So, the spiffy new wi-fi thermostats want power on the C wire from thermostat, but the old thermostat doesn't have a C wire at it. What's the easiest way to add the C wire/24 volt to the thermostat location?

BMitch
  • 42,687
  • 14
  • 92
  • 197
Aaron
  • 6,391
  • 7
  • 38
  • 60
  • Are there any extra wires in the cable? – Tester101 Dec 06 '11 at 18:25
  • 1
    Sadly, no, just the 4 that are already terminated on the thermostat - Red, White, Green, Yellow – Aaron Dec 14 '11 at 13:36
  • Can you run a jumper from one of the other wires? Like jump the red to the C –  Dec 29 '12 at 01:34
  • 1
    @EarlCook jumping the neutral with the hot is just going to result in a short. You'd need an unused wire, or one that you don't mind always being on (e.g. the fan). – BMitch Dec 29 '12 at 01:53
  • So, if you have no AC, could you use the yellow wire by connecting it to the C terminal in the Thermostat and the Furnace? –  Jan 07 '13 at 00:16
  • 1
    @user9956 yes, all of the wires really don't do anything except where you have them plugged into. If you choose to completely rearrange them to suit your purpose, that's fine. – Aaron Jan 07 '13 at 19:22
  • What is the brand and model of the thermostat? The Emerson sensi wifi thermostats will work just fine with 4 wires if used to control heating and cooling. They call it power sharing - when heat is on, the cool circuit is used to power the thermostat and vice versa. No need for a C wire. – Vasuvius Aug 01 '17 at 17:59

7 Answers7

156

More than you've ever wanted to know about the C wire:

Lets start by explaining what the C wire is, and why it's needed.

Ye olde thermostat

In the olden days thermostats were simple switch devices, that used Mercury Switches to complete the circuit and turn on the heat/AC.

Mercury switches were commonly used in bimetal thermostats. The weight of the movable mercury drop provided some hysteresis by moving the bimetal spring slightly beyond the point it would normally assume, thereby holding the thermostat off slightly longer before flipping to the on state and then holding the thermostat on slightly longer before flipping back to the off state. The mercury also provided a very positive on/off switching action and could withstand millions of cycles without degradation of the contacts. Source

Because of this, there was no reason to run a return wire to the thermostat. For example a thermostat that only controlled heat, would only require 2 wires.

Thermostat wiring without a C wire

Thermostat wiring without a C wire showing electricity

Welcome to the future

Newer thermostats that offer clocks, backlit displays, WiFi, etc. are controlled using circuit boards and integrated circuits. These new circuits require a path for electricity to return to the source, and so require an extra wire. This new wire is known as the C wire, or Common wire.

Thermostat wiring with a C wire

Thermostat wiring with a C wire showing electricity

How do I get a C wire?

If you're lucky when you upgrade to a newer thermostat that requires this connection, there will be an extra (unused) wire in the cable at the thermostat. If you're not, you'll have to run new cable to the thermostat.

If you have heat and AC, you'll have to pull an 18/5 cable. If you have just heat you can get away with pulling 18/3 cable, but you may want to pull 18/5 anyway to make adding AC in the future easier.

enter image description here

What do all these wires do anyway?

There are no standards for wire color, so any wire could be used for any purpose. The most common color code would be (note: this is for forced air furnaces, heat pumps and other systems may be different).

  • Red - R - 24VAC
  • Red - Rh - 24VAC (dedicated to heat call)
  • Red - Rc - 24VAC (dedicated to cooling call)
  • Green - G - Fan on
  • White - W - Heat call
  • Yellow - Y - Cool call
  • Blue or Black - C - Common

Alternative Solution

This solution is illustrated in this video from Honeywell. With this solution you lose the ability to manually turn on the blower fan, but the fan will still run properly in the Auto position.

WARNING: This procedure involves modifying the wiring in the furnace, and may not be approved by every manufacturer. Check with the furnace manufacturer, and all local codes before attempting this procedure. Make sure the breaker for the furnace is OFF before you begin.

  1. Make sure the breaker for the furnace is OFF.
  2. Start by removing the access panel on the furnace, and locating the thermostat wires.
  3. Remove the wire from the G terminal, and connect it to the C terminal.
  4. Using a short piece of 18 AWG wire, make a jumper and connect it between the Y and G terminals (this is only required if you have both heat and central air).
  5. Replace the access panel.
  6. Remove the thermostat from the wall to gain access to the wiring.
  7. Remove the wire from the G terminal, and connect it to the C terminal.
  8. Replace the thermostat.
  9. Turn the furnace breaker back on.

A bit more about transformers and C wires.

A transformer uses coils of wire, magnetism, and a bit of magic to transfer energy from the primary side of the transformer to the secondary side of the transformer. Usually during the transfer, the voltage is either increased or decreased. In the case of our furnace we're likely talking about taking 120VAC, and transforming it into 24VAC. Once the voltage has been reduced, we can use the lower voltage and a thermostat to control the furnace.

Now that you know even less about transformers than you did before, lets look at a diagram.

Highlighted Furnace Wiring Diagram

This is an actual wiring diagram from a furnace, but you'll notice I've highlighted a few things. First, in red I've highlighted the 120V primary side of the transformer. I've also highlighted the secondary side of the transformer in a couple shades of blue. This was done to illustrate that one side of the transformers secondary winding (light blue), is attached to the R or power terminal. While the other side of the secondary winding (dark blue), is attached to the C or "neutral" terminal.

Locating transformers

On a schematic

On a schematic or wiring diagram, a transformer will look something like this.

Transformer Symbol

Often you'll see a number written on each side, which denotes the expected voltages on each side of the transformer. Notice in the schematic above that the top side lists 120V (120 volts), while the bottom lists 24V (24 volts).

In the real world

When actually digging through HVAC equipment, a transformer will look something like this.

Transformer Transformer

Notice the rectangular middle section, flanked by a bulge on each side. These are the typical physical characteristics of a transformer.

Volt-Amperes

Transformers typically have a volt-ampere (VA) rating, which can be used to determine the amount of current that can safely flow through the transformers coil wires. To determine the maximum current, simply divide the VA value by the voltage.

For example, a 120V/24V 40 VA transformer would be capable of 1.66667 amperes on the secondary.

40VA / 24V = 1.66667A

and .3333 amperes on the primary

40VA / 120V = .3333A

Normally this is not a problem, since the only things supplied by the transformer are switches and relays. If you install a thermostat that draws more current than the transformer can carry, you're going run into problems. So in this case, you'll have to upgrade the transformer and any fuses that protect it (since the fuses are sized based on the VA rating).

What about systems with multiple transformers?

In some systems, there will be separate transformers for the heating and cooling systems. In these situations, you'll have to check with the thermostat manufacturer, to determine which system should provide the C wire. In the case of Nest and Honeywell (and probably others), their thermostats expect the C wire to come from the cooling system.

When you're connecting the wires to the thermostat in these systems, you'll have to remove any jumpers between the R terminals. You'll wire the R wire from the heating system, to R or Rh, and the R wire from the cooling system, to Rc. Then you'll have to wire the C wire from the cooling system, to the C terminal of the thermostat.

Tester101
  • 131,097
  • 78
  • 316
  • 608
  • 1
    If you have an 18/4 thermostat wire, is there any harm in running an extra 18/2 wire to connect the C? Rather than disconnecting everything, reconnecting, and spending more money to replace the 4 wires in the 18/4 already working? – eaglei22 Dec 07 '17 at 23:50
  • @eaglei22 there is no problem running an extra wire, it can even be 18/1. For Tester101 great answer. You might note that 24VAC can mean approximately, you might see 23VAC or 27VAC on your voltmeter. – Bryce Dec 08 '17 at 20:51
  • @Tester101 Is the solution numbered steps 1-9 the "Alternative Solution" that forfeits the ability to control your fan? Or is it only the one in the honeywell video? – Aww_Geez May 26 '20 at 21:43
  • @Aww_Geez Yes. The steps labeled 1-9 describes the steps from the video – Tester101 Jun 02 '20 at 20:17
  • if you only started with the `In the case of Nest and Honeywell (and probably others), their thermostats expect the C wire to come from the cooling system` i would have been done way earlier, gotta take us attention deficit folks into consideration ... that having been said - many thanks (found unused lead on my wire to the air handler and i never saw it cuz i always looked for one on the furnace-bound wire for some reason, maybe because on my nest the AC wires are on left and heat wires, and `C` are on right), thanks again – nhed Jul 02 '20 at 05:56
  • I have a simple two wire system as per your first diagram. From what I understand, I should be able to add my own C wire, attaching it to the "second" pole of the 24V transformer. And my only concern should be confirming that transformer can supply enough current to power my new smart thermostat? (ecobee3 lite). Is that correct? On the external panel it notes the rating is just 200mA. – Mtl Dev Oct 18 '20 at 16:22
  • @Mtl Dev I have the 2 wire system too and I plugged the 'C' wire to the second pole, my Honeywell T5 did power up but it will restart when it tries to turn on the heat. I am suspecting the same as you, the transformer is not providing enough power. Have you solved the problem? – Felix Cen Nov 10 '20 at 19:38
  • @FelixCen Short answer: spent $15 on a 24V AC wall-wart transformer, about $15 on an isolation relay. Wired it up like [this](https://support.ecobee.com/hc/en-us/articles/227874527-ecobee-thermostat-installation-with-an-isolation-relay) . The transformer I installed in my basement, using three wires to the thermostat - so the installation looks clean and professional where the thermostat is installed. – Mtl Dev Nov 10 '20 at 23:23
  • @Mtl Dev it was my bad, I wired it up to the red instead of the white wire. Now it is working. – Felix Cen Nov 13 '20 at 19:19
  • @Tester101 Thanks for the good explanation! In my case, the 2nd output of the secondary wiring is GROUNDED to the chassis. This is the place where I'd expect the C wire. Can this be correct? Is C wire just connected to chassis/ground of the furnace? – divB Dec 11 '22 at 01:02
  • @Tester101 Can you tell me what the brown device on the right is on this picture https://snipboard.io/DXNMJn.jpg ? On the left side it has the "G" wire (=Fan?) from the thermostat as well as Chassis ground (=connected to the first transformer). On the right side seems to be supply and others. Is this another transformer (for the fan) or is this the relay ? – divB Dec 11 '22 at 01:04
13

Use an Add-a-Wire Device

Assuming your thermostat and furnace are compatible and you're just short on conductors between them, you could use one of these add-a-wire devices.

This device won't work for C wires. However, it does allow one to combine two of the other relay wires down to 1, freeing up a dedicated wire for C. For example, in a standard 4-wire (R/W-heat/Y-cool/G-fan) thermostat, you could combine the Y and G wires through the Add-A-Wire device, and use the freed-up wire as C directly.

alx9r
  • 1,325
  • 2
  • 9
  • 22
  • 2
    You should note that using one of these things prevents manual control of the fan. – Gordon Nov 12 '18 at 00:39
  • I wonder if you could use two microcontrollers to multiplex multiple signals over one wire...probably more trouble than it's worth, but it'd allow manual control of the fan and everything else while still using just four (or even three) wires – Radvylf Programs Oct 04 '21 at 22:09
7

If your furnace has a C terminal then you can run a new wire from the C terminal to your thermostat. You can connect as many wires to the C terminal as you'd like as long as you do it in parallel (ie: all wires must terminate on the terminal itself, do not "daisy chain" them). In the case when your furnace does not have a C terminal, you can utilize an external transformer to provide the neutral line that would otherwise be provided by the C wire. While most of the WiFi thermostats accept a range of voltages, my experience is thats best to use a 24V transformer. Make sure to verify the voltage and amperage requirements with your thermostat specs.

Steven
  • 27,594
  • 9
  • 53
  • 88
  • Can you give a product that is a 24V transformer? I would want to make sure that I'm looking at the right piece of equipment. – Aaron Dec 12 '11 at 18:31
  • There are two types really. Direct wire and plug-in. Direct wire usually attach to an electrical box: http://www.homedepot.com/h_d1/N-5yc1vZ12kxZ12ky/R-202278728/h_d2/ProductDisplay?langId=-1&storeId=10051&catalogId=10053 The plug-in type you'll recognize as those black boxes that come with most electronics: http://www.homedepot.com/h_d1/N-5yc1vZ12kxZ12ky/R-100201044/h_d2/ProductDisplay?langId=-1&storeId=10051&catalogId=10053 – Steven Dec 12 '11 at 19:06
  • 3
    I have seen this answer, but don't understand how a 2nd transformer, connected with one side of the secondary connected at 'C' of the thermostat, will allow a current sink for the electronics (which are supplied with 'hot' from the furnace transformer (seems like spooky action at a distance)). – HerrBag Jul 20 '13 at 13:41
4

Forget the wires. Use a wireless thermostat, placing the receiver in the basement at your furnace and the transmitter wherever you want it. The Venstar Add-A-Wireless Thermostat T1119RF might do the trick. If you musts have the wifi thermostat, put it in the basement, and add a remote sensor to the mix.

Bryce
  • 10,693
  • 14
  • 65
  • 108
4

The obvious answer is to run a new thermostat cable with five wires instead of trying to use jumpers etc that in the end just end up causing more troubles, like destroying a circuit board. In most cases if can be as simple as attaching a new one where the old one goes up the wall from the basement if it's open. If it's a finished basement then a little more thinking is involved. Then there's the ultimate question, would you totally trust a wireless system to control your furnace if you were away for a month?

Richard
  • 242
  • 1
  • 7
3

You could technically use the G wire (connected to common at the furnace and common at the stat. Then jumper G to Y at the furnace. This will remove your ability to bring the fan on independently of the air conditioner and depending on the stat may not work. Some of them sense what wires are connected and can be difficult to bypass that step. Some smart stats like Ecobee come with a device to add the fifth wire through a little device that mounts in the blower compartment. FastStat offers an after market solution that does the same thing. You could also see if your stat allows for a power stealing resistor to be installed (unlikely normally only on hydronic radiant heating stats)

Joe Fala
  • 6,314
  • 8
  • 34
0

I just ran an 18/2 in addition to the 18/4. No sense in pulling out perfectly good wires. Saves some money too, and avoided disconnecting the old one. Paid $10 for 50ft of 18/2.

eaglei22
  • 1,075
  • 6
  • 23