Questions tagged [electric-vehicle]

Plug-in electric vehicles can use a variety of chargers. These chargers are often high-current, 240V installations and typically require dedicated circuits. Chargers may be hard-wired or plug in to sockets. Specifics vary by manufacturer and vehicle model.

62 questions
21
votes
7 answers

Why does Tesla recommend such a small gauge wire for their chargers compared to this chart I found online?

We are looking to install two NEMA 14-50 outlets for our kids to charge their electric cars, and I'm confused about wire choice. I thought I understood the correct wire to use, but then ran across a Tesla document that said something completely…
Nicholas
  • 889
  • 2
  • 12
  • 19
10
votes
2 answers

80amp EVSE on subpanel

I’ve got a trivial problem that has become complicated by a non-trivial setup. My goal is to install an 80amp (100amp breaker) EVSE to charge my electric truck. An incentive from my electric provider will pay up to $850 for the installation of an…
cyclops
  • 857
  • 1
  • 9
  • 18
8
votes
3 answers

1AWG with a smaller breaker?

I am thinking about having an electric vehicle supply equipment (EVSE) installed. In the interest of future proofing for an electric pickup truck coming on the market about a year from now, i would like to have 1 AWG wire installed for 100 amps @…
Nathan R
  • 81
  • 4
7
votes
1 answer

How to properly run a EVCE circuit for Tesla Wall Charger in an unfinished garage

I have a 200A Square D QO (US-Maryland) primary panel and I’d like to install Tesla Wall Charger in my unfinished garage with exposed wood studs and be able to operate at its highest rating, which is 48A sustained charge rate load. Service panel and…
Matt
  • 193
  • 9
7
votes
2 answers

What current capacity does 6 AWG AL TYPE SE have for an EV charger?

We recently finished our basement and had electrician run a cable to the garage for an electric vehicle charger that terminates in a junction box in the garage. From the 200A panel the cable is connected to a 2-pole 40A breaker and connected to…
user163047
  • 73
  • 3
7
votes
3 answers

Can I safely run nm-b below 8' exposed perpendicularly between stud cavities in an unfinished garage?

My Siemens flush mount combo electrical panel is installed to the exterior of my garage. The garage isn't finished (open studs) and eventually I'd like to close it up with drywall (but not for this). Can I safely run nm-b below 8' exposed…
alan
  • 73
  • 6
6
votes
4 answers

EV charger wiring - sub-panel requirements

I am looking to add a 30A outlet in my garage for the purpose of charging an EV. My home has 200A service coming through the main panel, and currently there are no sub-panels except one for the central air AC unit. My dryer is located on the other…
KM001
  • 61
  • 1
  • 4
6
votes
3 answers

Can I install two 60 amp EV chargers on a 100 amp subpanel?

I have 200amp service for the house and I'm looking to potentially add capacity for two EV chargers in the garage. I'm hoping to install two EV chargers that can charge up to 48 amps each. I know that in order to fit into the 125% continuous use…
will74
  • 117
  • 1
  • 6
5
votes
1 answer

AC line voltage sharing conduit with DC conductors for solar PV

I have an existing solar PV system; conduit to the house carries DC pairs for two "strings" of solar panels plus EGC ground. It'd be very convenient for wiring of an EV charger (EVSE), if I could run its AC wiring in the same conduit. The EVSE…
RustyShackleford
  • 2,411
  • 4
  • 28
  • 50
5
votes
2 answers

How do I test for voltage drop?

I have a Tesla that I'm plugging in at work (NEMA 5-20 outlet) and my EV says I'm getting between 107-109 volts. NEMA 5-15 adapter registers 12 amps, and the NEMA 5-20 adapter, which should be 16 amps, lowers to 12 amps and gives a low voltage…
WillyWonka
  • 53
  • 4
5
votes
3 answers

How much power can I supply for an EV charging circuit?

I would like to install an EVSE. The main panel is in the garage and I should have no problems running conduit a few feet to the location where I plan on mounting the charger. I will make sure I get the correct breaker, wire size, and receptacle…
bigchief
  • 761
  • 5
  • 9
4
votes
3 answers

sizing a Level2 EVSE to add to an existing subpanel

I have an existing 40-amp subpanel: a 125-amp main-lug load center, wired to a 40-amp breaker in the main panel with 8-3 NM-B. The subpanel has one existing load - a minisplit heat pump. I wish to add a Level 2 EV charger to it. I'm unclear as to…
RustyShackleford
  • 2,411
  • 4
  • 28
  • 50
4
votes
4 answers

I want to install generic capability for future car charging. What 240v outlet on the outside of the house is acceptable?

I am wiring an old house with new wires and want to have an outlet outside for charging a potential electric car. There is no carport or roof overhang, so weather resistance is important. The wall is still fully open to studs and I have full access…
Steve Foutz
  • 190
  • 7
3
votes
2 answers

Is there a problem oversizing a circuit for a car charger?

I am wiring a Tesla wall connector with #6 gauge THHN in conduit and installing a 60 amp breaker to allow for a max 48 amp charge. If I only need a 48 amp charge every so often and choose to continually set the car charger to charge using a lower…
john s
  • 129
  • 1
  • 8
3
votes
4 answers

40A GFCI Breaker keeps tripping when charging EV after about 1.5 hours

I had an electrician come and install a NEMA 14-50 outlet (on a 40A GFCI breaker) for an EV charger. I have the 32A charger that plugs into it, but it is also plugged into a 30 ft 50Amp RV extension cord. I noticed that after about an hour or an…
1
2 3 4 5