48

I have been doing some electrical work in my house and I noticed it has old knob and tube wiring that is still hot, should this be replaced as found or is it fine to just leave it? It seems really old and brittle, so I'm a little concerned.

Bryce
  • 10,693
  • 14
  • 65
  • 108
Tester101
  • 131,097
  • 78
  • 316
  • 608

10 Answers10

37

Generally, it is a good idea to replace it, especially if you can easily access it. One thing you don't want to do, is replace part of a circuit. Then the next guy might see the new romex and make some assumptions about the rest of the wiring. The other time you really really should replace it is if it runs through insulation, especially blown-in cellulose. That is a serious fire hazard. Knob and tube was designed to use open space as an insulator.

Josh Goldshlag
  • 926
  • 7
  • 8
  • Cellulose is fire resistance isn't it? – Joe Phillips Jul 21 '10 at 21:01
  • 4
    In theory it is treated with some awful chemical to make it fire resistant. Even in that case, you are going to have the wires heat up, especially since they are often carrying more load than was anticipated when first installed. If they get too hot, they might start a fire anyway. They really need the open space for cooling. – Josh Goldshlag Jul 21 '10 at 21:50
  • 2
    It is actually illegal in almost every jurisdiction to join modern copper multi-conductor wire to knob & tube, for the reason stated; the electrician you hire will see the modern wire and assume the whole circuit is up to code, slap a 20-amp breaker on it to handle the new load he's adding, and your house burns down. – KeithS Jun 22 '11 at 18:51
  • You can also just downrate certain circuits. Install a 10 AMP breaker for example, on a light circuit, and any theoretical "heat issues" go away. Modern wire is plastic wrapped which holds heat better than K&T, the heat issue is overblown. – Bryce Oct 30 '13 at 04:14
  • 3
    @KeithS, the NEC 300.16(A) seems to contradict your claim: *"A box, conduit body, or terminal fitting having a separately bushed hole for each conductor shall be used wherever a change is made from conduit, electrical metallic tubing, electrical nonmetallic tubing, nonmetallic-sheathed cable, Type AC cable, Type MC cable, or mineral-insulated, metal-sheathed cable and surface raceway wiring to open wiring or to concealed knob-and-tube wiring. "* – Nate Jan 05 '14 at 13:07
  • @Nate in this situation I've put old wire in place (salvaged from the property) to avoid the confusion. But, using modern wiring technique. – Bryce Jan 23 '14 at 00:12
  • 1
    re: "awful chemical" and Cellulose: boric acid, a safe compound that sometimes washes off w/leaky roofs. – dandavis Oct 04 '17 at 08:03
  • 1
    Fire resistant is not the same as non-flammable. Cellulose insulation will burn (first-hand experience). – Jean-Paul Calderone Nov 15 '18 at 17:31
  • Nothing about K&T presents a fire hazard when in contact with insulation. It is a completely myth that K&T gets hot in use. Badly overloaded K&T maybe, but the same applies to modern wire. – Bryce Nov 27 '18 at 17:08
  • I'm that "next guy". None of the k&t went to my breaker and was almost entirely replaced by nm. The run to a light changed to old k&t wires 5' after its switch. It gave me two problems: frayed neutral in an ungrounded box, and a neutral shared on a different circuit than the hot. I was surprised when putting a gfci on one circuit got tripped when the light on a different circuit turned on. – Josh from Qaribou Oct 18 '21 at 20:22
32

Myths abound about K&T, and lots of it is ripped out unnecessarily.

The K&T wire is exactly as thick as modern wire, and was installed by skilled craftsmen using bulletproof soldered joints rather than plastic wire nuts. The ceramic tubes will outlast civilizations. With certain important exceptions your K&T will outlast the house itself, unlike modern wire.

K&T is more heat resistant than the equivalent modern wire, because the conductors are separated by an air gap. The ceramic tubes mean that even if the insulation deteriorates it creates no fire hazard. And in fact, if you check fire statistics you'll find K&T wiring is as, or more, safe than modern wiring. Hammered nails or screws can create subtle shorts and sparks in modern wire, but have little to no effect even if they pierce K&T wires. Poor installation is more common on modern wire, compared to K&T which was installed only by guild trained electricians.

From Home Energy Magazine 'Knob and Tube Not a Fire Hazard':

Legislation was enacted in Washington state to allow insulating over knob-and-tube wiring per Bonneville Power Administration (BPA) specifications. This resulted because there were no documented cases of a fire being caused by knob-and-tube wiring, whether insulation covered it or not.

Leaving light fixtures on K&T is especially practical, as grounding matters much less, and these are typically the hardest runs to replace.

--

That said, much K&T wiring is either overloaded by modern uses, or has been hacked to death by bad renovation. Our jurisdiction (Berkeley, CA) requires an inspection by a licensed electrician prior to insulating over Knob & Tube (see here).

It is important to check:

  • Fuses have been replaced with appropriate circuit breakers (15 amp for 14 gauge wire). MANY problems with K&T were caused not by the K&T, but by the fuse box -- it used to be possible to put any size fuse into any position.
  • No branch circuit is overloaded (selectively add circuits to bring things in balance. Rewire your kitchen. Run separate new circuits for the dishwasher and laundry and any place within 6 feet of water).
  • If you have a shared neutral (common) be sure to have a 2-Pole AFCI breaker (See https://diy.stackexchange.com/a/36456/5960 )
  • Check insulating loom where K&T enters metal junction boxes is still in acceptable shape. This is weak point on K&T installs. Slip new shrink wrap insulation over the old.
  • Check no wire can sag, and touch a plumbing pipe.
  • Consider an AFCI breaker for K&T circuits.

This bears repeating:

  • Use great care when changing a light fixture or outlet on K&T. The loom where the wire enters metal boxes is a weak point, and is easily damaged.

For more on insurance issues see: http://www.nachi.org/bbsystem/usrfiles/E/ESA_article_knob_and_tube.pdf

Example K&T from Wikipedia

The True Knob & Tube Danger: Modern Rework

The danger with K&T is that somebody messed with it. Here's a picture of a pretty typical example. Someone jacked a new circuit in. They cut the old knob & tube short, destroyed the original insulation, did a hack tape job, then installed a modern metallic cable almost touching that mess. This particular instance created a big spark some years later as the grounded metal cable hit the now bare wire. Original K&T installers never let the wires touch except protected by ceramic tubes.

Bad Knob and Tube Fire Hazard

Bryce
  • 10,693
  • 14
  • 65
  • 108
  • Asbestos insulation is also less prone to degradation over time: oxidation, depolymerization than is modern plastic insulated wire. – Wayfaring Stranger Mar 14 '15 at 17:11
  • And if it's asbestos, best policy is to leave it in place. Moving it, even with care, has been shown to increase the number of fibers in the air. – Bryce Mar 17 '15 at 21:02
  • 1
    Yikes! That is a scary splice! I became frightfully aware of the hazards of K&T wiring when I was mopping the floor in a closet. Most of my wiring runs were replaced with Romex, but not all. I got a little water on a pair of wires and heard a diabolical sizzling. I shut off the circuit and replaced the wires with Romex as soon as the floor was dry. No more K&T for me. – Suncat2000 May 09 '19 at 12:34
30

The advice my family once got from an electrician on this question was that if you have low amperage service and NEVER touch it, you're probably okay. If you have regular electrical service or touch the circuits at all, remove ALL of it. His basic theory was that if you keep the wires cool, and they haven't caused you trouble yet, it's unlikely to cause a problem. Granted that advice was about 15 years ago and none of that wiring is improving with age.

Once you touch the lines at all, rip it all out. It's very likely that you will introduce a problem between the coating and the wire. The house we were dealing with went another 10 years before we needed to rewire one of the old circuits. Once that happened we rewired the entire house all at once.

If you're concerned at all, turn off the affected circuits, and get rid of it. Better safe than sorry on this one.

gregmac
  • 28,910
  • 15
  • 84
  • 160
acrosman
  • 1,619
  • 17
  • 22
  • 1
    The "keep it cool" advice, while often repeated, seems a myth. Check your k&t is not overloaded compared to the wire size, and it's just as good as modern copper wire, even if insulated over. – Bryce Mar 17 '18 at 18:33
6

There may be issues with your insurance company. I recently bought a house and asked two insurance companies about the knob-and-tube wiring.

  • Liberty Mutual said that they would insure the house, but would require that the knob-and-tube wiring be removed within 30 days by an electrician.

  • Met Life said that they would not be able to insure the house until the knob-and-tube wiring had been removed.

Vebjorn Ljosa
  • 9,575
  • 18
  • 58
  • 86
  • This was similar to my experience. Removing it became a condition of receiving insurance. – Alex Feinman Jan 25 '11 at 19:37
  • When pressed, I found insurers were willing to insure if the K&T was inspected by an electrician. Since we had to do that anyway to insulate, it was no problem. K&T is very robust and does not 'wear out' as long as it has not been extended improperly. – Bryce Oct 28 '12 at 00:02
  • 1
    A friend was OK after removing "90 percent" of the K&T. After subtracting dishwasher/range/furnace, the remaining minor outlets and lights (the hardest to do) were OK. Inspection by a qualified electrician was important. – Bryce Oct 30 '13 at 04:11
  • 6
    I have Liberty Mutual insurance for a K&T house **right now**. (and yes, I did tell them about it) – Nate Nov 21 '13 at 06:31
5

A big problem with K&T is the horizontal runs - sagging over time means stress on the insulation, which becomes brittle from oxidation (not the wire - the rubber insulation), and can break off. You then have (a) bare wire(s). Should those wires come in contact with horizontal piping - particularly after something like a renovation, which usually redistributes loads and causes fresh settling - you have a recipe for a short and a fire. This exact thing happened to a balloon framed Victorian (vint. 1898) in RI, causing a fire on the third floor. Fortunately, the smoke was spotted by a passerby who came in, woke the occupants, and saved their lives. The water damage was extensive, and the cost to restore with matching full dimension lumber, lath/horsehair/grey coat and finish plaster was very high. A beautiful Italianate Victorian was nearly lost to history but for the passerby. All K&T was replaced, and worth doing.

Note that a proper K&T installation added tubes at the point of crossing a pipe or another wire. Probably the pipe was added later in the fire above:

Knob and Tube wiring proper crossing detail extra tube

Bryce
  • 10,693
  • 14
  • 65
  • 108
George Steele
  • 51
  • 1
  • 1
  • Do youy have a news or trade reference to this fire? K&T fires are rare as it takes an additional actor (like a bad rennovagtion, or the metal pipe you mention) to cause a problem, even if the insulation is completely gone. Smoke detectors that call the fire department a good idea in any building, doubly so in a old one with minimal inter-floor fire breaks! – Bryce Mar 17 '18 at 18:20
5

A house in San Carlos CA, Having 50% knob-and-tube, 50% 1980 romex:

Insurance was no problem: No company cared (I ended up getting it from Travelers, via GEICO). So, I wouldn't let the insurance stories scare you until you pick up the phone and ask. What they do care about is the type of Circuit Breakers you have. The modern ones that look like switches, or the old wire ones (that burn). That may be an issue if you have the old plugs.

knob-and-tube has 2 disadvantages:

  1. Theoretical fire hazard: you see, they need to be able to "breathe". That is why they say that it is a problem to insulate over K&T. And why everyone will say, that if "you touch it" you may disturb it and hence you should remove it.
  2. They have no grounding. So that "3rd" leg some appliances may have even if your socket accepts it, will do nothing. That is a higher risk of getting an electric shock.

Recommendation: It might be a problem with putting things "on paper" vs. verbally, but I interviewed many electricians and 3 permit employees (since I was remodeling the kitchen and "touched' some of the old K&T). My experience is that most of them, when not motivated to just make money out of you, say that K&T is just fine, there are plenty of old houses with it and you don't really see houses go up in flames around you do you? and when fire happens on the news, when did you hear that it was blamed on old K&T system (most likely you hear it was a heater or candles)

my personal conclusion, if it is not broken, don't fix it. do it only if you are doing some other thing which justifies the work.

  • Expect $3,000 to $10,000 to re-wire the house or portion of it (I only needed 50%, and I had some walls and ceiling open anyway)
  • notice that some electricians put in the quoted work the electric work, but you will have some cleanup work of patching walls and painting after they are done

Expect anything from $3000 to $10,000.

Bryce
  • 10,693
  • 14
  • 65
  • 108
csmba
  • 1,041
  • 6
  • 13
  • 23
  • 3
    Solved. You can cure the supposed fire hazard (from arcing) pretty conclusively with AFCI breakers, assuming neutrals aren't tangled up. GFCI solves ground-faulting problems, e.g. from material dragged in by rodents getting wet. Under 2014 rules you are free to retrofit grounds. Downrating breakers can hedge against heat problems from blown-in insulation preventing the wires from cooling. – Harper - Reinstate Monica Mar 07 '17 at 19:54
  • Consider replacing outlet wiring, but leaving lighting circuits. Just slip new shrink tube over the old brittle K&T wires in any light fixtures. – Bryce May 09 '17 at 17:42
  • 1
    The notion that k&t must "breathe" is entirely and completely false. It needs less breathing per unit of power, compared to modern NM cable. – Bryce Jun 03 '18 at 17:53
  • @Harper my problem there is that as soon as you find a neutral shared across branches, the GFCI will trip every time. The options then are either to rewire, or put the gfci after the shared neutral. – Josh from Qaribou Oct 18 '21 at 20:36
2

As foreman for a licensed bonded electrician, in San Francisco CA, ca 1980's... K&T wiring was NEC code approved.... and approved by the more stringent local city code... that said I code rewired a lot of Victorian houses, w/ K&T as the original wiring... it could be Western Union, solder-spliced, to repair or extend it... very tedious... and needed to add supporting knobs for those 'code splices'...

biggest issue was inside ceiling fixtures.... where the old TW wire's 'asphalt' insulation became brittle due to fixture heat... and the slightest bending often cracked the insulation... usually requiring replacing that lead back to a supported splice... very tedious... if inexperienced persons had changed the fixture insulation was usually cracked...

you could still buy knobs, and loom sheathing ATT.... but not tubes, nor the metal wedges, to lock the TW wire and loom sheath, as it enters the old metal box....which could necessitate replacing the old junction box, w/ a new one that had built in wire clamps or would accept standard connectors.... and carefully setting those connectors..... I learned to salvage the wedges, and tubes, for reuse when had to...

In all, after a couple tedious years dealing with old K&T circuits, I decided it best just tear it out in a rewire... and replaced it w/ new boxes and wire runs..romex or EMT runs... It was usually more efficient, and the customer had a better product in the end.... Only in rare cases would I work w/ it to preserve the original finish, of the ceiling escutcheons, in the old Victorian homes.... and code still required cutting and capping off the old supporting gaslight pipes, if still connected and live....

I'll take romex, or THHN in pipe, if I have a choice... lot easier to work with... I became adept at 'fishing' romex, and the tricks of cutting lathe and plaster...

jdriskell
  • 31
  • 1
  • 1
    I slip new loom over the top of the old brittle wire. Or, modern heat shrink, and don't have to splice anything. The salvage places (Ohmega and Urban Ore near San Francisco) have the tubes. – Bryce Mar 13 '15 at 23:56
1

Yes definitely. In some spots, knob and tube is a deal breaker for a house sale and must be replaced before the house is sold. It's fairly dangerous to have around, even more so if it's brittle. I'd hire an electrician if you're not comfortable replacing it all yourself.

  • 3
    After a review showing no fire history due to inspected K&T, California, Washington, Nebraska, and Oregon have modified the National Electric Code to permit insulating over it. – Bryce Oct 27 '12 at 23:59
  • 3
    Who requires knob and tube to be replaced before a house is sold? – Pat James Dec 03 '12 at 19:55
-1

K&T wire was the only wiring method used in the 1st part of the 20th century. Houses had lights and radios. Maybe a house had a toaster. After many years of heat build up and over use, any wire will degrade and its ampacity will diminish. Today, we ask an 80 year old wire to run things that require more then the century old wire can deliver. Would you ask an 80 year old car to take you to Florida from Ohio while pulling a trailer? Of course you wouldn't That is exactly what we are asking an old electrical system to do. Nothing lasts forever. It is a safety issue and so in my opinion, after 30 years in the electrical business this is what I would suggest. Replace that old overused outdated wire before you spend money on the pretty kitchen.

  • 3
    That's a bad analogy. An 80 year old car would have no trouble making a trip to Florida, as long as it's been maintained well. – Tester101 Mar 12 '14 at 12:18
  • 6
    80 years is nothing to copper. 80 year old copper is fine. And the 80 year old wood in the same house is probably better than modern wood. The wire used in knob & tube is generally 14 or 12 gauge, same as modern wire, except spaced better. – Bryce Mar 13 '15 at 23:53
-2

Yes K&T is ancient wiring and in some locations it is pretty safe. I have even seen some of it on MASH 4077 where wires are run in pairs and held by cleats.

As mentioned elsewhere, there are NO grounds and it could be possible since there is no color code like "black for HOT or UNGROUNDED CONDUCTORS" "WHITE FOR GROUNDED" to put in a new circuit and share a neutral and this could be "VERY BAD" as the neutral could be overloaded and start a fire. If the Neutral is 12ga wire (which is good for a 20 amp circuit) that is fine, BUT if you share said neutral with another circuit because the neutral for the new circuit got broke or is not accessible than the 1st neutral could be carrying a lot more current. The fuse for the new circuit will not "blow" if its ampacity is not reached but it will if the return is through a 'loaded neutral from another circuit.

The best way to tell is to get a rubber lightbulb socket with 20 or 30 foot ends with crocodile ends. Put one end on water pipe or known ground and touch the other end to the wires; if the lamp lights, the wire is a "HOT" wire, then the wire running along side by a few inches would most likely be a ground but you could take lamp test wire and put to a "known "hot wire and using other lamp wire touch to ground then spray paint the wire with the ground connection white.

Niall C.
  • 20,739
  • 17
  • 92
  • 133
  • 6
    *"I have even seen some of it on MASH 4077 where wires are run in pairs and held by cleats."* Are you suggesting that a TV show produced 40 years ago depicting a war zone 60 years ago should be used to help one determine if their house is wired safely? – Adam Davis Jan 14 '14 at 16:36