI, GFCI, etc.), and most are calling it "plug-on neutral". What's different here is
  1. The neutral bar distributed behind the hot rails for your breakers (Square D shown)
    Distributed neutral
  2. The "plug-on neutral" breakers have an extra clip to pick up the neutral bar
    Plug-on neutral clip
Images above from this video
These panels still support a pigtail breaker, but the purpose of the clip is to remove the need for a pigtail. You connect the hot and neutral to both types of breaker. The clip is what provides the connection to the neutral bar.
My hunch is that your appliances have nothing to do with this. Rather, you have bad wires.
GFCI is not the same as AFCI. They serve very different functions and operate quite differently.
GFCI is for life safety and is conceptually incredibly simple - check to see if hot and neutral have the same current. That's it. Self-testing, indicator lights, etc. are all icing on the cake. But the core is: Compare the current. That can be done with very basic components, which is why it has been available for decades, with gradual increase in required locations as the cost has gone down.
AFCI is for fire safety. It is conceptually, and practically, quite complex. You don't need a microprocessor to figure out GFCI. You can - and modern GFCI (whether breaker or receptacle) uses a microprocessor for self-test and other features, but you don't need it. But AFCI is a much more complex thing, that pretty much requires a microprocessor to analyze the power flow to determine if it is doing "bad things" that would indicate a likely arcing situation that could lead to a fire.
As a result, GFCI is required primarily in wet places - kitchen, bathroom, laundry, outdoors, though recently expanded to include other areas. AFCI, on the other hand, started in the other areas - bedrooms, then living rooms, etc.
Another important difference is that GFCI is primarily a user (wet hands) and device (hot leaking to metal case, or wet stuff touching the user) problem, though it can (with immediate trip every time you use the circuit with any appliance) be due to a wiring problem. On the other hand, with the exception of some motor, compressor, etc. issues (which can affect refrigerators, among things), AFCI is mostly about wires, not about appliances. Which points to an AFCI tripping on every appliance being a wiring problem and not an appliance problem.
There is some overlap now, and it will likely increase over time, depending on NEC version. So you may be required to include AFCI for new circuits in your kitchen. If these are existing circuits, I would recommend installing GFCI (either receptacle or breaker) if you do not already have it (the life safety advantage in a kitchen has been obvious for decades) but not to install AFCI unless required by your jurisdiction.
If you do not already have GFCI (i.e., GFCI/receptacle) then you could install GFCI/receptacle (usually the cheaper method) and get the important safety protection. You could, instead, return that AFCI/breaker and get a comparable GFCI/breaker. If that breaker works fine (I bet it will) then you know that you do not have any ground issues and that your problem with the AFCI is actually arc faults.
That leaves open the question of: Assuming you have arc faults, what should you do about them? If they are real, and not just nuisance trips (e.g., due to heavy machinery somewhere causing noisy power problems in nearby circuits) then replacing those circuits may be a good idea, depending on the age of the wires and the effort required.
  • Quick question: If @peter has bad wires, would it be a good idea to look for problems instead of only installing GFCIs? Maybe a fire is in the offing. – Triplefault May 05 '23 at 16:48
  • @Triplefault Yes. But it is a question of priority and cost/benefit. AFCIs can trip due to: hot/neutral imbalance (depending on the type of AFCI - but GFCI will catch that by design, so not worried about that here), actual arcing (which you *want* to catch and fix), *nearby* arcing (i.e., a different circuit, if the arcing is strong enough), **other stuff that isn't arcing but is similar enough to trip the AFCI** - and that is a real issue with a number of AFCI devices over the years. – manassehkatz-Moving 2 Codidact May 05 '23 at 16:54
  • I understand the difference between GFCI and AFCI. I'm totally fine with skipping AFCI if not needed (I already added GFCI through receptacles, and it's working fine), but have been assuming it's needed due to major rerouting of those circuits (moving by >6') requiring new code to kick in, and we're on NEC 2020 which requires AFCI in kitchens. – peter May 05 '23 at 17:18
  • re. wiring -- I was assuming that if the breaker didn't trip for 24hr+ without those appliances turned on, then the wiring is fine and the issue is with the appliances. But now you got me thinking -- could there be an arc fault that only shows up when devices start to pull lots of current? – peter May 05 '23 at 17:20
    Absolutely! Or even just a little current. Comparing to GFCI (the technology is totally different, but conceptually)...if 10% of your current leaked, then at 1 A it would be 100mA and trip the GFCI. But if your current is 0A then 10% = 0A and GFCI would not trip. Same idea with AFCI - lots of current = lots of arcing, little current = little arcing, no current = no arcing. – manassehkatz-Moving 2 Codidact May 05 '23 at 17:22
  • That (does moving these existing kitchen circuits around trigger AFCI requirement) is a question for your local inspector. – manassehkatz-Moving 2 Codidact May 05 '23 at 17:23
I don't know of any earned reputation that SqD AFCI breakers have for nuisance trips - in fact I have installed more than 20 of the SqD CAFCI breakers in various panels and can't think of one that has nuisance tripped.
I suggest performing these tests:
  1. Take your toaster and air fryer into the bedroom and plug them in (assuming your bedroom(s) are on a different circuit which is also AFCI-protected). Hell, pretend you're in college and make some bedroom toast. Does either appliance trip the AFCI in there? If yes, you can probably start blaming the appliances themselves (things wear out). If not, then it doesn't necessarily mean the cause is the AFCI breakers themselves, but something on the kitchen circuits. That leads you to number 2.
  2. Replace the receptacles on the kitchen small appliance circuits. In my experience, receptacles with dirty or worn internal terminals can cause arcing, even during normal use if they are worn enough (i.e. not while actively plugging/unplugging). For extra peace-of-mind, buy spec-grade receptacles with screw-clamp cable connections. Don't use the back-stab or wire-wrap the screws. They're only a couple of bucks more, but they are faster to connect and more reliable to use.
Chris O
  • 6,604
  • 45
  • I don't have AFCI anywhere else in the house unfortunately (it's a 1993 build, and only my new kitchen remodel requires upgrading to AFCI), though perhaps I can move my new AFCI breaker to a new circuit and test there? And all the receptacles are new and expensive ones, no backstabs, all screws are tight, all receptacles are wrapped with electric tape. – peter May 05 '23 at 17:22
  • @peter Good idea on moving the AFCI. If possible, choose a circuit with a small number of outlets on it. Replace its breaker with your AFCI and test. If the circuit works without trips, then plug your kitchen appliances into it and check. If you get trips, you know you need to go appliance shopping. – Chris O May 05 '23 at 17:26