My American house was built in 1942, and much of the wiring is still knob-and-tube wiring (2-wire, no ground). Over the years new modern wiring has been added to the house, but we still have some KnT wiring for the ceiling lights, and a few branch circuits, etc. We are planning to replace the KnT wiring when we have the budget to do so. I have replaced many of the receptacles on the KnT circuits with GFCI receptacles to provide added protection, which is recommended.
I have seen AFCI and GFCI circuit breakers which plug into the service panel, and they are reasonably priced at $30-50 per breaker). Would these AFCI or GFCI circuit breakers provide any protection on old, knob-and-tube wiring?
Stefan Lasiewski
  • 908
  • 25
Arc-Fault Circuit Interrupter (AFCI)
An arc-fault circuit interruption device is designed to detect dangerous arcing within the protected circuit, and open (turn off) the circuit to prevent damage caused by the arcing. It does this using special circuitry to analyse the electrical characteristics of the circuit, looking for characteristics that match specific pre-programmed values. If the AFCI detects suspicious goings on, it opens the circuit.
AFCI breakers are typically combination devices, meaning they also provide similar overcurrent and short-circuit protection to a standard breaker.
Installing a combination AFCI breaker on a circuit containing knob and tube wiring would be a great idea, and could potentially prevent a fire.
Ground-Fault Circuit Interrupter (GFCI)
Ground-fault circuit interruption devices are designed to detect ground-faults, and open (turn off) the circuit when a ground-fault is detected. They work by using a current transformer (CT) to detect current imbalances between the ungrounded (hot), and grounded (neutral) conductors of a circuit. This blog entry might help you understand how GFCI devices work.
GFCI breakers are typically combination devices, meaning they also provide similar overcurrent and short-circuit protection to a standard breaker.
Installing a GFCI breaker on a circuit containing knob and tube wiring, probably won't provide any benefit. GFCI devices are designed to prevent electrocution, not to protect the wiring.
Combination AFCI GFCI Circuit Breakers
Circuit breakers that provide AFCI, GFCI, overload, and overcurrent protection are becoming more widely available. If you can find them for your panel (and afford therm), these would be the best option.
    Agree that a combination AFCI/GFCI breaker is a good idea, but disagree that GFCI won't provide any benefit. Since KnT is poorly insulated wiring, there is a high risk of accidental electrocution, and a GFCI may detect and stop that from becoming fatal. – BMitch Oct 29 '13 at 12:34
    While nearly all AFCI breakers provide Ground-Fault Protection of Equipment (GFPE 30-50 mA), it's nearly impossible to find one that provides GFCI protection (4-6 mA). So given the choice between an AFCI breaker and a GFCI breaker, I'd choose the AFCI breaker. – Tester101 Oct 30 '13 at 10:56
  • At first I was thinking that an Arc Fault is unlikely with KnT wiring since the hot and neutral conductors are typically placed on either side of the cavity between stud & in some cases are even separated by a stud themselves. The gap between conductors varies with the stud placement (In my house it's 16" On-Center). I would think that this air gap would reduce the chance of an arc-fault in household wiring. But then I realized both conductors need to be stuffed into the same box at some point, perhaps through the same hole. At that point it seems that an Arc Fault is much more likely. – Stefan Lasiewski Oct 30 '13 at 22:47
    @StefanLasiewski You can also have an arc along a wire, especially near splices. One frequent problem with KnT wiring is the capacity is much lower than modern demands, leading to overloading. Sometimes that overload will result in a failed junction and arcing. – BMitch Nov 01 '13 at 10:57
  • GFCIs are still going to be needed in a K&T retrofit to protect the users of appliances due to the lack of an EGC in K&T wiring. – ThreePhaseEel Mar 10 '15 at 02:56
  • @ThreePhaseEel I was just saying that given the choice between an AFCI and a GFCI, the AFCI is probably a better choice. GFCI receptacles, or standalone GFCI units can be used to provide protection to the circuit. Now that breakers are availavle that offer both types of protection, there's no need to settle for one or the other. – Tester101 Mar 10 '15 at 03:25
  • @Tester101 Aye, exactly the point of my answer -- save for those pesky shared neutrals! (Two-pole DFCIs aren't quite a thing yet, AFAICT.) – ThreePhaseEel Mar 10 '15 at 03:26
While Tester101's answer was OK when it was written, the situation has changed now. CAFCI/GFCI dual function breakers (Square-D calls them DFCIs) are now widely available online through the big-box stores' websites; in fact, the green box nearest to me has the QO DFCI I linked in stock!
Of course, any electrical supply house worth their weight will be able to order in anything from the Eaton or Square-D catalogs, DFCI's included.
One caveat, though: DFCIs are not yet available in two-pole configurations, so shared neutral circuits without a ground wire are stuck with a CAFCI for now. (It's one of those cases where perfect Code compliance is literally impossible at the moment because the parts needed to do it just don't exist yet.)
ThreePhaseEel
  • 81,744
  • 227
An AFCI is a great addition to K&T wiring. While the conductors in K&T are separated by large distances, and even studs, they do come together at junction boxes which are often metallic. An AFCI adds a layer of peace of mind to the situation.
Be sure to measure your K&T wire to determine gauge. It can take slightly more current than the modern equivalent at the same wire size, but to be safe stick with the modern values. You'll probably need a 2-pole (not tandem) AFCI, as K&T was often wired with a shared neutral. Two pole AFCI for knob and tube wiring Fora more complete writeup of K&T retrofit see https://diy.stackexchange.com/a/20279/5960
Note: when I replace a fixture in a K&T circuit I address the metal box weak point with some new loom, slipped over the wires as they come into the box. The old loom, which could easily be 50 to 100 years old, is sometimes but not always brittle. I'll also pull out the wire and wrap the exposed area with friction tape. This is the only point in the entire K&T system that even needs insulation.
Update March 2018: I now use shrink tubing to strengthen the insulation when changing a fixture on old wiring. It just slips over the old wire, and I shrink whatever section of it my heat gun can reag.
Bryce
  • 10,693
  • 108
  • _You'll probably need a double AFCI, as K&T was often wired with a shared neutral._ Whoa, what? Can you explain how a double AFCI will help here? Yes, I definitely think I've seen a shared neutral up there. – Stefan Lasiewski Dec 06 '13 at 16:34
  • FYI, I'm also in Berkeley. I've heard many of the same arguments that you have. The East Bay seems to be Knob & Tube central. – Stefan Lasiewski Dec 06 '13 at 16:34
  • @StefanLasiewski I clarified the answer: I mean a 2-Pole breaker like the Siemens Q215AFCP (Carried by Lanner Electric). Note that the AFCI might detect existing faults in your system, and trip right away. – Bryce Dec 08 '13 at 08:40
Your best best, if you can't do both, is AFCI breakers -- after all, AFCIs are designed to protect wiring from arc-faults, which start fires, and Knob-and-Tube era homes are vulnerable to this. And then GFCI receptacles -- GFCIs are designed to protect humans from shock.
As of NEC 2014 (adopted 2015-16 most places) you can now retrofit grounds, and the ground wires do not need to run with the paired hot and neutral. You can ground to any grounded point as long as it chains back to the same service panel, or the grounding electrode system from that panel. The entire run/chain of ground wire must be large enough for the job.
You will probably find that installing an AFCI breaker will be very annoying. Many electricians don't like them because they go off very unreliably. For example, if you run a vacuum cleaner, or a sump pump, those could trigger the AFCI circuit even if there is no arc fault. I believe it is code to install AFCI breakers in new electrical work, but many electricians were replace them back with regular breakers after inspection, because of how annoying they are.
If you have already replaced the older outlets with GFCI, that's about all you really need to do.
steve8918
  • 95
    It's not likely that a licensed Electrician is changing out items after inspection. If they are, they should lose their license. Secondly, this is old, outdated information that constantly propagates throughout the internet. Modern AFCI breakers are less prone to nuisance tripping. If you're going to form an opinion based on others opinions, please check the date of the sources. – Tester101 Nov 01 '13 at 21:01
    @Tester101 here's a source dated August 2014: every time the cleaners come they trip our AFCI with their vacuum (a generic Kirby HEPA canister). The AFCI was purchased new in 2012. – Bryce Aug 21 '14 at 05:37
  • @Bryce Did you forget the link, or are you saying you're the source? Did you inspect the vacuum? If your vacuum is tripping the AFCI, there's a problem with your vacuum not the AFCI. – Tester101 Aug 21 '14 at 10:00
  • @Tester101 I am the source. The vacuum appears normal, is owned by the house cleaner. I have not put an oscilloscope to the line, at least not yet. The house lights don't dim or anything. The vacuum is presumably used every day. – Bryce Aug 21 '14 at 10:42
  • @Bryce The AFCI is detecting an arc- or ground-fault within the vacuum, and is working as designed. There's a problem with the vacuum, or the manufacturer didn't get the memo about creating AFCI friendly products. Now that AFCI devices are required in more locations, I'd guess newer products are going to be less prone to tripping them. Could be a good marketing technique "*Now AFCI friendly!*" – Tester101 Aug 21 '14 at 11:32
  • @Tester101 it's still a nuisance trip. Agreed on the eventual harmony between devices and AFCI's. – Bryce Aug 21 '14 at 19:13
  • @Tester101: I had an electrician pull AFCI breakers after discovering they are incompatible with Ethernet by their design choice of including GFCI-like short-to-ground detection. – Joshua Dec 18 '16 at 22:21
  • @Tester101 now my dryer is tripping the AFCI. And, a newer vacuum. I hate it. The AFCI in question is from Siemens: and yes I contacted Siemens and basically they don't care. – Bryce Jan 15 '17 at 21:57
  • I gave Bryce a + because even today I still see AFCI problems with motor loads and dimmer circuits, luckily my state allows the removal of these devices if nuncence tripping is a problem. So with that I can legally remove a required breaker and put a non AFCI model in. – Ed Beal Jan 01 '19 at 20:34