Can 3/4" Liquid Tight Non Metallic Flexible Conduit be run inside a PVC Sch 40 and buried 18" below ground for extra water tight for electrical wires (3 of 6awg and 1 of 10g bare copper)?

The length is about 50ft.

isherwood
  • 129,178
  • 7
  • 160
  • 386
wyciwug
  • 1
  • 2
  • Regardless of how hard you try, buried wires will always be considered 'wet'. – Jon Custer Oct 05 '23 at 16:28
  • There's no "water tight" for underground wiring. You have to use wet-rated wire. – popham Oct 05 '23 at 16:46
  • I'm beginning to think this is an [XY Problem](https://meta.stackexchange.com/questions/66377/what-is-the-xy-problem). _WHY_ is it that you keep wanting to use LT conduit? Is there a difficult run that you don't want to try to fit rigid into? Do you think you're going to make a wet environment into a dry one by using it? Something else? – FreeMan Oct 05 '23 at 17:15
  • because I already run the wires through the LT and it is easier for me, i did it under 1 hour. https://www.youtube.com/watch?v=pVV7kwzuxug – wyciwug Oct 05 '23 at 17:33

2 Answers2

2

Can you?

Yes, if the PVC is big enough to get the Liquid Tight through it. (It'll need to be REALLY big to get that through there!)

The real question is:

why would you want to?

You will not be keeping your actual wires dry by doing this. You're still going to need to run UF-B (no, really, please don't do this it's a total waste of time, money & effort, but it is code legal), or individual THHN-2/THWN wires through your conduit whether you've got the Liquid Tight in there or not.

Simply bury your PVC (use the appropriate size for your wires) and pull your individual wires through and be done with it.

You'll save money. You'll save time. You'll significantly reduce your frustration level. You'll regret trying to get the Liquid Tight through there within about 3 minutes of starting, probably sooner.

FreeMan
  • 43,073
  • 21
  • 81
  • 173
  • All exterior conduit is **defined** as wet. Almost all of it meets the definition. The wire insulation on appropriate wires is made to handle that...so indeed the extra conduit does nothing useful. – Ecnerwal Oct 05 '23 at 16:49
  • Are you adding clarifying points, @Ecnerwal, or correction? I thought I basically said what you said (except for being explicit about it being a wet location), so I'm not sure which you're intending. – FreeMan Oct 05 '23 at 17:05
  • Oh ok, then I have to buy THWN n resell THHN I bought by mistake. Thanks. Can LT be ran above ground outside and also above ground in the crawlspace? If yes then I can just use LT for that and PVC below ground. – wyciwug Oct 05 '23 at 17:08
  • 2
    A) AIUI, most wire is labeled both THHN-2 _and_ THWN. B) Yes, LT can be run above ground, it's commonly used between a disconnect and outside HVAC equipment. C) Yes, you could use it in your crawl space. The question remains _WHY_??? AIUI, pulling wire through LT is _difficult_ because it moves on you. Rigid conduit doesn't move and makes pulling much easier. – FreeMan Oct 05 '23 at 17:14
  • 1
    Just reenforcing that no matter what you do, because it's wet by definition, wet-rated wiring methods are required. – Ecnerwal Oct 05 '23 at 17:27
  • It's actually easy for me to use LT with little lube to run the wire through and I did all 100 ft within hour. I guess It is ok for me to run LT above ground and use PVC 18" below ground. I will go home and check the wire to see if it is THHN-2 or THWN. If it is THHN, I might have to figure out the next step – wyciwug Oct 05 '23 at 17:30
  • 1
    Almost any THHN you bought in the last 10 years is multi-marked as THHN-2, THWN, MTW, and a few other ratings I forget – Ecnerwal Oct 05 '23 at 17:33
0

In a nutshell, NO. The problem you'll have is making the connections into a box or panel. The non metallic connectors are large and won't allow a PVC connector to then be mounted into the box or panel.

JACK
  • 78,739
  • 18
  • 72
  • 188
  • I thought this chart says I can fit 4 #6awg inside a 3/4" LT. https://electricalestimating101.com/wp-content/uploads/2019/06/NEC-Table-C-Combined-Conduit-Types-THHN-XHHW.pdf – wyciwug Oct 05 '23 at 17:05
  • @wyciwug Edited answer to remove conduit fill. I had an old chart. – JACK Oct 05 '23 at 17:21
  • Not sure why the DV. Someone didn't know enough to understand the answer. – JACK Oct 15 '23 at 15:00